Re: [Emc-users] Acceleration Settings?

2024-05-15 Thread Peter Wallace

On Wed, 15 May 2024, John Dammeyer wrote:


Date: Wed, 15 May 2024 16:57:44 -0700
From: John Dammeyer 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "'Enhanced Machine Controller (EMC)'" 
Subject: Re: [Emc-users] Acceleration Settings?





-Original Message-
From: Jon Elson [mailto:el...@pico-systems.com]
Sent: May 15, 2024 4:20 PM
To: emc-users@lists.sourceforge.net
Subject: Re: [Emc-users] Acceleration Settings?

On 5/15/24 12:23, Todd Zuercher via Emc-users wrote:
> I'm trying to figure out something goofy that seems to be going on with my
acceleration settings.
> I'm running Linuxcnc 2.9.0 and Axis ui.
> I have all of the max_acceleration settings set for 20.0 (and
stepgen_maxaccel = 25), and for some reason everything only  moves with
an acceleration of 10 ipsps for G0 and G1 moves (confirmed with Halscope),
but jogging does go at 20.  Is there normal behavior or am I missing some
setting somewhere that is limiting the acceleration?
>
In the latest LinuxCNC there are TWO places that have accel
and max velocity settings.?? Jogging is in the JOINT_x part,
and CNC moves are in the AXIS_x section.?? In general, you
want the same settings in both JOINT and AXIS sections.

Jon



That's interesting.  What is then the major difference between Joint and 
Axis?  Just jogging parameters?

John


LinuxCNC versions 2.8 and > separate joints (think of these as actuators or 
motors) and Axis. Axis are normally cartesian or rotary axis. This makes sense
for machines where joint and axis do not map exactly, such as gantry devices 
that may have duplicated X,Y,Z joints (so up to 6) but only 3 axis or say a 
CoreXY laser cutter where the joints and cartesian axis are related by a 
kinematics equation.


Peter Wallace
Mesa Electronics___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Mesa Card Stepgens?

2024-05-10 Thread Peter Wallace

On Fri, 10 May 2024, John Dammeyer wrote:


Date: Fri, 10 May 2024 18:26:21 -0700
From: John Dammeyer 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "'Enhanced Machine Controller (EMC)'" 
Subject: Re: [Emc-users] Mesa Card Stepgens?

What type of output driver is used on the 7i84?
John


The 7I84/7I84D use the  (now obsolete) NCV7608
It has flyback protection (turnoff speed modulation)
but that's only good to ~60 mA so for more you need
flyback diodes

It, replacement (7I84U) uses the NCV7224

The 7724 is a bit nicer as it can do sink,source,
or push-pull under software control
(and 350 mA on inductive or non-inductive loads with no flyback diodes)




-Original Message-
From: Peter Wallace [mailto:p...@mesanet.com]
Sent: May 10, 2024 1:54 PM
To: Todd Zuercher
Cc: Todd Zuercher via Emc-users
Subject: Re: [Emc-users] Mesa Card Stepgens?

On Fri, 10 May 2024, Todd Zuercher wrote:


Date: Fri, 10 May 2024 20:40:53 +
From: Todd Zuercher 
To: Peter Wallace 
Cc: Todd Zuercher via Emc-users 
Subject: RE: [Emc-users] Mesa Card Stepgens?

Peter,

I've ran into another bit of a snag.  I have a couple of 24v relays from
Automationdirect.  The resistance on the coils is about 635ohms.  I

thought

that the outputs on the 7i84 were supposed to be ok with running a small
relay with up to about 40mA without needing a flyback diode.  It's close

but

just under that.  Well, I've managed to kill 3 of the outputs with those
relays (the outputs are stuck always on).  I've put a couple of diodes

on

the relay coils, I hope that works and I don't ruin any more.  What does

it

take to replace the chip or chips that would be damaged by this?


40 mA should be fine, it is possible this is the card that had power

applied

backwards?

We can replace the chips



Todd Zuercher
P. Graham Dunn Inc.
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031

-Original Message-
From: Peter Wallace 
Sent: Monday, April 15, 2024 5:09 PM
To: Todd Zuercher 
Cc: Todd Zuercher via Emc-users 
Subject: RE: [Emc-users] Mesa Card Stepgens?

[EXTERNAL EMAIL] Be sure links are safe.

On Mon, 15 Apr 2024, Todd Zuercher wrote:


Date: Mon, 15 Apr 2024 20:22:03 +
From: Todd Zuercher 
To: Peter Wallace ,
Todd Zuercher via Emc-users 
Subject: RE: [Emc-users] Mesa Card Stepgens?

Thanks Peter,

We've had this 7i85s for quite a while, and it must be one of the
early ones because I see DS34C87TM chips on it.

I'm not sure I like the idea of using them single ended.  But is a
+5v-0v single ended signal actually any better or even much different
than a +/-3v differential signal?  How hard would it be to move the
last steepen over to the 7i88 and have all 8 of these stepgens on one
card?  I am not planning on using the Smart Serial output on the 7i88.
The 3 servos have been working on the 7i85S for years and can stay

there.


Differential is needed and advised for servo drives with line receiver

inputs,

however, with optocoupled input step/dir drives, there is little advantage

to

differential mode. With optocoupled input step/dir drives the input will

only

see ~3V drive in differential mode with the DS34C87 driver, so its better

to

run in single ended mode with the 7I85S sinking so you get full 5V drive.




I am using the Smart Serial connection on the 7i85s to connect a 7i84.

If all else fails I can simply set all of the other steppers the same
as the slow one and leave it be.  Even the slow one is working as fast
or faster than I was hoping it would, but a little more safety margin

would

be nice.


The drives are likely not rated for 3V input so you would probably be

better

off if you ran single ended.





Todd Zuercher
P. Graham Dunn Inc.
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031

-Original Message-
From: Peter Wallace 
Sent: Monday, April 15, 2024 3:41 PM
To: Todd Zuercher via Emc-users 
Cc: Todd Zuercher 
Subject: Re: [Emc-users] Mesa Card Stepgens?

[EXTERNAL EMAIL] Be sure links are safe.

On Mon, 15 Apr 2024, Todd Zuercher via Emc-users wrote:


Date: Mon, 15 Apr 2024 19:27:19 +
From: Todd Zuercher via Emc-users 
To: "Enhanced Machine Controller (EMC)"

Cc: Todd Zuercher 
Subject: [Emc-users] Mesa Card Stepgens?

I was working on this machine where I need a whole bunch of extra

stepgens.  I am using a Mesa 7i85S and a 7i88 connected to a 5i25 card.  I

was

testing some of the stepper drives and I noticed that with one of the
drive/motor combinations I am needing to use slightly longer step timing

and

lower max velocity.  I thought that this was odd, because all of the

drives,

motors, and mechanicals are the same for all of the ones I was testing.

The

only difference is that the slower one was connected to a stepgen on the
7i85S and all of the others are on the 7i88.  So just for curiosity sake I

checked

the voltage at the input terminals of step/dir signals of the drive.  On

the

terminals conne

Re: [Emc-users] Mesa Card Stepgens?

2024-05-10 Thread Peter Wallace

On Fri, 10 May 2024, Todd Zuercher wrote:


Date: Fri, 10 May 2024 20:40:53 +
From: Todd Zuercher 
To: Peter Wallace 
Cc: Todd Zuercher via Emc-users 
Subject: RE: [Emc-users] Mesa Card Stepgens?

Peter,

I've ran into another bit of a snag.  I have a couple of 24v relays from 
Automationdirect.  The resistance on the coils is about 635ohms.  I thought 
that the outputs on the 7i84 were supposed to be ok with running a small 
relay with up to about 40mA without needing a flyback diode.  It's close but 
just under that.  Well, I've managed to kill 3 of the outputs with those 
relays (the outputs are stuck always on).  I've put a couple of diodes on 
the relay coils, I hope that works and I don't ruin any more.  What does it 
take to replace the chip or chips that would be damaged by this?


40 mA should be fine, it is possible this is the card that had power applied 
backwards?


