Dear Prof. Zimmerman,

I want to use first solution. It is much more easier than the second one.
In this case, how can I compare the results with and without OLTC?

Kind regards

S.M.


On Mon, Feb 13, 2012 at 15:07, Ray Zimmerman <[email protected]> wrote:

> So it seems you could model it two different ways in MATPOWER.
>
> 1) Exclude bus GSP and the OLTC from the model and let Tx be the slack bus
> with a dummy generator and VMIN = VMAX = 1.078.
> 2) Include GSP and the OLTC, with a dummy generator at GSP (the slack
> bus), with VMIN = VMAX = 1.0. In this case, you would have to iteratively
> run the OPF, then update the tap setting until the voltage at Tx is close
> enough to your target. I suppose you could use VMIN = VMAX = 1.078 at Tx
> and then adjust the tap ratio until you get a feasible solution. You may
> need to leave a small epsilon difference between VMIN and VMAX at GSP or Tx
> in order to get feasibility.
>
> I expect the results for the rest of the system to be (at least nearly)
> identical in the two cases.
>
> --
>  Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
>
>
>
>
> On Feb 10, 2012, at 8:32 PM, Silvio Miceli wrote:
>
>
>
> The information of the network is as follows:
>
> The one-line diagram of a typical rural section of the Irish 38-kV
> distribution network  was shown in above Figure. The feeders are supplied
> by one 31.5-MVA 110/38-kV transformer (capable of handling reverse power
> flows). The voltage at the grid supply point is assumed to be nominal. In
> the original configuration (no DG), the on-load tap changer at the
> substation has a target voltage of 1.078 pu (41 kV) at the busbar, well
> within the +-10% nominal voltage limits of Irish practice.
>
> Best Wishes
>
> Silvio Miceli
>
>
> On Fri, Feb 10, 2012 at 23:07, Ray Zimmerman <[email protected]> wrote:
>
>> You haven't said which bus is your slack bus. Can I assume that it would
>> be the one labeled GSP? I don't see a slack generator at that bus. Is the
>> OLTC the *only* voltage control you have in the network? Is the voltage at
>> GSP fixed?
>>
>>   --
>> Ray Zimmerman
>> Senior Research Associate
>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>> phone: (607) 255-9645
>>
>>
>>
>>
>> On Feb 10, 2012, at 2:51 PM, Silvio Miceli wrote:
>>
>> I want to have an OLTC at slack bus only in order to control centrally
>> the network voltage (active network) as below figure. How can I compare the
>> results with and without OLTC? with changing tap ratio or with changing
>> voltage setpoints?
>>
>> <image.png>
>>
>> Best Wishes
>>
>> Silvio Miceli
>>
>>
>> On Fri, Feb 10, 2012 at 20:43, Ray Zimmerman <[email protected]> wrote:
>>
>>> In order to understand clearly what you are trying to compare, I would
>>> need to see the network topology.
>>>
>>> But, it both cases include the OLTC in the topology and in one case you
>>> are modifying the tap ratio to control voltage and in the other you are
>>> simply modifying the generator voltage setpoints, then the two solutions
>>> will not be equivalent.
>>>
>>>  --
>>> Ray Zimmerman
>>> Senior Research Associate
>>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>>> phone: (607) 255-9645
>>>
>>>
>>>
>>>
>>> On Feb 10, 2012, at 10:46 AM, Silvio Miceli wrote:
>>>
>>> Dear Ray,
>>>
>>> As far as I know, taking into account the voltage at slack bus as
>>> optimization variable is equal to have an OLTC. So, how can I compare the
>>> results with and without voltage control at slack? Can it be done either by
>>> changing the tap ratio or voltage limits?
>>> Best Wishes
>>>
>>> Silvio Miceli
>>>
>>>
>>> On Thu, Feb 9, 2012 at 18:57, Silvio Miceli <[email protected]>wrote:
>>>
>>>> Dear Ray,
>>>>
>>>> 1. Can I say MATPOWER's OPF considers the power factor angle of
>>>> generators as optimization variable? If not, how can I consider as
>>>> optimization variable?
>>>>
>>>> 2. Also, according to one of your replies to a post with regards to
>>>> considering the slack bus voltage as optimization variable, why you want to
>>>> implement OLTC in MATPOWER? In my idea, considering the slack bus as
>>>> optimization variable is equal to have an OLTC and consequently considering
>>>> the secondary voltage as optimization variable. Because usually the OLTC is
>>>> used in order to control the voltage of slack bus and in MATPOWER is
>>>> already considered as optimization variable. If I am not right, please let
>>>> me know?
>>>>
>>>> Best Wishes
>>>>
>>>> Silvio
>>>>
>>>>
>>>>
>>>> On Wed, Feb 8, 2012 at 17:47, Ray Zimmerman <[email protected]> wrote:
>>>>
>>>>> On Feb 8, 2012, at 10:01 AM, Silvio Miceli wrote:
>>>>>
>>>>> 1. What kind of generator has been taken into account in MATPOWER in
>>>>> Section 5.4.3 of MANUAL in order to consider the capability curve?
>>>>>
>>>>>
>>>>> It is simply intended to be a piecewise linear approximation to the
>>>>> kind of capability curve exhibited by many types of conventional
>>>>> generators, such as this 
>>>>> one<http://images.pennnet.com/articles/hrm/cap/cap_coord%2003.gif> from
>>>>> Figure 2 in [1].
>>>>>
>>>>> 2. I want to minimize losses instead of maximizing social welfare
>>>>> considering offers and bids. How can I do it in MATPOWER?
>>>>>
>>>>>
>>>>> The answer to this one is readily available in the list archives ...
>>>>> e.g.
>>>>> http://www.mail-archive.com/[email protected]/msg00817.html
>>>>>
>>>>> 3. How can I maximize profit for generators in MATPOWER instead of
>>>>> maximizing Social welfare?
>>>>> Also, by which formula I can obtain profits (for generators), revenue
>>>>> and cost in MATPOWER? Could you please address it?
>>>>>
>>>>>
>>>>> I'm not aware of a method to maximize profits, since that would
>>>>> involve an objective that is a function of price, a very unconventional
>>>>> type of optimization problem. You can compute revenue directly as the
>>>>> product of quantity and price, and the cost is available in the dispatch
>>>>> matrix returned by runmarket. See help idx_disp for a description of each
>>>>> column of the dispatch matrix.
>>>>>
>>>>>   - Ray
>>>>>
>>>>> [1]
>>>>> http://www.hydroworld.com/index/display/article-display/353952/articles/hydro-review/volume-28/issue-2/feature-articles/system-protection/coordinating-generator-protection-and-controls-an-overview.html
>>>>>
>>>>> --
>>>>> Ray Zimmerman
>>>>> Senior Research Associate
>>>>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>>>>> phone: (607) 255-9645
>>>>>
>>>>>
>>>>
>>>>
>>>
>>>
>>
>>
>
>

Reply via email to