actually just another question here gene

so following along that analogy you made with the single bolt for all
ground wires.  if I connect the pc case to the bolt and also the 0v from
24v dc outputs,

 does that mean that I don't have to connect between the mesa 7i76 field io
0v and logic power 0v?  I think it does.
just triple checking as things get expensive if I get them wrong and I
don't want to go down that track

regards

Andrew

On Sat, May 30, 2020 at 2:14 PM andrew beck <andrewbeck0...@gmail.com>
wrote:

> sweet thanks gene
>
> I will take your advice and connect the pc chassis to the main ground.
>
> I think I will continue to use my grounding blocks for now though as there
> are about 20 ground cables to connect up and that is getting a bit much for
> one bolt I think.  hopefully I don't have a problem.  I will let you know
> if I do haha
>
>
> regards
>
> Andrew
>
>
> On Sat, May 30, 2020 at 2:00 PM Gene Heskett <ghesk...@shentel.net> wrote:
>
>> On Friday 29 May 2020 21:22:09 andrew beck wrote:
>>
>> > thanks guys
>> >
>> > just one question about all this gene
>> >
>> > why do you suggest breaking the ground off the the computer
>> > powersupply cable and connecting a ground from the pc chassis to the
>> > machine main ground?
>> >
>> > does the grounding that goes through the cable now good enough?
>> The computers 3rd wire should remain if its the ONLY ground connection in
>> the whole system. But since we power gear thru EMT tubing, and that also
>> includes a generally better ground, the power cord to the computer
>> should have that 2nd or 3rd ground removed, and the computers ground
>> taken back to this common bolt by a direct from its chassis ground wire,
>> UNLESS the computer is mounted to and mechanically connected to the
>> frame of the machine and this frame is grounded to that common bolt.
>>
>> Anytime you can lift just one of those wires from that bolt, and still
>> get ground continuity because its grounded someplace else too, is bad
>> kharma, find that "other" ground and disconnect it.  Once, done well, is
>> enough.  A shielded cable where the shield is grounded at the far end
>> can inject many volts of noise, enough to blow the interface card.
>> Disconnect that far end. That bolt should connect to the power
>> wirings "static" ground, and the only allowable cross connected point to
>> the powerline neutral is in the main entrance box. You don't care if a
>> nearby lightning strike might cause that bolt to be 200,000 volts from
>> ground for a microsecond during that strike, but the +5 volt line will
>> be 200,005 volts, or 5 volts from what it considers its ground might be
>> at that exact instant.  You will be damaged ONLY if some other point in
>> the circuit breaks down and some of that lightning bolts energy actually
>> flows thru your system to get to that better ground. Block it with air,
>> the more the merrier.
>>
>> > regards
>> >
>> > Andrew
>> >
>> > On Fri, May 29, 2020 at 11:53 AM Leonardo Marsaglia
>> > <ldmarsag...@gmail.com>
>> >
>> > wrote:
>> > > > Connect all grounds to this bolt, checking that they are not
>> > > > grounded at the far end.  By doing this, you are establishing a
>> > > > single point ground that is the zero volt reference for the whole
>> > > > system. Connect this bolt to the building static ground, the bare
>> > > > wire in most power cabling.
>> > > >
>> > > > Connect the machines frame to this bolt.
>> > > >
>> > > > Connect the - rails of all supplies to this bolt.
>> > > >
>> > > > Connect the - terminals of all cards to this bolt.
>> > > >
>> > > > Break the 3rd pin off the computers supply cable and connect the
>> > > > computers chassis to this bolt. Power the computer not from the
>> > > > wall, but from the same power feeding this box.
>> > > >
>> > > > Connect the shielding of all shielded cabling to this bolt. Do not
>> > > > connect the far end of this shielding to anything that is
>> > > > otherwise grounded.
>> > > >
>> > > > By making sure these grounds are not connected anyplace else you
>> > > > are breaking any ground loops which can and will act as antennas
>> > > > to insert noise into your control signals.
>> > > >
>> > > > By having this single point ground, a nearby lightning strike can
>> > > > inject a 100k volt pulse into the system ground as what would be
>> > > > called a "ground bounce",  but the system will not see it as noise
>> > > > nor be damaged, because everything is bouncing in unison.
>> > > >
>> > > > Regardless of what that bolt does during the strike, the 5 volt
>> > > > supply remains at 5 volts to this bolt, and the 24 volt supply