We can replace the chips



Todd Zuercher
P. Graham Dunn Inc.
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031

-Original Message-
From: Peter Wallace 
Sent: Monday, April 15, 2024 5:09 PM
To: Todd Zuercher 
Cc: Todd Zuercher via Emc-users 
Subject: RE: [Emc-users] Mesa Card Stepgens?

[EXTERNAL EMAIL] Be sure links are safe.

On Mon, 15 Apr 2024, Todd Zuercher wrote:


Date: Mon, 15 Apr 2024 20:22:03 +
From: Todd Zuercher 
To: Peter Wallace ,
Todd Zuercher via Emc-users 
Subject: RE: [Emc-users] Mesa Card Stepgens?

Thanks Peter,

We've had this 7i85s for quite a while, and it must be one of the
early ones because I see DS34C87TM chips on it.

I'm not sure I like the idea of using them single ended.  But is a
+5v-0v single ended signal actually any better or even much different
than a +/-3v differential signal?  How hard would it be to move the
last steepen over to the 7i88 and have all 8 of these stepgens on one
card?  I am not planning on using the Smart Serial output on the 7i88.
The 3 servos have been working on the 7i85S for years and can stay there.


Differential is needed and advised for servo drives with line receiver inputs, 
however, with optocoupled input step/dir drives, there is little advantage to 
differential mode. With optocoupled input step/dir drives the input will only 
see ~3V drive in differential mode with the DS34C87 driver, so its better to 
run in single ended mode with the 7I85S sinking so you get full 5V drive.



I am using the Smart Serial connection on the 7i85s to connect a 7i84.

If all else fails I can simply set all of the other steppers the same
as the slow one and leave it be.  Even the slow one is working as fast
or faster than I was hoping it would, but a little more safety margin would be 
nice.


The drives are likely not rated for 3V input so you would probably be better 
off if you ran single ended.




Todd Zuercher
P. Graham Dunn Inc.
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031

-Original Message-
From: Peter Wallace 
Sent: Monday, April 15, 2024 3:41 PM
To: Todd Zuercher via Emc-users 
Cc: Todd Zuercher 
Subject: Re: [Emc-users] Mesa Card Stepgens?

[EXTERNAL EMAIL] Be sure links are safe.

On Mon, 15 Apr 2024, Todd Zuercher via Emc-users wrote:


Date: Mon, 15 Apr 2024 19:27:19 +
From: Todd Zuercher via Emc-users 
To: "Enhanced Machine Controller (EMC)"

Cc: Todd Zuercher 
Subject: [Emc-users] Mesa Card Stepgens?

I was working on this machine where I need a whole bunch of extra stepgens.  I 
am using a Mesa 7i85S and a 7i88 connected to a 5i25 card.  I was testing some 
of the stepper drives and I noticed that with one of the drive/motor 
combinations I am needing to use slightly longer step timing and lower max 
velocity.  I thought that this was odd, because all of the drives, motors, and 
mechanicals are the same for all of the ones I was testing.  The only 
difference is that the slower one was connected to a stepgen on the 7i85S and 
all of the others are on the 7i88.  So just for curiosity sake I checked the 
voltage at the input terminals of step/dir signals of the drive.  On the 
terminals connected to the 7i88 I found +/-5v, and on the one connected to the 
7i85S there is only +/-3v.  This is the only difference I've been able to find 
between the different joints in question.

Does it make sense that the voltages would be different on the step/dir outputs 
between the 7i85s and the 7i88?  Does it make sense that the difference would 
cause a difference in the required step timing?  Why might there be a 
difference between the output voltage on the two cards?

Both cards are getting their 5v from the 5i25.  The 7i85S is also connected to 
3 step/gen servo drives and their encoder's feedbacks.  Is it possible that the 
5v drain from the encoders might be causing the lower voltage on the 7i85S's 
outputs?



I would check the 5V rail at the 7I85S card, and if its low, power the
7I85S directly from 5V rather the through the parallel cable. ALso the
very first lot (many years ago) of 7I85S 

Re: [Emc-users] Mb2hal 2.9?

2024-05-07 Thread Peter Wallace

On Tue, 7 May 2024, Todd Zuercher via Emc-users wrote:


Date: Tue, 7 May 2024 19:59:55 +
From: Todd Zuercher via Emc-users 
To: "Enhanced Machine Controller (EMC)" 
Cc: Todd Zuercher 
Subject: [Emc-users] Mb2hal 2.9?

The machine that I've been working on updating from 2.7 to 2.9 has hit a snag.  
The one thing I didn't change now seems to be giving me the most trouble.

The machine has 8 vfds for running 8 router spindles, they are/were connected 
to Linuxcnc using Mb2hal and a usb RS485 dongle.  It was working find on the 
old pc running Ubuntu, RTAi, and Linuxcnc 2.7.  I copied the old mb2hal.ini and 
it's associated hal file over to the new machine and added them to the config, 
but I can not seem to establish communication between Linuxcnc and the drives.  
Starting Linuxcnc from the terminal, and it pukes out this string of error 
messages, so fast that I can't find any other possibly more informative error 
messages further up the log, (beacaue I can't scroll past all this other junk.) 
 My mb2hal config has 32 transactions, and there is an error msg like below for 
each of the 32, then the list repeats ad nauseum.   Any one have any ideas 
what's going on?  The PC is running Debian 12, with Linuxcnc installed from the 
Debian repos.

mb2hal get_tx_connection ERR: mb_tx_num[0] mb_links[0] cannot connect to link, 
ret[-1] fd[-1]
mb2hal get_tx_connection ERR: mb_tx_num[1] mb_links[0] cannot connect to link, 
ret[-1] fd[-1]
mb2hal get_tx_connection ERR: mb_tx_num[2] mb_links[0] cannot connect to link, 
ret[-1] fd[-1]
mb2hal get_tx_connection ERR: mb_tx_num[3] mb_links[0] cannot connect to link, 
ret[-1] fd[-1]
mb2hal get_tx_connection ERR: mb_tx_num[4] mb_links[0] cannot connect to link, 
ret[-1] fd[-1]
mb2hal get_tx_connection ERR: mb_tx_num[5] mb_links[0] cannot connect to link, 
ret[-1] fd[-1]
mb2hal get_tx_connection ERR: mb_tx_num[6] mb_links[0] cannot connect to link, 
ret[-1] fd[-1]
mb2hal get_tx_connection ERR: mb_tx_num[7] mb_links[0] cannot connect to link, 
ret[-1] fd[-1]
mb2hal get_tx_connection ERR: mb_tx_num[8] mb_links[0] cannot connect to link, 
ret[-1] fd[-1]

Moving the RS485 dongle back to the old pc and loading the mb2hal config there 
gives no errors.  So it shouldn't be a hardware or config issue that I'm aware 
of.  Did something significant change in mb2hal between 2.7 and 2.9 that would 
require a change to the mb2hal configuration files?

Todd Zuercher
P. Graham Dunn Inc.<http://www.pgrahamdunn.com/index.php>
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031



Could this be some permissions or device name error with USB--> RS-485
device driver?


Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Big Tree Tech Re: Mesa Card Stepgens?

2024-04-18 Thread Peter Wallace

On Thu, 18 Apr 2024, Nicklas SB Karlsson wrote:


Date: Thu, 18 Apr 2024 13:33:20 +0200
From: Nicklas SB Karlsson 
Reply-To: "Enhanced Machine Controller (EMC)"

To: emc-users@lists.sourceforge.net
Subject: Re: [Emc-users] Big Tree Tech Re: Mesa Card Stepgens?


...


If it can revert back to the way LinuxCNC works ( which requires realtime),
there is no real advantage to queueing at all. Queueing is used to make
up for the lack of realtime. For example Mach3 can do decent spindle
synchronized motion, but only if this feature is implemented in the interface
hardware. This would be a big step backwards for LinuxCNC.


And then it will come back to the problem how to send enough queued data to 
actuators.

Queue may make sense if for example sending position commands to follow over an 
Ethernet network as position is small
compared to the header. In that case sending many positions in one message 
reduce overhead.


