Re: [RE-wrenches] Canadian Solar / MC4 connectors in a marine environment

2016-06-07 Thread Bill Brooks
Kirk, I ran into a very similar problem with a system where the connectors were left unmated for a period of time. Salts got into the connectors and whenever the humidity was high, the salt would track current through the connector seals. Replace all the connectors first before trying anything

Re: [RE-wrenches] Pv wire

2014-06-27 Thread Bill Brooks
Kirk, The tables in Appendix C are just for reference. They are not part of the Code. The only real part of the code is in chapter 9: Table 1 Percent of Cross Section of Conduit and Tubing for Conductors and Cables Number of Conductors and/or Cables Cross-Sectional Area (%) 1

Re: [RE-wrenches] Combining Multiple Inverters

2014-06-27 Thread Bill Brooks
Jason, It sounds like you want to get involved with the PV industry forum. We have about 30+ active members this year so your input would be welcome. I think your idea about organization needs to be informed about some details. First of all, you need to read the new, very different, 705.12(

Re: [RE-wrenches] Pv wire

2014-06-27 Thread Bill Brooks
Kirk and All, I just got back from PV America and one of the venders there had a new PV Wire that was a completely different construction (not XLP). Their outer jacket is a more UV resilient material. There are also PV Wire with PVC jackets that are less resilient to UV than XLP. Ask for details

Re: [RE-wrenches] Module Degradation - voltage or current?

2014-06-04 Thread Bill Brooks
een it seems like panels that degrade at 0.5%/year are outliers on the low side. Thoughts from other wrenches? On Tue, Jun 3, 2014 at 11:59 PM, Bill Hoffer mailto:suneng...@gmail.com> > wrote: Dana Bill Brooks, passed on past data, ( correct me Bill if I am out of date

Re: [RE-wrenches] Module Degradation - voltage or current?

2014-06-04 Thread Bill Brooks
m: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Hoffer Sent: Tuesday, June 03, 2014 9:00 PM To: RE-wrenches Subject: Re: [RE-wrenches] Module Degradation - voltage or current? Dana Bill Brooks, passed on past data, ( correct me Bill if I am out of date

Re: [RE-wrenches] Module Degradation - voltage or current?

2014-06-03 Thread Bill Brooks
Read this article from SolarPro: “Array Voltage Considerations”, SolarPro Magazine, October/November 2010, pp 68-78. Bill. From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dana Brandt Sent: Tuesday, June 03, 2014 3:42 PM To: RE-wrenches Subject: [RE-wrenc

Re: [RE-wrenches] 2014 NEC

2014-05-27 Thread Bill Brooks
-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jay Peltz Sent: Tuesday, May 27, 2014 11:32 AM To: RE-wrenches Subject: Re: [RE-wrenches] 2014 NEC Hi nick Good to know, I was told this by bill brooks at a training a few months ago. Jay Sent from my iPhone On May 27, 2014, at 9:00 AM

Re: [RE-wrenches] 1000 volt conduit??

2014-05-16 Thread Bill Brooks
Kirk, That is correct. Raceways are not rated for voltage. The key is whether the conductor is intended to be installed in a raceway or not. Raceways are also allowed to be used for physical protection only for direct buried cables and exposed cables. The raceway is only required to prevent phy

Re: [RE-wrenches] Rapid shutdown for pole mounts

2014-05-02 Thread Bill Brooks
Martin, I agree that this would meet the requirement. Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Martin Herzfeld Sent: Friday, May 02, 2014 10:49 AM To: RE-wrenches Subject: Re: [RE-wrenches] Rapid shutdown for pol

Re: [RE-wrenches] (no subject)

2014-04-28 Thread Bill Brooks
dule(s) or panel(s) secured by removable fasteners and connected by a flexible wiring system. This is not a change. Please help me understand the concern. Bill Brooks. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of R

Re: [RE-wrenches] Nano cleaning and sealing products.

