Lones is correct as usual

The newer Mate3 when battery charging with the generator has to have time below 
rebuik or it won’t work.

So your options are to raise the rebulk voltage, this allows more time below 
the rebulk, which allows for a complete charge.  
This situation is especially often when someone is trying to keep their 
batteries at a higher SOC.  

So again, raise the rebulk voltage, it doesn’t have any impact on offgrid 
systems.  

It will fix the problem.

jay

> On Jan 8, 2021, at 12:54 PM, William Miller <[email protected]> wrote:
> 
> Drake:
>  
> I would suggest the following course of action:
>  
> 1.      Reboot Mate
> 2.      Reboot inverter 
> 3.      Reset all equipment to factory defaults and manually reprogram each 
> item
> 4.      Update Mate Firmware
> 5.      Update Inverter Firmware.
>  
> We have solved mystery Radian problems with a firmware update.
>  
> Good luck!
>  
> William Miller
> Miller Solar
> 17395 Oak Road, Atascadero, CA 93422
> 805-438-5600
> www.millersolar.com <http://www.millersolar.com/>
> CA Lic. 773985
>  
>  
>  
> -----Original Message-----
> From: RE-wrenches [mailto:[email protected] 
> <mailto:[email protected]>] On Behalf Of 
> [email protected] 
> <mailto:[email protected]>
> Sent: Friday, January 8, 2021 10:34 AM
> To: [email protected] 
> <mailto:[email protected]>
> Subject: [RE-wrenches] Radian Charges 1 hour per calendar day
>  
> Hello Wrenches,
>  
> An off grid, Radian / Mate 3 system we set up some years back has worked
> flawlessly. The client is now reporting that his system will only go
> into absorption charge for 1 hour per calendar day. The setting was
> previously to absorb for 2 hours.
>  
> He has tried shutting off the generator and then restarting. The
> inverter will connect, but not go into absorb.
>  
> During this cloudy period, he is only able to get the batteries to about
> 80 percent before he needs to leave the site for a week or so.
>  
> I finally go through to Outback, and they think it is a Firmware
> problem. As it is a long drive out, it seems worth while to run it by
> the list. Does FW this seem like the issue?
>  
> Thank you,
>  
> Drake
>  
> --
> _______________________________________________
> List sponsored by Redwood Alliance
>  
> List Address: [email protected] 
> <mailto:[email protected]>
>  
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>  
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/ 
> <https://www.mail-archive.com/[email protected]/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>  
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
>  
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/ 
> <https://www.mail-archive.com/[email protected]/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to