Nicklas Karlsson



The equivalent of sending many positions is already done to some extent with 
interfaces that interpolate (or are velocity or velocity+acceleration 
controlled) This includes most stepgens, Ethercat servo drives etc


Queueing does make sense for some higher data rate applications like 
motion synchronized video data for engraving.






___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Big Tree Tech Re: Mesa Card Stepgens?

2024-04-17 Thread Peter Wallace

On Wed, 17 Apr 2024, Chris Albertson wrote:


Date: Wed, 17 Apr 2024 17:50:46 -0700
From: Chris Albertson 
To: "Enhanced Machine Controller (EMC)" 
Cc: Peter Wallace 
Subject: Re: [Emc-users] Big Tree Tech Re: Mesa Card Stepgens?

No it does not fail, we can always send new commands in real time to be 
executed ??right away?? (at the current time) and make the queued execution 
system look and act as if there were no queue.  A command taged with the 
current time will jump to the front of the queue.


The system also allows for very delayed execution of commands, like ??in 
five minutes??.  This works well because you can queue a macro to do 
something like poll the voltage of a battery and then place itself back in 
the queue for five minutes later.  But as said with a current time or a 
special tag that says ??now?? it reverts back to the way LCNC works.


Remember that a time-tagged queue is not executed in order.  It is not FIFO, 
so a command that is placed in the queue, even with 100 commands waiting 
does not need to wait for the others.




If it can revert back to the way LinuxCNC works ( which requires realtime), 
there is no real advantage to queueing at all. Queueing is used to make 
up for the lack of realtime. For example Mach3 can do decent spindle 
synchronized motion, but only if this feature is implemented in the interface 
hardware. This would be a big step backwards for LinuxCNC.







On Apr 17, 2024, at 5:05??PM, Ray Henry  wrote:

On Wed, 2024-04-17 at 09:13 -0700, Peter Wallace wrote:



LCNC really should be doing this.  If the Measa cards would
maintain a queue
and a synchronized clock we would not care at all about latency.
Klipper
proves the idea works.


This is basically what Mach 3/4 do

This fails as soon as you need the control to repond to
feedback in real time (Spindle synchronized motion, plasma THC
etc etc) Its possible of course to build this feedback into the
interface hardware, but there is a big advantage to having
this feedback in LinuxCNC where is works with any interface
hardware, is extensible and open, and where the feedback
control math/logic has unlimited resources.



Peter Wallace



The message on my 25+ year old coffee cup from the NIST Intelligent
Systems Division reminds me at least three times a week to "SENSE ->
MODEL -> ACT." in that order.  Thanks.
Peter.

Ray




___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users




Peter Wallace
Mesa Electronics___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Home to index triggers following error

2024-04-17 Thread Peter Wallace

On Wed, 17 Apr 2024, Todd Zuercher wrote:


Date: Wed, 17 Apr 2024 18:14:10 +
From: Todd Zuercher 
To: Peter Wallace ,
Todd Zuercher via Emc-users 
Subject: RE: [Emc-users] Home to index triggers following error

The machine is currently running Linuxcnc 2.7, but the Mesa cards, are 
significantly older, dating back to the Linuxcnc 2.5 era.


I'm not sure how comfortable a feel about updating this machine to current 
at the moment.  It is running 32-bit RTAI, and I'm not confident I'll be 
able to achieve the necessary latencies with the currently available 
mainstream 64-bit real time kernels required for the current version of 
Linuxcnc on the machine's current computer.


All of my actively running Linuxcnc machines are still on 2.7.  I am in the 
midst of a major overhaul of one machine that will be current version of 
Linuxcnc.  But I'm very hesitant to pull the other running machines out of 
production to upgrade until after I have more experience working with the 
newer versions.  (JA and the move to requiring 64-bit kernels were very big 
changes.)


Todd Zuercher
P. Graham Dunn Inc.
630 Henry Street 
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031



Yeah, its not a firmware issue so the old cards should be fine,
but the driver fix is only in 2.9. Theres no specific reason the
(one line) fix could not be applied to 2.7/RTAI except I dont
have a build environment for that anymore.


Peter Wallace
Mesa Electronics
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Home to index triggers following error

2024-04-17 Thread Peter Wallace

On Wed, 17 Apr 2024, Todd Zuercher via Emc-users wrote:


Date: Wed, 17 Apr 2024 17:00:31 +
From: Todd Zuercher via Emc-users 
To: "Enhanced Machine Controller (EMC)" 
Cc: Todd Zuercher 
Subject: Re: [Emc-users] Home to index triggers following error

Sorry to hijack the thread, but I've had to live with this on a machine that 
I'm using cascaded double PID loops on.  I have the velocity loop PIDs running 
in a fast floating point base thread to help with the tuning of some 
cantankerous torque mode servos.  The position loops are still in the servo 
thread (because I can't run the whole servo thread as fast as I can the 
floating point base thread.)  Reading/writing to the Mesa hardware in a faster 
loop than the servo thread seems to break the f-error disable for the encoder 
reset.  I think because the encoder reset doesn't always occur when the it is 
expecting it or something to that effect.  I've tried just running a faster 
servo-thread, but I can run the lighter floating point base thread about 4x 
faster than I can the whole servo-thread.

Todd Zuercher
P. Graham Dunn Inc.
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031


What LinuxCNC version?


There was a bug in the hostmot driver index handling that was fixed fairly 
recently (a couple of years ago)




-Original Message-
From: andy pugh 
Sent: Wednesday, April 17, 2024 8:47 AM
To: Enhanced Machine Controller (EMC) 
Subject: Re: [Emc-users] Home to index triggers following error

[EXTERNAL EMAIL] Be sure links are safe.

On Wed, 17 Apr 2024 at 12:45, Tomaz T.  wrote:

now it doesn't trigger following error any more (homing completes

successfully), interesting thing is, that on first attempt of homing
after fresh starting LinuxCNC I see quite large spike on f-error when
hitting index pulse, this large spike doesn't accrue on any more on
second attempt of homing or later, only after fresh start and on first one.




It will only trigger the f-error  if the difference between the current encoder 
position and the zero position is larger than the f-error limit.
Once you have homed once jump will be at most a few encoder counts.

--
atp
"A motorcycle is a bicycle with a pandemonium attachment and is designed for the 
especial use of mechanical geniuses, daredevils and lunatics."
- George Fitch, Atlanta Constitution Newspaper, 1912

___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://nam04.safelinks.protection.outlook.com/?url=https%3A%2F%2Flists.sourceforge.net%2Flists%2Flistinfo%2Femc-users=05%7C02%7Ctoddz%40pgrahamdunn.com%7Cebfea5c501924f029c5308dc5edcaa7a%7C5758544c573f47cebee96c3e0806fb43%7C0%7C0%7C638489549065500531%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C0%7C%7C%7C=iNxGqNzkAKwXtD4PmQ2hHgkBuriUCq88Wl5WraibpAA%3D=0<https://lists.sourceforge.net/lists/listinfo/emc-users>

___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Big Tree Tech Re: Mesa Card Stepgens?

2024-04-17 Thread Peter Wallace



LCNC really should be doing this.  If the Measa cards would maintain a queue 
and a synchronized clock we would not care at all about latency.  Klipper 
proves the idea works.


This is basically what Mach 3/4 do

This fails as soon as you need the control to repond to
feedback in real time (Spindle synchronized motion, plasma THC
etc etc) Its possible of course to build this feedback into the
interface hardware, but there is a big advantage to having
this feedback in LinuxCNC where is works with any interface
hardware, is extensible and open, and where the feedback
control math/logic has unlimited resources.



Peter Wallace



___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Mesa Card Stepgens?

2024-04-15 Thread Peter Wallace

On Mon, 15 Apr 2024, Todd Zuercher wrote:


Date: Mon, 15 Apr 2024 20:22:03 +
From: Todd Zuercher 
To: Peter Wallace ,
Todd Zuercher via Emc-users 
Subject: RE: [Emc-users] Mesa Card Stepgens?

