Dear Ray,

As far as I know when we have an OLTC, the generated capacity is more than
that in the case without OLTC (i.e. Vmin=Vmax=1.06 p.u.). When I running an
OPF or runmarket, for example in the case57, I get more generated capacity
in the case without OLTC compared to with OLTC.

Best Wishes

Silvio


On Mon, Feb 13, 2012 at 16:09, Silvio Miceli <[email protected]>wrote:

> Thank you so much for your helpful comments.
>
> Best Wishes
>
> Silvio Miceli
>
>
>
> On Mon, Feb 13, 2012 at 15:27, Ray Zimmerman <[email protected]> wrote:
>
>> I don't know what you mean by the first solution with and without the
>> OLTC. In the first solution, I am assuming that the OLTC maintains the
>> voltage at Tx at your target, so it is not in the model. I suppose if by
>> "without OLTC" you mean that the OLTC is not keeping the voltage at the
>> target, then you can simply set the VMIN and VMAX to 1.0 p.u.  Or you could
>> use the setup for the 2nd option, and simply run it once with the taps at
>> the nominal setting.
>>
>>   --
>> Ray Zimmerman
>> Senior Research Associate
>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>> phone: (607) 255-9645
>>
>>
>>
>>
>> On Feb 13, 2012, at 9:19 AM, Silvio Miceli wrote:
>>
>> Dear Prof. Zimmerman,
>>
>> I want to use first solution. It is much more easier than the second one.
>> In this case, how can I compare the results with and without OLTC?
>>
>> Kind regards
>>
>> S.M.
>>
>>
>> On Mon, Feb 13, 2012 at 15:07, Ray Zimmerman <[email protected]> wrote:
>>
>>> So it seems you could model it two different ways in MATPOWER.
>>>
>>> 1) Exclude bus GSP and the OLTC from the model and let Tx be the slack
>>> bus with a dummy generator and VMIN = VMAX = 1.078.
>>> 2) Include GSP and the OLTC, with a dummy generator at GSP (the slack
>>> bus), with VMIN = VMAX = 1.0. In this case, you would have to iteratively
>>> run the OPF, then update the tap setting until the voltage at Tx is close
>>> enough to your target. I suppose you could use VMIN = VMAX = 1.078 at Tx
>>> and then adjust the tap ratio until you get a feasible solution. You may
>>> need to leave a small epsilon difference between VMIN and VMAX at GSP or Tx
>>> in order to get feasibility.
>>>
>>> I expect the results for the rest of the system to be (at least nearly)
>>> identical in the two cases.
>>>
>>> --
>>>  Ray Zimmerman
>>> Senior Research Associate
>>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>>> phone: (607) 255-9645
>>>
>>>
>>>
>>>
>>> On Feb 10, 2012, at 8:32 PM, Silvio Miceli wrote:
>>>
>>>
>>>
>>> The information of the network is as follows:
>>>
>>> The one-line diagram of a typical rural section of the Irish 38-kV
>>> distribution network  was shown in above Figure. The feeders are supplied
>>> by one 31.5-MVA 110/38-kV transformer (capable of handling reverse power
>>> flows). The voltage at the grid supply point is assumed to be nominal. In
>>> the original configuration (no DG), the on-load tap changer at the
>>> substation has a target voltage of 1.078 pu (41 kV) at the busbar, well
>>> within the +-10% nominal voltage limits of Irish practice.
>>>
>>> Best Wishes
>>>
>>> Silvio Miceli
>>>
>>>
>>> On Fri, Feb 10, 2012 at 23:07, Ray Zimmerman <[email protected]> wrote:
>>>
>>>> You haven't said which bus is your slack bus. Can I assume that it
>>>> would be the one labeled GSP? I don't see a slack generator at that bus. Is
>>>> the OLTC the *only* voltage control you have in the network? Is the voltage
>>>> at GSP fixed?
>>>>
>>>>   --
>>>> Ray Zimmerman
>>>> Senior Research Associate
>>>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>>>> phone: (607) 255-9645
>>>>
>>>>
>>>>
>>>>
>>>> On Feb 10, 2012, at 2:51 PM, Silvio Miceli wrote:
>>>>
>>>> I want to have an OLTC at slack bus only in order to control centrally
>>>> the network voltage (active network) as below figure. How can I compare the
>>>> results with and without OLTC? with changing tap ratio or with changing
>>>> voltage setpoints?
>>>>
>>>> <image.png>
>>>>
>>>> Best Wishes
>>>>
>>>> Silvio Miceli
>>>>
>>>>
>>>> On Fri, Feb 10, 2012 at 20:43, Ray Zimmerman <[email protected]> wrote:
>>>>
