Re: NEC Question

2001-10-24 Thread Jacob Schanker
Mike: There is no Federal requirement for the manufacturer to have equipment listed or NRTL approved. The requirements are set by localities, as Richard Woods clearly points out. I can understand that in some companies, the powers-that-be have little patience with the time and expense of

Re: skinny power cords.

2001-10-24 Thread Nick Rouse
Hello Gary, Sounds like your making a case for the wider adoption of the UK system with fused plugs rated to protect the power cord Nick Rouse - Original Message - From: Gary McInturff gary.mcintu...@worldwidepackets.com To: EMC-PSTC (E-mail) emc-p...@ieee.org Sent: Wednesday, October

Re: skinny power cords.

2001-10-24 Thread Rich Nute
Hi Gary: Somewhere in my past, I've heard the rationale for this conundrum. I'm just guessing here. Power cords and similar mains devices are sized based on rated load, and are not sized based on fault-condition load. The requirement should be that, under fault conditions, the device is

Re: EFT Failures..Update!

2001-10-24 Thread Jacob Schanker
Excuse a slightly peripheral question. I always called it (an oily sort of brownish paper) Fish paper. I assumed the name came from the use of fish oil to prepare it in the 1800's. I see you are referring to it (is it the same thing?) as fische paper. Is that what it is sold as? Was it invented

RE: Shrunk-die power MOSFET's and compliance

2001-10-24 Thread Jim Eichner
Well for example, I have just finished specifying what compliance re-testing I am going to need to do on 4 different products whose power conversion stages use IRF630's, IRF740's, IRF840's, and RFP50N06's, but the list goes on and on. If you are using power FET's in power electronics, chances

RE: NEC Question

2001-10-24 Thread BurchJ
Hi Mike, I don't know if this will help but, CFR 29 Section 1910.399 subpart S.. is where the NRTL'S hang their hats on this issue. Good Luck Joe Josiah P. Burch Compliance Engineer II Andover Controls Corporation 300 Brickstone Square Andover,Ma 01810 (978)-470-0555 x335

skinny power cords.

2001-10-24 Thread georgea
Gary, It was always my understanding that house fuses/breakers were to protect all the upstream stuff, e.g. service entry box, external transformers etc. They cannot realistically protect downstream stuff, as they have no knowledge of how much current is too much for a given appliance.

RE: EFT Failures..Update!

2001-10-24 Thread Chris Maxwell
I agree with Paul's take. One of the trees in the forest is keyboards. Do you have any keyboards attached to the DUT? I have personally seen an instance where EFT was coupling to a keyboard cable and causing all sorts of wierd effects. I thought it was our design's fault, so I tried filtering,

Re: skinny power cords.

2001-10-24 Thread Ken Javor
I am NOT an expert in this field so I could likely stand some educating but the following seem to me to be common sense: 1) Household circuit breakers protect household wiring - only. They prevent wiring damage and fires. There is no practical way to provide breakers for every different kind

Re: Insulated Electrolytic Capacitors

2001-10-24 Thread Douglas_Beckwith
From: Douglas Beckwith@MITEL on 10/24/2001 02:05 PM Hi Peter, My understanding of 60950 is that distance through insulation applies here (0.4mm). I have never had this issue with CSA. Regards Doug Beckwith Mitel Networks Peter Merguerian pmerguer...@itl.co.il on 10/24/2001 09:38:19 AM

Re: NEC Question

2001-10-24 Thread Rich Nute
Hi Mike: Can someone point me to a section in the NEC that says a piece of RESIDENTIAL computer equipment must be listed (NEC definition). Article 645 which requires a listed piece of equipment appears to apply to a computer room and not a residence. In terms of the NEC, a

Class Designation under the RTTE directive

2001-10-24 Thread Kevin Harris
Dear Group, I just was reading the a list to assist one in choosing one's class designation under the RTTE directive at http://www.europa.eu.int/comm/enterprise/rtte/listeq.htm http://www.europa.eu.int/comm/enterprise/rtte/listeq.htm and I noticed that there are items under Class 1 that I never

RE: Too small to print Fcc Verification label!!!

2001-10-24 Thread Benoit Nadeau
Bonjour de Montreal, It all depends of the procedure you used for your product : If it is a Class B digital device using the, now obsolete, certification process, you have to put at a minimum the FCC ID of your granted certificate. The only way it could be used now is by the mean of a permissive

AW: Insulated Electrolytic Capacitors

2001-10-24 Thread Horst Haug
Peter, my experience is, that you will not receive a statement from the manufacturer of the capacitor about the foil around the cap. This would be required to proof, that it is good for basic insulation. Our company (we are a GS-mark certification body) does not accept the foil around a

RE: Insulated Electrolytic Capacitors

2001-10-24 Thread Jim Eichner
I asked a similar question a couple of years ago, and was told that the bodies of plastic encapsulated Y1 capacitors are considered by CENELEC to be reinforced insulation, except in the vicinity of the leads. I don't know if this extends to types of X and Y caps other than Y1. Hope this is

Tantalum Capacitors

2001-10-24 Thread liviu_dinulescu
Hi all, Some companies make through-hole polarized caps which cannot be loaded backwards; they are 3 pin in-line parts that are assigned +/-/+. Does anyone make SM parts that have the same attribute of not capable of being loaded backwards? Also where may I find reliability data for the so

RE: NEC Question

2001-10-24 Thread WOODS
Mike, regardless of what the NEC says, and it is not very clear in this regard, it is the state, county and city electrical codes and other local regulations that apply. Many jurisdictions have deviations from the NEC and/or have other regulations that require electrical equipment sold to the

skinny power cords.

