On 2/27/2012 8:18 PM, Darrell Fuhriman wrote:
utilizing less storage elements, and producing less waste.  That is true.
Or you can just design a smarter A2D power supply, which efficiently uses
the 120V single phase power.

I continue to wonder why more data centers don't use -48V DC distribution.



Because it would hugely expensive in terms of copper. to deliver 200W at -48V DC requires copper capable of carrying 4A. To do so at 208V requires a cable capable of 1A. There are some ways around this by distributing at what is called high voltage DC out to the floor which gets a slight advantage because at the same AWG, DC has a 5% efficiency advantage vs AC. But then you have to have some significant power infrastructure distributed at every row (almost 1 of every 3 racks) to convert from HVDC to low voltage DC. There are not very many vendors to do this, it's relatively new, and so the costs are a bit higher. It does have some further advantages at the UPS because you don't have to worry about phase matching and you can save efficiency in AC to DC and DC back to AC conversions. The failover is simplified to some specialized diodes, which is cool. The capital costs typically end up making the decision a wash at the current time.


_______________________________________________
Tech mailing list
[email protected]
https://lists.lopsa.org/cgi-bin/mailman/listinfo/tech
This list provided by the League of Professional System Administrators
http://lopsa.org/

Reply via email to