OPF result for the system of nine nodes ($ 5,296.69 / h), it considers only the 
missing I^2*Z?
Thanks

Date: Mon, 28 Apr 2014 09:32:01 -0500
Subject: Re: Reactive Losses Power Flow
From: [email protected]
To: [email protected]

If your are running ACPF simply change that value and the limits:

from:
39      1000    78.4674 300     -100    1.03    100     1       1100    0       
0       0       0       0       0       0       0       0       0       0       
0;
to:
39      500     78.4674 300     -100    1.03    100     1       500     0       
0       0       0       0       0       0       0       0       0       0       
0;

Those 500MW will be generated by the slack bus.



2014-04-12 12:53 GMT-05:00 Mahmoud Abdallah <[email protected]>:


  dear sir I use matpower 3.2 
I use runpf on case 39 and I wish to limit power generated at bus 39 to certain 
value how can I do that ?

first guess for power generated from generator at bus 39 = 1000 MWI wish to 
make it generate only 500 MW 
thank you in advance Eng. Mahmoud abdallah

Teaching Assistant
Ain Shams University
Faculty of Engineering
 
    On Friday, April 11, 2014 6:19 AM, Ray Zimmerman <[email protected]> wrote:

    I assume you are referring to the “System Summary” part of the MATPOWER 
output?================================================================================
|     System Summary                                                           
|================================================================================
How many?                How much?              P (MW)            Q (MVAr)
---------------------    -------------------  -------------  
-----------------Buses              9     Total Gen Capacity     820.0        
-900.0 to 900.0
Generators         3     On-line Capacity       820.0 
       -900.0 to 900.0Committed Gens     3     Generation (actual)    320.0     
         34.9Loads              3     Load                   315.0             
115.0
  Fixed            3       Fixed                315.0             115.0  
Dispatchable     0       Dispatchable          -0.0 of -0.0      -0.0
Shunts             0     Shunt (inj)             -0.0               0.0Branches 
          9     Losses (I^2 * Z)         4.95             51.31
Transformers       0     Branch Charging (inj)     -              
131.4Inter-ties         0     Total Inter-tie Flow     0.0               0.0
Areas   
           1If so, please notice that series losses and the branch charging are 
listed separately. So the total reactive loss in the line is the series loss 
minus the branch charging injection.
     Ray




-- Ray ZimmermanSenior Research AssociateB30 Warren Hall, Cornell University,
 Ithaca, NY 14853phone: (607) 255-9645

On Apr 10, 2014, at 5:59 PM, Angie Joaqui Rendon <[email protected]> wrote:



RegardsI am working with the module of power flow, and i want  know if the 
reactive losses that shows me the program considers the capacitive effects of 
the lines?.
I am comparing results with other malingerers and these do not coincide with 
some results that gives me MATPOWER, and differ for the lines that possess a 
high capacitive value. 
I appreciate the information that you can give me.                              
          


      
                                          