dear sir 
I use matpower 3.2 

I use runpf on case 39 and I wish to limit power generated at bus 39 to certain 
value how can I do that ?

first guess for power generated from generator at bus 39 = 1000 MW
I wish to make it generate only 500 MW 

thank you in advance 
Eng. Mahmoud abdallah
Teaching Assistant
Ain Shams University
Faculty of Engineering

On Friday, April 11, 2014 6:19 AM, Ray Zimmerman <[email protected]> wrote:
  
I assume you are referring to the “System Summary” part of the MATPOWER output?

================================================================================
|     System Summary                                                           |
================================================================================

How many?                How much?              P (MW)            Q (MVAr)
---------------------    -------------------  -------------  -----------------
Buses              9     Total Gen Capacity     820.0        -900.0 to 900.0
Generators         3     On-line Capacity       820.0        -900.0 to 900.0
Committed Gens     3     Generation (actual)    320.0              34.9
Loads              3     Load                   315.0             115.0
  Fixed            3       Fixed                315.0             115.0
  Dispatchable     0       Dispatchable          -0.0 of -0.0      -0.0
Shunts             0     Shunt (inj)             -0.0               0.0
Branches           9     Losses (I^2 * Z)         4.95             51.31
Transformers       0     Branch Charging (inj)     -              131.4
Inter-ties         0     Total Inter-tie Flow     0.0               0.0
Areas              1


If so, please notice that series losses and the branch charging are listed 
separately. So the total reactive loss in the line is the series loss minus the 
branch charging injection.

     Ray



-- 
Ray Zimmerman
Senior Research Associate
B30 Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645

 

On Apr 10, 2014, at 5:59 PM, Angie Joaqui Rendon <[email protected]> wrote:

 
>Regards
>
>
>I am working with the module of power flow, and i want  know if the reactive 
>losses that shows me the program considers the capacitive effects of the 
>lines?.
>
>
>I am comparing results with other malingerers and these do not coincide with 
>some results that gives me MATPOWER, and differ for the lines that possess a 
>high capacitive value. 
>
>
>I appreciate the information that you can give me.  