In most cases the booth is smaller than the design area needs to be so every booth I've ever designed has been every sprinkler in the booth and throughout the plenum and exhaust, so you would be calculating the booth according to NFPA 33 not NFPA 13, the phantom flow is for NFPA 13 calculations
NFPA 33 9.6.2.1 The sprinkler design area shall not be required to exceed the area of the booth or room in which spraying or resin application is conducted. 9.6.5 The sprinkler system shall be controlled by a separate, listed indicating valve(s), operable from floor level. 9.6.6 (6) The system demand shall include the discharge from the hydraulically most remote adjacent sprinklers in a common 30.5 m (100 linear ft) area of duct (horizontal and/or vertical). (4) Sprinklers shall provide a minimum flow of 114 L/min (30 gpm) per sprinkler at a minimum of 1 bar (15 psi) pressure. Thanks Brett Peters General Manager Installation & Design Proudline Fire Protection Services Ltd. [email protected] 780 490 7602 office ext 202 780 490 7605 fax 780 777 0568 cell 780 718 2676 24h Visit us at www.proudline.ca Proudline now offers ULc listed monitoring services, please contact [email protected] for more information On Fri, Mar 31, 2023 at 12:41 PM Anthony Johnson < [email protected]> wrote: > As an additional note NFPA 2019: 26.4.1.3 says that the sprinkler design > area shall not be required to exceed the area of the booth so my question > basically becomes is it still neccessary to add a phantom flow for the > difference of flow? > > Anthony > > > <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail> > Virus-free.www.avg.com > <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail> > <#m_-9154397238494389454_m_685596472348810006_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2> > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to > [email protected]
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]