Do you need to?  We want them all to go to the earth eventually right?

On 3/31/2016 7:38 PM, Jaime Solorza wrote:

Are you isolating your DC and AC grounds?

On Mar 31, 2016 4:44 PM, "Ken Hohhof" <[email protected] <mailto:[email protected]>> wrote:

    If the two pieces of metal are not connected together, like if one
    of them is floating except for stray high resistance paths to
    ground, then I wouldn’t pay much attention to the voltmeter
    reading. Especially if you are using a high impedance digital meter.
    Or if they are connected via a wire carrying high current, 0.1
    volt may not mean much.  If you have 10 amps flowing through a
    wire with 0.01 ohms resistance, there’s your 0.1 volt.
    If that second piece of metal is grounded to your common ground
    point with a wire that should not be carrying any current, then I
    might worry about the 0.1 volt.  You might have a ground loop.
    Are you seeing a DC or AC voltage?
    *From:* George Skorup <mailto:[email protected]>
    *Sent:* Thursday, March 31, 2016 5:32 PM
    *To:* [email protected] <mailto:[email protected]>
    *Subject:* Re: [AFMUG] Another ground question
    That's what i was going to say. If it's a cheap meter, don't worry
    about it. Bond everything and you should be fine.

    On 3/31/2016 5:27 PM, Chuck McCown wrote:
    Depends on the meter.  Does the meter read 0.0 when the leads are
    shorted together?
    Some meters have some random fluctuations in the least
    significant digit all the time.
    *From:* Josh Baird <mailto:[email protected]>
    *Sent:* Thursday, March 31, 2016 3:24 PM
    *To:* [email protected] <mailto:[email protected]>
    *Subject:* [AFMUG] Another ground question
    I'm working on a new DC enclosure (steel 19" rackmount cabinet).
    When using a DC volt meter, and putting the 'red' lead on a
    common ground point (my ground bus, a metal rack rail, etc), and
    the 'black' lead on something metal, I'm seeing ~0.1V.

    I'm assuming this is bad.  On the bench currently, I have the AC
    ground connected to my PSU.  I have all other devices (switch,
    surge suppressors, rack rails, etc) tied to a common ground that
    isn't yet connected to earth.  My PSU and power distribution is
    on a metal DIN rail which in turn is mounted to the metal rack
    rails.
    Should I be concerned with this?  As much as I try (or not), I
    still have trouble wrapping my head around ground/ground
    potential/etc.
    Josh


Reply via email to