On Friday 29 May 2020 22:14:57 andrew beck wrote:

> sweet thanks gene
>
> I will take your advice and connect the pc chassis to the main ground.
>
> I think I will continue to use my grounding blocks for now though as
> there are about 20 ground cables to connect up and that is getting a
> bit much for one bolt I think.  hopefully I don't have a problem.  I
> will let you know if I do haha
>
Use only one block, and put them as close together as you can.
>
> regards
>
> Andrew
>
> On Sat, May 30, 2020 at 2:00 PM Gene Heskett <ghesk...@shentel.net> 
wrote:
> > On Friday 29 May 2020 21:22:09 andrew beck wrote:
> > > thanks guys
> > >
> > > just one question about all this gene
> > >
> > > why do you suggest breaking the ground off the the computer
> > > powersupply cable and connecting a ground from the pc chassis to
> > > the machine main ground?
> > >
> > > does the grounding that goes through the cable now good enough?
> >
> > The computers 3rd wire should remain if its the ONLY ground
> > connection in the whole system. But since we power gear thru EMT
> > tubing, and that also includes a generally better ground, the power
> > cord to the computer should have that 2nd or 3rd ground removed, and
> > the computers ground taken back to this common bolt by a direct from
> > its chassis ground wire, UNLESS the computer is mounted to and
> > mechanically connected to the frame of the machine and this frame is
> > grounded to that common bolt.
> >
> > Anytime you can lift just one of those wires from that bolt, and
> > still get ground continuity because its grounded someplace else too,
> > is bad kharma, find that "other" ground and disconnect it.  Once,
> > done well, is enough.  A shielded cable where the shield is grounded
> > at the far end can inject many volts of noise, enough to blow the
> > interface card. Disconnect that far end. That bolt should connect to
> > the power wirings "static" ground, and the only allowable cross
> > connected point to the powerline neutral is in the main entrance
> > box. You don't care if a nearby lightning strike might cause that
> > bolt to be 200,000 volts from ground for a microsecond during that
> > strike, but the +5 volt line will be 200,005 volts, or 5 volts from
> > what it considers its ground might be at that exact instant.  You
> > will be damaged ONLY if some other point in the circuit breaks down
> > and some of that lightning bolts energy actually flows thru your
> > system to get to that better ground. Block it with air, the more the
> > merrier.
> >
> > > regards
> > >
> > > Andrew
> > >
> > > On Fri, May 29, 2020 at 11:53 AM Leonardo Marsaglia
> > > <ldmarsag...@gmail.com>
> > >
> > > wrote:
> > > > > Connect all grounds to this bolt, checking that they are not
> > > > > grounded at the far end.  By doing this, you are establishing
> > > > > a single point ground that is the zero volt reference for the
> > > > > whole system. Connect this bolt to the building static ground,
> > > > > the bare wire in most power cabling.
> > > > >
> > > > > Connect the machines frame to this bolt.
> > > > >
> > > > > Connect the - rails of all supplies to this bolt.
> > > > >
> > > > > Connect the - terminals of all cards to this bolt.
> > > > >
> > > > > Break the 3rd pin off the computers supply cable and connect
> > > > > the computers chassis to this bolt. Power the computer not
> > > > > from the wall, but from the same power feeding this box.
> > > > >
> > > > > Connect the shielding of all shielded cabling to this bolt. Do
> > > > > not connect the far end of this shielding to anything that is
> > > > > otherwise grounded.
> > > > >
> > > > > By making sure these grounds are not connected anyplace else
> > > > > you are breaking any ground loops which can and will act as
> > > > > antennas to insert noise into your control signals.
> > > > >
> > > > > By having this single point ground, a nearby lightning strike
> > > > > can inject a 100k volt pulse into the system ground as what
> > > > > would be called a "ground bounce",  but the system will not
> > > > > see it as noise nor be damaged, because everything is bouncing
> > > > > in unison.
> > > > >
> > > > > Regardless of what that bolt does during the strike, the 5
> > > > > volt supply remains at 5 volts to this bolt, and the 24 volt
> > > > > supply remains at 24 volts to this bolt.
> > > > >
> > > > > And when the storm is done, your chances of having anything
> > > > > damaged is reduced to the vanishing point.
> > > >
> > > > Thanks for this Gene. It's more than useful to remember how to
> > > > properly ground logic circuits to avoid external noise and
> > > > dangerous voltage spikes.