>> > > > remains at 24 volts to this bolt.
>> > > >
>> > > > And when the storm is done, your chances of having anything
>> > > > damaged is reduced to the vanishing point.
>> > >
>> > > Thanks for this Gene. It's more than useful to remember how to
>> > > properly ground logic circuits to avoid external noise and dangerous
>> > > voltage spikes.
>> > >
>> > > El jue., 28 may. 2020 a las 20:35, Gene Heskett
>> > > (<ghesk...@shentel.net>)
>> > >
>> > > escribió:
>> > > > On Thursday 28 May 2020 18:36:10 andrew beck wrote:
>> > > > > hey gene
>> > > > >
>> > > > > sorry for the slow reply
>> > > > >
>> > > > > just getting to this grounding thing now.
>> > > > >
>> > > > > currently I have single large copper block with a lot of holes
>> > > > > in it for terminals, this is connected to the earth(ground) wire
>> > > > > that goes back to the whole shed main ground wire rod in the
>> > > > > dirt
>> > > > >
>> > > > > all my servo drives and vfd main grounds go back to this point
>> > > > > as do all motor grounds etc.  this is how heidenhain set up the
>> > > > > machine originally and they have a whole grounding schematic
>> > > > > showing how it all works.  I have basically copied that.
>> > > > >
>> > > > > I have 2 meanwell 24v powersupplies that have the ground wire on
>> > > > > the input side also connected to ground.  the output side (phase
>> > > > > and neutral) are floating relative to ground and not connected
>> > > > > to ground at all I think.  as the meanwell switching powersupply
>> > > > > output should be isolated from the input.  I think this is
>> > > > > correct
>> > > > >
>> > > > > the computer cord ground wire is currently connected to this
>> > > > > same large copper block.
>> > > >
>> > > > The sheer bulk of that copper bother me a bit because it can
>> > > > function as an antenna.  A single bolt, tightened well into the
>> > > > chassis with all the connections stacked up on this bolt will be
>> > > > quieter.
>> > > >
>> > > > > my computer via the 5i25 currently supplies 5v logic power to
>> > > > > the 7i76
>> > > >
>> > > > Thats fine, but if using a std bob on the other 5i25 port, do NOT
>> > > > enable the jumper for that port as the bobs std grounding will
>> > > > short circuit that, you must supply a separated 5 volts to that
>> > > > bob, or plug in a usb cable to steal it from the pc's usb
>> > > > circuitry,
>> > > >
>> > > > > and one of the 24v meanwell powersupplys supplies the 24v field
>> > > > > io for the 7i76
>> > > >
>> > > > I have all supplies - outputs tied to ground.  It might work 99%
>> > > > of the time without it, till the first nearby lightning strike...
>> > > > With all that grounded, it will probably keep right on working
>> > > > after the strike.
>> > > >
>> > > > > my encoder problems started when I connected up the servo drive
>> > > > > simulated encoder output to the 7i76 encoder counter.  I haven't
>> > > > > connected the 5v and 24 v grounds together.  they did work for
>> > > > > awhile but don't now
>> > > >
>> > > > Tie the -'s to the ground bolt. Then do a full powerdown on the
>> > > > whole thing, with about a 10 count in the dark, then boot
>> > > > everything back up and test it.  And report what you get now...
>> > > >
>> > > > > I have a 7i89 and 7i84 coming soon and will need a external 5v
>> > > > > powersupply anyway i think so will change when they arrive here
>> > > > > from america.
>> > > > >
>> > > > > anyway I read your reply and got a bit confused could you read
>> > > > > my email here and let me know what I need to change and why I
>> > > > > should do it this way just so I understand.
>> > > >
>> > > > Basicly, your lack of a common ground has possibly allowed
>> > > > voltages well above the breakdown voltages of the chips on these
>> > > > cards, between the - connections and a real ground. They all have
>> > > > what can look like an SCR as an isolation tub under each
>> > > > transistor its built from, and these SCR's can upset the whole
>> > > > thing if they get turned on.  Thats why the count to 10 or more
>> > > > powerdown is done, giving these SCR's time enough at a low enough
>> > > > voltage to turn them off, at which point the circuit looks more
>> > > > normal and may even work. If not, then something has been damaged
>> > > > on the card and it should be replaced or tested and repaired as
>> > > > needed by Peter. His turnaround time from CA to WV here in the
>> > > > states has been very good. Its several thousand miles.  But if I
>> > > > recall correctly, you are not exactly local.
>> > > >