Thanks Peter,

We've had this 7i85s for quite a while, and it must be one of the early ones 
because I see DS34C87TM chips on it.


I'm not sure I like the idea of using them single ended.  But is a +5v-0v 
single ended signal actually any better or even much different than a +/-3v 
differential signal?  How hard would it be to move the last steepen over to 
the 7i88 and have all 8 of these stepgens on one card?  I am not planning on 
using the Smart Serial output on the 7i88.  The 3 servos have been working 
on the 7i85S for years and can stay there.


Differential is needed and advised for servo drives with line receiver inputs,
however, with optocoupled input step/dir drives, there is little advantage to 
differential mode. With optocoupled input step/dir drives the input will only 
see ~3V drive in differential mode with the DS34C87 driver, so its better to 
run in single ended mode with the 7I85S sinking so you get full 5V drive.




I am using the Smart Serial connection on the 7i85s to connect a 7i84.

If all else fails I can simply set all of the other steppers the same as the 
slow one and leave it be.  Even the slow one is working as fast or faster 
than I was hoping it would, but a little more safety margin would be nice.


The drives are likely not rated for 3V input so you would probably be better 
off if you ran single ended.





Todd Zuercher
P. Graham Dunn Inc.
630 Henry Street 
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031

-Original Message-
From: Peter Wallace 
Sent: Monday, April 15, 2024 3:41 PM
To: Todd Zuercher via Emc-users 
Cc: Todd Zuercher 
Subject: Re: [Emc-users] Mesa Card Stepgens?

[EXTERNAL EMAIL] Be sure links are safe.

On Mon, 15 Apr 2024, Todd Zuercher via Emc-users wrote:


Date: Mon, 15 Apr 2024 19:27:19 +
From: Todd Zuercher via Emc-users 
To: "Enhanced Machine Controller (EMC)"

Cc: Todd Zuercher 
Subject: [Emc-users] Mesa Card Stepgens?

I was working on this machine where I need a whole bunch of extra stepgens.  I 
am using a Mesa 7i85S and a 7i88 connected to a 5i25 card.  I was testing some 
of the stepper drives and I noticed that with one of the drive/motor 
combinations I am needing to use slightly longer step timing and lower max 
velocity.  I thought that this was odd, because all of the drives, motors, and 
mechanicals are the same for all of the ones I was testing.  The only 
difference is that the slower one was connected to a stepgen on the 7i85S and 
all of the others are on the 7i88.  So just for curiosity sake I checked the 
voltage at the input terminals of step/dir signals of the drive.  On the 
terminals connected to the 7i88 I found +/-5v, and on the one connected to the 
7i85S there is only +/-3v.  This is the only difference I've been able to find 
between the different joints in question.

Does it make sense that the voltages would be different on the step/dir outputs 
between the 7i85s and the 7i88?  Does it make sense that the difference would 
cause a difference in the required step timing?  Why might there be a 
difference between the output voltage on the two cards?

Both cards are getting their 5v from the 5i25.  The 7i85S is also connected to 
3 step/gen servo drives and their encoder's feedbacks.  Is it possible that the 
5v drain from the encoders might be causing the lower voltage on the 7i85S's 
outputs?



I would check the 5V rail at the 7I85S card, and if its low, power the 7I85S 
directly from 5V rather the through the parallel cable. ALso the very first lot 
(many years ago) of 7I85S cards were built with DS34C87 drivers which do not 
have full 5V drive. If you have this card, you can get 5V drive by using single 
ended sinking outputs and 5V+ to drive step+ and 7i85s step- to drive
step-



Todd Zuercher
P. Graham Dunn
Inc.<https://nam04.safelinks.protection.outlook.com/?url=http%3A%2F%2F
www.pgrahamdunn.com%2Findex.php=05%7C02%7Ctoddz%40pgrahamdunn.com
%7Cc87909c9a4b6452a9e7008dc5d83f6a5%7C5758544c573f47cebee96c3e0806fb43
%7C0%7C0%7C638488068569795566%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAw
MDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C0%7C%7C%7C=
%2BkgiY%2FC9l6%2BqT2O6bnpxqPKur7Myu6%2BaULa01B910Ck%3D=0>
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://nam04.safelinks.protection.outlook.com/?url=https%3A%2F%2Flist
s.sourceforge.net%2Flists%2Flistinfo%2Femc-users=05%7C02%7Ctoddz%
40pgrahamdunn.com%7Cc87909c9a4b6452a9e7008dc5d83f6a5%7C5758544c573f47c
ebee96c3e0806fb43%7C0%7C0%7C638488068569804807%7CUnknown%7CTWFpbGZsb3d
8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C
0%7C%7C%7C=sb3DbNBIrWxq9OqYRv32Q6KHka%2FvXqAzp1QV8vF5EeA%3D
rved=0

Re: [Emc-users] Mesa Card Stepgens?

2024-04-15 Thread Peter Wallace

On Mon, 15 Apr 2024, Todd Zuercher via Emc-users wrote:


Date: Mon, 15 Apr 2024 19:27:19 +
From: Todd Zuercher via Emc-users 
To: "Enhanced Machine Controller (EMC)" 
Cc: Todd Zuercher 
Subject: [Emc-users] Mesa Card Stepgens?

I was working on this machine where I need a whole bunch of extra stepgens.  I 
am using a Mesa 7i85S and a 7i88 connected to a 5i25 card.  I was testing some 
of the stepper drives and I noticed that with one of the drive/motor 
combinations I am needing to use slightly longer step timing and lower max 
velocity.  I thought that this was odd, because all of the drives, motors, and 
mechanicals are the same for all of the ones I was testing.  The only 
difference is that the slower one was connected to a stepgen on the 7i85S and 
all of the others are on the 7i88.  So just for curiosity sake I checked the 
voltage at the input terminals of step/dir signals of the drive.  On the 
terminals connected to the 7i88 I found +/-5v, and on the one connected to the 
7i85S there is only +/-3v.  This is the only difference I've been able to find 
between the different joints in question.

Does it make sense that the voltages would be different on the step/dir outputs 
between the 7i85s and the 7i88?  Does it make sense that the difference would 
cause a difference in the required step timing?  Why might there be a 
difference between the output voltage on the two cards?

Both cards are getting their 5v from the 5i25.  The 7i85S is also connected to 
3 step/gen servo drives and their encoder's feedbacks.  Is it possible that the 
5v drain from the encoders might be causing the lower voltage on the 7i85S's 
outputs?



I would check the 5V rail at the 7I85S card, and if its low, power the 7I85S 
directly from 5V rather the through the parallel cable. ALso the very first 
lot (many years ago) of 7I85S cards were built with DS34C87 drivers which do 
not have full 5V drive. If you have this card, you can get 5V drive by using 
single ended sinking outputs and 5V+ to drive step+ and 7i85s step- to drive 
step-




Todd Zuercher
P. Graham Dunn Inc.<http://www.pgrahamdunn.com/index.php>
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] 7i84 Trouble?

2024-04-02 Thread Peter Wallace

On Tue, 2 Apr 2024, Todd Zuercher wrote:


Date: Tue, 2 Apr 2024 15:01:10 +
From: Todd Zuercher 
To: "Enhanced Machine Controller (EMC)" ,
Peter Wallace 
Subject: RE: [Emc-users] 7i84 Trouble?

Went and powered up the machine again today to give it a another look, and now 
I only get the two yellow LEDs on the 7i84 card (no red or green) and Linuxcnc 
isn't seeing the 7i84.

Yesterday it was at least half working with the proper LEDs on at the correct 
times (two yellow, and red with Linuxcnc not running, and two yellow, and 
blinking green with Linuxcnc.

Todd Zuercher
P. Graham Dunn Inc.
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031



Sounds like maybe the processor has failed in some way
(flash memory failure maybe, rare but can happen)
I will issue a RMA for repair/replacement later today



-Original Message-
From: Todd Zuercher via Emc-users 
Sent: Tuesday, April 02, 2024 7:57 AM
To: Peter Wallace ; Todd Zuercher via Emc-users 

Cc: Todd Zuercher 
Subject: Re: [Emc-users] 7i84 Trouble?

