Hi Jon,I have seen this early on, when the Mate3 first came out. The slave back 
fed the master. The Mate3 didn't accept our programming, a firmware update 
corrected this glitch. Chris Worcester [email protected] 
from my Samsung Galaxy s9.
-------- Original message --------From: Jon Siegenthaler 
<[email protected]> Date: 12/11/20  6:01 PM  (GMT-08:00) To: 
[email protected] Subject: [RE-wrenches] Outback AC Backfeed 
Error Hey wrenches,I have a client who has a couple of the Radian 8048's and 
has an error code of "AC Backfeed Error GS-1". Looking at the manual it states 
that "Usually indicates another AC power source (out of phase with the 
inverter) was connected to the unit’s AC output. Can also occur if an 
out-of-phase AC source is connected to the inverter’s AC input."However when 
this happened the generator wasn't running and it's an off grid system. Is 
there a way that the master is looking to the slave as another power source? 
The system had been running fine this week, auto running the generator early 
morning and shutting down on its own. Anyone seen something like this before? 
Thanks,Jon Siegenthaler
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to