>> > > > > regards
>> > > > >
>> > > > > Andrew
>> > > > >
>> > > > > On Thu, May 21, 2020 at 9:31 PM Gene Heskett
>> > > > > <ghesk...@shentel.net>
>> > > >
>> > > > wrote:
>> > > > > > On Thursday 21 May 2020 01:57:06 andrew beck wrote:
>> > > > > > > hey peter
>> > > > > > >
>> > > > > > > I had a look and the unless there is a shorted out pin in
>> > > > > > > the servo drive connector itself I think the wiring is all
>> > > > > > > good.
>> > > > > > >
>> > > > > > > and I highly doubt the servo drive has problems all I did
>> > > > > > > was connect the 24v back into the servo on pin which is how
>> > > > > > > it has been running for the last ages.
>> > > > > > >
>> > > > > > > anyway how do you recommend commoning the grounds?
>> > > > > > >
>> > > > > > > it is as simple as connecting the field power 0v ground with
>> > > > > > > a wire to the logic power 0v ground?
>> > > > > >
>> > > > > > Yes, but how you do it can be very important.
>> > > > > >
>> > > > > > In your control box, install a longer bolt, #6 or #8-32 to the
>> > > > > > chassis. 4mm if metric.
>> > > > > >
>> > > > > > Connect all grounds to this bolt, checking that they are not
>> > > > > > grounded at the far end.  By doing this, you are establishing
>> > > > > > a single point ground that is the zero volt reference for the
>> > > > > > whole system. Connect this bolt to the building static ground,
>> > > > > > the bare wire in most power cabling.
>> > > > > >
>> > > > > > Connect the machines frame to this bolt.
>> > > > > >
>> > > > > > Connect the - rails of all supplies to this bolt.
>> > > > > >
>> > > > > > Connect the - terminals of all cards to this bolt.
>> > > > > >
>> > > > > > Break the 3rd pin off the computers supply cable and connect
>> > > > > > the computers chassis to this bolt. Power the computer not
>> > > > > > from the wall, but from the same power feeding this box.
>> > > > > >
>> > > > > > Connect the shielding of all shielded cabling to this bolt. Do
>> > > > > > not connect the far end of this shielding to anything that is
>> > > > > > otherwise grounded.
>> > > > > >
>> > > > > > By making sure these grounds are not connected anyplace else
>> > > > > > you are breaking any ground loops which can and will act as
>> > > > > > antennas to insert noise into your control signals.
>> > > > > >
>> > > > > > By having this single point ground, a nearby lightning strike
>> > > > > > can inject a 100k volt pulse into the system ground as what
>> > > > > > would be called a "ground bounce",  but the system will not
>> > > > > > see it as noise nor be damaged, because everything is bouncing
>> > > > > > in unison.
>> > > > > >
>> > > > > > Regardless of what that bolt does during the strike, the 5
>> > > > > > volt supply remains at 5 volts to this bolt, and the 24 volt
>> > > > > > supply remains at 24 volts to this bolt.
>> > > > > >
>> > > > > > And when the storm is done, your chances of having anything
>> > > > > > damaged is reduced to the vanishing point.
>> > > > > >
>> > > > > > Stay well Andrew.
>> > > >
>> > > > Cheers, Gene Heskett
>> > > > --
>> > > > "There are four boxes to be used in defense of liberty:
>> > > >  soap, ballot, jury, and ammo. Please use in that order."
>> > > > -Ed Howdershelt (Author)
>> > > > If we desire respect for the law, we must first make the law
>> > > > respectable. - Louis D. Brandeis
>> > > > Genes Web page <http://geneslinuxbox.net:6309/gene>
>> > > >
>> > > >
>> > > > _______________________________________________
>> > > > Emc-users mailing list
>> > > > Emc-users@lists.sourceforge.net
>> > > > https://lists.sourceforge.net/lists/listinfo/emc-users
>> > >
>> > > _______________________________________________
>> > > Emc-users mailing list
>> > > Emc-users@lists.sourceforge.net
>> > > https://lists.sourceforge.net/lists/listinfo/emc-users
>> >
>> > _______________________________________________
>> > Emc-users mailing list
>> > Emc-users@lists.sourceforge.net
>> > https://lists.sourceforge.net/lists/listinfo/emc-users
>>
>>
>> Cheers, Gene Heskett
>> --
>> "There are four boxes to be used in defense of liberty:
>>  soap, ballot, jury, and ammo. Please use in that order."
>> -Ed Howdershelt (Author)
>> If we desire respect for the law, we must first make the law respectable.
>>  - Louis D. Brandeis
>> Genes Web page <http://geneslinuxbox.net:6309/gene>
>>
>>
>> _______________________________________________
>> Emc-users mailing list
>> Emc-users@lists.sourceforge.net
>> https://lists.sourceforge.net/lists/listinfo/emc-users
>>
>

_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users