Pete "you-are-the-man" Spud!

does not "permanence" also imply a permanent connection, as in a hard
ground stud? (no Viagra jokes, please) 

ever know a telecom guy named Henry Lederman? I think he's at NORTEL,
formerly of Canadian Marconi...

D


Peter Tarver wrote:
> 
> Ron, you are correct that 6.4.1 makes testing between a TNV-1 or -3 circuit
> and an SELV circuit moot, if there is a common earthing connection between
> them.  With regard to determining the reliability of the earthing of the
> TNV-1 or -3 circuit, the method of 2.5.11 would be used, with the test
> current set to 2A.  UL, CSA and TUV Rheinland NA have endorsed the 2A value.
> 
> Regards,
> 
> Peter L. Tarver, PE
> Senior Regulatory Engineer
> Homologation Engineering
> Nortel, MPK
> ESN 655
> V:  408-565-2453
> F:  408-565-2575
> 
> > -----Original Message-----
> > From: [email protected] [SMTP:[email protected]]
> > Sent: Thursday, July 09, 1998 4:57 PM
> >
> >  Alan,
> >
> >  You stated that:
> >  >Paragraph 5 of clause 6.4 of EN60950/A4 which follows items a) b)
> >  >and c) states the following:
> >  >
> >  >'These requirements do not apply where circuit analysis and
> >  >equipment investigation indicate that safety is provided by
> >  >other means, for example between two circuits each of which
> >  >has a permanent connection to earth.'
> >
> >  Your reference to 6.4 above should actually be 6.4.1 which specifically
> > refers
> >  to electrical separation (see also Table 19), not the impulse test of
> > 6.4.2.1.
> >  However, if a TNV-1 or TNV-3 circuit and an SELV circuit are permanently
> >  connected to earth, then there may be no separation requirements between
> > them,
> >  therefore, no testing should be required, if I'm reading the standard
> >  correctly.
> >
> >  If an overvoltage fault occurred (such as an impulse of 6.4.2.1 that you
> >  mentioned) between unearthed TNV-1 or TNV-3 circuits or conductive parts
> > and an
> >  SELV circuit (in this case), that fault current must be reliably routed
> > to
> >  earth (see 2.3.3.3). In particular, the "permanence" of the SELV
> > connection to
> >  earth is described in 2.5.11, particularly the 2nd to last paragraph. See
> > also
> >  6.3.2.
> >
> >  I hope this answers your questions and that you will be soon out of your
> >  misery. :-)
> >
> >  Comments anyone?
> >
> >  Best regards,
> >  Ron Pickard
> >  [email protected]
> >

-- 