Igor Chudov wrote:
> On Tue, Mar 8, 2011 at 1:12 PM, Kirk Wallace 
> <kwall...@wallacecompany.com>wrote:
>
>   
>> Another thing is that for all static and rotary converters I have seen,
>> the single phase is passed right through and the converter creates a 90
>> (or 270) degree phase, so you get 0, 90 and 180 degrees instead of 0,
>> 120 and 240 degrees. A three phase motor should run more smoothly with
>> evenly spaced phases, but on the other hand, I haven't noticed any
>> problem with my lathe that uses the converter.
>>
>>
>>     
> This is not true, phases are evenly spaced on mine. I use run capacitors. My
> voltages are very close to each other L1-L2, L1-L3, L2-L3.
>
>   
Right.  Although the generated leg is at a right angle to the other 
legs, it is added at the
CENTER tap of the 220 V mains.  It just so happens if you work out the 
trig, it DOES produce
the right phase relationship.  If you draw an isoceles triangle, the 
base is the 220 V mains,
the center of that is your neutral.  The generated leg is 207 V from the 
neutral to the peak
of the triangle.  If you find the center between the three vertices, 
each vertex will be at a
120 degree angle.  The trick is the center-point voltage in this system 
is not at neutral,
as it would be in a 120/208 Wye system.

You really HAVE to draw this out on paper to understand it.

Jon

------------------------------------------------------------------------------
Colocation vs. Managed Hosting
A question and answer guide to determining the best fit
for your organization - today and in the future.
http://p.sf.net/sfu/internap-sfd2d
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to