2014-04-21 Thread Bill Brooks
James, This product is probably much like Rain-X. While you could put it on PV modules, it would require reapplication on a fairly regular basis to keep it working. As you pointed out, I don’t think many, if any, module manufacturers that would specifically warranty their product with Rain-X

Re: [RE-wrenches] Rapid shutdown for pole mounts

2014-04-18 Thread Bill Brooks
Aaron, An exterior utility service panel with an underground service lateral is not considered in or on the building. Keep the dc conductors off of the building and you will be fine with a ground-mounted PV system. Don't bring them inside the building, and don't run them along the exterior of th

Re: [RE-wrenches] Three Inverters, One Disconnect?

2014-04-04 Thread Bill Brooks
nverters? Good, bad, or ugly? Thanks, Garrison From: Bill Brooks [mailto:billbroo...@yahoo.com] Sent: Friday, April 04, 2014 2:09 PM To: 'RE-wrenches'; 'Garrison Riegel' Subject: RE: [RE-wrenches] Three Inverters, One Disconnect? Don and Garrison, The word “dedicated

Re: [RE-wrenches] Three Inverters, One Disconnect?

2014-04-04 Thread Bill Brooks
Don and Garrison, The word “dedicated” means “no loads”. That is why, the way the code is written today, you cannot plug a microinverter into a wall outlet. There is no limit to the number of inverters that can be placed on a single breaker. The limitation for inverters, is the maximum overcu

Re: [RE-wrenches] Busbar 120% rule

2014-03-28 Thread Bill Brooks
Dave and Troy, I don't think JW had his facts correct on this. The standard test for a busbar is to place the highest allowable breakers directly below the main breaker to test for overtemperature of the busbar. With the requirement for Article 220 compliance of the panel, a panel that actually

Re: [RE-wrenches] AC Combiner with main breaker as system disconnect

2014-03-12 Thread Bill Brooks
re else in the panel that changes this? Glenn From: re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks Sent: Wednesday, March 12, 2014 7:24 PM To: 'RE-wrenc

Re: [RE-wrenches] Autocad

2014-03-12 Thread Bill Brooks
William, Go to http://www.associatedsoftwaresales.com/home.php . They do a 48-month lease of 2013 AutoCAD LT for $325. If you really need AutoCAD, there is no cheaper route that I know of. Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wre

Re: [RE-wrenches] AC Combiner with main breaker as system disconnect

2014-03-12 Thread Bill Brooks
Glenn, The vast majority of service equipment for residences is rated 10k AIC. Although utilities may say they have some residential services that exceed 10k short circuit availability, it is still pretty rare. Using single phase gear on a 3-phase commercial installation is a different sto

Re: [RE-wrenches] California State Fire Marshal's "Solar Photovoltaic Installation Guidelines"

2014-02-13 Thread Bill Brooks
required of the building. At least that's the interpretation I initially got from my local building and safety office. They've been sitting on my plans for two weeks so far. When they turn them around, I may have more to talk about. /wk William Korthof 714.875.3576 Sustainable Solution

Re: [RE-wrenches] California State Fire Marshal's "Solar Photovoltaic Installation Guidelines"

2014-02-13 Thread Bill Brooks
Yes Peter, It is called the 2012 International Fire Code. The California guidelines were turned into code in 2012. There is an explanation document I wrote available online at: http://solarabcs.org//about/publications/reports/fireguideline/index.html For those states that are using NFPA 1 as th

Re: [RE-wrenches] 208 V 240 in residential applications

2014-02-10 Thread Bill Brooks
WK, Marco, and William, Agreed that 208V versus 240V is not an issue for 240V single phase loads. Phase angle is not an issue for single phase loads--same reason that a single-phase inverter can work with 208/240/277V. In the case of the inverter, typically it is simply a winding count difference

Re: [RE-wrenches] Solar Module fire ratings

2014-02-07 Thread Bill Brooks
Mark, You should know better than anyone else that you can't corner the sun market. If you read the reports you will find that your deepest fears are unfounded. Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Fry

Re: [RE-wrenches] conductor properties of PV wire

2014-02-07 Thread Bill Brooks
Kirk, There is no standard diameter for PV Wire so Chapter 9 table 1 must be used. By the way, Table 1 is the code and the table in Annex C are not officially the code. They are simply informational based on the standard nominal diameters of various conductors. Many conductors have non-standard

