The information of the network is as follows:

The one-line diagram of a typical rural section of the Irish 38-kV
distribution network  was shown in above Figure. The feeders are supplied
by one 31.5-MVA 110/38-kV transformer (capable of handling reverse power
flows). The voltage at the grid supply point is assumed to be nominal. In
the original configuration (no DG), the on-load tap changer at the
substation has a target voltage of 1.078 pu (41 kV) at the busbar, well
within the +-10% nominal voltage limits of Irish practice.

Best Wishes

Silvio Miceli


On Fri, Feb 10, 2012 at 23:07, Ray Zimmerman <[email protected]> wrote:

> You haven't said which bus is your slack bus. Can I assume that it would
> be the one labeled GSP? I don't see a slack generator at that bus. Is the
> OLTC the *only* voltage control you have in the network? Is the voltage at
> GSP fixed?
>
>   --
> Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
>
>
>
>
> On Feb 10, 2012, at 2:51 PM, Silvio Miceli wrote:
>
> I want to have an OLTC at slack bus only in order to control centrally the
> network voltage (active network) as below figure. How can I compare the
> results with and without OLTC? with changing tap ratio or with changing
> voltage setpoints?
>
> <image.png>
>
> Best Wishes
>
> Silvio Miceli
>
>
> On Fri, Feb 10, 2012 at 20:43, Ray Zimmerman <[email protected]> wrote:
>
>> In order to understand clearly what you are trying to compare, I would
>> need to see the network topology.
>>
>> But, it both cases include the OLTC in the topology and in one case you
>> are modifying the tap ratio to control voltage and in the other you are
>> simply modifying the generator voltage setpoints, then the two solutions
>> will not be equivalent.
>>
>>  --
>> Ray Zimmerman
>> Senior Research Associate
>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>> phone: (607) 255-9645
>>
>>
>>
>>
>> On Feb 10, 2012, at 10:46 AM, Silvio Miceli wrote:
>>
>> Dear Ray,
>>
>> As far as I know, taking into account the voltage at slack bus as
>> optimization variable is equal to have an OLTC. So, how can I compare the
>> results with and without voltage control at slack? Can it be done either by
>> changing the tap ratio or voltage limits?
>> Best Wishes
>>
>> Silvio Miceli
>>
>>
>> On Thu, Feb 9, 2012 at 18:57, Silvio Miceli <[email protected]>wrote:
>>
>>> Dear Ray,
>>>
>>> 1. Can I say MATPOWER's OPF considers the power factor angle of
>>> generators as optimization variable? If not, how can I consider as
>>> optimization variable?
>>>
>>> 2. Also, according to one of your replies to a post with regards to
>>> considering the slack bus voltage as optimization variable, why you want to
>>> implement OLTC in MATPOWER? In my idea, considering the slack bus as
>>> optimization variable is equal to have an OLTC and consequently considering
>>> the secondary voltage as optimization variable. Because usually the OLTC is
>>> used in order to control the voltage of slack bus and in MATPOWER is
>>> already considered as optimization variable. If I am not right, please let
>>> me know?
>>>
>>> Best Wishes
>>>
>>> Silvio
>>>
>>>
>>>
>>> On Wed, Feb 8, 2012 at 17:47, Ray Zimmerman <[email protected]> wrote:
>>>
>>>> On Feb 8, 2012, at 10:01 AM, Silvio Miceli wrote:
>>>>
>>>> 1. What kind of generator has been taken into account in MATPOWER in
>>>> Section 5.4.3 of MANUAL in order to consider the capability curve?
>>>>
>>>>
>>>> It is simply intended to be a piecewise linear approximation to the
>>>> kind of capability curve exhibited by many types of conventional
>>>> generators, such as this 
>>>> one<http://images.pennnet.com/articles/hrm/cap/cap_coord%2003.gif> from
>>>> Figure 2 in [1].
>>>>
>>>> 2. I want to minimize losses instead of maximizing social welfare
>>>> considering offers and bids. How can I do it in MATPOWER?
>>>>
>>>>
>>>> The answer to this one is readily available in the list archives ...
>>>> e.g.
>>>> http://www.mail-archive.com/[email protected]/msg00817.html
>>>>
>>>> 3. How can I maximize profit for generators in MATPOWER instead of
>>>> maximizing Social welfare?
>>>> Also, by which formula I can obtain profits (for generators), revenue
>>>> and cost in MATPOWER? Could you please address it?
>>>>
>>>>
>>>> I'm not aware of a method to maximize profits, since that would involve
>>>> an objective that is a function of price, a very unconventional type of
>>>> optimization problem. You can compute revenue directly as the product of
>>>> quantity and price, and the cost is available in the dispatch matrix
>>>> returned by runmarket. See help idx_disp for a description of each column
>>>> of the dispatch matrix.
>>>>
>>>>   - Ray
>>>>
>>>> [1]
>>>> http://www.hydroworld.com/index/display/article-display/353952/articles/hydro-review/volume-28/issue-2/feature-articles/system-protection/coordinating-generator-protection-and-controls-an-overview.html
>>>>
>>>> --
>>>> Ray Zimmerman
>>>> Senior Research Associate
>>>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>>>> phone: (607) 255-9645
>>>>
>>>>
>>>
>>>
>>
>>
>
>

Reply via email to