On 17 Apr 2018 at 14:45, Rush Dougherty via EV wrote:

> if the ground is used as a neutral leg to get 120vac, the EVSE,
> according to the spec will ground fault. 

You'd expect it to do this.  Its GFI circuit just sees current that isn't 
balanced across the mains.  It can't tell the difference between current 
going through your body to ground, and current going through a 120v charger 
to ground.  So it's gong to say "nope" just to be safe.

Also, using the ground connection as a neutral return in wiring is an NEC 
violation for a reason.  If there should be a fault in the building's ground 
connection, using the ground that way puts line voltage on the enclosure of 
every other grounded appliance!  The same thing can happen if it's done in 
connected equipment.

David Roden - Akron, Ohio, USA
EVDL Administrator

= = = = = = = = = = = = = = = = = = = = = = = = = = = = =