> > > >
> > > > El jue., 28 may. 2020 a las 20:35, Gene Heskett
> > > > (<ghesk...@shentel.net>)
> > > >
> > > > escribió:
> > > > > On Thursday 28 May 2020 18:36:10 andrew beck wrote:
> > > > > > hey gene
> > > > > >
> > > > > > sorry for the slow reply
> > > > > >
> > > > > > just getting to this grounding thing now.
> > > > > >
> > > > > > currently I have single large copper block with a lot of
> > > > > > holes in it for terminals, this is connected to the
> > > > > > earth(ground) wire that goes back to the whole shed main
> > > > > > ground wire rod in the dirt
> > > > > >
> > > > > > all my servo drives and vfd main grounds go back to this
> > > > > > point as do all motor grounds etc.  this is how heidenhain
> > > > > > set up the machine originally and they have a whole
> > > > > > grounding schematic showing how it all works.  I have
> > > > > > basically copied that.
> > > > > >
> > > > > > I have 2 meanwell 24v powersupplies that have the ground
> > > > > > wire on the input side also connected to ground.  the output
> > > > > > side (phase and neutral) are floating relative to ground and
> > > > > > not connected to ground at all I think.  as the meanwell
> > > > > > switching powersupply output should be isolated from the
> > > > > > input.  I think this is correct
> > > > > >
> > > > > > the computer cord ground wire is currently connected to this
> > > > > > same large copper block.
> > > > >
> > > > > The sheer bulk of that copper bother me a bit because it can
> > > > > function as an antenna.  A single bolt, tightened well into
> > > > > the chassis with all the connections stacked up on this bolt
> > > > > will be quieter.
> > > > >
> > > > > > my computer via the 5i25 currently supplies 5v logic power
> > > > > > to the 7i76
> > > > >
> > > > > Thats fine, but if using a std bob on the other 5i25 port, do
> > > > > NOT enable the jumper for that port as the bobs std grounding
> > > > > will short circuit that, you must supply a separated 5 volts
> > > > > to that bob, or plug in a usb cable to steal it from the pc's
> > > > > usb circuitry,
> > > > >
> > > > > > and one of the 24v meanwell powersupplys supplies the 24v
> > > > > > field io for the 7i76
> > > > >
> > > > > I have all supplies - outputs tied to ground.  It might work
> > > > > 99% of the time without it, till the first nearby lightning
> > > > > strike... With all that grounded, it will probably keep right
> > > > > on working after the strike.
> > > > >
> > > > > > my encoder problems started when I connected up the servo
> > > > > > drive simulated encoder output to the 7i76 encoder counter. 
> > > > > > I haven't connected the 5v and 24 v grounds together.  they
> > > > > > did work for awhile but don't now
> > > > >
> > > > > Tie the -'s to the ground bolt. Then do a full powerdown on
> > > > > the whole thing, with about a 10 count in the dark, then boot
> > > > > everything back up and test it.  And report what you get
> > > > > now...
> > > > >
> > > > > > I have a 7i89 and 7i84 coming soon and will need a external
> > > > > > 5v powersupply anyway i think so will change when they
> > > > > > arrive here from america.
> > > > > >
> > > > > > anyway I read your reply and got a bit confused could you
> > > > > > read my email here and let me know what I need to change and
> > > > > > why I should do it this way just so I understand.
> > > > >
> > > > > Basicly, your lack of a common ground has possibly allowed
> > > > > voltages well above the breakdown voltages of the chips on
> > > > > these cards, between the - connections and a real ground. They
> > > > > all have what can look like an SCR as an isolation tub under
> > > > > each transistor its built from, and these SCR's can upset the
> > > > > whole thing if they get turned on.  Thats why the count to 10
> > > > > or more powerdown is done, giving these SCR's time enough at a
> > > > > low enough voltage to turn them off, at which point the
> > > > > circuit looks more normal and may even work. If not, then
> > > > > something has been damaged on the card and it should be
> > > > > replaced or tested and repaired as needed by Peter. His
> > > > > turnaround time from CA to WV here in the states has been very
> > > > > good. Its several thousand miles.  But if I recall correctly,
> > > > > you are not exactly local.
> > > > >
> > > > > > regards
> > > > > >
> > > > > > Andrew
> > > > > >
> > > > > > On Thu, May 21, 2020 at 9:31 PM Gene Heskett
> > > > > > <ghesk...@shentel.net>
> > > > >
> > > > > wrote:
> > > > > > > On Thursday 21 May 2020 01:57:06 andrew beck wrote:
> > > > > > > > hey peter
> > > > > > > >
> > > > > > > > I had a look and the unless there is a shorted out pin
> > > > > > > > in the servo drive connector itself I think the wiring
> > > > > > > > is all good.
