Re: Draining System below ground....

2018-02-22 Thread bcasterline


Quoting Matt Grise :


I am also getting phishing notices.

Matt


-Original Message-
From: Sprinklerforum  
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of  
Steve Leyton

Sent: Thursday, February 22, 2018 4:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Draining System below ground

[This message was identified as a phishing scam. Learn about  
phishing at http://aka.ms/LearnAboutPhishing]


Attn:  AFSA Admin

Re:   Phishing scam notice

Am I the only one getting the notice, "This message was identified  
as a phishing scam."?


If others are seeing it, there may be something wrong with the  
site's security certificate or some attribute has been added to  
emails generated by the list-server.


Steve



-Original Message-
From: Sprinklerforum  
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of  
bcasterl...@fsc-inc.com

Sent: Thursday, February 22, 2018 2:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Draining System below ground

[This message was identified as a phishing scam. Learn about  
phishing at http://aka.ms/LearnAboutPhishing]


Mr Prahl been smokin hot here lately - on fire.
Can I get a witness?
b.
Quoting "Prahl, Craig/GVL" :


40 gallon trash can and portable sump pump with hose to exterior or
suitable drain.

That or bucket brigade.  :)


Craig L. Prahl
Fire Protection Group Lead/SME
Direct - 864.920.7540
Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
http://www.jacobs.com

-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Brian Harris
Sent: Thursday, February 22, 2018 3:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Draining System below ground [EXTERNAL]

Any suggestions on draining a system located in a basement below grade?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

-- next part -- An HTML attachment was
scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
er.org/attachments/20180222/54cd69ae/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org ___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org


probably my fault for saying -smoking hot-

I'll crawl back into bed now, er uhh,


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Draining System below ground....

2018-02-22 Thread Matt Grise
I am also getting phishing notices.

Matt 


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: Thursday, February 22, 2018 4:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Draining System below ground

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

Attn:  AFSA Admin

Re:   Phishing scam notice

Am I the only one getting the notice, "This message was identified as a 
phishing scam."?

If others are seeing it, there may be something wrong with the site's security 
certificate or some attribute has been added to emails generated by the 
list-server.

Steve



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of bcasterl...@fsc-inc.com
Sent: Thursday, February 22, 2018 2:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Draining System below ground

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

Mr Prahl been smokin hot here lately - on fire.
Can I get a witness?
b.
Quoting "Prahl, Craig/GVL" :

> 40 gallon trash can and portable sump pump with hose to exterior or 
> suitable drain.
>
> That or bucket brigade.  :)
>
>
> Craig L. Prahl
> Fire Protection Group Lead/SME
> Direct - 864.920.7540
> Fax - 864.920.7129
> Direct Extension  77540
> CH2M is now Jacobs.
> 200 Verdae Blvd.
> Greenville, SC  29607
> craig.pr...@ch2m.com
> http://www.jacobs.com
>
> -Original Message-
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
> Brian Harris
> Sent: Thursday, February 22, 2018 3:30 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Draining System below ground [EXTERNAL]
>
> Any suggestions on draining a system located in a basement below grade?
>
> Brian Harris, CET
> BVS Systems Inc.
> Design Manager
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
>
> -- next part -- An HTML attachment was 
> scrubbed...
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
> er.org/attachments/20180222/54cd69ae/attachment.html>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Draining System below ground....

2018-02-22 Thread Steve Leyton
Attn:  AFSA Admin

Re:   Phishing scam notice

Am I the only one getting the notice, "This message was identified as a 
phishing scam."?

If others are seeing it, there may be something wrong with the site's security 
certificate or some attribute has been added to emails generated by the 
list-server.   

Steve



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of bcasterl...@fsc-inc.com
Sent: Thursday, February 22, 2018 2:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Draining System below ground

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

Mr Prahl been smokin hot here lately - on fire.
Can I get a witness?
b.
Quoting "Prahl, Craig/GVL" :

> 40 gallon trash can and portable sump pump with hose to exterior or 
> suitable drain.
>
> That or bucket brigade.  :)
>
>
> Craig L. Prahl
> Fire Protection Group Lead/SME
> Direct - 864.920.7540
> Fax - 864.920.7129
> Direct Extension  77540
> CH2M is now Jacobs.
> 200 Verdae Blvd.
> Greenville, SC  29607
> craig.pr...@ch2m.com
> http://www.jacobs.com
>
> -Original Message-
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
> Brian Harris
> Sent: Thursday, February 22, 2018 3:30 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Draining System below ground [EXTERNAL]
>
> Any suggestions on draining a system located in a basement below grade?
>
> Brian Harris, CET
> BVS Systems Inc.
> Design Manager
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
>
> -- next part -- An HTML attachment was 
> scrubbed...
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
> er.org/attachments/20180222/54cd69ae/attachment.html>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Draining System below ground....

