Thank you so much for your helpful comments.

Best Wishes

Silvio Miceli


On Mon, Feb 13, 2012 at 15:27, Ray Zimmerman <[email protected]> wrote:

> I don't know what you mean by the first solution with and without the
> OLTC. In the first solution, I am assuming that the OLTC maintains the
> voltage at Tx at your target, so it is not in the model. I suppose if by
> "without OLTC" you mean that the OLTC is not keeping the voltage at the
> target, then you can simply set the VMIN and VMAX to 1.0 p.u.  Or you could
> use the setup for the 2nd option, and simply run it once with the taps at
> the nominal setting.
>
>   --
> Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
>
>
>
>
> On Feb 13, 2012, at 9:19 AM, Silvio Miceli wrote:
>
> Dear Prof. Zimmerman,
>
> I want to use first solution. It is much more easier than the second one.
> In this case, how can I compare the results with and without OLTC?
>
> Kind regards
>
> S.M.
>
>
> On Mon, Feb 13, 2012 at 15:07, Ray Zimmerman <[email protected]> wrote:
>
>> So it seems you could model it two different ways in MATPOWER.
>>
>> 1) Exclude bus GSP and the OLTC from the model and let Tx be the slack
>> bus with a dummy generator and VMIN = VMAX = 1.078.
>> 2) Include GSP and the OLTC, with a dummy generator at GSP (the slack
>> bus), with VMIN = VMAX = 1.0. In this case, you would have to iteratively
>> run the OPF, then update the tap setting until the voltage at Tx is close
>> enough to your target. I suppose you could use VMIN = VMAX = 1.078 at Tx
>> and then adjust the tap ratio until you get a feasible solution. You may
>> need to leave a small epsilon difference between VMIN and VMAX at GSP or Tx
>> in order to get feasibility.
>>
>> I expect the results for the rest of the system to be (at least nearly)
>> identical in the two cases.
>>
>> --
>>  Ray Zimmerman
>> Senior Research Associate
>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>> phone: (607) 255-9645
>>
>>
>>
>>
>> On Feb 10, 2012, at 8:32 PM, Silvio Miceli wrote:
>>
>>
>>
>> The information of the network is as follows:
>>
>> The one-line diagram of a typical rural section of the Irish 38-kV
>> distribution network  was shown in above Figure. The feeders are supplied
>> by one 31.5-MVA 110/38-kV transformer (capable of handling reverse power
>> flows). The voltage at the grid supply point is assumed to be nominal. In
>> the original configuration (no DG), the on-load tap changer at the
>> substation has a target voltage of 1.078 pu (41 kV) at the busbar, well
>> within the +-10% nominal voltage limits of Irish practice.
>>
>> Best Wishes
>>
>> Silvio Miceli
>>
>>
>> On Fri, Feb 10, 2012 at 23:07, Ray Zimmerman <[email protected]> wrote:
>>
>>> You haven't said which bus is your slack bus. Can I assume that it would
>>> be the one labeled GSP? I don't see a slack generator at that bus. Is the
>>> OLTC the *only* voltage control you have in the network? Is the voltage at
>>> GSP fixed?
>>>
>>>   --
>>> Ray Zimmerman
>>> Senior Research Associate
>>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>>> phone: (607) 255-9645
>>>
>>>
>>>
>>>
>>> On Feb 10, 2012, at 2:51 PM, Silvio Miceli wrote:
>>>
>>> I want to have an OLTC at slack bus only in order to control centrally
>>> the network voltage (active network) as below figure. How can I compare the
>>> results with and without OLTC? with changing tap ratio or with changing
>>> voltage setpoints?
>>>
>>> <image.png>
>>>
>>> Best Wishes
>>>
>>> Silvio Miceli
>>>
>>>
>>> On Fri, Feb 10, 2012 at 20:43, Ray Zimmerman <[email protected]> wrote:
>>>
>>>> In order to understand clearly what you are trying to compare, I would
>>>> need to see the network topology.
>>>>
>>>> But, it both cases include the OLTC in the topology and in one case you
