On Mon, 10 Aug 2026, Viesturs L?cis wrote:

I can only notice that W2 is down instead of UP as per picture in page
4 of this manual: https://www.mesanet.com/pdf/parallel/6i24man.pdf
Although the description is a little strange: "The default is to
enable the pull-ups To enable the built-in pull-ups,
(the default condition) jumper W2 should be placed in the UP position.
To disable the
internal pull-ups, W4 should be in the DOWN position."
Is that meant to be W2 in last sentence?

Yes

Also make sure W10 is in the down position

Can you remind me of the firmware used?

I'll try and duplicate your setup here


Viesturs

pirmd., 2026. g. 10. aug., plkst. 22:51 ? lietot?js Viesturs L?cis
(<[email protected]>) rakst?ja:

pirmd., 2026. g. 10. aug., plkst. 22:45 ? lietot?js Peter Wallace
(<[email protected]>) rakst?ja:
>
> Are the 6I24 jumpers in their default (as shipped) positions?
>

Jumpers were not touched, this picture was taken on 6th of August - I
am showing it just to make sure that jumpers (at least then) are in
correct positions
 https://photos.app.goo.gl/VjA5j5SaGN9nQPvJ9

If you say that here they are in correct positions, in morning I will
recheck the board once more to make sure they are still the same.

Viesturs