> > > > > > > >
> > > > > > > > and I highly doubt the servo drive has problems all I
> > > > > > > > did was connect the 24v back into the servo on pin which
> > > > > > > > is how it has been running for the last ages.
> > > > > > > >
> > > > > > > > anyway how do you recommend commoning the grounds?
> > > > > > > >
> > > > > > > > it is as simple as connecting the field power 0v ground
> > > > > > > > with a wire to the logic power 0v ground?
> > > > > > >
> > > > > > > Yes, but how you do it can be very important.
> > > > > > >
> > > > > > > In your control box, install a longer bolt, #6 or #8-32 to
> > > > > > > the chassis. 4mm if metric.
> > > > > > >
> > > > > > > Connect all grounds to this bolt, checking that they are
> > > > > > > not grounded at the far end.  By doing this, you are
> > > > > > > establishing a single point ground that is the zero volt
> > > > > > > reference for the whole system. Connect this bolt to the
> > > > > > > building static ground, the bare wire in most power
> > > > > > > cabling.
> > > > > > >
> > > > > > > Connect the machines frame to this bolt.
> > > > > > >
> > > > > > > Connect the - rails of all supplies to this bolt.
> > > > > > >
> > > > > > > Connect the - terminals of all cards to this bolt.
> > > > > > >
> > > > > > > Break the 3rd pin off the computers supply cable and
> > > > > > > connect the computers chassis to this bolt. Power the
> > > > > > > computer not from the wall, but from the same power
> > > > > > > feeding this box.
> > > > > > >
> > > > > > > Connect the shielding of all shielded cabling to this
> > > > > > > bolt. Do not connect the far end of this shielding to
> > > > > > > anything that is otherwise grounded.
> > > > > > >
> > > > > > > By making sure these grounds are not connected anyplace
> > > > > > > else you are breaking any ground loops which can and will
> > > > > > > act as antennas to insert noise into your control signals.
> > > > > > >
> > > > > > > By having this single point ground, a nearby lightning
> > > > > > > strike can inject a 100k volt pulse into the system ground
> > > > > > > as what would be called a "ground bounce",  but the system
> > > > > > > will not see it as noise nor be damaged, because
> > > > > > > everything is bouncing in unison.
> > > > > > >
> > > > > > > Regardless of what that bolt does during the strike, the 5
> > > > > > > volt supply remains at 5 volts to this bolt, and the 24
> > > > > > > volt supply remains at 24 volts to this bolt.
> > > > > > >
> > > > > > > And when the storm is done, your chances of having
> > > > > > > anything damaged is reduced to the vanishing point.
> > > > > > >
> > > > > > > Stay well Andrew.
> > > > >
> > > > > Cheers, Gene Heskett
> > > > > --
> > > > > "There are four boxes to be used in defense of liberty:
> > > > >  soap, ballot, jury, and ammo. Please use in that order."
> > > > > -Ed Howdershelt (Author)
> > > > > If we desire respect for the law, we must first make the law
> > > > > respectable. - Louis D. Brandeis
> > > > > Genes Web page <http://geneslinuxbox.net:6309/gene>
> > > > >
> > > > >
> > > > > _______________________________________________
> > > > > Emc-users mailing list
> > > > > Emc-users@lists.sourceforge.net
> > > > > https://lists.sourceforge.net/lists/listinfo/emc-users
> > > >
> > > > _______________________________________________
> > > > Emc-users mailing list
> > > > Emc-users@lists.sourceforge.net
> > > > https://lists.sourceforge.net/lists/listinfo/emc-users
> > >
> > > _______________________________________________
> > > Emc-users mailing list
> > > Emc-users@lists.sourceforge.net
> > > https://lists.sourceforge.net/lists/listinfo/emc-users
> >
> > Cheers, Gene Heskett
> > --
> > "There are four boxes to be used in defense of liberty:
> >  soap, ballot, jury, and ammo. Please use in that order."
> > -Ed Howdershelt (Author)
> > If we desire respect for the law, we must first make the law
> > respectable. - Louis D. Brandeis
> > Genes Web page <http://geneslinuxbox.net:6309/gene>
> >
> >
> > _______________________________________________
> > Emc-users mailing list
> > Emc-users@lists.sourceforge.net
> > https://lists.sourceforge.net/lists/listinfo/emc-users
>
> _______________________________________________
> Emc-users mailing list
> Emc-users@lists.sourceforge.net
> https://lists.sourceforge.net/lists/listinfo/emc-users


Cheers, Gene Heskett
-- 
"There are four boxes to be used in defense of liberty:
 soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author)