On Saturday 30 May 2020 01:36:25 andrew beck wrote:

> sweet as gene
>
> actually on this currently I have 2 big blocks for grounding.  both
> connected together with a decent 6 mm cable.  is that enough to work
> as one ground block or do I really need to get and machine/ buy
> another grounding block that is all one piece
>
>
> the latest is the E stop circuit wasn't working.  So I disconnected it
> and put a push botton right at the servo on input on the servo drives
> and that works to trigger control power on and off to the servos.  so
> I will go looking through the rest of the E stop circuit.  there is
> something on the estop circuit that didn't like me connecting the 
> field io power 0v to the machine frame ground.

Thats wierd, but doesn't trigger any memories here.
> regards
>
> Andrew
>
> On Sat, May 30, 2020 at 4:55 PM Gene Heskett <ghesk...@shentel.net> 
wrote:
> > On Friday 29 May 2020 22:14:57 andrew beck wrote:
> > > sweet thanks gene
> > >
> > > I will take your advice and connect the pc chassis to the main
> > > ground.
> > >
> > > I think I will continue to use my grounding blocks for now though
> > > as there are about 20 ground cables to connect up and that is
> > > getting a bit much for one bolt I think.  hopefully I don't have a
> > > problem.  I will let you know if I do haha
> >
> > Use only one block, and put them as close together as you can.
> >
> > > regards
> > >
> > > Andrew
> > >
> > > On Sat, May 30, 2020 at 2:00 PM Gene Heskett
> > > <ghesk...@shentel.net>
> >
> > wrote:
> > > > On Friday 29 May 2020 21:22:09 andrew beck wrote:
> > > > > thanks guys
> > > > >
> > > > > just one question about all this gene
> > > > >
> > > > > why do you suggest breaking the ground off the the computer
> > > > > powersupply cable and connecting a ground from the pc chassis
> > > > > to the machine main ground?
> > > > >
> > > > > does the grounding that goes through the cable now good
> > > > > enough?
> > > >
> > > > The computers 3rd wire should remain if its the ONLY ground
> > > > connection in the whole system. But since we power gear thru EMT
> > > > tubing, and that also includes a generally better ground, the
> > > > power cord to the computer should have that 2nd or 3rd ground
> > > > removed, and the computers ground taken back to this common bolt
> > > > by a direct from its chassis ground wire, UNLESS the computer is
> > > > mounted to and mechanically connected to the frame of the
> > > > machine and this frame is grounded to that common bolt.
> > > >
> > > > Anytime you can lift just one of those wires from that bolt, and
> > > > still get ground continuity because its grounded someplace else
> > > > too, is bad kharma, find that "other" ground and disconnect it. 
> > > > Once, done well, is enough.  A shielded cable where the shield
> > > > is grounded at the far end can inject many volts of noise,
> > > > enough to blow the interface card. Disconnect that far end. That
> > > > bolt should connect to the power wirings "static" ground, and
> > > > the only allowable cross connected point to the powerline
> > > > neutral is in the main entrance box. You don't care if a nearby
> > > > lightning strike might cause that bolt to be 200,000 volts from
> > > > ground for a microsecond during that strike, but the +5 volt
> > > > line will be 200,005 volts, or 5 volts from what it considers
> > > > its ground might be at that exact instant.  You will be damaged
> > > > ONLY if some other point in the circuit breaks down and some of
> > > > that lightning bolts energy actually flows thru your system to
> > > > get to that better ground. Block it with air, the more the
> > > > merrier.
> > > >
> > > > > regards
> > > > >
> > > > > Andrew
> > > > >
> > > > > On Fri, May 29, 2020 at 11:53 AM Leonardo Marsaglia
> > > > > <ldmarsag...@gmail.com>
> > > > >
> > > > > wrote:
> > > > > > > Connect all grounds to this bolt, checking that they are
> > > > > > > not grounded at the far end.  By doing this, you are
> > > > > > > establishing a single point ground that is the zero volt
> > > > > > > reference for the whole system. Connect this bolt to the
> > > > > > > building static ground, the bare wire in most power
> > > > > > > cabling.
> > > > > > >
> > > > > > > Connect the machines frame to this bolt.
> > > > > > >
> > > > > > > Connect the - rails of all supplies to this bolt.
