ENFORCE_Q_LIM simply means that it will dispatch QG to maintain the voltage set 
point as long QG is within limits, if QG hits a limit, it will switch it to a 
fixed injection and voltage will be what it will be. So if that's the behavior 
you want to simulate, that's perfectly appropriate.

If you use the BS column of the bus matrix, then it's modeled as a capacitor 
(i.e. fixed impedance) so you simply compute Q as the imaginary part of V * 
conj(I)  = V * conj(V / Z).

-- 
Ray Zimmerman
Senior Research Associate
B30 Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645





On Aug 2, 2013, at 7:25 AM, Power Engineer <[email protected]> wrote:

> Thanks for your respond
> I use PF not OPF.
> If  SVC modeled with a gen with PG=0 Do we need to set ENFORCE_Q_LIM  to 1 or 
> not? Because if it isn't set to 1 may exceeds its limits.
> If it modeled in BS column of bus matrix, How much is the generated reactive 
> power at voltages except 1 p.u.? 
> 
> 
> From: Ray Zimmerman <[email protected]>
> To: MATPOWER discussion forum <[email protected]> 
> Sent: Thursday, August 1, 2013 5:46 PM
> Subject: Re: PF by removing Line
> 
> I am assuming you are using PF, not OPF ...
> 
> 1. You can model it with a gen with PG = 0, then QG will be solved to keep 
> the bus voltage at the set point. Or you can model it as a reactive injection 
> (in QD column of bus matrix). Or you can model it as a capacitor bank (BS 
> column of bus matrix).
> 
> 2. By default MATPOWER's power flow enforces the voltage set point at the 
> expense of the Q limit.
> 
> -- 
> Ray Zimmerman
> Senior Research Associate
> B30 Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> 
> 
> 
> On Aug 1, 2013, at 3:30 AM, Power Engineer <[email protected]> 
> wrote:
> 
>> 1. for modeling SVC by zero P-output generator does we need a reference 
>> voltage? Can wemodel SVC  by a reactive power injection like capacitor bank?
>> 2. I use default MATPOWER options for PF.
>> 
>> From: "[email protected]" <[email protected]>
>> To: [email protected] 
>> Sent: Wednesday, July 31, 2013 2:27 PM
>> Subject: RE: PF by removing Line
>> 
>> 1, zero P-output might imply SVC or synchronous condenser
>> 2. your PF might have option that ignore the Q-limit.
>>  
>> BR//Yongtao
>>  
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of Power 
>> Engineer
>> Sent: 31. juli 2013 10:38
>> To: MATPOWER forum
>> Subject: PF by removing Line
>>  
>> Dear all 
>> I have 2 questions
>> 1. in case 57 and 118 we have some generators with zero active output, Do 
>> they model special equipment? 
>> 2. I run PF for case 57 by removing line between 8 and 9 while the power 
>> flow is converging the reactive limit of generator at bus 9 violated.
>> results.success
>>  
>> ans =
>>  
>>      1
>>  
>> results.gen(:,1:5)
>>  
>> ans =
>>  
>>             1       511.91     142.3          200         -140
>>             2            0       -1.9005           50          -17
>>             3           40       16.317           60          -10
>>             6            0        6.774           25           -8
>>             8          450       34.892          200         -140
>>             9            0        86.611            9           -3
>>            12          310       151.03          155         -150
>>  
>>  
>> 
>> **************************************************************************************
>>  The contents of this e-mail message and any attachments are confidential 
>> and are intended solely for the addressee. If you have received this 
>> transmission in error, please immediately notify the sender by return e-mail 