Alan,
 
 You stated that:
 >Paragraph 5 of clause 6.4 of EN60950/A4 which follows items a) b)
 >and c) states the following:
 >
 >'These requirements do not apply where circuit analysis and
 >equipment investigation indicate that safety is provided by
 >other means, for example between two circuits each of which
 >has a permanent connection to earth.'
 
 Your reference to 6.4 above should actually be 6.4.1 which specifically refers 
 to electrical separation (see also Table 19), not the impulse test of 6.4.2.1. 
 However, if a TNV-1 or TNV-3 circuit and an SELV circuit are permanently 
 connected to earth, then there may be no separation requirements between them, 
 therefore, no testing should be required, if I'm reading the standard 
 correctly.
 
 If an overvoltage fault occurred (such as an impulse of 6.4.2.1 that you 
 mentioned) between unearthed TNV-1 or TNV-3 circuits or conductive parts and 
an 
 SELV circuit (in this case), that fault current must be reliably routed to 
 earth (see 2.3.3.3). In particular, the "permanence" of the SELV connection to 
 earth is described in 2.5.11, particularly the 2nd to last paragraph. See also 
 6.3.2.
 
 I hope this answers your questions and that you will be soon out of your 
 misery. :-)
 
 Comments anyone?
 
 Best regards,
 Ron Pickard
 [email protected]

Reply via email to