2018-02-22 Thread bcasterline

Mr Prahl been smokin hot here lately - on fire.
Can I get a witness?
b.
Quoting "Prahl, Craig/GVL" :

40 gallon trash can and portable sump pump with hose to exterior or  
suitable drain.


That or bucket brigade.  :)


Craig L. Prahl
Fire Protection Group Lead/SME
Direct - 864.920.7540
Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
http://www.jacobs.com

-Original Message-
From: Sprinklerforum  
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of  
Brian Harris

Sent: Thursday, February 22, 2018 3:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Draining System below ground [EXTERNAL]

Any suggestions on draining a system located in a basement below grade?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

-- next part --
An HTML attachment was scrubbed...
URL:  
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/54cd69ae/attachment.html>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Lumberyard fire flows

2018-02-22 Thread Steve Leyton
Which edition are you citing?  2018 doesn't have those Annex sections.

SL

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Thursday, February 22, 2018 2:37 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Lumberyard fire flows

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

NFPA 1 in A.1.3.3.2.2 and A.3.4.3.1 provides some guidance regarding flow and 
hydrant spacing for outside storage such as you are dealing with.

Best regards,

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: February-22-18 1:54 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Lumberyard fire flows

This isn't a sprinkler question specifically, but FP-related:   Has anyone ever 
worked on design of a private fire main for a lumberyard?   Huge outdoor piles 
of stored wood products, engineered members mostly, some smaller amounts of 
dimensional lumber. We're trying to establish a fire flow for hydrants but 
there are no buildings of any size to benchmark and tables in the fire code are 
not of much use because they're based on building area and construction type.   
The fire load here is not in buildings ...

[Steve Signature (3)]

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.html>
-- next part --
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 23565 bytes
Desc: image003.png
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.png>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Lumberyard fire flows

2018-02-22 Thread Larry Keeping
NFPA 1 in A.1.3.3.2.2 and A.3.4.3.1 provides some guidance regarding flow and 
hydrant spacing for outside storage such as you are dealing with.

Best regards,

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: February-22-18 1:54 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Lumberyard fire flows

This isn't a sprinkler question specifically, but FP-related:   Has anyone ever 
worked on design of a private fire main for a lumberyard?   Huge outdoor piles 
of stored wood products, engineered members mostly, some smaller amounts of 
dimensional lumber. We're trying to establish a fire flow for hydrants but 
there are no buildings of any size to benchmark and tables in the fire code are 
not of much use because they're based on building area and construction type.   
The fire load here is not in buildings ...

[Steve Signature (3)]

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.html>
-- next part --
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 23565 bytes
Desc: image003.png
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.png>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: EC OH Horizontal Sidewall Sprinklers

2018-02-22 Thread Ben Young
Reliable has the MBEC, but it can't do anything close to what the SW20 and
24 can do.


Benjamin Young

On Thu, Feb 22, 2018 at 9:59 AM, Mike Hairfield  wrote:

> Who besides TYCO makes a Extended Coverage Ordinary Hazard Sidewall
> sprinkler?
>
>
> Mike
> -- next part --
> An HTML attachment was scrubbed...
> URL: <http://lists.firesprinkler.org/private.cgi/
> sprinklerforum-firesprinkler.org/attachments/20180222/
> efde34b4/attachment.html>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/a8890894/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Draining System below ground....

2018-02-22 Thread Matt Grise
We will tie the main drain/inspectors test to the drain manifold. It will blow 
water uphill for alarm testing. Then use a drain valve with a capped garden 
hose connection to empty the pipe into a sink or sump - or bucket brigade!

Matt 


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Thursday, February 22, 2018 2:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Draining System below ground

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

Any suggestions on draining a system located in a basement below grade?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/54cd69ae/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Draining System below ground....

