We had one like that once and neutral and ground were swapped.

On Wed, Jan 7, 2015 at 9:30 PM, Sean Heskett <[email protected]> wrote:

> There is for sure something wrong that a good electrician should be able
> to fix
>
>
>
> On Wednesday, January 7, 2015, Nate Burke <[email protected]> wrote:
>
>> Our temps are Below 0 now, and one of my APC UPS's at a site keeps
>> sending an alert 'Site wiring fault'  then clears a few minutes later.  The
>> APC Knowledge base lists off some various reasons, Overloaded Neutral,
>> Disconnected Groud, but basically says call an electrician.  Is this
>> something I should be worried about, or just figure that there is a loose
>> ground connection in the cold.  This is at a grain facility which is new
>> within the last year, so it's not like it's old electric.  He installed our
>> own breaker back at the panel, but we are sharing a neutral.
>>
>> Anyone else had to troubleshoot this before, or just don't worry about
>> it.  The UPS is still self testing just fine.
>>
>> Nate
>>
>