[EXTERNAL EMAIL] Be sure links are safe.

Yes I have both VFIELDA and VFIELDB connected (I have a jumper wire between 
them).

Todd Zuercher
P. Graham Dunn Inc.
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031

-Original Message-----
From: Peter Wallace 
Sent: Monday, April 01, 2024 5:30 PM
To: Todd Zuercher via Emc-users 
Cc: Todd Zuercher 
Subject: Re: [Emc-users] 7i84 Trouble?

[EXTERNAL EMAIL] Be sure links are safe.

On Mon, 1 Apr 2024, Todd Zuercher via Emc-users wrote:


Date: Mon, 1 Apr 2024 20:49:01 +
From: Todd Zuercher via Emc-users 
To: "Enhanced Machine Controller (EMC)"

Cc: Todd Zuercher 
Subject: [Emc-users] 7i84 Trouble?

I am working at trying to set up a 7i84 io card on a machine that I am
refitting and I'm having some trouble with it.

The outputs all seem to be working correctly, but I can only seem to
get half of the inputs to work.  I have 24v DC to all of the Vin terminals.
The inputs on TB2 seem to all be ok.  But the ones on TB3 are not.  In
Hal, the 1st 8 inputs (0-7) all read false (no mater what I connect to
them, and the 2nd 8 all read true (8-15) no mater what is connected to
them.> The 7i84 is connected to the SS port on a 7i85S that is connected to a 
5i25.

Any ideas what I might have messed up?   My best guess is that while I was 
wiring up and testing limit switches I may have had a stray loose wire with 24v 
touch against some place it shouldn't have.  (In hind sight, I probably should 
have turned off the 24v while I was working on that.)



Do you have both VFIELDA and VFIELDB connected? sounds like an issue there




Todd Zuercher
P. Graham Dunn
Inc.<https://nam04.safelinks.protection.outlook.com/?url=http%3A%2F%2F
http://www.p/
grahamdunn.com%2F=05%7C02%7Ctoddz%40pgrahamdunn.com%7Ce662d0e5ba5
4462b099908dc53111a7a%7C5758544c573f47cebee96c3e0806fb43%7C0%7C0%7C638
476580144714557%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2
luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C0%7C%7C%7C=2O6%2FRohCfn9f
ji0EZDM7Hp6nCBbvIyFU4fmDXUxGqyE%3D=0%2Findex.php=05%7C02
%7Ctoddz%40pgrahamdunn.com
%7C186c62e7c8e744291a7008dc5292f955%7C5758544c573f47cebee96c3e0806fb43
%7C0%7C0%7C638476038415014930%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAw
MDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C0%7C%7C%7C=
ccrEHvkZWcpQ9FU9Z6v%2B0A9SBejjH0hFMty1aNEg520%3D=0>
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://list/
%2F=05%7C02%7Ctoddz%40pgrahamdunn.com%7Ce662d0e5ba54462b099908dc5
3111a7a%7C5758544c573f47cebee96c3e0806fb43%7C0%7C0%7C63847658014472077
0%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6
Ik1haWwiLCJXVCI6Mn0%3D%7C0%7C%7C%7C=z0vE8WEGy63egCOnOyoYxHVqMMWV
5r2QCHznB0Lw2LY%3D=0
s.sourceforge.net%2Flists%2Flistinfo%2Femc-users=05%7C02%7Ctoddz%
40pgrahamdunn.com%7C186c62e7c8e744291a7008dc5292f955%7C5758544c573f47c
ebee96c3e0806fb43%7C0%7C0%7C638476038415023302%7CUnknown%7CTWFpbGZsb3d
8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C
0%7C%7C%7C=BVn076kBBUwINxm1WL%2BuwiDZQhSzcDPl5KdAHBvBjOE%3D
rved=0



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] 7i84 Trouble?

2024-04-01 Thread Peter Wallace

On Mon, 1 Apr 2024, Todd Zuercher via Emc-users wrote:


Date: Mon, 1 Apr 2024 20:49:01 +
From: Todd Zuercher via Emc-users 
To: "Enhanced Machine Controller (EMC)" 
Cc: Todd Zuercher 
Subject: [Emc-users] 7i84 Trouble?

I am working at trying to set up a 7i84 io card on a machine that I am 
refitting and I'm having some trouble with it.


The outputs all seem to be working correctly, but I can only seem to get 
half of the inputs to work.  I have 24v DC to all of the Vin terminals. 
The inputs on TB2 seem to all be ok.  But the ones on TB3 are not.  In Hal, 
the 1st 8 inputs (0-7) all read false (no mater what I connect to them, and 
the 2nd 8 all read true (8-15) no mater what is connected to them.>

The 7i84 is connected to the SS port on a 7i85S that is connected to a 5i25.

Any ideas what I might have messed up?   My best guess is that while I was 
wiring up and testing limit switches I may have had a stray loose wire with 24v 
touch against some place it shouldn't have.  (In hind sight, I probably should 
have turned off the 24v while I was working on that.)



Do you have both VFIELDA and VFIELDB connected? sounds like an issue there




Todd Zuercher
P. Graham Dunn Inc.<http://www.pgrahamdunn.com/index.php>
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Mesa 7i84 Field IO?

2024-03-09 Thread Peter Wallace

On Sat, 9 Mar 2024, Todd Zuercher wrote:


Date: Sat, 9 Mar 2024 05:02:49 +
From: Todd Zuercher 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "Enhanced Machine Controller (EMC)" 
Subject: Re: [Emc-users] Mesa 7i84 Field IO?

Peter,

But the only 5v output I need is for the servo drive enable(s) All the 
limits are 24v prox sensors etc.



You can split the I/O on a 7I84 so half (16 inputa and 8 outputs)
are 5V and the other half are 24V



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Mesa 7i84 Field IO?

2024-03-08 Thread Peter Wallace

On Fri, 8 Mar 2024, Todd Zuercher wrote:


Date: Fri, 8 Mar 2024 19:59:14 +
From: Todd Zuercher 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "Enhanced Machine Controller (EMC)" 
Subject: [Emc-users] Mesa 7i84 Field IO?

Hello,

I am working at connecting a 7i84 IO card to a machine that I am refitting a 
newer Linuxcnc PC to.  The old PC used an ISA card for IO.  That will no 
longer be an option with a newer PC.


My questions, the servo drives used 5v TTL signals for IO signals 
specifically the ready/fault output, and the enable input.  How should I 
interface these with the new 7i84 card (which is using 24v field power)?


The ready/fault output seems simple enough.  It is an "open collector 
outputs without pull-up resistors, they are rated for switching 
non-inductive loads up to 40V at a maximum of 100mA" (quote from the drive's 
manual).  So I simply need to add a 24v pullup for each of those signals. 
The question is what size pullup resistor should I use?


The harder question for me is how to handle the 5v drive enables?  Would it 
be best just to connect them to via a relay?  Or would there be a better 
way?


Other Mesa cards in this system, a 5i25, 7i85S, and 7i88.  Both parallel 
port headers are used on the 5i25.  The smart serial port on the 7i85s is 
used to connect the 7i84.  All of the step/dir outputs on the 7i88 are being 
used.  The only IO not being used are on the 7i84, one encoder input and one 
step/dir output pair on the 7i85s.


Would it be ok to try to use one of the free the step or dir outputs as the 
5v enable signal for all 3 servo drives or is a relay on one of the 7i84 
outputs a better idea?


Todd Zuercher
P. Graham Dunn Inc.<http://www.pgrahamdunn.com/index.php>
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



You can use a 7I84 with 5V I/O

In this case you supply VIN with 12 or 24V
but supply VFIELDA and VFIELDB with 5V
This will make the I/O all 5V

If you happen to have a REV A 7I84
you can run the whole card on 5V only
(VIN,VFIELDA,VFIELDB)


(none of this applies to the 7I84D)

Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] MESA card suggestions

2023-12-15 Thread Peter Wallace

On Fri, 15 Dec 2023, alanmthomason--- via Emc-users wrote:


Date: Fri, 15 Dec 2023 17:14:51 -0500
From: alanmthomason--- via Emc-users 
To: "'Enhanced Machine Controller (EMC)'" 
Cc: alanmthoma...@icloud.com
Subject: [Emc-users] MESA card suggestions

Hi There.