2018-02-22 Thread Bruce Verhei
If I had to I’d go back to first principles.

The main drain has two functions. 

A high flow, that should be fixed in configuration, to test water system supply.

And to drain the system to work on the system, or drain after a head opens.

Is it possible to split these functions?

Best.

Bruce Verhei 

> On Feb 22, 2018, at 12:29, Brian Harris  wrote:
> 
> Any suggestions on draining a system located in a basement below grade?
> 
> Brian Harris, CET
> BVS Systems Inc.
> Design Manager
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
> 
> -- next part --
> An HTML attachment was scrubbed...
> URL: 
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/54cd69ae/attachment.html>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Lumberyard fire flows

2018-02-22 Thread Bruce Verhei
In the end if you can’t confirm by a rational analysis that supports a 
reasonable goal, (extinguish a fire of X size, if that fails protect important 
on site exposures and all off site exposures) require ‘technical assistance ‘. 

Best.

> On Feb 22, 2018, at 12:44, Bruce Verhei  wrote:
> 
> Steve
> 
> You are required to calculate flows by an ‘approved method’.
> 
> If you haven’t previously put out for public comment and signed a scheme for 
> this I’d see what is already in use.
> 
> You might consider FMGlobal Data Sheet 7-10, 2-2.5. 
> 
> Before I went very far with this I’d compare pile sizes, fire access lanes 
> and widths to the sizes the IFC uses. Are the comparable?
> 
> And I’d ask how much water do you reserve for exposures.
> 
> Are they involving an insurance firm that has an engineering review section. 
> They’re often quite helpful. 
> 
> Locations of hydrants. Fire suppression activities are not helped if during 
> the fight you need to relocate engines as the plastic light bars are melting, 
> the paint is darkening, and the glass is crazing.
> 
> And equipment is heavy. You might confirm that the CE is considering this in 
> pipe type, depth, and bedding.
> 
> And are you in freezing country?
> The water just sits there. Enumclaw WA is not especially cold country. But a 
> root cause of failure to extinguish a fire in a Weyerhaeuser mill was a 
> frozen main. It was a little more complicated than that, but in the end an 
> ice plug occurred. Total loss of course. 
> 
> Best.
> 
> Bruce Verhei 
> 
>> On Feb 22, 2018, at 10:54, Steve Leyton  wrote:
>> 
>> This isn't a sprinkler question specifically, but FP-related:   Has anyone 
>> ever worked on design of a private fire main for a lumberyard?   Huge 
>> outdoor piles of stored wood products, engineered members mostly, some 
>> smaller amounts of dimensional lumber. We're trying to establish a fire 
>> flow for hydrants but there are no buildings of any size to benchmark and 
>> tables in the fire code are not of much use because they're based on 
>> building area and construction type.   The fire load here is not in 
>> buildings ...
>> 
>> [Steve Signature (3)]
>> 
>> -- next part --
>> An HTML attachment was scrubbed...
>> URL: 
>> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.html>
>> -- next part --
>> A non-text attachment was scrubbed...
>> Name: image003.png
>> Type: image/png
>> Size: 23565 bytes
>> Desc: image003.png
>> URL: 
>> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.png>
>> ___
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Lumberyard fire flows

2018-02-22 Thread Bruce Verhei
Steve

You are required to calculate flows by an ‘approved method’.

If you haven’t previously put out for public comment and signed a scheme for 
this I’d see what is already in use.

You might consider FMGlobal Data Sheet 7-10, 2-2.5. 

Before I went very far with this I’d compare pile sizes, fire access lanes and 
widths to the sizes the IFC uses. Are the comparable?

And I’d ask how much water do you reserve for exposures.

Are they involving an insurance firm that has an engineering review section. 
They’re often quite helpful. 

Locations of hydrants. Fire suppression activities are not helped if during the 
fight you need to relocate engines as the plastic light bars are melting, the 
paint is darkening, and the glass is crazing.

And equipment is heavy. You might confirm that the CE is considering this in 
pipe type, depth, and bedding.

And are you in freezing country?
The water just sits there. Enumclaw WA is not especially cold country. But a 
root cause of failure to extinguish a fire in a Weyerhaeuser mill was a frozen 
main. It was a little more complicated than that, but in the end an ice plug 
occurred. Total loss of course. 

Best.