> > > > > > >
> > > > > > > Connect the - terminals of all cards to this bolt.
> > > > > > >
> > > > > > > Break the 3rd pin off the computers supply cable and
> > > > > > > connect the computers chassis to this bolt. Power the
> > > > > > > computer not from the wall, but from the same power
> > > > > > > feeding this box.
> > > > > > >
> > > > > > > Connect the shielding of all shielded cabling to this
> > > > > > > bolt. Do not connect the far end of this shielding to
> > > > > > > anything that is otherwise grounded.
> > > > > > >
> > > > > > > By making sure these grounds are not connected anyplace
> > > > > > > else you are breaking any ground loops which can and will
> > > > > > > act as antennas to insert noise into your control signals.
> > > > > > >
> > > > > > > By having this single point ground, a nearby lightning
> > > > > > > strike can inject a 100k volt pulse into the system ground
> > > > > > > as what would be called a "ground bounce",  but the system
> > > > > > > will not see it as noise nor be damaged, because
> > > > > > > everything is bouncing in unison.
> > > > > > >
> > > > > > > Regardless of what that bolt does during the strike, the 5
> > > > > > > volt supply remains at 5 volts to this bolt, and the 24
> > > > > > > volt supply remains at 24 volts to this bolt.
> > > > > > >
> > > > > > > And when the storm is done, your chances of having
> > > > > > > anything damaged is reduced to the vanishing point.
> > > > > >
> > > > > > Thanks for this Gene. It's more than useful to remember how
> > > > > > to properly ground logic circuits to avoid external noise
> > > > > > and dangerous voltage spikes.
> > > > > >
> > > > > > El jue., 28 may. 2020 a las 20:35, Gene Heskett
> > > > > > (<ghesk...@shentel.net>)
> > > > > >
> > > > > > escribió:
> > > > > > > On Thursday 28 May 2020 18:36:10 andrew beck wrote:
> > > > > > > > hey gene
> > > > > > > >
> > > > > > > > sorry for the slow reply
> > > > > > > >
> > > > > > > > just getting to this grounding thing now.
> > > > > > > >
> > > > > > > > currently I have single large copper block with a lot of
> > > > > > > > holes in it for terminals, this is connected to the
> > > > > > > > earth(ground) wire that goes back to the whole shed main
> > > > > > > > ground wire rod in the dirt
> > > > > > > >
> > > > > > > > all my servo drives and vfd main grounds go back to this
> > > > > > > > point as do all motor grounds etc.  this is how
> > > > > > > > heidenhain set up the machine originally and they have a
> > > > > > > > whole grounding schematic showing how it all works.  I
> > > > > > > > have basically copied that.
> > > > > > > >
> > > > > > > > I have 2 meanwell 24v powersupplies that have the ground
> > > > > > > > wire on the input side also connected to ground.  the
> > > > > > > > output side (phase and neutral) are floating relative to
> > > > > > > > ground and not connected to ground at all I think.  as
> > > > > > > > the meanwell switching powersupply output should be
> > > > > > > > isolated from the input.  I think this is correct
> > > > > > > >
> > > > > > > > the computer cord ground wire is currently connected to
> > > > > > > > this same large copper block.
> > > > > > >
> > > > > > > The sheer bulk of that copper bother me a bit because it
> > > > > > > can function as an antenna.  A single bolt, tightened well
> > > > > > > into the chassis with all the connections stacked up on
> > > > > > > this bolt will be quieter.
> > > > > > >
> > > > > > > > my computer via the 5i25 currently supplies 5v logic
> > > > > > > > power to the 7i76
> > > > > > >
> > > > > > > Thats fine, but if using a std bob on the other 5i25 port,
> > > > > > > do NOT enable the jumper for that port as the bobs std
> > > > > > > grounding will short circuit that, you must supply a
> > > > > > > separated 5 volts to that bob, or plug in a usb cable to
> > > > > > > steal it from the pc's usb circuitry,
> > > > > > >
> > > > > > > > and one of the 24v meanwell powersupplys supplies the
> > > > > > > > 24v field io for the 7i76
> > > > > > >
> > > > > > > I have all supplies - outputs tied to ground.  It might
> > > > > > > work 99% of the time without it, till the first nearby
> > > > > > > lightning strike... With all that grounded, it will
> > > > > > > probably keep right on working after the strike.