>>>> are modifying the tap ratio to control voltage and in the other you are
>>>> simply modifying the generator voltage setpoints, then the two solutions
>>>> will not be equivalent.
>>>>
>>>>  --
>>>> Ray Zimmerman
>>>> Senior Research Associate
>>>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>>>> phone: (607) 255-9645
>>>>
>>>>
>>>>
>>>>
>>>> On Feb 10, 2012, at 10:46 AM, Silvio Miceli wrote:
>>>>
>>>> Dear Ray,
>>>>
>>>> As far as I know, taking into account the voltage at slack bus as
>>>> optimization variable is equal to have an OLTC. So, how can I compare the
>>>> results with and without voltage control at slack? Can it be done either by
>>>> changing the tap ratio or voltage limits?
>>>> Best Wishes
>>>>
>>>> Silvio Miceli
>>>>
>>>>
>>>> On Thu, Feb 9, 2012 at 18:57, Silvio Miceli <[email protected]>wrote:
>>>>
>>>>> Dear Ray,
>>>>>
>>>>> 1. Can I say MATPOWER's OPF considers the power factor angle of
>>>>> generators as optimization variable? If not, how can I consider as
>>>>> optimization variable?
>>>>>
>>>>> 2. Also, according to one of your replies to a post with regards to
>>>>> considering the slack bus voltage as optimization variable, why you want 
>>>>> to
>>>>> implement OLTC in MATPOWER? In my idea, considering the slack bus as
>>>>> optimization variable is equal to have an OLTC and consequently 
>>>>> considering
>>>>> the secondary voltage as optimization variable. Because usually the OLTC 
>>>>> is
>>>>> used in order to control the voltage of slack bus and in MATPOWER is
>>>>> already considered as optimization variable. If I am not right, please let
>>>>> me know?
>>>>>
>>>>> Best Wishes
>>>>>
>>>>> Silvio
>>>>>
>>>>>
>>>>>
>>>>> On Wed, Feb 8, 2012 at 17:47, Ray Zimmerman <[email protected]> wrote:
>>>>>
>>>>>> On Feb 8, 2012, at 10:01 AM, Silvio Miceli wrote:
>>>>>>
>>>>>> 1. What kind of generator has been taken into account in MATPOWER in
>>>>>> Section 5.4.3 of MANUAL in order to consider the capability curve?
>>>>>>
>>>>>>
>>>>>> It is simply intended to be a piecewise linear approximation to the
>>>>>> kind of capability curve exhibited by many types of conventional
>>>>>> generators, such as this 
>>>>>> one<http://images.pennnet.com/articles/hrm/cap/cap_coord%2003.gif> from
>>>>>> Figure 2 in [1].
>>>>>>
>>>>>> 2. I want to minimize losses instead of maximizing social welfare
>>>>>> considering offers and bids. How can I do it in MATPOWER?
>>>>>>
>>>>>>
>>>>>> The answer to this one is readily available in the list archives ...
>>>>>> e.g.
>>>>>> http://www.mail-archive.com/[email protected]/msg00817.html
>>>>>>
>>>>>> 3. How can I maximize profit for generators in MATPOWER instead of
>>>>>> maximizing Social welfare?
>>>>>> Also, by which formula I can obtain profits (for generators), revenue
>>>>>> and cost in MATPOWER? Could you please address it?
>>>>>>
>>>>>>
>>>>>> I'm not aware of a method to maximize profits, since that would
>>>>>> involve an objective that is a function of price, a very unconventional
>>>>>> type of optimization problem. You can compute revenue directly as the
>>>>>> product of quantity and price, and the cost is available in the dispatch
>>>>>> matrix returned by runmarket. See help idx_disp for a description of each
>>>>>> column of the dispatch matrix.
>>>>>>
>>>>>>   - Ray
>>>>>>
>>>>>> [1]
>>>>>> http://www.hydroworld.com/index/display/article-display/353952/articles/hydro-review/volume-28/issue-2/feature-articles/system-protection/coordinating-generator-protection-and-controls-an-overview.html
>>>>>>
>>>>>> --
>>>>>> Ray Zimmerman
>>>>>> Senior Research Associate
>>>>>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>>>>>> phone: (607) 255-9645
>>>>>>
>>>>>>
>>>>>
>>>>>
>>>>
>>>>
>>>
>>>
>>
>>
>
>

Reply via email to