Bruce Verhei 

> On Feb 22, 2018, at 10:54, Steve Leyton  wrote:
> 
> This isn't a sprinkler question specifically, but FP-related:   Has anyone 
> ever worked on design of a private fire main for a lumberyard?   Huge outdoor 
> piles of stored wood products, engineered members mostly, some smaller 
> amounts of dimensional lumber. We're trying to establish a fire flow for 
> hydrants but there are no buildings of any size to benchmark and tables in 
> the fire code are not of much use because they're based on building area and 
> construction type.   The fire load here is not in buildings ...
> 
> [Steve Signature (3)]
> 
> -- next part --
> An HTML attachment was scrubbed...
> URL: 
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.html>
> -- next part --
> A non-text attachment was scrubbed...
> Name: image003.png
> Type: image/png
> Size: 23565 bytes
> Desc: image003.png
> URL: 
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.png>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Draining System below ground....

2018-02-22 Thread Prahl, Craig/GVL
40 gallon trash can and portable sump pump with hose to exterior or suitable 
drain.  

That or bucket brigade.  :) 


Craig L. Prahl 
Fire Protection Group Lead/SME
Direct - 864.920.7540
Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
http://www.jacobs.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Thursday, February 22, 2018 3:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Draining System below ground [EXTERNAL]

Any suggestions on draining a system located in a basement below grade?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/54cd69ae/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Draining System below ground....

2018-02-22 Thread Brian Harris
Any suggestions on draining a system located in a basement below grade?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/54cd69ae/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Lumberyard fire flows

2018-02-22 Thread Prahl, Craig/GVL
The 2015 IFC states:
LUMBER YARDS AND AGRO-INDUSTRIAL, SOLID BIOMASS AND WOODWORKING FACILITIES
2809.5 Fire protection. An approved hydrant and hose system
or portable fire-extinguishing equipment suitable for the
fire hazard involved shall be provided for open storage yards.
Hydrant and hose systems shall be installed in accordance
with NFPA 24. Portable fire extinguishers complying with
Section 906 shall be located so that the distance of travel
from the nearest unit does not exceed 75 feet (22 860 mm).


To get that "approved hydrant and hose system" we'd typically have a layout 
showing the yard and anticipated loading.  Take that to the local fire code 
official (FCO) and talk about what kind of flow is available (I've have gotten 
this from local water purveyor before meeting the FCO).  If you only have 1500 
gpm flow rate available at 20 psi for example, how many hydrants will have to 
be involved with how many pumpers for the required hose streams.  We also talk 
about apparatus access through the yard and minimum aisle widths and turn radii 
so the owner knows there are stacking limitations.

Some of the answers depend on how the local FD is equipped.  

I agree, this is not a building related issue and even if there were a building 
on site, providing adequate resources for fighting a yard fire is a totally 
different hazard from a building.  

Also, for industrial or high flow rate areas I typically spec out the American 
Flow Control's American Darling Industrial hydrant with the 6" valve opening in 
lieu of the standard commercial hydrant with the 4.5 - 5" valve opening.  The 
AFC American-Darling hydrant # is B84B-BB-5. These can typically deliver up to 
4800 gpm through the 4.5" pumper connection at 100 psig.  

A lot of times we've just gotten hydrant spacing recommendations with no 
specific pressure or flow rates required.  I guess most FDs have resolved that 
they will get what they get and do the best with that.  


Craig L. Prahl 
Fire Protection Group Lead/SME
Direct - 864.920.7540
Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
http://www.jacobs.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: Thursday, February 22, 2018 1:54 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Lumberyard fire flows [EXTERNAL]

This isn't a sprinkler question specifically, but FP-related:   Has anyone ever 
worked on design of a private fire main for a lumberyard?   Huge outdoor piles 
of stored wood products, engineered members mostly, some smaller amounts of 
dimensional lumber. We're trying to establish a fire flow for hydrants but 
there are no buildings of any size to benchmark and tables in the fire code are 
not of much use because they're based on building area and construction type.   
The fire load here is not in buildings ...

[Steve Signature (3)]

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.html>
-- next part --
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 23565 bytes
Desc: image003.png
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.png>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Lumberyard fire flows

2018-02-22 Thread Steve Leyton
This isn't a sprinkler question specifically, but FP-related:   Has anyone ever 
worked on design of a private fire main for a lumberyard?   Huge outdoor piles 
of stored wood products, engineered members mostly, some smaller amounts of 
dimensional lumber. We're trying to establish a fire flow for hydrants but 
there are no buildings of any size to benchmark and tables in the fire code are 
not of much use because they're based on building area and construction type.   
The fire load here is not in buildings ...