Re: [RE-wrenches] (RE-wrenches) 2x200 amp meter main panel question

2014-01-23 Thread Bill Brooks
William and John, A "320" as it is affectionately called is a 400-amp panel with a 320-amp continuous duty. This is identical to two 200-amp panels that each has a 160-amp continuous duty-that we put 40-amp breakers into on a routine basis. The "busbars" are rated for 200-amps each, just like a

Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-23 Thread Bill Brooks
Jeffrey and Ray, Batteries can off-gas hydrogen-sulfide gas when under heavy charge or overcharge. It is the nasty rotten egg smelling gas. Definitely not to be inhaled since when it hits your lungs it turns back into sulfuric acid. To address Ray’s point, the new 690.12 regulation that has

Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-23 Thread Bill Brooks
Dan, I believe you are referring to the Sedona fire when you talk of the energized fence. I believe the fire department was in error when they reported that the rooftop EMT energized the fence. It is pretty clear from a review of the facts that the ac service drop burned free from the house and

Re: [RE-wrenches] Temperature Compensation calcs for wire

2014-01-22 Thread Bill Brooks
William, One way to think about this is that temperature correction is used based on the location of the ambient temperature you are concerned about. Mostly, we are worried about the very high temperature of conductors in a sunlit raceway on a roof. This gives us very high temperatures and we

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-21 Thread Bill Brooks
Frye Sent: Tuesday, January 21, 2014 6:03 PM To: RE-wrenches Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown OK. So I will have a high rate of acceptance if it buy an Tyco vacuum relay, and mount it in a Hoffman enclosure, and then put it on my roof? On 1/21/2014 5:45 PM, Bill Brooks

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-21 Thread Bill Brooks
Brian, The requirement is generic. A listed contactor can meet the requirement. A standard is only necessary for products that want to be innovative in meeting the 30V, 240VA. Killing all power is an option with existing listed equipment. NEC 90.4 does not apply. Bill. From: re-wrenches

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-16 Thread Bill Brooks
subject since it was a very far-reaching and potentially confusing new requirement in the NEC. Thanks for your interest and let's keep the constructive dialogue going on the subject. It is time to get involved in the NEC update process again. Bill Brooks. From: re-wrenches-boun...@lists.re

Re: [RE-wrenches] EGC ground impedance

2014-01-15 Thread Bill Brooks
delivers more than we could ever use in just about 8 minutes. And it's wireless!" ~William McDonough On Tue, Jan 14, 2014 at 10:47 PM, Bill Brooks mailto:billbroo...@yahoo.com> > wrote: Andy, How are you testing the ground impedance of the EGC? Bill. Fr

Re: [RE-wrenches] EGC ground impedance

2014-01-14 Thread Bill Brooks
Andy, How are you testing the ground impedance of the EGC? Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Andrew Truitt Sent: Tuesday, January 14, 2014 7:25 AM To: RE-wrenches Subject: [RE-wrenches] EGC ground impeda

Re: [RE-wrenches] CA Fire code

2014-01-09 Thread Bill Brooks
Martin, Regarding your reference to installations west of I-280 requiring Class A, I did not find that in Palo Alto's materials. The City of Woodside fire department was very involved in the CalFire Guidelines and I would not be surprised if they implemented such a requirement. If you can find

Re: [RE-wrenches] CA Fire code

2014-01-07 Thread Bill Brooks
ystem will result in a Class A fire-rated roof-mounted PV system. At least that's how I understood the presentation delivered by Christopher Flueckinger from UL during the "Fire Safety" session at SPI in Chicago. I'm sure Bill Brooks will chime in shortly and provide more clarit

Re: [RE-wrenches] SB 240 - No Neutral Sense Conductor

2013-12-19 Thread Bill Brooks
nominal voltage. Generally, this is not a problem since an inverter that does not act quickly enough will damage itself. Bill. Bill Brooks, PE Principal Brooks Engineering 3949 Joslin Lane Vacaville, CA 95688 707-332-0761 (office and mobile) b...@brooksolar.com (email) www.brooksolar.com

Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town, limited time only

2013-12-09 Thread Bill Brooks
nding electrode for PV arrays. He used everything short of drum rolls to build anticipation for this part of the presentation. Having personally contributed a short piece on this subject for SolarPro magazine along with Bill Brooks and John Wiles in 2008, I looked forward to this discussion. Finally, m