I am looking for a suggestion for the best MESA card to be used with

an ethernet connection

4axes

Teknic servo / stepper taking a step/direction input of 5 to 24V

Ideally this would be in a format that I could mount in a simple enclosure.

3digital inputs per axis, so 12inputs

1 additional digital output.



I will be using a fresh build of linuxcnc on a 64bit Ubuntu platform.



Thanks very much,

Alan


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users





As Andy suggested, a 7I96S is close but shy of one input.
If the three inputs per axis include limits, you could save
inputs by sharing limit inputs between axis, In addition
you can share a limit and home on the same axis.

With maximum sharing you could get away with only 5 inputs
(4 home switches and a combined limit input)

Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Trajectory planning

2023-11-23 Thread Peter Wallace

On Thu, 23 Nov 2023, John Dammeyer wrote:


Date: Thu, 23 Nov 2023 17:07:57 -0800
From: John Dammeyer 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "'Enhanced Machine Controller (EMC)'" 
Subject: [Emc-users] Trajectory planning

Quick question here.   The HAL file has two time intervals I believe in 
nanoseconds?
BASE_PERIOD = 24000
SERVO_PERIOD = 100

So BASE_PERIOD is about 41.67kHz and SERVO_PERIOD is 1kHz?



Yes


I'm guessing the encoder edges are counted between BASE_PERIOD Ticks to 
determine spindle velocity?  Is that correct?

Yes


That the trajectory planner calculates a new velocity relative to the 
spindle every SERVO_PERIOD?  In other words the step rate to say the Z axis 
for threading is changed (or left the same) every 1mS.

Yes


Have I got that right?  Just looking for an overall simple description.



Yep


Thanks
John




___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] LinuxCNC 2.9 is Released

2023-11-05 Thread Peter Wallace

On Sun, 5 Nov 2023, andy pugh wrote:


Date: Sun, 5 Nov 2023 00:39:13 +
From: andy pugh 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "Enhanced Machine Controller (EMC)" 
Subject: [Emc-users] LinuxCNC 2.9 is Released

LinuxCNC 2.9.1 has been released


Thanks for all you hard work on this.

Its great to have an official release that
leaves the Python 2/3 mess behind

Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Mesa Step Pulses?

2023-10-25 Thread Peter Wallace

On Wed, 25 Oct 2023, John Dammeyer wrote:


Date: Wed, 25 Oct 2023 09:12:46 -0700
From: John Dammeyer 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "'Enhanced Machine Controller (EMC)'" 
Subject: Re: [Emc-users] Mesa Step Pulses?

This might be a silly question but if you only want to move it one step then
does the step line stay high?  When does it go low?  After all the next step
might be in 30 minutes so should it go low in 15 minutes?  That's quite the
lookahead.
Enquiring minds wish to know.  ;-)
John


In square wave mode, the step pin state can be in the active
state indefinately (when stopped) How low it's actual frequency
can be depends on the hardware. On Mesa hardware and a 100 MHz base
clock the lowest settable frequency is about 1 step per 40 seconds
(100e6/2^32) but since there is high resolution position feedback
(1/65536ths of a step) LinuxCNCs control loop can dither between
stopped and the 1/40 Hz minimum at 1/servo period rate to get much
lower actual step rates (days per step)






-Original Message-
From: Peter Wallace [mailto:p...@mesanet.com]
Sent: October 25, 2023 8:35 AM
To: Enhanced Machine Controller (EMC)
Subject: Re: [Emc-users] Mesa Step Pulses?

On Wed, 25 Oct 2023, Todd Zuercher wrote:


Date: Wed, 25 Oct 2023 15:15:36 +
From: Todd Zuercher 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "Enhanced Machine Controller (EMC)" 
us...@lists.sourceforge.net>

Subject: Re: [Emc-users] Mesa Step Pulses?

Peter,

Thanks, But is it even going to be worth the effort?  Since I'm sure the
regular minimum pulse length signal is still going to at least work

albeit

with some possible theoretical performance limitations.  I may not even
require step rates beyond where this is a non-issue?


Well since you can certainly get near square waves at the maximum speed
with the current setup, it doesnt seem that much is gained by always

having

square wave step signals, since the minimum timings are always met.

That said, there is an advantage of square wave outputs in simplifying
setup (since the step length and step space settings are unnecessary)



I've asked the drive manufacturer.  See if they get back to me.

Todd Zuercher
P. Graham Dunn Inc.
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031

-----Original Message-
From: Peter Wallace 
Sent: Wednesday, October 25, 2023 10:36 AM
To: Enhanced Machine Controller (EMC) 
us...@lists.sourceforge.net>

Subject: Re: [Emc-users] Mesa Step Pulses?

[EXTERNAL EMAIL] Be sure links are safe.

On Wed, 25 Oct 2023, Todd Zuercher wrote:


Date: Wed, 25 Oct 2023 12:22:40 +
From: Todd Zuercher 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "Enhanced Machine Controller (EMC)"

Subject: [Emc-users] Mesa Step Pulses?

Hello,

It is my understanding that the step pulses generated by Mesa cards
are always the minimum pulse length set by for example
hm2_5i25.0.stepgen.00.steplen, only the space between the pulses is
varied by the step rate, is that correct?

I was reading the manual for the new drive I was planning to use in my
next build and see that the drive calls a preference of a 50% duty
cycle for step pulse inputs.  I am guessing that it may have something
to do with how the drive's pulse filtering system works, such that for
maximum noise filtering and step reliability having the pulse length
be approximately equal to the step spacing gives the best results.

So my questions are;  Would it be possible to make a Mesa card output
a 50% duty cycle step pattern instead of the current default pattern?
And would doing this even be worth the effort?


Its possible with a minor firmware change and LinuxCNC driver change to

enable the mode.




Todd Zuercher
P. Graham Dunn


Inc.<https://nam04.safelinks.protection.outlook.com/?url=http%3A%2F%2F



http://www.pgrahamdunn.com/%2Findex.php=05%7C01%7Ctoddz%4
0pgrahamdunn.com



%7Ce5da628e16d4477d2d4008dbd567e82f%7C5758544c573f47cebee96c3e08
06fb43



%7C0%7C0%7C638338414483169698%7CUnknown%7CTWFpbGZsb3d8eyJWIj
oiMC4wLjAw



MDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%
7C



ta=Zwbdv69ESSXKwXR%2FvXYbyijq1wOtyar%2FYeCMJAr6fgg%3D
=0>

630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://list/
s.sourceforge.net%2Flists%2Flistinfo%2Femc-

users=05%7C01%7Ctoddz%



40pgrahamdunn.com%7Ce5da628e16d4477d2d4008dbd567e82f%7C5758544c
573f47c



ebee96c3e0806fb43%7C0%7C0%7C638338414483169698%7CUnknown%7CT
WFpbGZsb3d



8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%
3D%7C



3000%7C%7C%7C=f1ssQLGo0gn0%2B2tjHAUXLZOjfsSHNrJWTjJDkkDR
uAA%3D

eserved=0



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listin

Re: [Emc-users] Mesa Step Pulses?

2023-10-25 Thread Peter Wallace

On Wed, 25 Oct 2023, Todd Zuercher wrote:


Date: Wed, 25 Oct 2023 15:15:36 +
From: Todd Zuercher 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "Enhanced Machine Controller (EMC)" 
Subject: Re: [Emc-users] Mesa Step Pulses?

Peter,

Thanks, But is it even going to be worth the effort?  Since I'm sure the 
regular minimum pulse length signal is still going to at least work albeit 
with some possible theoretical performance limitations.  I may not even 
require step rates beyond where this is a non-issue?


Well since you can certainly get near square waves at the maximum speed
with the current setup, it doesnt seem that much is gained by always having 
square wave step signals, since the minimum timings are always met.


