+1

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

----- Original Message -----
From: "That One Guy" <[email protected]>
To: [email protected]
Sent: Wednesday, January 7, 2015 3:52:02 PM
Subject: Re: [AFMUG] APC Site Wiring Fault

Good luck with calling an electrician. APC is just tempermental, half of
ours say site wiring fault. We gave up trying to figure it out when the
electricians couldnt.

On Wed, Jan 7, 2015 at 3:46 PM, Josh Luthman <[email protected]>
wrote:

> If it was me I'd call the landlord and let them know your unit is
> detecting a problem on the AC side.  Ask if they can take a look at it
> before there are any electrical problems.
>
>
> Josh Luthman
> Office: 937-552-2340
> Direct: 937-552-2343
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
>
> On Wed, Jan 7, 2015 at 4:44 PM, Nate Burke <[email protected]> wrote:
>
>> Our temps are Below 0 now, and one of my APC UPS's at a site keeps
>> sending an alert 'Site wiring fault'  then clears a few minutes later.  The
>> APC Knowledge base lists off some various reasons, Overloaded Neutral,
>> Disconnected Groud, but basically says call an electrician.  Is this
>> something I should be worried about, or just figure that there is a loose
>> ground connection in the cold.  This is at a grain facility which is new
>> within the last year, so it's not like it's old electric.  He installed our
>> own breaker back at the panel, but we are sharing a neutral.
>>
>> Anyone else had to troubleshoot this before, or just don't worry about
>> it.  The UPS is still self testing just fine.
>>
>> Nate
>>
>
>


-- 
All parts should go together without forcing. You must remember that the
parts you are reassembling were disassembled by you. Therefore, if you
can't get them together again, there must be a reason. By all means, do not
use a hammer. -- IBM maintenance manual, 1925