Re: [RE-wrenches] PV Wiring methods

2013-11-14 Thread Bill Brooks
not helping at all. The trend has been to make it harder to protect wiring. This trend will result in accidents. I think we should do better. Sincerely, William Miller From: re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org> [mailto:r

Re: [RE-wrenches] RE-wrenches Digest, Vol 6, Issue 423

2013-11-11 Thread Bill Brooks
William and David, This particular problem goes away with arc fault detection. The longer we wait to introduce arc fault detection into our systems, the more we will have opportunities for news reports such as the one William brings forward. Wire ties are not the problem. Could a wire tie cause

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-08 Thread Bill Brooks
Kirpal, I'm not aware of a 15-degree allowance for NEMA 3R. Others on this forum may be more familiar. Bottom line, if the installation instructions do no specifically allow for an angle, you have to assume that vertical is the only allowable orientation. The only rooftop disconnects that

Re: [RE-wrenches] MC Cable for DC runs

2013-10-21 Thread Bill Brooks
Howie, I think your electrician friend either misheard John or John was wrong. I believe the truth is that AC cable (aluminum clad) would have to be listed for dc. The NEC is specific about the grounding capabilities of the MC. I am unaware of any specific dc or ac requirements that MC has. There

Re: [RE-wrenches] smaller 3-phase commercial inverters

2013-10-18 Thread Bill Brooks
Marco, Besides the good responses you have already received, 20-30kW, 480V machines are really targeting larger installations that would be on facilities with 480V. I would generally not build a system with 480V inverters on a 208V service. For large systems, there are large inverters runnin

Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-27 Thread Bill Brooks
William, Just to add one more thing. I said that the M215 does not match well, but if you have them on hand, they would still work. You will probably power limit in the spring and fall, but the rest of the year you will probably do fine. The M250 has a higher operating voltage for 72-cell arran

Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-27 Thread Bill Brooks
William, Here is what I would recommend. 1. Put pairs of SQ-150s in parallel on an M250. 2. Put PC4JFs as two in series by two in parallel on M250. 3. For leftovers-two PC4JFs in series are the same as one SQ-150 so mix and match to your heart's content. The issue

Re: [RE-wrenches] GEC sizing for a high amp, low voltage PV system with microinverters

2013-09-18 Thread Bill Brooks
Nick, Thanks for the clarification-it is a mysterious threaded hole.. Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick Soleil Sent: Wednesday, September 18, 2013 10:19 AM To: RE-wrenches Subject: Re: [RE-wrenches]

Re: [RE-wrenches] GEC sizing for a high amp, low voltage PV system with microinverters

2013-09-18 Thread Bill Brooks
Dave, Gary, and Charlie, First, the directions from the manufacturer should be the guide as to whether a GEC is required or not. Just because a GEC terminal is located on the equipment, does not mean that one is required. Case in point-Enphase's new IG product does not require a GEC, yet it has

Re: [RE-wrenches] double insulated wire

2013-06-28 Thread Bill Brooks
Dave, To add to your point, the typical way to wire an ungrounded PV system is to use modules with PV Wire-connect them to homeruns of PV Wire-then transition at some point to standard wire in raceways. This means that the only change from a wiring method point of view is to use PV Wire whereve

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-05 Thread Bill Brooks
Troy, Overcurrent device size is matched to the conductor size. The inverse time constant nature of an overcurrent device can typically handle the surge currents as long as conductor sizing has truly been done correctly for the conductor. Circuit breakers are preferred to fuses because they can

Re: [RE-wrenches] P1 micro performance

2013-03-27 Thread Bill Brooks
Carl, Just to be clear, the performance tests mandated by the California Energy Commission, that all products in the U.S. follow, require that the maximum power rating is continuous (24/7). Actually, continuous means that it can operate for 3 hours straight at 40C (104F) (really hot). This does

Re: [RE-wrenches] Cable tray

2013-03-26 Thread Bill Brooks
William, I have all the respect in the world for you, but I'm not referring to "basket tray", which is only appropriate for small conductors. I'm talking about legitimate cable tray that can be up to 12" wide and that has a top and rungs every 12". The main facilities that use it in the United

