If the two pieces of metal are not connected together, like if one of them is 
floating except for stray high resistance paths to ground, then I wouldn’t pay 
much attention to the voltmeter reading.  Especially if you are using a high 
impedance digital meter.

Or if they are connected via a wire carrying high current, 0.1 volt may not 
mean much.  If you have 10 amps flowing through a wire with 0.01 ohms 
resistance, there’s your 0.1 volt.

If that second piece of metal is grounded to your common ground point with a 
wire that should not be carrying any current, then I might worry about the 0.1 
volt.  You might have a ground loop.

Are you seeing a DC or AC voltage?


From: George Skorup 
Sent: Thursday, March 31, 2016 5:32 PM
To: [email protected] 
Subject: Re: [AFMUG] Another ground question

That's what i was going to say. If it's a cheap meter, don't worry about it. 
Bond everything and you should be fine.


On 3/31/2016 5:27 PM, Chuck McCown wrote:

  Depends on the meter.  Does the meter read 0.0 when the leads are shorted 
together?
  Some meters have some random fluctuations in the least significant digit all 
the time.  

  From: Josh Baird 
  Sent: Thursday, March 31, 2016 3:24 PM
  To: [email protected] 
  Subject: [AFMUG] Another ground question

  I'm working on a new DC enclosure (steel 19" rackmount cabinet).  When using 
a DC volt meter, and putting the 'red' lead on a common ground point (my ground 
bus, a metal rack rail, etc), and the 'black' lead on something metal, I'm 
seeing ~0.1V.

  I'm assuming this is bad.  On the bench currently, I have the AC ground 
connected to my PSU.  I have all other devices (switch, surge suppressors, rack 
rails, etc) tied to a common ground that isn't yet connected to earth.  My PSU 
and power distribution is on a metal DIN rail which in turn is mounted to the 
metal rack rails. 

  Should I be concerned with this?  As much as I try (or not), I still have 
trouble wrapping my head around ground/ground potential/etc.