Jim,

You are correct that if a product is being evaluated to a standard, then in 
order to say it complies with the standard it must comply with the whole 
thing.The key here is that you don't necessarily List a product to a 
standard, you List it under a category. There is a difference between a 
standard and a category. Often the two are completely integrated and 
inseparable but not always. 

UL's category for ITE (NWGQ) is directly linked to UL1950. Therefore, a 
Listing to NWGQ automatically says that the unit complies with UL1950 (all 
of it!). The same was true for the Telephone Equipment Category (WYQQ) 
which indicated compliance with UL1459. This has changed now since under 
the Telephone Equipment Category a product can now comply with either 
UL1459 or UL1950. So here the category no longer is tied to only one 
standard and Listing under WYQQ indicates compliance with either UL1950 3rd 
edition or Ul1459.

In UL's "Custom-Built Telecom Equipment" category (WYKM) for service 
provider installed modular equipment, additional requirements, over and 
above UL1459 or UL1950, are added to take into account the modular, field 
installed nature of the equipment this category covers. So here, Listing 
under this category indicates compliance with a set of requirements that 
goes beyond just UL1950 or UL1459.

Another good example is our category for "Static Neutralizing Equipment" 
(VWWZ). This category now uses UL1950 for its basic requirements but also 
references UL867 (Electrostatic Air Cleaners) for some high voltage 
requirements. In this example, the resulting evaluation again exceeds the 
requirements in UL1950. However, this does not necessarily have to be the 
case. 

The Communication Service Equipment Category (DUZO) covers equipment that 
is similar to other telecom equipment but is installed by highly trained 
personnel in a harsher environment (often on the unprotected side of the NI 
or actually is the NI). It seemed natural, therefore to start with the 
telecom equipment standards when looking for requirements so UL1459 or 
Ul1950 are used. To deal with the harsh environment issues, additional 
requirements are added from various other standards better suited to deal 
with these issues. However, since the level of training of the installer 
amd maintainer is usually high, some requirements are relaxed in the area 
of markings, instructions and what is allowed to be covered in installation 
practices. So here it is possible that a unit may not meet all of the 
clauses of UL1950 or UL1459 in some areas but will probably exceed the 
UL1950 or UL1459 requirements in others.

To deal with specific equipment issues like the type of equipment, 
installation criteria, etc., a category can call on one or several 
standards or a new standard can be written. A recent trend is for new 
requirements, or even a new standard, to call on an existing standard (like 
UL1950) then add or subtract requirements as necessary. This is being done 
in the area of DC Distribution Equipment for Telecommunications Equipment, 
UL Subject 1801. 

As an example, a standard can be written that states:
"1.     Equipment shall comply with UL1950.". 
"2.     Exception: Spacings in telecommunications circuits may be judged on 
the basis of the dielectric voltage-withstand test in                           
UL1459." 
Of course a product Listed under a category that uses this mythical new 
standard could not be claimed to comply with UL1950 but this would be made 
clear in the category description. Actually, it would have to be made very 
clear so there would be no chance of mis-representation of what a product 
complies (or doesn't comply) with.

There would have to be an expressed interest or need to develop such a 
category or standard but it would not be too difficult to do so.As I 
mentioned before, I brought up the idea of possibly maintaining UL1459 for 
specialized domestic equipment (where there was no need to go to 
international requirements) a long time ago at the TIA TR41.7 meetings but 
there was no interest expressed.  If you want to discuss this further, 
please give me a call at (516) 271-6200 X22269


Randy Ivans
Business Sector Coordinator
Telecommunications Industry
email: [email protected]

Reply via email to