If your are running ACPF simply change that value and the limits:
from: 39 1000 78.4674 300 -100 1.03 100 1 1100 0 0 0 0 0 0 0 0 0 0 0 0; to: 39 500 78.4674 300 -100 1.03 100 1 500 0 0 0 0 0 0 0 0 0 0 0 0; Those 500MW will be generated by the slack bus. 2014-04-12 12:53 GMT-05:00 Mahmoud Abdallah <[email protected]> : > > dear sir > I use matpower 3.2 > > I use runpf on case 39 and I wish to limit power generated at bus 39 to > certain value how can I do that ? > > first guess for power generated from generator at bus 39 = 1000 MW > I wish to make it generate only 500 MW > > thank you in advance > > > > > *Eng. Mahmoud abdallahTeaching AssistantAin Shams UniversityFaculty of > Engineering* > On Friday, April 11, 2014 6:19 AM, Ray Zimmerman <[email protected]> > wrote: > I assume you are referring to the "System Summary" part of the MATPOWER > output? > > > ================================================================================ > | System Summary > | > > ================================================================================ > > How many? How much? P (MW) Q (MVAr) > --------------------- ------------------- ------------- > ----------------- > Buses 9 Total Gen Capacity 820.0 -900.0 to > 900.0 > Generators 3 On-line Capacity 820.0 -900.0 to > 900.0 > Committed Gens 3 Generation (actual) 320.0 34.9 > Loads 3 Load 315.0 115.0 > Fixed 3 Fixed 315.0 115.0 > Dispatchable 0 Dispatchable -0.0 of -0.0 -0.0 > Shunts 0 Shunt (inj) -0.0 0.0 > Branches 9 Losses (I^2 * Z) 4.95 51.31 > Transformers 0 Branch Charging (inj) - 131.4 > Inter-ties 0 Total Inter-tie Flow 0.0 0.0 > Areas 1 > > > If so, please notice that series losses and the branch charging are listed > separately. So the total reactive loss in the line is the series loss minus > the branch charging injection. > > Ray > > > -- > Ray Zimmerman > Senior Research Associate > B30 Warren Hall, Cornell University, Ithaca, NY 14853 > phone: (607) 255-9645 > > > > On Apr 10, 2014, at 5:59 PM, Angie Joaqui Rendon <[email protected]> > wrote: > > Regards > > I am working with the module of power flow, and i want know if the > reactive losses that shows me the program considers the capacitive effects > of the lines?. > > I am comparing results with other malingerers and these do not coincide > with some results that gives me MATPOWER, and differ for the lines that > possess a high capacitive value. > > I appreciate the information that you can give me. > > > > >