[Steve Signature (3)]

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.html>
-- next part --
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 23565 bytes
Desc: image003.png
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.png>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Boats

2018-02-22 Thread Prahl, Craig/GVL
If you have lay-up areas where they are spraying fiberglas, with low heads, 
they can get a lot of residue on them.  Also if there is a sanding/finishing 
area the dust can cake on sprinklers as well if they don't have booths and 
adequate ventilation.

These operations can be real messy and the overhead sprinklers really need to 
be inspected and maintained more often than in typical manufacturing areas just 
due to the airborne residue.


Craig L. Prahl 
Fire Protection Group Lead/SME
Direct - 864.920.7540
Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
http://www.jacobs.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bruce Verhei
Sent: Thursday, February 22, 2018 10:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Boats [EXTERNAL]

I’d also be concerned with heads being loaded. Slow, but hard to observe.

Maybe in a modern plant with adequate exhaust this isn’t a problem.

EH2.

Best.

Bruce Verhei 

> On Feb 22, 2018, at 06:35, John Irwin  wrote:
> 
> Thanks Craig
> 
> John Irwin
> DynaFire Inc.
> 
> -Original Message-
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Prahl, Craig/GVL
> Sent: Thursday, February 22, 2018 9:29 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Boats
> 
> In addition to resin storage and spraying, also look for releasing 
> agents and solvent storage.  Typically acetone is used for cleaning 
> equipment.  You might find MEK as well.
> 
> Are the hulls stored outside or on cantilever racks or inside during 
> different stages of finishing and finally once completed?
> 
> You may also have exhaust system ductwork and hoods in some areas that 
> need to be protected.
> 
> Typically EHII covers most of the operation.  Storage methodology of 
> the hulls may drive some storage criteria.  Depending on the location 
> of, quantity and type of solvents, foam-water systems might also be warranted.
> 
> The fiberglass itself won't burn, at high temps it melts.  But in some 
> cases, other materials are added to the fiberglass for strength or 
> resiliency that can alter the combustible nature of the product.  It's 
> the composite materials that can bite you.  Ask what is in the process 
> to be sure of no surprises.
> 
> Also ask for a chemical list if you can, also to be sure you don't 
> have any unique, unexpected hazards that need special attention.
> 
> 
> Craig L. Prahl
> Fire Protection Group Lead/SME
> Direct - 864.920.7540
> Fax - 864.920.7129
> Direct Extension  77540
> CH2M is now Jacobs.
> 200 Verdae Blvd.
> Greenville, SC  29607
> craig.pr...@ch2m.com
> http://www.jacobs.com
> 
> -Original Message-
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Matt Grise
> Sent: Thursday, February 22, 2018 7:31 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Boats [EXTERNAL]
> 
> I have visited a couple - watch out for resin storage. I don't know if 
> the actual fiberglass is flammable, but the goo they put on it is. The 
> places I visited also had lots of Styrofoam that was used to fill hull 
> cavities.
> 
> Matt
> 
> 
> -Original Message-
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of John Irwin
> Sent: Thursday, February 22, 2018 6:26 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Boats
> 
> [This message was identified as a phishing scam. Learn about phishing 
> at http://aka.ms/LearnAboutPhishing]
> 
> I know boat storage is a bad word … how about boat production?
> 
> 
> 
> I’m looking at a 40,000sqft production building. I am guessing 
> fiberglass molds and fit outs going on in these bays. Other than that 
> there is a couple small offices and a small varnish room.
> 
> 
> 
> Anyone protect a building like this before?
> 
> 
> 
> John Irwin
> 
> Fire Sprinkler Specialist
> 
> DynaFire, Inc.
> 
> 727-282-9243 – Cell
> 
> 
> 
> *“A customer is the most important visitor on our premises. He is not 
> dependent on us. We are dependent on him. He is not an interruption on 
> our work. He is the purpose of it. He is not an outsider on our 
> business. He is a part of it. We are not doing him a favour by serving 
> him. He is doing us a favour by giving us an opportunity to do so.”*
> -- next part -- An HTML attachment was 
> scrubbed...
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
> er.org/attachm

Re: Boats

2018-02-22 Thread Bruce Verhei
I’d also be concerned with heads being loaded. Slow, but hard to observe.