Re: [RE-wrenches] AFCI

2013-03-26 Thread Bill Brooks
Wrenches, Fronius is releasing their AFCI inverters this month. They sent them to me for CEC approval. Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nathan Stumpff Sent: Tuesday, March 26, 2013 9:09 AM To: re-wrenches

Re: [RE-wrenches] Cable tray

2013-03-25 Thread Bill Brooks
William, I would strongly disagree that conduit is tried and true on rooftops. I have rarely seen good conduit runs on rooftops. Most electricians have no clue how to work with expansion joints. Conduit on rooftops is a bad idea in general. Most conduit runs in big buildings are all done indoor

Re: [RE-wrenches] Cable tray

2013-03-25 Thread Bill Brooks
All, Here is the language that has been accepted into the 2014 NEC: 690.31(C)(2) (2) Cable Trays. PV source circuits and PV output circuits using single-conductor cable listed and labeled as Photovoltaic (PV) wire of all sizes with or without a Cable Tray marking/rating shall be permitt

Re: [RE-wrenches] finding array ground faults

2013-02-06 Thread Bill Brooks
Marco, This should be fairly straightforward. If the whole roof is truly grounded, you have nothing to worry about. If it is not well grounded, then you have cause for pause. I would recommend the new Megger MIT410 (or420 or 430) device. It has a 50V setting which is hugely beneficial for t

Re: [RE-wrenches] Wire management

2013-01-09 Thread Bill Brooks
William, Nice work on the wire management side. For you and others that may not be aware, the U.S. Dept. of Energy funded the development of an online training version of my Field Inspection Guide for PV Systems (http://irecusa.org/wp-content/uploads/2010/07/PV-Field-Inspection-Guide-Jun e-2010-F-

Re: [RE-wrenches] center fed main panel and 120% rule

2012-10-15 Thread Bill Brooks
August, I'm not really worried about residential center fed buswork since the 120% exception only applied residential prior to the 2008 NEC and the location of the OCPD was not specified. The location of the OCPD was specified in the 2008 NEC to address commercial panelboards that are run a

Re: [RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread Bill Brooks
boB, The limit of 80-volts was to make an exception for single module devices like micro-inverters and for 48-volt battery systems and smaller. A change controller operating above 80V would be required to have an AFCI whether on or off grid if the array is mounted on a building. Bill. F

Re: [RE-wrenches] Two NEC questions

2012-10-14 Thread Bill Brooks
August, Who at SMA said that they won't be shipping AFCI inverters? I know they have been manufacturing. I have two of the AFCI inverters in operation at my office and they are very impressive. Three months of operation since startup without a single nuisance trip and it trips every time I simu

Re: [RE-wrenches] Solmetric PVA and Tigo

2012-08-27 Thread Bill Brooks
ugust 26, 2012 11:03 AM To: RE-wrenches Subject: Re: [RE-wrenches] Solmetric PVA and Tigo On 8/26/2012 7:54 AM, Jesse Dahl wrote: > Hello, > > Has anyone has experience using the Solmetric PVA and optimizers? Is there any issues? > > Jesse > You might ask Bill Brooks. He has a

Re: [RE-wrenches] Ilsco SGB bonding lug

2012-08-27 Thread Bill Brooks
Benn, This product appears to be significantly superior to the old-school ILSCO tin-plated copper lugs. While those lugs may have been the best thing going 10 years ago, there have been many improvements. This looks like one of them. I would argue with the statement that tin-plated copper is in

Re: [RE-wrenches] Line side taps in Hawai'i

2012-05-21 Thread Bill Brooks
May 16, 2012 10:48 PM > *Subject:* [RE-wrenches] Line side taps in Hawai'i > > Aloha Wrenches, > > I have recently started working in Hawaii on the island of Oahu and > have run into some interesting problems with the AHJ's. The biggest > issue is nobody is allowing lin

Re: [RE-wrenches] 120% Rule - applying to multiple load centers etc

2012-05-08 Thread Bill Brooks
Andy, August, and Eric, There will likely be significant changes in the 2014 NEC to clarify the situation you are discussing. Fault current has very little to do with this issue. The key distinction was used in my proposal to the 2014 NEC that removed the statement "and conductor" in 705.1

