Yes and no, I think this is a tap, "a tap shall be permitted anywhere along
a feeder"  ' as long as it is less than a 10-foot rule or 25-foot rule
ending in a listed OCPD with a rating sufficient to handle the maximum
overcurrent'.  Service equipment residential is rated for fault currents of
up to 10,000 amps withstand.    Refer to 240.4.B and 240.21 (B) (1 & 2)

On Sun, Apr 17, 2022 at 10:39 AM Jason Szumlanski via RE-wrenches <
[email protected]> wrote:

> But this isn't a tap. It's a feeder conductor connected to an OCPD.
>
> I guess if you don't have a grid in or generator in or AC Coupled PV, you
> could just call it an inverter output circuit and it could be sized
> accordingly. But it would still need to be protected at it's source by an
> appropriately rated OCPD. Don't get me wrong... I don't think there is a
> real safety issue here, but I also don't see how the NEC allows the
> conductor to be sized for anything less than 200A.
>
> Jason
>
>
> On Sun, Apr 17, 2022, 11:29 AM Darryl Thayer via RE-wrenches <
> [email protected]> wrote:
>
>> The tap rule says you can reduce to 10% of the nominal size for 10 feet
>> and protect at the downstream OCPD or 25% for 25 feet for solar with
>> multiple sources see 705
>>
>> On Sat, Apr 16, 2022 at 9:16 PM Jason Szumlanski via RE-wrenches <
>> [email protected]> wrote:
>>
>>> That's what I'm thinking. You would need to use a 200A conductor to a
>>> separate load out OCPD before downsizing the wire. I guess there are pros
>>> and cons, but it seems this is geared toward whole house backup for 200A
>>> services. I'm eager to get an opportunity to use it in that scenario.
>>>
>>> Jason
>>>
>>>
>>>
>>>
>>> On Sat, Apr 16, 2022, 10:06 PM Chris Sparadeo via RE-wrenches <
>>> [email protected]> wrote:
>>>
>>>> Jason,
>>>>
>>>> Any additional OCPD downstream of the 200A load output breaker could
>>>> allow for a smaller wire size to be used at these terminals. For example,
>>>> load output conductors run to a 100A main breaker panel board.  Obviously
>>>> depending on circumstances, a #4 copper could fit the bill.
>>>>
>>>> What I’m not extremely  excited about with the new design is that in an
>>>> off-grid scenario with a generator and smart load, we would now need to
>>>> integrate an AC disconnect for generator input (grid)  and either a fused
>>>> disconnect or loads panel for any smart load output. With the 12K unit, the
>>>> integrated breakers help cut down on BOS and install time.
>>>>
>>>> -Chris
>>>>
>>>> On Sat, Apr 16, 2022 at 5:35 PM Darryl Thayer via RE-wrenches <
>>>> [email protected]> wrote:
>>>>
>>>>> Hello, The overcurrent device is to protect the conductors.  you can
>>>>> put any size wire, but you must protect with the overcurrent device.
>>>>> REmember in solar equipment; you may have more than one supply source.  
>>>>> The
>>>>> DC best example is solar modules connected in parallel,      on
>>>>>
>>>>> On Fri, Apr 15, 2022 at 8:26 PM Jerry Shafer via RE-wrenches <
>>>>> [email protected]> wrote:
>>>>>
>>>>>> You must meet all expected source output potentials within the design
>>>>>> and operating limits, as long as the distribution panel and connected
>>>>>> wiring is rated for the max output of the protected source then you are
>>>>>> good. A 200 ATS connected to a 10 kW genny does not require 2/0 as it 
>>>>>> will
>>>>>> never meet that rating. Just remember its whatever the max output can be
>>>>>> plus your margin.
>>>>>>
>>>>>> On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches <
>>>>>> [email protected]> wrote:
>>>>>>
>>>>>>> Hi Jason,
>>>>>>>
>>>>>>> You bring up a valid point….in an off-grid scenario with the 15k do
>>>>>>> you size the conductors to the continuous capacity, surge capacity or 
>>>>>>> the
>>>>>>> OCPD of the unit?
>>>>>>>
>>>>>>> -Chris
>>>>>>>
>>>>>>> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches <
>>>>>>> [email protected]> wrote:
>>>>>>>
>>>>>>>> P.S. ICYMI, this inverter has a massive combined AC coupled and DC
>>>>>>>> coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
>>>>>>>> [email protected]> wrote:
>>>>>>>>
>>>>>>>>> I'm not following the wiring diagrams for this new inverter. It
>>>>>>>>> has 200A pass-through capability with an integrated 200A load 
>>>>>>>>> disconnect.
>>>>>>>>> But then it says the wire gauge for the load out wiring can be #4 to 
>>>>>>>>> 2/0.
>>>>>>>>>
>>>>>>>>> In an off-grid scenario where there is no generator, the max
>>>>>>>>> continuous output is 62.5A, so I assume 80A circuit protection could 
>>>>>>>>> be
>>>>>>>>> used with 80A rated wire (#4), but how is that circuit protection
>>>>>>>>> implemented if the 200A breaker is integrated? Do you have to run a 
>>>>>>>>> short
>>>>>>>>> piece of 2/0 to an external 80A rated OCPD and then step down to #4?
>>>>>>>>>
>>>>>>>>> Jason Szumlanski
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>> _______________________________________________
>>>>>>>>
>>>>>>>
>>>> _______________________________________________
>>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to