If your are running ACPF simply change that value and the limits:

from:

39 1000 78.4674 300 -100 1.03 100 1 1100 0 0 0 0 0 0 0 0 0 0 0 0;
to:

39 500 78.4674 300 -100 1.03 100 1 500 0 0 0 0 0 0 0 0 0 0 0 0;

Those 500MW will be generated by the slack bus.




2014-04-12 12:53 GMT-05:00 Mahmoud Abdallah <[email protected]>
:

>
>  dear sir
> I use matpower 3.2
>
> I use runpf on case 39 and I wish to limit power generated at bus 39 to
> certain value how can I do that ?
>
> first guess for power generated from generator at bus 39 = 1000 MW
> I wish to make it generate only 500 MW
>
> thank you in advance
>
>
>
>
> *Eng. Mahmoud abdallahTeaching AssistantAin Shams UniversityFaculty of
> Engineering*
>   On Friday, April 11, 2014 6:19 AM, Ray Zimmerman <[email protected]>
> wrote:
>  I assume you are referring to the "System Summary" part of the MATPOWER
> output?
>
>
> ================================================================================
> |     System Summary
>     |
>
> ================================================================================
>
> How many?                How much?              P (MW)            Q (MVAr)
> ---------------------    -------------------  -------------
> -----------------
> Buses              9     Total Gen Capacity     820.0        -900.0 to
> 900.0
> Generators         3     On-line Capacity       820.0        -900.0 to
> 900.0
> Committed Gens     3     Generation (actual)    320.0              34.9
> Loads              3     Load                   315.0             115.0
>   Fixed            3       Fixed                315.0             115.0
>   Dispatchable     0       Dispatchable          -0.0 of -0.0      -0.0
> Shunts             0     Shunt (inj)             -0.0               0.0
> Branches           9     Losses (I^2 * Z)         4.95             51.31
> Transformers       0     Branch Charging (inj)     -              131.4
> Inter-ties         0     Total Inter-tie Flow     0.0               0.0
> Areas              1
>
>
> If so, please notice that series losses and the branch charging are listed
> separately. So the total reactive loss in the line is the series loss minus
> the branch charging injection.
>
>      Ray
>
>
> --
> Ray Zimmerman
> Senior Research Associate
> B30 Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
>
>
>
> On Apr 10, 2014, at 5:59 PM, Angie Joaqui Rendon <[email protected]>
> wrote:
>
> Regards
>
> I am working with the module of power flow, and i want  know if the
> reactive losses that shows me the program considers the capacitive effects
> of the lines?.
>
> I am comparing results with other malingerers and these do not coincide
> with some results that gives me MATPOWER, and differ for the lines that
> possess a high capacitive value.
>
> I appreciate the information that you can give me.
>
>
>
>
>