In message <F2AB2587B6C64E3F84E0E5C609459D5B@harrington09269>, dated 
Wed, 13 May 2009, John Harrington <[email protected]> writes:

>Thanks for the feedback.  I was looking at the wording of the LVD 
>guidance document which states
>
> 
>
>?The Directive covers electrical equipment designed for use with a 
>voltage rating of between 50 and 1000 V for alternating current and 
>between 75 and 1500 V for direct current. It should be noted that these 
>voltage ratings refer to the voltage of the electrical input or output, 
>not to voltages that may appear inside the equipment?
>
> 
>
>and seems to imply that the 1500 V dc rating limit is for outputs as 
>well as inputs.  Is this a wrong interpretation?

Not at all; there was a lot of confusion about this, because the 
original wording was obscure and appeared, for example, to exclude 
CRT-type TV sets from the LVD. The fact that 60065, 61010 and other 
standards include stuff about higher voltages doesn't change the meaning 
of the Directive.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
Things can always get better. But that's not the only option.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to