Maybe in a modern plant with adequate exhaust this isn’t a problem.

EH2.

Best.

Bruce Verhei 

> On Feb 22, 2018, at 06:35, John Irwin  wrote:
> 
> Thanks Craig
> 
> John Irwin
> DynaFire Inc.
> 
> -Original Message-
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Prahl, Craig/GVL
> Sent: Thursday, February 22, 2018 9:29 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Boats
> 
> In addition to resin storage and spraying, also look for releasing agents
> and solvent storage.  Typically acetone is used for cleaning equipment.  You
> might find MEK as well.
> 
> Are the hulls stored outside or on cantilever racks or inside during
> different stages of finishing and finally once completed?
> 
> You may also have exhaust system ductwork and hoods in some areas that need
> to be protected.
> 
> Typically EHII covers most of the operation.  Storage methodology of the
> hulls may drive some storage criteria.  Depending on the location of,
> quantity and type of solvents, foam-water systems might also be warranted.
> 
> The fiberglass itself won't burn, at high temps it melts.  But in some
> cases, other materials are added to the fiberglass for strength or
> resiliency that can alter the combustible nature of the product.  It's the
> composite materials that can bite you.  Ask what is in the process to be
> sure of no surprises.
> 
> Also ask for a chemical list if you can, also to be sure you don't have any
> unique, unexpected hazards that need special attention.
> 
> 
> Craig L. Prahl
> Fire Protection Group Lead/SME
> Direct - 864.920.7540
> Fax - 864.920.7129
> Direct Extension  77540
> CH2M is now Jacobs.
> 200 Verdae Blvd.
> Greenville, SC  29607
> craig.pr...@ch2m.com
> http://www.jacobs.com
> 
> -Original Message-
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Matt Grise
> Sent: Thursday, February 22, 2018 7:31 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Boats [EXTERNAL]
> 
> I have visited a couple - watch out for resin storage. I don't know if the
> actual fiberglass is flammable, but the goo they put on it is. The places I
> visited also had lots of Styrofoam that was used to fill hull cavities.
> 
> Matt
> 
> 
> -Original Message-
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of John Irwin
> Sent: Thursday, February 22, 2018 6:26 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Boats
> 
> [This message was identified as a phishing scam. Learn about phishing at
> http://aka.ms/LearnAboutPhishing]
> 
> I know boat storage is a bad word … how about boat production?
> 
> 
> 
> I’m looking at a 40,000sqft production building. I am guessing fiberglass
> molds and fit outs going on in these bays. Other than that there is a couple
> small offices and a small varnish room.
> 
> 
> 
> Anyone protect a building like this before?
> 
> 
> 
> John Irwin
> 
> Fire Sprinkler Specialist
> 
> DynaFire, Inc.
> 
> 727-282-9243 – Cell
> 
> 
> 
> *“A customer is the most important visitor on our premises. He is not
> dependent on us. We are dependent on him. He is not an interruption on our
> work. He is the purpose of it. He is not an outsider on our business. He is
> a part of it. We are not doing him a favour by serving him. He is doing us a
> favour by giving us an opportunity to do so.”*
> -- next part --
> An HTML attachment was scrubbed...
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/80d25bb9/attachment.html>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


EC OH Horizontal Sidewall Sprinklers

2018-02-22 Thread Mike Hairfield
Who besides TYCO makes a Extended Coverage Ordinary Hazard Sidewall sprinkler?


Mike
-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/efde34b4/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Boats

2018-02-22 Thread John Irwin
Thanks Craig

John Irwin
DynaFire Inc.

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Prahl, Craig/GVL
Sent: Thursday, February 22, 2018 9:29 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Boats

In addition to resin storage and spraying, also look for releasing agents
and solvent storage.  Typically acetone is used for cleaning equipment.  You
might find MEK as well.

Are the hulls stored outside or on cantilever racks or inside during
different stages of finishing and finally once completed?

You may also have exhaust system ductwork and hoods in some areas that need
to be protected.

Typically EHII covers most of the operation.  Storage methodology of the
hulls may drive some storage criteria.  Depending on the location of,
quantity and type of solvents, foam-water systems might also be warranted.