2001-10-24 Thread Gary McInturff
Fuses and breakers etc, are provided to protect the wiring downstream from these devices. A 15 amp breaker is allowed to have 14 AWG wire attached and run all though my house, and terminates in a 15 amp rated receptacle - parallel blade with ground pin. Why then can I plug in a

NEC Question

2001-10-24 Thread Mike Morrow
Can someone point me to a section in the NEC that says a piece of RESIDENTIAL computer equipment must be listed (NEC definition). Article 645 which requires a listed piece of equipment appears to apply to a computer room and not a residence. Basically I've been asked where its says a piece of

Re: Insulated Electrolytic Capacitors

2001-10-24 Thread Patrick Lawler
Our company manufactures switching power supplies to EN60950 and EN60601-1 standards, and our safety group looks for these issues. In fact, I got 'bit' by that same problem last week. Spacing was OK when the PWB was mounted in the chassis, but when the cover was installed, it failed

RE: TNV Circuits

2001-10-24 Thread Bill Owsley
It's over on Bizarre Street. At 10:33 AM 10/24/2001 , Cortland Richmond wrote: telephone products destroyed by all sorts of bazaar events Where IS that bazaar? (grin) Cortland --- This message is from the IEEE EMC Society Product Safety Technical

RE: EFT Failures..Update!

2001-10-24 Thread Hare, Paul
Alex, make sure you investigate whether or not energy is coupling to other cables of the EUT and causing problems. In other words, try to reduce the system (remove cables) and see if the EFT failures persist. If you can't remove a cable due to functionality, place ferrites on it instead (near

RE: TNV Circuits

2001-10-24 Thread Cortland Richmond
telephone products destroyed by all sorts of bazaar events Where IS that bazaar? (grin) Cortland --- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at:

Insulated Electrolytic Capacitors

2001-10-24 Thread Peter Merguerian
Dear All, I have submitted an ac input to dc output switching power supply for NRTL approval. One deviation is that the primary ac insulated capacitor is too close to the earthed chassis and that the insulation cannot be relied to provide the required basic insulation. 1. What is the group's

RE: TNV Circuits

2001-10-24 Thread Gregg Kervill
Thanks Joe - that was the very point that I was trying to make - and that is why TNV is treated as hazardous. -Original Message- From: owner-emc-p...@majordomo.ieee.org [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of j...@aol.com Sent: Tuesday, October 23, 2001 10:44 PM To:

Standards applicable to crane equipment

2001-10-24 Thread Kristiaan . Carpentier
Dear all, The product concerned is a metal box located on the (metal) roller bridge of a crane and controls the movement of that bridge. It is powered by min. 48Vac and receives commands from an operator with a battery powered hand-held radio transmitter command box. The 48V ac power supply

Too small to print Fcc Verification label!!!

2001-10-24 Thread upuaut
Hi EMC members. I have a question about Fcc Label. This model is too small to insert Fcc verification statement on device. This is Compactflash memory card. I read Fcc Part 15. rules but I couldn't understand meaning. On Section 15.19 said "alternatively,shall be placed on the

SV: EFT Failures..Update!

2001-10-24 Thread amund
Alex, What happened during the burst test ? Did the EUT break down or did you only have minor disturbances/faults during the test ? I assume that you know that EFT/bursts usually is a performance criteria B test, which means that temporary faults are accepted during the test, as long that the

SV: EMC testing above 1GHz

2001-10-24 Thread amund
Hi Cecil, You're coming up with a good question, but could you be more precise what you are looking for ? Limits? EUT configuration ? Measurement equipment? . You name it! EMC above 1GHz could fill serveral pages Best regards Amund Westin, Oslo/Norway -Opprinnelig melding-

Re: TNV Circuits

2001-10-24 Thread JPR3
In a message dated 10/23/01, Gregg Kervill writes: Have lines ever been struck by Lightning? One of my clients had a cupboard full of telephone products destroyed by all sorts of bazaar events - like the temporary three phase power line to a factory that fell' across domestic phone

RE: TNV Circuits

2001-10-24 Thread Gregg Kervill
Have lines ever been struck by Lightning? One of my clients had a cupboard full of telephone products destroyed by all sorts of bazaar events - like the temporary three phase power line to a factory that fell' across domestic phone lines Anything outside must be considered hazardous and

RE: Shrunk-die power MOSFET's and compliance

2001-10-24 Thread Jim Eichner
No takers? I haven't had any responses, but I can't believe that ins't an issue for many of you. The switch-mode power supplies used in almost all equipment these days are the main users of these FET's, and the FET design change does effect compliance. Have none of you run into this issue?

Failure analysis

2001-10-24 Thread Peter Tarver
We are looking for a good failure analysis company in the SF Bay area. Anyone have any leads for companies you've had a positive experience with? Regards, Peter L. Tarver, PE Product Safety Manager Sanmina Homologation Services peter.tar...@sanmina.com

SV: EMC testing above 1GHz

2001-10-24 Thread amund
Hi Cecil, You're coming up with a good question, but could you be more precise what you are looking for ? Limits? EUT configuration ? Measurement equipment? . You name it! EMC above 1GHz could fill serveral pages Best regards Amund Westin, Oslo/Norway -Opprinnelig melding-