sweet thanks gene

I will take your advice and connect the pc chassis to the main ground.

I think I will continue to use my grounding blocks for now though as there
are about 20 ground cables to connect up and that is getting a bit much for
one bolt I think.  hopefully I don't have a problem.  I will let you know
if I do haha


regards

Andrew


On Sat, May 30, 2020 at 2:00 PM Gene Heskett <ghesk...@shentel.net> wrote:

> On Friday 29 May 2020 21:22:09 andrew beck wrote:
>
> > thanks guys
> >
> > just one question about all this gene
> >
> > why do you suggest breaking the ground off the the computer
> > powersupply cable and connecting a ground from the pc chassis to the
> > machine main ground?
> >
> > does the grounding that goes through the cable now good enough?
> The computers 3rd wire should remain if its the ONLY ground connection in
> the whole system. But since we power gear thru EMT tubing, and that also
> includes a generally better ground, the power cord to the computer
> should have that 2nd or 3rd ground removed, and the computers ground
> taken back to this common bolt by a direct from its chassis ground wire,
> UNLESS the computer is mounted to and mechanically connected to the
> frame of the machine and this frame is grounded to that common bolt.
>
> Anytime you can lift just one of those wires from that bolt, and still
> get ground continuity because its grounded someplace else too, is bad
> kharma, find that "other" ground and disconnect it.  Once, done well, is
> enough.  A shielded cable where the shield is grounded at the far end
> can inject many volts of noise, enough to blow the interface card.
> Disconnect that far end. That bolt should connect to the power
> wirings "static" ground, and the only allowable cross connected point to
> the powerline neutral is in the main entrance box. You don't care if a
> nearby lightning strike might cause that bolt to be 200,000 volts from
> ground for a microsecond during that strike, but the +5 volt line will
> be 200,005 volts, or 5 volts from what it considers its ground might be
> at that exact instant.  You will be damaged ONLY if some other point in
> the circuit breaks down and some of that lightning bolts energy actually
> flows thru your system to get to that better ground. Block it with air,
> the more the merrier.
>
> > regards
> >
> > Andrew
> >
> > On Fri, May 29, 2020 at 11:53 AM Leonardo Marsaglia
> > <ldmarsag...@gmail.com>
> >
> > wrote:
> > > > Connect all grounds to this bolt, checking that they are not
> > > > grounded at the far end.  By doing this, you are establishing a
> > > > single point ground that is the zero volt reference for the whole
> > > > system. Connect this bolt to the building static ground, the bare
> > > > wire in most power cabling.
> > > >
> > > > Connect the machines frame to this bolt.
> > > >
> > > > Connect the - rails of all supplies to this bolt.
> > > >
> > > > Connect the - terminals of all cards to this bolt.
> > > >
> > > > Break the 3rd pin off the computers supply cable and connect the
> > > > computers chassis to this bolt. Power the computer not from the
> > > > wall, but from the same power feeding this box.
> > > >
> > > > Connect the shielding of all shielded cabling to this bolt. Do not
> > > > connect the far end of this shielding to anything that is
> > > > otherwise grounded.
> > > >
> > > > By making sure these grounds are not connected anyplace else you
> > > > are breaking any ground loops which can and will act as antennas
> > > > to insert noise into your control signals.
> > > >
> > > > By having this single point ground, a nearby lightning strike can
> > > > inject a 100k volt pulse into the system ground as what would be
> > > > called a "ground bounce",  but the system will not see it as noise
> > > > nor be damaged, because everything is bouncing in unison.
> > > >
> > > > Regardless of what that bolt does during the strike, the 5 volt
> > > > supply remains at 5 volts to this bolt, and the 24 volt supply
> > > > remains at 24 volts to this bolt.
> > > >
> > > > And when the storm is done, your chances of having anything
> > > > damaged is reduced to the vanishing point.
> > >
> > > Thanks for this Gene. It's more than useful to remember how to
> > > properly ground logic circuits to avoid external noise and dangerous