The fiberglass itself won't burn, at high temps it melts.  But in some
cases, other materials are added to the fiberglass for strength or
resiliency that can alter the combustible nature of the product.  It's the
composite materials that can bite you.  Ask what is in the process to be
sure of no surprises.

Also ask for a chemical list if you can, also to be sure you don't have any
unique, unexpected hazards that need special attention.


Craig L. Prahl
Fire Protection Group Lead/SME
Direct - 864.920.7540
Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
http://www.jacobs.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Matt Grise
Sent: Thursday, February 22, 2018 7:31 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Boats [EXTERNAL]

I have visited a couple - watch out for resin storage. I don't know if the
actual fiberglass is flammable, but the goo they put on it is. The places I
visited also had lots of Styrofoam that was used to fill hull cavities.

Matt


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of John Irwin
Sent: Thursday, February 22, 2018 6:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Boats

[This message was identified as a phishing scam. Learn about phishing at
http://aka.ms/LearnAboutPhishing]

I know boat storage is a bad word … how about boat production?



I’m looking at a 40,000sqft production building. I am guessing fiberglass
molds and fit outs going on in these bays. Other than that there is a couple
small offices and a small varnish room.



Anyone protect a building like this before?



John Irwin

Fire Sprinkler Specialist

DynaFire, Inc.

727-282-9243 – Cell



*“A customer is the most important visitor on our premises. He is not
dependent on us. We are dependent on him. He is not an interruption on our
work. He is the purpose of it. He is not an outsider on our business. He is
a part of it. We are not doing him a favour by serving him. He is doing us a
favour by giving us an opportunity to do so.”*
-- next part --
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/80d25bb9/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Boats

2018-02-22 Thread Prahl, Craig/GVL
In addition to resin storage and spraying, also look for releasing agents and 
solvent storage.  Typically acetone is used for cleaning equipment.  You might 
find MEK as well.

Are the hulls stored outside or on cantilever racks or inside during different 
stages of finishing and finally once completed?

You may also have exhaust system ductwork and hoods in some areas that need to 
be protected.  

Typically EHII covers most of the operation.  Storage methodology of the hulls 
may drive some storage criteria.  Depending on the location of, quantity and 
type of solvents, foam-water systems might also be warranted.

The fiberglass itself won't burn, at high temps it melts.  But in some cases, 
other materials are added to the fiberglass for strength or resiliency that can 
alter the combustible nature of the product.  It's the composite materials that 
can bite you.  Ask what is in the process to be sure of no surprises.

Also ask for a chemical list if you can, also to be sure you don't have any 
unique, unexpected hazards that need special attention.


Craig L. Prahl 
Fire Protection Group Lead/SME
Direct - 864.920.7540
Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
http://www.jacobs.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Thursday, February 22, 2018 7:31 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Boats [EXTERNAL]

I have visited a couple - watch out for resin storage. I don't know if the 
actual fiberglass is flammable, but the goo they put on it is. The places I 
visited also had lots of Styrofoam that was used to fill hull cavities. 

Matt 


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Irwin
Sent: Thursday, February 22, 2018 6:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Boats

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

I know boat storage is a bad word … how about boat production?



I’m looking at a 40,000sqft production building. I am guessing fiberglass molds 
and fit outs going on in these bays. Other than that there is a couple small 
offices and a small varnish room.



Anyone protect a building like this before?



John Irwin

Fire Sprinkler Specialist

DynaFire, Inc.

727-282-9243 – Cell



*“A customer is the most important visitor on our premises. He is not dependent 
on us. We are dependent on him. He is not an interruption on our work. He is 
the purpose of it. He is not an outsider on our business. He is a part of it. 
We are not doing him a favour by serving him. He is doing us a favour by giving 
us an opportunity to do so.”*
-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/80d25bb9/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Boats

2018-02-22 Thread John Irwin
It's not Irwin Yachts. =)

John Irwin
DynaFire Inc.

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Fpdcdesign
Sent: Thursday, February 22, 2018 7:51 AM
To: Sprinklerforum 
Subject: Re: Boats




 I’ve always looked at it as Extra Hazard II. A lot of things on that list
seemed to fit. I don’t know the specifics so it is tough to tell. It’s not
Irwin Yachts, is it?



