Could you clarify the question?

    Ray

On May 2, 2014, at 1:12 PM, Angie Joaqui Rendon <[email protected]> wrote:

> Regards
> 
> OPF result for the system of nine nodes ($ 5,296.69 / h), it considers only 
> the missing I^2*Z?
> 
> Thanks
> 
> Date: Mon, 28 Apr 2014 09:32:01 -0500
> Subject: Re: Reactive Losses Power Flow
> From: [email protected]
> To: [email protected]
> 
> If your are running ACPF simply change that value and the limits:
> 
> 
> from:
> 
> 39    1000    78.4674 300     -100    1.03    100     1       1100    0       
> 0       0       0       0       0       0       0       0       0       0     
>   0;
> to:
> 
> 39    500     78.4674 300     -100    1.03    100     1       500     0       
> 0       0       0       0       0       0       0       0       0       0     
>   0;
> 
> Those 500MW will be generated by the slack bus.
> 
> 
> 
> 
> 2014-04-12 12:53 GMT-05:00 Mahmoud Abdallah <[email protected]>:
>  
>  dear sir
> I use matpower 3.2
> 
> I use runpf on case 39 and I wish to limit power generated at bus 39 to 
> certain value how can I do that ?
> 
> first guess for power generated from generator at bus 39 = 1000 MW
> I wish to make it generate only 500 MW 
> 
> thank you in advance
> Eng. Mahmoud abdallah
> Teaching Assistant
> Ain Shams University
> Faculty of Engineering
> On Friday, April 11, 2014 6:19 AM, Ray Zimmerman <[email protected]> wrote:
> I assume you are referring to the “System Summary” part of the MATPOWER 
> output?
> 
> ================================================================================
> |     System Summary                                                          
>  |
> ================================================================================
> 
> How many?                How much?              P (MW)            Q (MVAr)
> ---------------------    -------------------  -------------  -----------------
> Buses              9     Total Gen Capacity     820.0        -900.0 to 900.0
> Generators         3     On-line Capacity       820.0        -900.0 to 900.0
> Committed Gens     3     Generation (actual)    320.0              34.9
> Loads              3     Load                   315.0             115.0
>   Fixed            3       Fixed                315.0             115.0
>   Dispatchable     0       Dispatchable          -0.0 of -0.0      -0.0
> Shunts             0     Shunt (inj)             -0.0               0.0
> Branches           9     Losses (I^2 * Z)         4.95             51.31
> Transformers       0     Branch Charging (inj)     -              131.4
> Inter-ties         0     Total Inter-tie Flow     0.0               0.0
> Areas              1
> 
> 
> If so, please notice that series losses and the branch charging are listed 
> separately. So the total reactive loss in the line is the series loss minus 
> the branch charging injection.
> 
>      Ray
> 
> 
> -- 
> Ray Zimmerman
> Senior Research Associate
> B30 Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> 
> On Apr 10, 2014, at 5:59 PM, Angie Joaqui Rendon <[email protected]> wrote:
> 
> Regards
> 
> I am working with the module of power flow, and i want  know if the reactive 
> losses that shows me the program considers the capacitive effects of the 
> lines?.
> 
> I am comparing results with other malingerers and these do not coincide with 
> some results that gives me MATPOWER, and differ for the lines that possess a 
> high capacitive value. 
> 
> I appreciate the information that you can give me.