> > > voltage spikes.
> > >
> > > El jue., 28 may. 2020 a las 20:35, Gene Heskett
> > > (<ghesk...@shentel.net>)
> > >
> > > escribió:
> > > > On Thursday 28 May 2020 18:36:10 andrew beck wrote:
> > > > > hey gene
> > > > >
> > > > > sorry for the slow reply
> > > > >
> > > > > just getting to this grounding thing now.
> > > > >
> > > > > currently I have single large copper block with a lot of holes
> > > > > in it for terminals, this is connected to the earth(ground) wire
> > > > > that goes back to the whole shed main ground wire rod in the
> > > > > dirt
> > > > >
> > > > > all my servo drives and vfd main grounds go back to this point
> > > > > as do all motor grounds etc.  this is how heidenhain set up the
> > > > > machine originally and they have a whole grounding schematic
> > > > > showing how it all works.  I have basically copied that.
> > > > >
> > > > > I have 2 meanwell 24v powersupplies that have the ground wire on
> > > > > the input side also connected to ground.  the output side (phase
> > > > > and neutral) are floating relative to ground and not connected
> > > > > to ground at all I think.  as the meanwell switching powersupply
> > > > > output should be isolated from the input.  I think this is
> > > > > correct
> > > > >
> > > > > the computer cord ground wire is currently connected to this
> > > > > same large copper block.
> > > >
> > > > The sheer bulk of that copper bother me a bit because it can
> > > > function as an antenna.  A single bolt, tightened well into the
> > > > chassis with all the connections stacked up on this bolt will be
> > > > quieter.
> > > >
> > > > > my computer via the 5i25 currently supplies 5v logic power to
> > > > > the 7i76
> > > >
> > > > Thats fine, but if using a std bob on the other 5i25 port, do NOT
> > > > enable the jumper for that port as the bobs std grounding will
> > > > short circuit that, you must supply a separated 5 volts to that
> > > > bob, or plug in a usb cable to steal it from the pc's usb
> > > > circuitry,
> > > >
> > > > > and one of the 24v meanwell powersupplys supplies the 24v field
> > > > > io for the 7i76
> > > >
> > > > I have all supplies - outputs tied to ground.  It might work 99%
> > > > of the time without it, till the first nearby lightning strike...
> > > > With all that grounded, it will probably keep right on working
> > > > after the strike.
> > > >
> > > > > my encoder problems started when I connected up the servo drive
> > > > > simulated encoder output to the 7i76 encoder counter.  I haven't
> > > > > connected the 5v and 24 v grounds together.  they did work for
> > > > > awhile but don't now
> > > >
> > > > Tie the -'s to the ground bolt. Then do a full powerdown on the
> > > > whole thing, with about a 10 count in the dark, then boot
> > > > everything back up and test it.  And report what you get now...
> > > >
> > > > > I have a 7i89 and 7i84 coming soon and will need a external 5v
> > > > > powersupply anyway i think so will change when they arrive here
> > > > > from america.
> > > > >
> > > > > anyway I read your reply and got a bit confused could you read
> > > > > my email here and let me know what I need to change and why I
> > > > > should do it this way just so I understand.
> > > >
> > > > Basicly, your lack of a common ground has possibly allowed
> > > > voltages well above the breakdown voltages of the chips on these
> > > > cards, between the - connections and a real ground. They all have
> > > > what can look like an SCR as an isolation tub under each
> > > > transistor its built from, and these SCR's can upset the whole
> > > > thing if they get turned on.  Thats why the count to 10 or more
> > > > powerdown is done, giving these SCR's time enough at a low enough
> > > > voltage to turn them off, at which point the circuit looks more
> > > > normal and may even work. If not, then something has been damaged
> > > > on the card and it should be replaced or tested and repaired as
> > > > needed by Peter. His turnaround time from CA to WV here in the
> > > > states has been very good. Its several thousand miles.  But if I
> > > > recall correctly, you are not exactly local.
> > > >
> > > > > regards
> > > > >
> > > > > Andrew
> > > > >
> > > > > On Thu, May 21, 2020 at 9:31 PM Gene Heskett
> > > > > <ghesk...@shentel.net>
> > > >
> > > > wrote:
