Are you isolating your DC and AC grounds?
On Mar 31, 2016 4:44 PM, "Ken Hohhof" <[email protected]> wrote:

> If the two pieces of metal are not connected together, like if one of them
> is floating except for stray high resistance paths to ground, then I
> wouldn’t pay much attention to the voltmeter reading.  Especially if you
> are using a high impedance digital meter.
>
> Or if they are connected via a wire carrying high current, 0.1 volt may
> not mean much.  If you have 10 amps flowing through a wire with 0.01 ohms
> resistance, there’s your 0.1 volt.
>
> If that second piece of metal is grounded to your common ground point with
> a wire that should not be carrying any current, then I might worry about
> the 0.1 volt.  You might have a ground loop.
>
> Are you seeing a DC or AC voltage?
>
>
> *From:* George Skorup <[email protected]>
> *Sent:* Thursday, March 31, 2016 5:32 PM
> *To:* [email protected]
> *Subject:* Re: [AFMUG] Another ground question
>
> That's what i was going to say. If it's a cheap meter, don't worry about
> it. Bond everything and you should be fine.
>
> On 3/31/2016 5:27 PM, Chuck McCown wrote:
>
> Depends on the meter.  Does the meter read 0.0 when the leads are shorted
> together?
> Some meters have some random fluctuations in the least significant digit
> all the time.
>
> *From:* Josh Baird <[email protected]>
> *Sent:* Thursday, March 31, 2016 3:24 PM
> *To:* [email protected]
> *Subject:* [AFMUG] Another ground question
>
> I'm working on a new DC enclosure (steel 19" rackmount cabinet).  When
> using a DC volt meter, and putting the 'red' lead on a common ground point
> (my ground bus, a metal rack rail, etc), and the 'black' lead on something
> metal, I'm seeing ~0.1V.
>
> I'm assuming this is bad.  On the bench currently, I have the AC ground
> connected to my PSU.  I have all other devices (switch, surge suppressors,
> rack rails, etc) tied to a common ground that isn't yet connected to
> earth.  My PSU and power distribution is on a metal DIN rail which in turn
> is mounted to the metal rack rails.
>
> Should I be concerned with this?  As much as I try (or not), I still have
> trouble wrapping my head around ground/ground potential/etc.
>
> Josh
>
>
>
>
>