Re: [RE-wrenches] Transformerless inverters

2012-04-20 Thread Bill Brooks
Joel, It ain't over until it's over. The statewide effort will not limit transformerless inverters if I have anything to do with it. This is something these guys got on their brain, and they won't let it go-YET. Once they understand better that these inverters are safer, we will get them to bac

Re: [RE-wrenches] WOW Something Gone Very Wrong

2012-03-29 Thread Bill Brooks
http://solarprofessional.com/article/?file=SP4_3_pg14_QA_2 <http://solarprofessional.com/article/?file=SP4_3_pg14_QA_2&search=> &search= (Bill Brooks article on Fuse Servicing disconnect requirements) http://solarprofessional.com/article/?file=SP4_3_pg64_Hren <http://solarprofessional.com/article

Re: [RE-wrenches] a PV titan is to be no more

2011-12-21 Thread Bill Brooks
ches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks Sent: Tuesday, December 20, 2011 7:44 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] a PV titan is to be no more Marco, With "BP" on the module, it means a lot more than some no name brand. Just because

Re: [RE-wrenches] a PV titan is to be no more

2011-12-20 Thread Bill Brooks
Marco, With "BP" on the module, it means a lot more than some no name brand. Just because they are not producing anymore does not have any impact on their warranty obligation unless BP goes out of business-that is not likely to happen in your lifetime. Bill. From: re-wrenches-boun...@li

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Bill Brooks
On 12/1/2011 14:56, Gary Willett wrote: Ray: Look at Appendix F in the Expedited Permit Process for PV Systems - A Standardized Process for the Review of Small-Scale PV Systems Prepared by Bill Brooks, P.E. Brooks Engineering This document provides the ASHRE temperatures for a

Re: [RE-wrenches] module storage

2011-11-30 Thread Bill Brooks
Open circuit. If something comes apart internally at short circuit you have a possible arc. Bill. -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz Sent: Wednesday, November 30, 2011 7:07 AM To: RE-

Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Bill Brooks
Folks, One factor often overlooked when calculating minimum system voltage is degradation of the array and rating variations of the modules. If you assume 0.5% loss in voltage per year, you need to factor a 10% higher voltage at year one. Manufacturers tolerance on voltage and current c

Re: [RE-wrenches] Bifacial modules

2011-11-01 Thread Bill Brooks
Keith, This is easy to test. Simple take an irradiance sensor, turn it upside-down and test the irradiance on the bottom surface of any PV array. It will vary greatly based on exposure to reflected light and so on, but it will rarely be above 100 W/m^2. 10% improvement is an absolute maximum fo

Re: [RE-wrenches] Solmetric PVA-600

2011-07-29 Thread Bill Brooks
Keith, As I board a flight from Maui to Oahu this evening, this curve tracer rocks. It is truly what I have been wait for over a decade. Everyone should buy one and I don't even get royalties for saying that. Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun

Re: [RE-wrenches] Anti-Islanding Explanantion

2011-07-20 Thread Bill Brooks
Google it. It is on the www.irecusa.org website. Click on publications. You probably missed part of the URL. Bill. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.

Re: [RE-wrenches] Anti-Islanding Explanantion

2011-07-19 Thread Bill Brooks
All, A resource that all wrenches need to be aware of and read is a document published by the Interstate Renewable Energy Council called, "Connecting to the Grid". It includes a good laymen's explanation of anti-islanding--which goes far beyond voltage and frequency limits. URL below http://irecu

Re: [RE-wrenches] how would you measure a partial short circuit

2011-07-01 Thread Bill Brooks
Nick, If your voltage is low and there is no ground fault, either positive and negative are connected mid string, bringing the voltage down, or a bunch of modules never got connected in series. In either case, the Voc difference between the two strings will create a significant current flow at

Re: [RE-wrenches] how would you measure a partial short circuit

2011-06-30 Thread Bill Brooks
Nick, How can you conclude that there was nothing wrong in regard to ground faults. What was your reasoning that lead you to that conclusion. I think there is doubt on your conclusion unless half the wiring in the second string is backwards. Bill. From: re-wrenches-boun...@lists.re-wren

Re: [RE-wrenches] Tigo to go?

