Jason, Any additional OCPD downstream of the 200A load output breaker could allow for a smaller wire size to be used at these terminals. For example, load output conductors run to a 100A main breaker panel board. Obviously depending on circumstances, a #4 copper could fit the bill.
What I’m not extremely excited about with the new design is that in an off-grid scenario with a generator and smart load, we would now need to integrate an AC disconnect for generator input (grid) and either a fused disconnect or loads panel for any smart load output. With the 12K unit, the integrated breakers help cut down on BOS and install time. -Chris On Sat, Apr 16, 2022 at 5:35 PM Darryl Thayer via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hello, The overcurrent device is to protect the conductors. you can put > any size wire, but you must protect with the overcurrent device. REmember > in solar equipment; you may have more than one supply source. The DC best > example is solar modules connected in parallel, on > > On Fri, Apr 15, 2022 at 8:26 PM Jerry Shafer via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> You must meet all expected source output potentials within the design and >> operating limits, as long as the distribution panel and connected wiring is >> rated for the max output of the protected source then you are good. A 200 >> ATS connected to a 10 kW genny does not require 2/0 as it will never meet >> that rating. Just remember its whatever the max output can be plus your >> margin. >> >> On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches < >> re-wrenches@lists.re-wrenches.org> wrote: >> >>> Hi Jason, >>> >>> You bring up a valid point….in an off-grid scenario with the 15k do you >>> size the conductors to the continuous capacity, surge capacity or the OCPD >>> of the unit? >>> >>> -Chris >>> >>> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches < >>> re-wrenches@lists.re-wrenches.org> wrote: >>> >>>> P.S. ICYMI, this inverter has a massive combined AC coupled and DC >>>> coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive. >>>> >>>> >>>> >>>> >>>> >>>> >>>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski < >>>> ja...@floridasolardesigngroup.com> wrote: >>>> >>>>> I'm not following the wiring diagrams for this new inverter. It has >>>>> 200A pass-through capability with an integrated 200A load disconnect. But >>>>> then it says the wire gauge for the load out wiring can be #4 to 2/0. >>>>> >>>>> In an off-grid scenario where there is no generator, the max >>>>> continuous output is 62.5A, so I assume 80A circuit protection could be >>>>> used with 80A rated wire (#4), but how is that circuit protection >>>>> implemented if the 200A breaker is integrated? Do you have to run a short >>>>> piece of 2/0 to an external 80A rated OCPD and then step down to #4? >>>>> >>>>> Jason Szumlanski >>>>> >>>>> >>>>> >>>>> >>>>> >>>>> _______________________________________________ >>>> List sponsored by Redwood Alliance >>>> >>>> Pay optional member dues here: http://re-wrenches.org >>>> >>>> List Address: RE-wrenches@lists.re-wrenches.org >>>> >>>> Change listserver email address & settings: >>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>>> >>>> There are two list archives for searching. When one doesn't work, try >>>> the other: >>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >>>> >>>> List rules & etiquette: >>>> http://www.re-wrenches.org/etiquette.htm >>>> >>>> Check out or update participant bios: >>>> http://www.members.re-wrenches.org >>>> >>>> -- >>> Chris Sparadeo >>> >>> >>> C_802-369-4458 >>> H_802-728-3059 >>> _______________________________________________ >>> List sponsored by Redwood Alliance >>> >>> Pay optional member dues here: http://re-wrenches.org >>> >>> List Address: RE-wrenches@lists.re-wrenches.org >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> >>> There are two list archives for searching. When one doesn't work, try >>> the other: >>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >>> >>> List rules & etiquette: >>> http://www.re-wrenches.org/etiquette.htm >>> >>> Check out or update participant bios: >>> http://www.members.re-wrenches.org >>> >>> _______________________________________________ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> >> _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > -- Chris Sparadeo C_802-369-4458 H_802-728-3059
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org