I had that at one grain handling site and also your fingers would tingle when 
you touched any of the electrical boxes.  It went away when they had the 
electrician fix the ground.  So I’d be at least mildly worried regarding 
personal safety.  Some rural electricians will interchange neutral and ground.  
If the 3rd prong is wired to the neutral, that’s probably enough to make the 
APC unhappy.  When a building is 500 feet from the transformer and has big 
motors and grain driers and stuff, neutral is definitely not the same as 
ground.  And god forbid the site has high-leg delta.

From: That One Guy 
Sent: Wednesday, January 07, 2015 3:52 PM
To: [email protected] 
Subject: Re: [AFMUG] APC Site Wiring Fault

Good luck with calling an electrician. APC is just tempermental, half of ours 
say site wiring fault. We gave up trying to figure it out when the electricians 
couldnt.

On Wed, Jan 7, 2015 at 3:46 PM, Josh Luthman <[email protected]> 
wrote:

  If it was me I'd call the landlord and let them know your unit is detecting a 
problem on the AC side.  Ask if they can take a look at it before there are any 
electrical problems.



  Josh Luthman
  Office: 937-552-2340
  Direct: 937-552-2343
  1100 Wayne St
  Suite 1337
  Troy, OH 45373

  On Wed, Jan 7, 2015 at 4:44 PM, Nate Burke <[email protected]> wrote:

    Our temps are Below 0 now, and one of my APC UPS's at a site keeps sending 
an alert 'Site wiring fault'  then clears a few minutes later.  The APC 
Knowledge base lists off some various reasons, Overloaded Neutral, Disconnected 
Groud, but basically says call an electrician.  Is this something I should be 
worried about, or just figure that there is a loose ground connection in the 
cold.  This is at a grain facility which is new within the last year, so it's 
not like it's old electric.  He installed our own breaker back at the panel, 
but we are sharing a neutral.

    Anyone else had to troubleshoot this before, or just don't worry about it.  
The UPS is still self testing just fine.

    Nate






-- 

All parts should go together without forcing. You must remember that the parts 
you are reassembling were disassembled by you. Therefore, if you can't get them 
together again, there must be a reason. By all means, do not use a hammer. -- 
IBM maintenance manual, 1925

Reply via email to