> > > > > > On Thursday 21 May 2020 01:57:06 andrew beck wrote:
> > > > > > > hey peter
> > > > > > >
> > > > > > > I had a look and the unless there is a shorted out pin in
> > > > > > > the servo drive connector itself I think the wiring is all
> > > > > > > good.
> > > > > > >
> > > > > > > and I highly doubt the servo drive has problems all I did
> > > > > > > was connect the 24v back into the servo on pin which is how
> > > > > > > it has been running for the last ages.
> > > > > > >
> > > > > > > anyway how do you recommend commoning the grounds?
> > > > > > >
> > > > > > > it is as simple as connecting the field power 0v ground with
> > > > > > > a wire to the logic power 0v ground?
> > > > > >
> > > > > > Yes, but how you do it can be very important.
> > > > > >
> > > > > > In your control box, install a longer bolt, #6 or #8-32 to the
> > > > > > chassis. 4mm if metric.
> > > > > >
> > > > > > Connect all grounds to this bolt, checking that they are not
> > > > > > grounded at the far end.  By doing this, you are establishing
> > > > > > a single point ground that is the zero volt reference for the
> > > > > > whole system. Connect this bolt to the building static ground,
> > > > > > the bare wire in most power cabling.
> > > > > >
> > > > > > Connect the machines frame to this bolt.
> > > > > >
> > > > > > Connect the - rails of all supplies to this bolt.
> > > > > >
> > > > > > Connect the - terminals of all cards to this bolt.
> > > > > >
> > > > > > Break the 3rd pin off the computers supply cable and connect
> > > > > > the computers chassis to this bolt. Power the computer not
> > > > > > from the wall, but from the same power feeding this box.
> > > > > >
> > > > > > Connect the shielding of all shielded cabling to this bolt. Do
> > > > > > not connect the far end of this shielding to anything that is
> > > > > > otherwise grounded.
> > > > > >
> > > > > > By making sure these grounds are not connected anyplace else
> > > > > > you are breaking any ground loops which can and will act as
> > > > > > antennas to insert noise into your control signals.
> > > > > >
> > > > > > By having this single point ground, a nearby lightning strike
> > > > > > can inject a 100k volt pulse into the system ground as what
> > > > > > would be called a "ground bounce",  but the system will not
> > > > > > see it as noise nor be damaged, because everything is bouncing
> > > > > > in unison.
> > > > > >
> > > > > > Regardless of what that bolt does during the strike, the 5
> > > > > > volt supply remains at 5 volts to this bolt, and the 24 volt
> > > > > > supply remains at 24 volts to this bolt.
> > > > > >
> > > > > > And when the storm is done, your chances of having anything
> > > > > > damaged is reduced to the vanishing point.
> > > > > >
> > > > > > Stay well Andrew.
> > > >
> > > > Cheers, Gene Heskett
> > > > --
> > > > "There are four boxes to be used in defense of liberty:
> > > >  soap, ballot, jury, and ammo. Please use in that order."
> > > > -Ed Howdershelt (Author)
> > > > If we desire respect for the law, we must first make the law
> > > > respectable. - Louis D. Brandeis
> > > > Genes Web page <http://geneslinuxbox.net:6309/gene>
> > > >
> > > >
> > > > _______________________________________________
> > > > Emc-users mailing list
> > > > Emc-users@lists.sourceforge.net
> > > > https://lists.sourceforge.net/lists/listinfo/emc-users
> > >
> > > _______________________________________________
> > > Emc-users mailing list
> > > Emc-users@lists.sourceforge.net
> > > https://lists.sourceforge.net/lists/listinfo/emc-users
> >
> > _______________________________________________
> > Emc-users mailing list
> > Emc-users@lists.sourceforge.net
> > https://lists.sourceforge.net/lists/listinfo/emc-users
>
>
> Cheers, Gene Heskett
> --
> "There are four boxes to be used in defense of liberty:
>  soap, ballot, jury, and ammo. Please use in that order."
> -Ed Howdershelt (Author)
> If we desire respect for the law, we must first make the law respectable.
>  - Louis D. Brandeis
> Genes Web page <http://geneslinuxbox.net:6309/gene>
>
>
> _______________________________________________
> Emc-users mailing list
> Emc-users@lists.sourceforge.net
> https://lists.sourceforge.net/lists/listinfo/emc-users
>

_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to