Hi folks

Yes, I agree with Paul, the function is too protect the wiring but, in the
permanent magnet dynamo (20amp) setup, the only component capable of
supplying 35amps or more throughout the system wiring is the battery thus
the circuit breaker should be immediately downstream of the battery (not in
the dynamo output where it can never trip thereby providing no insurance).
You can't get blood out of a stone.

Different story with a normal alternator (or a bigger dynamo) that is
capable of supplying 35 amps or more. By all means protect your wiring with
a breaker as per your usual arrangement in aircraft.

A dynamo regulator failure allowing excess unrectified AC or DC voltage
(depending on the failure) to pass into the system is dealt with using an
overvoltage circuit that should drive a relay in the dynamo outputs to
isolate the dynamo.  Excess voltage will not trip a circuit breaker that
relies on current for its function.

It is the load on the circuit from your equipment (as normal or in failure)
that will determine the current flow through the wiring but only up to the
maximum that the dynamo can produce (20 amp rating). Anything more comes out
of the battery (anything up to welding current)!!!.

Your KR must be getting really close now up there in Brissie....go the
cowboys :-)

Regards John.

John Martindale
29 Jane Circuit
Toormina NSW 2452
Australia

ph:61 2 6658 4767
m:0403 432179
email:john_martindale at bigpond.com
web site: 
-----Original Message-----
From: KRnet [mailto:krnet-bounces at list.krnet.org] On Behalf Of Paul & Karen
Smith via KRnet
Sent: Saturday, 3 October 2015 6:40 AM
To: 'KRnet'
Cc: Paul & Karen Smith
Subject: Re: KR> Electrical System

Hi all,
Circuit breakers and fuses are installed into systems solely to protect the
wiring form too high current that could cause a fire.
Selecting the amp rating of a breaker is a function of the maximum current
carrying capacity of the conductor/insulation pair based on whether it is in
free air or inside a mass bundle.
Using one as the trigger for overvoltage protection might damage the
generator but it will save the many thousands of dollars of other electronic
systems in your plane.
Good insurance I'd say.
Paul.

-----Original Message-----

Cc: John Martindale
Subject: Re: KR> Electrical System

Hmmm, in which case having a 35amp circuit breaker in its unregulated output
is pointless. 



-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.6140 / Virus Database: 4435/10744 - Release Date: 10/02/15


Reply via email to