So it seems you could model it two different ways in MATPOWER.

1) Exclude bus GSP and the OLTC from the model and let Tx be the slack bus with 
a dummy generator and VMIN = VMAX = 1.078.
2) Include GSP and the OLTC, with a dummy generator at GSP (the slack bus), 
with VMIN = VMAX = 1.0. In this case, you would have to iteratively run the 
OPF, then update the tap setting until the voltage at Tx is close enough to 
your target. I suppose you could use VMIN = VMAX = 1.078 at Tx and then adjust 
the tap ratio until you get a feasible solution. You may need to leave a small 
epsilon difference between VMIN and VMAX at GSP or Tx in order to get 
feasibility. 

I expect the results for the rest of the system to be (at least nearly) 
identical in the two cases.

-- 
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645




On Feb 10, 2012, at 8:32 PM, Silvio Miceli wrote:

> 
> 
> The information of the network is as follows: 
> 
> The one-line diagram of a typical rural section of the Irish 38-kV 
> distribution network  was shown in above Figure. The feeders are supplied by 
> one 31.5-MVA 110/38-kV transformer (capable of handling reverse power flows). 
> The voltage at the grid supply point is assumed to be nominal. In the 
> original configuration (no DG), the on-load tap changer at the substation has 
> a target voltage of 1.078 pu (41 kV) at the busbar, well within the +-10% 
> nominal voltage limits of Irish practice.
> 
> Best Wishes
> 
> Silvio Miceli
> 
> 
> On Fri, Feb 10, 2012 at 23:07, Ray Zimmerman <[email protected]> wrote:
> You haven't said which bus is your slack bus. Can I assume that it would be 
> the one labeled GSP? I don't see a slack generator at that bus. Is the OLTC 
> the *only* voltage control you have in the network? Is the voltage at GSP 
> fixed?
> 
> -- 
> Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> 
> 
> On Feb 10, 2012, at 2:51 PM, Silvio Miceli wrote:
> 
>> I want to have an OLTC at slack bus only in order to control centrally the 
>> network voltage (active network) as below figure. How can I compare the 
>> results with and without OLTC? with changing tap ratio or with changing 
>> voltage setpoints?
>> 
>> <image.png>
>> 
>> Best Wishes
>> 
>> Silvio Miceli
>> 
>> 
>> On Fri, Feb 10, 2012 at 20:43, Ray Zimmerman <[email protected]> wrote:
>> In order to understand clearly what you are trying to compare, I would need 
>> to see the network topology.
>> 
>> But, it both cases include the OLTC in the topology and in one case you are 
>> modifying the tap ratio to control voltage and in the other you are simply 
>> modifying the generator voltage setpoints, then the two solutions will not 
>> be equivalent.
>> 
>> -- 
>> Ray Zimmerman
>> Senior Research Associate
>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>> phone: (607) 255-9645
>> 
>> 
>> 
>> 
>> On Feb 10, 2012, at 10:46 AM, Silvio Miceli wrote:
>> 
>>> Dear Ray,
>>> 
>>> As far as I know, taking into account the voltage at slack bus as 
>>> optimization variable is equal to have an OLTC. So, how can I compare the 
>>> results with and without voltage control at slack? Can it be done either by 
>>> changing the tap ratio or voltage limits? 
>>> Best Wishes
>>> 
>>> Silvio Miceli
>>> 
>>> 
>>> On Thu, Feb 9, 2012 at 18:57, Silvio Miceli <[email protected]> wrote:
>>> Dear Ray,
>>> 
>>> 1. Can I say MATPOWER's OPF considers the power factor angle of generators 
>>> as optimization variable? If not, how can I consider as optimization 
>>> variable?
>>> 
>>> 2. Also, according to one of your replies to a post with regards to 
>>> considering the slack bus voltage as optimization variable, why you want to 
>>> implement OLTC in MATPOWER? In my idea, considering the slack bus as 
>>> optimization variable is equal to have an OLTC and consequently considering 
>>> the secondary voltage as optimization variable. Because usually the OLTC is 
>>> used in order to control the voltage of slack bus and in MATPOWER is 
>>> already considered as optimization variable. If I am not right, please let 
>>> me know?
>>> 
>>> Best Wishes
>>> 
>>> Silvio 
>>> 
>>> 
>>> 
>>> On Wed, Feb 8, 2012 at 17:47, Ray Zimmerman <[email protected]> wrote:
>>> On Feb 8, 2012, at 10:01 AM, Silvio Miceli wrote:
>>> 
>>>> 1. What kind of generator has been taken into account in MATPOWER in 
>>>> Section 5.4.3 of MANUAL in order to consider the capability curve?
>>> 
>>> It is simply intended to be a piecewise linear approximation to the kind of 
>>> capability curve exhibited by many types of conventional generators, such 
>>> as this one from Figure 2 in [1].
>>> 
>>>> 2. I want to minimize losses instead of maximizing social welfare 
>>>> considering offers and bids. How can I do it in MATPOWER?
>>> 
>>> The answer to this one is readily available in the list archives ... e.g. 
>>> http://www.mail-archive.com/[email protected]/msg00817.html
>>> 
>>>> 3. How can I maximize profit for generators in MATPOWER instead of 
>>>> maximizing Social welfare?
>>>> Also, by which formula I can obtain profits (for generators), revenue and 
>>>> cost in MATPOWER? Could you please address it? 
>>> 
>>> I'm not aware of a method to maximize profits, since that would involve an 
>>> objective that is a function of price, a very unconventional type of 
>>> optimization problem. You can compute revenue directly as the product of 
>>> quantity and price, and the cost is available in the dispatch matrix 
>>> returned by runmarket. See help idx_disp for a description of each column 
>>> of the dispatch matrix.
>>> 
>>>   - Ray
>>> 
>>> [1] 
>>> http://www.hydroworld.com/index/display/article-display/353952/articles/hydro-review/volume-28/issue-2/feature-articles/system-protection/coordinating-generator-protection-and-controls-an-overview.html
>>> 
>>> -- 
>>> Ray Zimmerman
>>> Senior Research Associate
>>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>>> phone: (607) 255-9645
>>> 
>>> 
>>> 
>>> 
>> 
>> 
> 
> 

Reply via email to