As William said... That is usually a relay issue.  In the older FX's, it
could also be a sticking issue like the hub or connections.

Steve Higgins.


On Fri, Dec 11, 2020 at 6:16 PM William Miller <[email protected]>
wrote:

> Jon:
>
>
>
> In the deep recess of my memory I recall this error code with FX
> inverters.  It was caused by a stuck transfer relay.  You might open the
> inverter cover and look for signs of smoke or arcing in the relay.
>
>
>
> Good luck!
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:[email protected]] *On
> Behalf Of *Jon Siegenthaler
> *Sent:* Friday, December 11, 2020 6:01 PM
> *To:* [email protected]
> *Subject:* [RE-wrenches] Outback AC Backfeed Error
>
>
>
> Hey wrenches,
>
>
>
> I have a client who has a couple of the Radian 8048's and has an error
> code of "AC Backfeed Error GS-1". Looking at the manual it states that
> "Usually indicates another AC power source (out of phase with the inverter)
> was connected to the unit’s AC output. Can also occur if an out-of-phase AC
> source is connected to the inverter’s AC input."
>
>
>
> However when this happened the generator wasn't running and it's an off
> grid system. Is there a way that the master is looking to the slave as
> another power source? The system had been running fine this week, auto
> running the generator early morning and shutting down on its own.
>
>
>
> Anyone seen something like this before? Thanks,
>
>
>
> Jon Siegenthaler
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to