 Todd G Williams, PE
Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-553-3553 (fax)

860-608-4559 (cell)







>
> On Feb 22, 2018 at 7:25 AM,  mailto:john.ir...@dynafire.com)>
> wrote:
>
>
>
>  I know boat storage is a bad word … how about boat production?
>
>
>
> I’m looking at a 40,000sqft production building. I am guessing
> fiberglass molds and fit outs going on in these bays. Other than that
> there is a couple small offices and a small varnish room.
>
>
>
> Anyone protect a building like this before?
>
>
>
> John Irwin
>
> Fire Sprinkler Specialist
>
> DynaFire, Inc.
>
> 727-282-9243 – Cell
>
>
>
> *“A customer is the most important visitor on our premises. He is not
> dependent on us. We are dependent on him. He is not an interruption on
> our work. He is the purpose of it. He is not an outsider on our
> business. He is a part of it. We are not doing him a favour by serving
> him. He is doing us a favour by giving us an opportunity to do so.”*
> -- next part -- An HTML attachment was
> scrubbed...
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
> er.org/attachments/20180222/80d25bb9/attachment.html>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
-- next part --
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/083f3c3f/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Boats

2018-02-22 Thread Fpdcdesign
  
  

 I’ve always looked at it as Extra Hazard II. A lot of things on that list 
seemed to fit. I don’t know the specifics so it is tough to tell. It’s not 
Irwin Yachts, is it?
  
  
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (ofc)
  
860-553-3553 (fax)
  
860-608-4559 (cell)
  
  
  
  

  
  
>   
> On Feb 22, 2018 at 7:25 AM,  mailto:john.ir...@dynafire.com)>  
> wrote:
>   
>   
>   
>  I know boat storage is a bad word … how about boat production?
>
>
>
> I’m looking at a 40,000sqft production building. I am guessing fiberglass
> molds and fit outs going on in these bays. Other than that there is a
> couple small offices and a small varnish room.
>
>
>
> Anyone protect a building like this before?
>
>
>
> John Irwin
>
> Fire Sprinkler Specialist
>
> DynaFire, Inc.
>
> 727-282-9243 – Cell
>
>
>
> *“A customer is the most important visitor on our premises. He is not
> dependent on us. We are dependent on him. He is not an interruption on our
> work. He is the purpose of it. He is not an outsider on our business. He is
> a part of it. We are not doing him a favour by serving him. He is doing us
> a favour by giving us an opportunity to do so.”*
> -- next part --
> An HTML attachment was scrubbed...
> URL:  
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/80d25bb9/attachment.html>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  
-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/083f3c3f/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Boats

2018-02-22 Thread Matt Grise
I have visited a couple - watch out for resin storage. I don't know if the 
actual fiberglass is flammable, but the goo they put on it is. The places I 
visited also had lots of Styrofoam that was used to fill hull cavities. 

Matt 


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Irwin
Sent: Thursday, February 22, 2018 6:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Boats

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

I know boat storage is a bad word … how about boat production?



I’m looking at a 40,000sqft production building. I am guessing fiberglass molds 
and fit outs going on in these bays. Other than that there is a couple small 
offices and a small varnish room.



Anyone protect a building like this before?



John Irwin

Fire Sprinkler Specialist

DynaFire, Inc.

727-282-9243 – Cell



*“A customer is the most important visitor on our premises. He is not dependent 
on us. We are dependent on him. He is not an interruption on our work. He is 
the purpose of it. He is not an outsider on our business. He is a part of it. 
We are not doing him a favour by serving him. He is doing us a favour by giving 
us an opportunity to do so.”*
-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/80d25bb9/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Boats

2018-02-22 Thread John Irwin
I know boat storage is a bad word … how about boat production?



I’m looking at a 40,000sqft production building. I am guessing fiberglass
molds and fit outs going on in these bays. Other than that there is a
couple small offices and a small varnish room.



Anyone protect a building like this before?



John Irwin

Fire Sprinkler Specialist

DynaFire, Inc.

727-282-9243 – Cell



*“A customer is the most important visitor on our premises. He is not
dependent on us. We are dependent on him. He is not an interruption on our
work. He is the purpose of it. He is not an outsider on our business. He is
a part of it. We are not doing him a favour by serving him. He is doing us
a favour by giving us an opportunity to do so.”*
-- next part --