Recently had this on a project. Turns out it was two things, the cat 5 cables 
needed to be shielded so I went to Cat7 and the firmware upgrades did not take 
on one of the radians. Had to do it 3 times. System works fine now.



Peter Giroux

American Solar



From: RE-wrenches <[email protected]> On Behalf Of Jon 
Siegenthaler
Sent: Friday, December 11, 2020 9:01 PM
To: [email protected]
Subject: [RE-wrenches] Outback AC Backfeed Error



Hey wrenches,



I have a client who has a couple of the Radian 8048's and has an error code of 
"AC Backfeed Error GS-1". Looking at the manual it states that "Usually 
indicates another AC power source (out of phase with the inverter) was 
connected to the unit’s AC output. Can also occur if an out-of-phase AC source 
is connected to the inverter’s AC input."



However when this happened the generator wasn't running and it's an off grid 
system. Is there a way that the master is looking to the slave as another power 
source? The system had been running fine this week, auto running the generator 
early morning and shutting down on its own.



Anyone seen something like this before? Thanks,



Jon Siegenthaler



--
This email has been checked for viruses by AVG.
https://www.avg.com
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to