That said, there is an advantage of square wave outputs in simplifying
setup (since the step length and step space settings are unnecessary)



I've asked the drive manufacturer.  See if they get back to me.

Todd Zuercher
P. Graham Dunn Inc.
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031

-Original Message-
From: Peter Wallace 
Sent: Wednesday, October 25, 2023 10:36 AM
To: Enhanced Machine Controller (EMC) 
Subject: Re: [Emc-users] Mesa Step Pulses?

[EXTERNAL EMAIL] Be sure links are safe.

On Wed, 25 Oct 2023, Todd Zuercher wrote:


Date: Wed, 25 Oct 2023 12:22:40 +
From: Todd Zuercher 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "Enhanced Machine Controller (EMC)"

Subject: [Emc-users] Mesa Step Pulses?

Hello,

It is my understanding that the step pulses generated by Mesa cards
are always the minimum pulse length set by for example
hm2_5i25.0.stepgen.00.steplen, only the space between the pulses is
varied by the step rate, is that correct?

I was reading the manual for the new drive I was planning to use in my
next build and see that the drive calls a preference of a 50% duty
cycle for step pulse inputs.  I am guessing that it may have something
to do with how the drive's pulse filtering system works, such that for
maximum noise filtering and step reliability having the pulse length
be approximately equal to the step spacing gives the best results.

So my questions are;  Would it be possible to make a Mesa card output
a 50% duty cycle step pattern instead of the current default pattern?
And would doing this even be worth the effort?


Its possible with a minor firmware change and LinuxCNC driver change to enable 
the mode.



Todd Zuercher
P. Graham Dunn
Inc.<https://nam04.safelinks.protection.outlook.com/?url=http%3A%2F%2F
http://www.pgrahamdunn.com/%2Findex.php=05%7C01%7Ctoddz%40pgrahamdunn.com
%7Ce5da628e16d4477d2d4008dbd567e82f%7C5758544c573f47cebee96c3e0806fb43
%7C0%7C0%7C638338414483169698%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAw
MDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C
ta=Zwbdv69ESSXKwXR%2FvXYbyijq1wOtyar%2FYeCMJAr6fgg%3D=0>
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://list/
s.sourceforge.net%2Flists%2Flistinfo%2Femc-users=05%7C01%7Ctoddz%
40pgrahamdunn.com%7Ce5da628e16d4477d2d4008dbd567e82f%7C5758544c573f47c
ebee96c3e0806fb43%7C0%7C0%7C638338414483169698%7CUnknown%7CTWFpbGZsb3d
8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C
3000%7C%7C%7C=f1ssQLGo0gn0%2B2tjHAUXLZOjfsSHNrJWTjJDkkDRuAA%3D
eserved=0



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Mesa Step Pulses?

2023-10-25 Thread Peter Wallace

On Wed, 25 Oct 2023, Todd Zuercher wrote:


Date: Wed, 25 Oct 2023 12:22:40 +
From: Todd Zuercher 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "Enhanced Machine Controller (EMC)" 
Subject: [Emc-users] Mesa Step Pulses?

Hello,

It is my understanding that the step pulses generated by Mesa cards are 
always the minimum pulse length set by for example 
hm2_5i25.0.stepgen.00.steplen, only the space between the pulses is varied 
by the step rate, is that correct?


I was reading the manual for the new drive I was planning to use in my next 
build and see that the drive calls a preference of a 50% duty cycle for step 
pulse inputs.  I am guessing that it may have something to do with how the 
drive's pulse filtering system works, such that for maximum noise filtering 
and step reliability having the pulse length be approximately equal to the 
step spacing gives the best results.


So my questions are;  Would it be possible to make a Mesa card output a 50% 
duty cycle step pattern instead of the current default pattern?  And would 
doing this even be worth the effort?


Its possible with a minor firmware change and LinuxCNC driver
change to enable the mode.



Todd Zuercher
P. Graham Dunn Inc.<http://www.pgrahamdunn.com/index.php>
630 Henry Street
Dalton, Ohio 44618
Phone:  (330)828-2105ext. 2031


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] 3 encoders on 7i76E?

2023-09-25 Thread Peter Wallace

On Mon, 25 Sep 2023, Viesturs L?cis wrote:


Date: Mon, 25 Sep 2023 18:47:03 +0300
From: "[UTF-8] Viesturs L?cis" 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "Enhanced Machine Controller (EMC)" 
Subject: [Emc-users] 3 encoders on 7i76E?

Hello!

I am trying to help a guy to sort out config changes for their LinuxCNC machine.
Currently they are running servo motors with step/dir signals and
there is no position feedback to LinuxCNC. They are having some issues
with machining errors and they want to change the config so that
encoder signal from servodrive is fed to LinuxCNC with an intention
that it will improve positioning precision. 7i76E is supposed to be
capable of reading 3 encoders - one for spindle and two for MPG. The
idea is to use these 3 encoders for X and Y axes (it is a gantry
machine with total of 3 joints for XY plane).

The problem is that this line in INI file:
CONFIG="num_encoders=3 num_stepgens=4 sserial_port_0=0xxx"

Gives an error on LinuxCNC startup and I believe this line to be the crucial:
config.num_encoders = 3, but only 1 are available, not loading the driver


The num-encoders line only applies to quadrature encoders built into the FPGA
(and there is only 1 quadrature encoder in the standard 7I76E firmware)

If you wish to use the MPG encoders, you must use sserial mode 2:
( sserial_port_0=2xxx ) and the 7i76 mpg encoder hal pins



Do I understand correctly that simple change of firmware is required?
Can someone suggest what would be correct firmware for this?



This is standard


And then one more question - are those inputs for MPG encoders
suitable to read "normal" encoder signal, meaning - are there any
limitations on max pulse frequency the inputs can handle for these 2
encoders?



They are quite limited (to say 40,000 counts per second)
In addition they are single ended only and do not support index

In general they are not recommended for motion applications
and rather just for supporting MPGs

A much better solution is to add a 7I85 or 7I85S



Thanks in advance!

Viesturs


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Q, switching machine from inch default to metric (mm's) default?

2023-09-21 Thread Peter Wallace

On Thu, 21 Sep 2023, gene heskett wrote:


Date: Thu, 21 Sep 2023 19:39:17 -0400
From: gene heskett 
Reply-To: "Enhanced Machine Controller (EMC)"

To: Emc-users@lists.sourceforge.net
Subject: [Emc-users] Q,
switching machine from inch default to metric (mm's) default?

Greetings said a confused guy;

If I want to keep the same physical speeds, basically what the machine can 
do, it makes sense the STEP_SCALE in each axis gets divided by 25.4 to make 
it a mm machine.


But when I've done that the machine moves extremely slow, and throws a 
following error when it has moved by about the amount set in FERROR and/or 
MIN_ERROR. What else besides the MAXVELS and ACCEL's need massaging, as it 
makes sense they should be multiplied by 25.4.  Which I did, but then it 
tries to move at several hundred mm/sec & crashes into all the stops.



You need to set the stepgen max-vels and max-accels to reasonable
values also (typically 25% higher than the machine max-vels and
max-accels)



Another problem, what is the input resistance load of a 7i76D when its set 
for 12 volt logic. I am using a prox switch for a home switch on this new A 
axis. I get 12 volts  back from the prox switch when triggered, and the prox 
switch is rated for srcing 300 milliamps when triggered, but when I hook it 
up to hm2_5i25.0.7i76.0.0.input-06, the switch does not heat, but only gives 
a few millivolts over 8 volts, like there is one hell of a load, and its the 
same for 2 different new prox switches and for 2 different inputs on the 
7i76D. The new A axis homes like it should, only axis that actually works for 
homing.




7I76Ds depending on vintage may have 22K, 20K or 10K input impedances


I could use some help. This is so frustrating that I'm ready to give up, copy 
the 3 axis inch config over this one and add the A axis stuff all over again.