> > > > > > >
> > > > > > > > my encoder problems started when I connected up the
> > > > > > > > servo drive simulated encoder output to the 7i76 encoder
> > > > > > > > counter. I haven't connected the 5v and 24 v grounds
> > > > > > > > together.  they did work for awhile but don't now
> > > > > > >
> > > > > > > Tie the -'s to the ground bolt. Then do a full powerdown
> > > > > > > on the whole thing, with about a 10 count in the dark,
> > > > > > > then boot everything back up and test it.  And report what
> > > > > > > you get now...
> > > > > > >
> > > > > > > > I have a 7i89 and 7i84 coming soon and will need a
> > > > > > > > external 5v powersupply anyway i think so will change
> > > > > > > > when they arrive here from america.
> > > > > > > >
> > > > > > > > anyway I read your reply and got a bit confused could
> > > > > > > > you read my email here and let me know what I need to
> > > > > > > > change and why I should do it this way just so I
> > > > > > > > understand.
> > > > > > >
> > > > > > > Basicly, your lack of a common ground has possibly allowed
> > > > > > > voltages well above the breakdown voltages of the chips on
> > > > > > > these cards, between the - connections and a real ground.
> > > > > > > They all have what can look like an SCR as an isolation
> > > > > > > tub under each transistor its built from, and these SCR's
> > > > > > > can upset the whole thing if they get turned on.  Thats
> > > > > > > why the count to 10 or more powerdown is done, giving
> > > > > > > these SCR's time enough at a low enough voltage to turn
> > > > > > > them off, at which point the circuit looks more normal and
> > > > > > > may even work. If not, then something has been damaged on
> > > > > > > the card and it should be replaced or tested and repaired
> > > > > > > as needed by Peter. His turnaround time from CA to WV here
> > > > > > > in the states has been very good. Its several thousand
> > > > > > > miles.  But if I recall correctly, you are not exactly
> > > > > > > local.
> > > > > > >
> > > > > > > > regards
> > > > > > > >
> > > > > > > > Andrew
> > > > > > > >
> > > > > > > > On Thu, May 21, 2020 at 9:31 PM Gene Heskett
> > > > > > > > <ghesk...@shentel.net>
> > > > > > >
> > > > > > > wrote:
> > > > > > > > > On Thursday 21 May 2020 01:57:06 andrew beck wrote:
> > > > > > > > > > hey peter
> > > > > > > > > >
> > > > > > > > > > I had a look and the unless there is a shorted out
> > > > > > > > > > pin in the servo drive connector itself I think the
> > > > > > > > > > wiring is all good.
> > > > > > > > > >
> > > > > > > > > > and I highly doubt the servo drive has problems all
> > > > > > > > > > I did was connect the 24v back into the servo on pin
> > > > > > > > > > which is how it has been running for the last ages.
> > > > > > > > > >
> > > > > > > > > > anyway how do you recommend commoning the grounds?
> > > > > > > > > >
> > > > > > > > > > it is as simple as connecting the field power 0v
> > > > > > > > > > ground with a wire to the logic power 0v ground?
> > > > > > > > >
> > > > > > > > > Yes, but how you do it can be very important.
> > > > > > > > >
> > > > > > > > > In your control box, install a longer bolt, #6 or
> > > > > > > > > #8-32 to the chassis. 4mm if metric.
> > > > > > > > >
> > > > > > > > > Connect all grounds to this bolt, checking that they
> > > > > > > > > are not grounded at the far end.  By doing this, you
> > > > > > > > > are establishing a single point ground that is the
> > > > > > > > > zero volt reference for the whole system. Connect this
> > > > > > > > > bolt to the building static ground, the bare wire in
> > > > > > > > > most power cabling.
> > > > > > > > >
> > > > > > > > > Connect the machines frame to this bolt.
> > > > > > > > >
> > > > > > > > > Connect the - rails of all supplies to this bolt.
> > > > > > > > >
> > > > > > > > > Connect the - terminals of all cards to this bolt.
> > > > > > > > >
> > > > > > > > > Break the 3rd pin off the computers supply cable and
> > > > > > > > > connect the computers chassis to this bolt. Power the
> > > > > > > > > computer not from the wall, but from the same power
> > > > > > > > > feeding this box.