2011-06-08 Thread Bill Brooks
Marco, The only argument you can make for a system like yours is to say that if the modules degrade at different rates, then the Tigo optimizers make sense. Otherwise, I can't see how it could be anything but a slight loss. Tough call for $15k. Other attributes like monitoring and shutting off

Re: [RE-wrenches] big combiner box

2011-06-06 Thread Bill Brooks
Marco, Why?-is this a low current string or a really high current feeder? Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco Mangelsdorf Sent: Monday, June 06, 2011 4:05 PM To: 'RE-wrenches' Subject: [RE-wrenches]

Re: [RE-wrenches] NABCEP Stamp

2011-03-30 Thread Bill Brooks
Andrew and Troy, While I can't speak for NABCEP, I would expect that NABCEP should be very opposed to this type of use of their logo. NABCEP does not certify the work that a NABCEP certificant does. They only certify that the installer has met the obligations for certification. There is a HUGE

Re: [RE-wrenches] Fire Access lane for ground mount

2011-03-17 Thread Bill Brooks
Jim, Having taught classes in New Jersey on the subject, I can tell you that the fire service is looking into these types of requirements for ground-mounted systems. The 2012 IFC only includes requirements for buffer areas around the perimeter. Whether a fire truck needs to get around a facilit

Re: [RE-wrenches] grounding the Enphase inverter

2011-03-05 Thread Bill Brooks
@lists.re-wrenches.org] On Behalf Of Bill Brooks Sent: Friday, March 04, 2011 5:51 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] grounding the Enphase inverter The better question is why is there a solid ground in the inverter. As I stated before-we are talking about system groun

Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread Bill Brooks
The better question is why is there a solid ground in the inverter. As I stated before-we are talking about system grounding-with 100+ years of electrical history and precedent to back it up. System grounding rules are not open to a lot of discussion. That is why my recommendation since be

Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread Bill Brooks
g] On Behalf Of Bill Brooks Sent: Thursday, March 03, 2011 10:48 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] grounding the Enphase inverter All, While there is ambiguity in the 2008 NEC in 690.47(C) on the requirements for system grounding of PV systems, the 2011 NEC in 690.47(C) clar

Re: [RE-wrenches] grounding the Enphase inverter

2011-03-03 Thread Bill Brooks
ional electrode, install a j-box at the point near ground-level where the conduit transitions from vertical to horizontal and install an irreversibly spliced bare 6AWG to run from the j-box to a ground rod below the j-box--mildly painful, but very doable. Bill. Bill Brooks, PE Principal Brooks Engine

Re: [RE-wrenches] NEC 690.11 - Arc Fault Protection Provision Questions ?

2011-03-02 Thread Bill Brooks
ercial buildings? How about an enclosed MW in a box solution in the middle of a MW power plant, is that a building? I like for example that in the 600V max limitation that it specifies 1 or 2 family dwellings, leaving small & large commercial buildings opportunity to have 1000V systems. Any c

Re: [RE-wrenches] "Keep that there PV off my grid!"

2011-02-15 Thread Bill Brooks
Karl, What you are referring to is a "reverse power relay." These are common devices used for customer-generators. Basler is one company that makes them. Just google the topic and you will find several companies. The utility may have a preferred product so go with them if they have one. Th

Re: [RE-wrenches] Calculation of Maximum Circuit Current

2011-02-11 Thread Bill Brooks
Peter and Larry, Brian's post was correct and consistent with the 2011 NEC. It is not correct to apply both 1.25 factors on the dc side. This has been done for years, but it is inconsistent with the rest of the code. Conditions of use are only applied to maximum current-defined by 690.8(A) as r

Re: [RE-wrenches] Calculation of Maximum Circuit Current

2011-02-11 Thread Bill Brooks
To add to Brian's well formulated response, the 2011 NEC is much more detailed and accurate on this subject. Oversizing wire is not a big deal on residential systems, but it is prohibitively expensive in megawatt jobs. Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenche

Re: [RE-wrenches] SolarEdge

2011-01-29 Thread Bill Brooks
Any chance for solar resource monitoring to help the data make sense? Irradiance monitoring is necessary to understand performance. Does SolarEdge have that option yet? Bill. -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.o

