Jon:


In the deep recess of my memory I recall this error code with FX
inverters.  It was caused by a stuck transfer relay.  You might open the
inverter cover and look for signs of smoke or arcing in the relay.



Good luck!



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:[email protected]] *On
Behalf Of *Jon Siegenthaler
*Sent:* Friday, December 11, 2020 6:01 PM
*To:* [email protected]
*Subject:* [RE-wrenches] Outback AC Backfeed Error



Hey wrenches,



I have a client who has a couple of the Radian 8048's and has an error code
of "AC Backfeed Error GS-1". Looking at the manual it states that "Usually
indicates another AC power source (out of phase with the inverter) was
connected to the unit’s AC output. Can also occur if an out-of-phase AC
source is connected to the inverter’s AC input."



However when this happened the generator wasn't running and it's an off
grid system. Is there a way that the master is looking to the slave as
another power source? The system had been running fine this week, auto
running the generator early morning and shutting down on its own.



Anyone seen something like this before? Thanks,



Jon Siegenthaler
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to