> > > > > > > > >
> > > > > > > > > Connect the shielding of all shielded cabling to this
> > > > > > > > > bolt. Do not connect the far end of this shielding to
> > > > > > > > > anything that is otherwise grounded.
> > > > > > > > >
> > > > > > > > > By making sure these grounds are not connected
> > > > > > > > > anyplace else you are breaking any ground loops which
> > > > > > > > > can and will act as antennas to insert noise into your
> > > > > > > > > control signals.
> > > > > > > > >
> > > > > > > > > By having this single point ground, a nearby lightning
> > > > > > > > > strike can inject a 100k volt pulse into the system
> > > > > > > > > ground as what would be called a "ground bounce",  but
> > > > > > > > > the system will not see it as noise nor be damaged,
> > > > > > > > > because everything is bouncing in unison.
> > > > > > > > >
> > > > > > > > > Regardless of what that bolt does during the strike,
> > > > > > > > > the 5 volt supply remains at 5 volts to this bolt, and
> > > > > > > > > the 24 volt supply remains at 24 volts to this bolt.
> > > > > > > > >
> > > > > > > > > And when the storm is done, your chances of having
> > > > > > > > > anything damaged is reduced to the vanishing point.
> > > > > > > > >
> > > > > > > > > Stay well Andrew.
> > > > > > >
> > > > > > > Cheers, Gene Heskett
> > > > > > > --
> > > > > > > "There are four boxes to be used in defense of liberty:
> > > > > > >  soap, ballot, jury, and ammo. Please use in that order."
> > > > > > > -Ed Howdershelt (Author)
> > > > > > > If we desire respect for the law, we must first make the
> > > > > > > law respectable. - Louis D. Brandeis
> > > > > > > Genes Web page <http://geneslinuxbox.net:6309/gene>
> > > > > > >
> > > > > > >
> > > > > > > _______________________________________________
> > > > > > > Emc-users mailing list
> > > > > > > Emc-users@lists.sourceforge.net
> > > > > > > https://lists.sourceforge.net/lists/listinfo/emc-users
> > > > > >
> > > > > > _______________________________________________
> > > > > > Emc-users mailing list
> > > > > > Emc-users@lists.sourceforge.net
> > > > > > https://lists.sourceforge.net/lists/listinfo/emc-users
> > > > >
> > > > > _______________________________________________
> > > > > Emc-users mailing list
> > > > > Emc-users@lists.sourceforge.net
> > > > > https://lists.sourceforge.net/lists/listinfo/emc-users
> > > >
> > > > Cheers, Gene Heskett
> > > > --
> > > > "There are four boxes to be used in defense of liberty:
> > > >  soap, ballot, jury, and ammo. Please use in that order."
> > > > -Ed Howdershelt (Author)
> > > > If we desire respect for the law, we must first make the law
> > > > respectable. - Louis D. Brandeis
> > > > Genes Web page <http://geneslinuxbox.net:6309/gene>
> > > >
> > > >
> > > > _______________________________________________
> > > > Emc-users mailing list
> > > > Emc-users@lists.sourceforge.net
> > > > https://lists.sourceforge.net/lists/listinfo/emc-users
> > >
> > > _______________________________________________
> > > Emc-users mailing list
> > > Emc-users@lists.sourceforge.net
> > > https://lists.sourceforge.net/lists/listinfo/emc-users
> >
> > Cheers, Gene Heskett
> > --
> > "There are four boxes to be used in defense of liberty:
> >  soap, ballot, jury, and ammo. Please use in that order."
> > -Ed Howdershelt (Author)
> > If we desire respect for the law, we must first make the law
> > respectable. - Louis D. Brandeis
> > Genes Web page <http://geneslinuxbox.net:6309/gene>
> >
> >
> > _______________________________________________
> > Emc-users mailing list
> > Emc-users@lists.sourceforge.net
> > https://lists.sourceforge.net/lists/listinfo/emc-users
>
> _______________________________________________
> Emc-users mailing list
> Emc-users@lists.sourceforge.net
> https://lists.sourceforge.net/lists/listinfo/emc-users


Cheers, Gene Heskett
-- 
"There are four boxes to be used in defense of liberty:
 soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author)
If we desire respect for the law, we must first make the law respectable.
 - Louis D. Brandeis
Genes Web page <http://geneslinuxbox.net:6309/gene>


_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to