Re: [RE-wrenches] Inverter oversizing

2011-01-19 Thread Bill Brooks
Power LLC 462 Solar Way Drive Hyde Park, VT 05655 www.independentpowerllc.com NABCEP Certified PV Installer Vermont Solar Partner 23 Years Experience, (802) 888-7194 From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill B

Re: [RE-wrenches] Inverter oversizing

2011-01-19 Thread Bill Brooks
energy to throw my graph off by very much. Kent Osterberg Blue Mountain Solar, Inc. Bill Brooks wrote: Kent, How often were your data records? To capture edge of cloud effects, you need one-second data. Not many people gather that fast or that much data on inverters. I don't thin

Re: [RE-wrenches] Inverter oversizing

2011-01-19 Thread Bill Brooks
Kent, How often were your data records? To capture edge of cloud effects, you need one-second data. Not many people gather that fast or that much data on inverters. I don't think there is that much energy in these spikes, but they are real and make some difference. 15-minute average data will c

Re: [RE-wrenches] Xslent?

2011-01-06 Thread Bill Brooks
ow on residential it makes no sense. However for commercial that might have to pay extra for PF issues, to have the inverter adjust for this makes sense. Its the reason they( inverter companies ) are doing it. I"ve heard a better more complete reason of course from Bill Brooks, who maybe can chime

Re: [RE-wrenches] Handy Map for ASHRAE temperatures

2010-12-14 Thread Bill Brooks
Jesse, The map is in degrees C not F and it is for the mean extreme minimum drybulb temperature from the ASHRAE Fundamentals 2009 edition. It is a statistical lowest expected temperature for calculating the maximum voltage of a PV array. Bill. -Original Message- From: re-wrenches-boun..

Re: [RE-wrenches] feed-in imbalance

2010-12-10 Thread Bill Brooks
Jamie, The 6kVA imbalance limit, as you point out, is for 120V/240 split phase services, not 3-phase. It comes from California’s Rule 21 interconnection rules adopted by each California utility. As the technical facilitator of the development of Rule 21, I had a lot to do with the 6kVA numbe

Re: [RE-wrenches] Tranformless inverter

2010-12-10 Thread Bill Brooks
...@luminalt.com> > > *From:*re-wrenches-boun...@lists.re-wrenches.org > <mailto:re-wrenches-boun...@lists.re-wrenches.org> > [mailto:re-wrenches-boun...@lists.re-wrenches.org > <mailto:re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of *Bill > Brook

Re: [RE-wrenches] feed-in imbalance

2010-12-10 Thread Bill Brooks
Marco, All 3-phase services, and single split-phase services has imbalances from time to time. The question of whether the imbalance is problematic depends on the size of the imbalance relative to the service transformer. Since 3-phase services are generally larger, a 10kW phase-to-phase connec

Re: [RE-wrenches] Driving Point Impedance of the Point of Connection of a Grid-tied PV System

2010-12-10 Thread Bill Brooks
Peter, Are you making your measurement before and after the inverter breaker? I believe what you are attributing to the breaker is actually the voltage rise from the service transformer, through the service conductors, through the service panel. A 3-Volt drop is common when adding a 4kW load to a

Re: [RE-wrenches] Wire Management and Panel Claw

2010-12-08 Thread Bill Brooks
Sam, Panel Claw requires conduit to properly protect conductors, particularly row-to-row. I have seen bundling done, but it will not last long. Panel Claw is just one of many companies that do not provide much, if any, wire management strategies. Bill. From: re-wrenches-boun...@lists.re

Re: [RE-wrenches] Megger for array testing

2010-11-18 Thread Bill Brooks
: www.alterisinc.com From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks Sent: Wednesday, November 17, 2010 9:11 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Megger for array testing Meggerers, Although sho

Re: [RE-wrenches] Megger for array testing

2010-11-17 Thread Bill Brooks
Meggerers, Although shorting the terminals to perform the megger tests may provide the most uniform voltage profile, it is difficult to perform on many arrays and adds unnecessary complexity to a test that needs to become routine for all PV installations. The appropriate way to perform the