If it was me I'd call the landlord and let them know your unit is detecting
a problem on the AC side.  Ask if they can take a look at it before there
are any electrical problems.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Jan 7, 2015 at 4:44 PM, Nate Burke <[email protected]> wrote:

> Our temps are Below 0 now, and one of my APC UPS's at a site keeps sending
> an alert 'Site wiring fault'  then clears a few minutes later.  The APC
> Knowledge base lists off some various reasons, Overloaded Neutral,
> Disconnected Groud, but basically says call an electrician.  Is this
> something I should be worried about, or just figure that there is a loose
> ground connection in the cold.  This is at a grain facility which is new
> within the last year, so it's not like it's old electric.  He installed our
> own breaker back at the panel, but we are sharing a neutral.
>
> Anyone else had to troubleshoot this before, or just don't worry about
> it.  The UPS is still self testing just fine.
>
> Nate
>

Reply via email to