Also:
This new atpid was not, at least for me, anywhere near ready for prime time. 
It gives huge, often unstable numbers for inch linear axis's, and left my 
bs-1 servo hunting so bad it burned up a $120 motor in about 3 minutes 
quietly hunting about half an arcminute, at around 10 hertz. It refuses to 
find usable settings for an angular axis. 6+ digits left of the decimal point 
for vars for that mode, yet when I asked, I'm told it should work with the 
hard to find procedure, but it doesn't.


Thanks.

Cheers, Gene Heskett.
--
"There are four boxes to be used in defense of liberty:
soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author, 1940)
If we desire respect for the law, we must first make the law respectable.
- Louis D. Brandeis
Genes Web page <http://geneslinuxbox.net:6309/>


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] question for Peter C. Wallace

2023-09-19 Thread Peter Wallace

On Tue, 19 Sep 2023, gene heskett wrote:


Date: Tue, 19 Sep 2023 19:23:23 -0400
From: gene heskett 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "'Enhanced Machine Controller (EMC)'" 
Subject: [Emc-users] question for Peter C. Wallace

Greeting Peter;

I hope this finds you well.

I am installing a new A axis on my go704, and am trying to exercise it before 
moving 99% of the actual driver code code in from another machine with 
identical hdwe for its B axis.
I have loaded a siggen to use its triangular drive as input to the 
joint.03.position-cmd, with the amplitude set to 2.5 and this for the rest of 
the dummy code:


setphm2_5i25.0.stepgen.03.enable true #turn it on
setpsiggen.0.frequency 10
setpsiggen.0.amplitude 2.5
setphm2_5i25.0.stepgen.03.steplen 4000
setphm2_5i25.0.stepgen.03.stepspace 1
setphm2_5i25.0.stepgen.03.dirhold 6000
setphm2_5i25.0.stepgen.03.dirsetup 6000
net 	mtr-test 




<= siggen.0.triangle => 
hm2_5i25.0.stepgen.03.position-cmd


So tb2-20 to 23 on the 7i76D is supposed to be stepgen.03.outputs.

man siggen says it should be symmetrical if no offset is set. But dir on 
neither pin is anywhere near 50/50, closer to 5/95, and faster than the above 
10 a sec by quite a bit, and the step terminals are a solid 5 volt or zero 
volts, no activity at all.


This on a 4 channel storage scope with a 350MHz bandwidth. Siglent's best. 
That puppy doesn't miss a thing.


Did I miss a setp above?

Thanks Peter.

Cheers, Gene Heskett.
--
"There are four boxes to be used in defense of liberty:
soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author, 1940)
If we desire respect for the law, we must first make the law respectable.
- Louis D. Brandeis
Genes Web page <http://geneslinuxbox.net:6309/>


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



You would also need to set reasonable stepgen acceleration and
velocity limits.

In addition, It may be that because you have a non-differentiable
position command (Triangle wave) that you have started an
instability in the built in position mode, so a sine wave would
be a better test.

For best performance where the are possible large following
errors it's better to use the stepgens in velocity mode and
close the (local) position with a PID loop.

Typical settings for the loop are

P = 1/servo period so 1000 for a 1 ms servo thread
FF1 = 1.000
FF2 = Time between Position read and velocity write
(say 20 us on a PCI card =.2, perhaps 200 usec on a
Ethernet card = .0002)



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] question for Peter C. W.

2023-09-07 Thread Peter Wallace

On Thu, 7 Sep 2023, gene heskett wrote:


Date: Thu, 7 Sep 2023 12:11:19 -0400
From: gene heskett 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "Enhanced Machine Controller (EMC)" 
Subject: [Emc-users] question for Peter C. W.

Greetings Peter;

Where on the 7i76, does pwmgen.00 of the 5i25 come out on?


Normally, nowhere, standard 7I76 firmware doesnt use a PWMgen for its analog 
output, its part of the field I/O sserial remote. Its control pins/parameters

would be:

pins:

hm2_5i25.0.7i76.0.0.spindir  # direction output
hm2_5i25.0.7i76.0.0.spinena  # high to enable ENA pin and Analog out
hm2_5i25.0.7i76.0.0.spinout  # analog value (positive only)

parameters:

hm2_5i25.0.7i76.0.0.spinout-scalemax  # sets scaling of analog value
hm2_5i25.0.7i76.0.0.spinout-minlim# sets minimum analog value, typically 0
hm2_5i25.0.7i76.0.0.spinout-maxlim# sets maximum analog value, typically
 same as scalemax = max RPM




Can I hal route the pwmgen.00 to the spindle pins on the 7i76 if not already 
there?  I'm putting a 3 phase stepper/servo, driving a 5/1 worm as an A drive 
on my GO704.  That means pwmgen.01 had to go, which I was using to run the 
spindle cuz I needed the stepgen-4 outputs that are overriding stepgen4 when 
2 pwmgens are loaded, Now I need that stepgen-4 for this A drive.


Cheers, Gene Heskett.
--
"There are four boxes to be used in defense of liberty:
soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author, 1940)
If we desire respect for the law, we must first make the law respectable.
- Louis D. Brandeis
Genes Web page <http://geneslinuxbox.net:6309/>


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Rigid tapping

2023-08-14 Thread Peter Wallace

On Mon, 14 Aug 2023, John Dammeyer wrote:


Date: Mon, 14 Aug 2023 16:36:16 -0700
From: John Dammeyer 
Reply-To: "Enhanced Machine Controller (EMC)"

To: "'Enhanced Machine Controller (EMC)'" 
Subject: Re: [Emc-users] Rigid tapping

Hi Andy,
I don't know.  How can I tell?  The encoder is connected to the MESA 7i92H 
and according to my documentation is noisy so needs to be filtered.  In 
either case it looks like the MESA board is providing Velocity and Position. 
I'd make a guess that based on its own internal clock it would provide a 
usable velocity.


The problem, and might only be fixed in hardware is when I made the disk I 
used a 4mm mill instead of the 3mm called for in the G-Code. Didn't notice 
until the second slot at which point it was already too late.  I'd guess at 
this slow a speed that the encoder will provide two different speeds between 
quadrature edges.


Must really fix that.

Here's some of the HAL file if that helps.
John


If you use LinuxCNC master, there is an interpolated position pin available 
for hostmot2 encoders. This basically uses the velocity estimation and the 
time since the last edge to get an estimated position between counts.


This should help the "staircase" motion of spindle synchronized moves
with low resolution encoders.


As far as noise goes and especially with low resolution encoders, this largely 
reflects quadrature errors (deviations from 50 % duty cycle and deviations 
from 90 degree phase shift between A and B).


Higher resolution encoders are better noise wise since since whatever 
quadrature errors exist, the estimated velocity noise caused by these errors 
gets divided by the counts per sample.


with low resolution encoders, you will typically have many samples between 
edges so the best you can do is calculate the time between edges so even a 
modest 10% duty cycle error causes relatively huge velocity noise.



Peter Wallace
Mesa Electronics


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Wiring Step Dir on KM5056E

2023-07-03 Thread Peter Wallace

On Mon, 3 Jul 2023, Alan Condit via Emc-users wrote:


Date: Mon, 3 Jul 2023 13:25:29 -0500
From: Alan Condit via Emc-users 
To: EMC-Users 
Cc: Alan Condit 
Subject: [Emc-users] Wiring Step Dir on KM5056E

I am in the process of wiring up a new controller for RPi4 using 7c81 and 7i76. 
In the process of doing so, I discovered that I had wired my controller for my 
PCBMill with a 7i76E Step+ to KM5056E Pulse-, Step- to KM5056E Pulse+, Dir+ to 
KM5056E Dir-, and Dir- to KM5056 Dir+.
It seems to run fine but, if I correct the connections Step+ to Pulse+, Step- 
to Pulse-, Dir+ to Dir+ and Dir- to Dir- what will happen. I don??t really 
want to break something that works.


Thanks in Advance,
Alan


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



If it works now and the timings were correct,
it should make no difference.

You would end up with longer active step pulse times
with inverted step polarity, though you may violate
the direction hold time if the hold time is set short
relative to the step pulse length.

Peter Wallace