>>>>> In order to understand clearly what you are trying to compare, I would
>>>>> need to see the network topology.
>>>>>
>>>>> But, it both cases include the OLTC in the topology and in one case
>>>>> you are modifying the tap ratio to control voltage and in the other you 
>>>>> are
>>>>> simply modifying the generator voltage setpoints, then the two solutions
>>>>> will not be equivalent.
>>>>>
>>>>>  --
>>>>> Ray Zimmerman
>>>>> Senior Research Associate
>>>>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>>>>> phone: (607) 255-9645
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> On Feb 10, 2012, at 10:46 AM, Silvio Miceli wrote:
>>>>>
>>>>> Dear Ray,
>>>>>
>>>>> As far as I know, taking into account the voltage at slack bus as
>>>>> optimization variable is equal to have an OLTC. So, how can I compare the
>>>>> results with and without voltage control at slack? Can it be done either 
>>>>> by
>>>>> changing the tap ratio or voltage limits?
>>>>> Best Wishes
>>>>>
>>>>> Silvio Miceli
>>>>>
>>>>>
>>>>> On Thu, Feb 9, 2012 at 18:57, Silvio Miceli 
>>>>> <[email protected]>wrote:
>>>>>
>>>>>> Dear Ray,
>>>>>>
>>>>>> 1. Can I say MATPOWER's OPF considers the power factor angle of
>>>>>> generators as optimization variable? If not, how can I consider as
>>>>>> optimization variable?
>>>>>>
>>>>>> 2. Also, according to one of your replies to a post with regards to
>>>>>> considering the slack bus voltage as optimization variable, why you want 
>>>>>> to
>>>>>> implement OLTC in MATPOWER? In my idea, considering the slack bus as
>>>>>> optimization variable is equal to have an OLTC and consequently 
>>>>>> considering
>>>>>> the secondary voltage as optimization variable. Because usually the OLTC 
>>>>>> is
>>>>>> used in order to control the voltage of slack bus and in MATPOWER is
>>>>>> already considered as optimization variable. If I am not right, please 
>>>>>> let
>>>>>> me know?
>>>>>>
>>>>>> Best Wishes
>>>>>>
>>>>>> Silvio
>>>>>>
>>>>>>
>>>>>>
>>>>>> On Wed, Feb 8, 2012 at 17:47, Ray Zimmerman <[email protected]> wrote:
>>>>>>
>>>>>>> On Feb 8, 2012, at 10:01 AM, Silvio Miceli wrote:
>>>>>>>
>>>>>>> 1. What kind of generator has been taken into account in MATPOWER in
>>>>>>> Section 5.4.3 of MANUAL in order to consider the capability curve?
>>>>>>>
>>>>>>>
>>>>>>> It is simply intended to be a piecewise linear approximation to the
>>>>>>> kind of capability curve exhibited by many types of conventional
>>>>>>> generators, such as this 
>>>>>>> one<http://images.pennnet.com/articles/hrm/cap/cap_coord%2003.gif> from
>>>>>>> Figure 2 in [1].
>>>>>>>
>>>>>>> 2. I want to minimize losses instead of maximizing social welfare
>>>>>>> considering offers and bids. How can I do it in MATPOWER?
>>>>>>>
>>>>>>>
>>>>>>> The answer to this one is readily available in the list archives ...
>>>>>>> e.g.
>>>>>>> http://www.mail-archive.com/[email protected]/msg00817.html
>>>>>>>
>>>>>>> 3. How can I maximize profit for generators in MATPOWER instead of
>>>>>>> maximizing Social welfare?
>>>>>>> Also, by which formula I can obtain profits (for generators),
>>>>>>> revenue and cost in MATPOWER? Could you please address it?
>>>>>>>
>>>>>>>
>>>>>>> I'm not aware of a method to maximize profits, since that would
>>>>>>> involve an objective that is a function of price, a very unconventional
>>>>>>> type of optimization problem. You can compute revenue directly as the
>>>>>>> product of quantity and price, and the cost is available in the dispatch
>>>>>>> matrix returned by runmarket. See help idx_disp for a description of 
>>>>>>> each
>>>>>>> column of the dispatch matrix.
>>>>>>>
>>>>>>>   - Ray
>>>>>>>
>>>>>>> [1]
>>>>>>> http://www.hydroworld.com/index/display/article-display/353952/articles/hydro-review/volume-28/issue-2/feature-articles/system-protection/coordinating-generator-protection-and-controls-an-overview.html
>>>>>>>
>>>>>>> --
>>>>>>> Ray Zimmerman
>>>>>>> Senior Research Associate
>>>>>>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>>>>>>> phone: (607) 255-9645
>>>>>>>
>>>>>>>
>>>>>>
>>>>>>
>>>>>
>>>>>
>>>>
>>>>
>>>
>>>
>>
>>
>

Reply via email to