[RE-wrenches] Huawei inverter tech support

2024-02-14 Thread Eric Smiley via RE-wrenches
We have a client with a Huawei 9KTL-USL0 who recently contacted us about his system. Does anyone know how to obtain tech support in NA for these products? *Eric Smiley,* Design Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENER

Re: [RE-wrenches] Fortress

2024-02-14 Thread Eric Smiley via RE-wrenches
. IMHO relying on firmware and circuit boards to keep your system running and protect it from catastrophic failure is not sustainable. *Eric Smiley,* Design Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.

Re: [RE-wrenches] Grid Tied Inverter back feed to Generator

2023-12-01 Thread Eric Smiley via RE-wrenches
We were called to repair a system where this happened. All the micro inverters were fried and so was the generator. It caused a voltage rise that the monitoring system recorded at 348 V before it went down, when the PV ran the generator as a motor. *Eric Smiley,* Design Manager e...@vecoop.ca T

Re: [RE-wrenches] Off Grid, Cloudy Days, Solar Tilt Question

2023-10-25 Thread Eric Smiley via RE-wrenches
so a shallow tilt is OK. *Eric Smiley,* Design Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>* * <https://viridianenergy.ca/>* On Wed, 25 Oct 2023 at 17:42, integrityenergy101 via R

Re: [RE-wrenches] Fronius USA available 2023 & 2024 ?

2023-08-25 Thread Eric Smiley via RE-wrenches
and good service in Australia and Europe. Not sure why the US gets short shrift. *Eric Smiley,* Design Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>* * <https://viridianenergy.ca/>* On F

Re: [RE-wrenches] Schneider XW+ Repair

2023-08-01 Thread Eric Smiley via RE-wrenches
Last time I had an AC relay go, I ordered a board from Mark Snyder. mseproje...@marksnyderelectric.com Eric Smiley Design Manager E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250-703-6004 W: viridianenergy.ca On Tue., Aug. 1, 2023, 16:00 Andrew Perkins via RE-wrenches, <

Re: [RE-wrenches] Lithium battery recommendation

2023-07-13 Thread Eric Smiley via RE-wrenches
Keep in mind the Fortress eVault is a 500 lb beast. Our installers complained about it and we've moved to smaller, rack-mount units and are currently testing the HomeGrid Stack'd in various configurations. *Eric Smiley,* Design Manager e...@vecoop.ca T: 250.703.6004 <+12507036004

[RE-wrenches] Thermal paste for battery connections

2023-06-21 Thread Eric Stevens via RE-wrenches
very thin coating is sufficient. I use it on all connections that I don't solder. Eric Stevens Vermont Made Energy Grafton VT___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenche

Re: [RE-wrenches] XWPro produces noise at low (<50 W Power)

2022-12-06 Thread Eric Smiley via RE-wrenches
to recommission the system. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>* * <https://viridianenergy.ca/>* On Tue, 6 Dec 2022 at 11:45, Tump via RE-wrenche

[RE-wrenches] XWPro produces noise at low (<50 W Power)

2022-12-06 Thread Eric Smiley via RE-wrenches
of resonance with the inverter enclosure. But it's the first time we have encountered this. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>* * <http

Re: [RE-wrenches] AC Coupling Standard?

2022-12-02 Thread Eric Smiley via RE-wrenches
stry keeps evolving and improving, which is great for keeping us on our toes and I find it very exciting. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>* * <https://v

Re: [RE-wrenches] 3 phase off-grid UL listed

2022-09-08 Thread Eric Smiley via RE-wrenches
configured for 3-phase, I would recommend an external transfer. The relays have a habit of welding. Once they were configured properly, there was no problem starting large HVAC loads and even large single phase loads were OK. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004

[RE-wrenches] Old Birdhouse systems

2022-09-07 Thread Eric Smiley via RE-wrenches
in the CAT5 cable anyway? *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>* * <https://viridianenergy.ca/>* ___ List sponsored

Re: [RE-wrenches] Battery Monitor for Li

2022-09-02 Thread Eric Smiley via RE-wrenches
I am having the same problem - same situation. I am going to tweak the efficiency value and see if it helps. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>* * <http

Re: [RE-wrenches] GT inverter for SWWP turbine

2022-08-11 Thread Eric Smiley via RE-wrenches
Skybox is discontinued and tech support is limited. There are still significant software issues with them that make them unreliable for battery back-up. We are in the process of replacing the 3 Skyboxes we wish we had never installed. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004

Re: [RE-wrenches] Magnum inverter/generator integration problems

2022-07-25 Thread Eric Smiley via RE-wrenches
Also check bonding and ground loops (e.g. genny neutral bonded and also bonded at main panel). This can cause voltage to bounce around and the inverter won't sync. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRID

[RE-wrenches] Sol-Ark arc fault issues

2022-05-10 Thread Eric Smiley via RE-wrenches
or if we are having poor luck. Our other string inverter systems are not displaying this problem, which leads us to believe it isn't due to installer error. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENER

[RE-wrenches] Outback Radian transfer time

2022-02-04 Thread Eric Smiley
. Does anyone know if there's a way to reduce the transfer time? The transition to charging is smooth. I don't understand why it's so clunky transitioning back to inverting. Eric Smiley Project Manager, North Island E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250-703-6004 W

Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600

2022-01-26 Thread Eric Smiley
I looked up the CSA record for the XW PDP and it shows: - Maximum System Voltage (DC) 150V dc - Maximum Battery System Voltage 62 V dc (48V nominal) - Maximum System Voltage (AC) 140/280V ac *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004

Re: [RE-wrenches] Conext XW Pro Compatible Generators?

2022-01-18 Thread Eric Smiley
Usually I wouldn't chime in with a single example but we have a single customer with a Kohler 12RES on propane and a Connext XW+. It's worked well for three years and was easy to connect. Eric Smiley Project Manager, North Island E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250

Re: [RE-wrenches] BP HI / Namaka with Sol-ark inverters

2022-01-06 Thread Eric Smiley
disappear. I can't recall the last time I had to repair/service a Magnum system unless it was user error. Keep it simple! Eric Smiley Project Manager, North Island E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250-703-6004 W: viridianenergy.ca On Thu., Jan. 6, 2022, 09:28 Jerry Shafer

Re: [RE-wrenches] Enphase Enpower Smart Switch as service disconnect

2021-09-10 Thread Eric Smiley
The spec sheet indicates it is rated as Service Equipment in the US but not in Canada. :-( *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>* * <https://viridianener

Re: [RE-wrenches] Is Solark UL 9540 Certified?

2021-07-20 Thread Eric Smiley
with Discover Magnum doesn't appear to have any UL9540 battery partners Sol-Ark has a long list on their website. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>* * <http

Re: [RE-wrenches] Generator and AC coupling on a Sol-Ark

2021-05-11 Thread Eric Smiley
Just remember to turn off the AC coupled solar when manually starting the generator! *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>* * <https://viridianenergy.ca/>

Re: [RE-wrenches] seeking 3ph battery based/backed inverters and experiences

2021-04-20 Thread Eric Smiley
I've done 3phase with 6 Schneider Conext XW. It worked well but when you convert to 3-phase you lose surge capacity because you are turning the inverters into 120V inverters from 240. *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18

[RE-wrenches] Trace DR inverter fan

2021-02-04 Thread Eric Smiley
I have a client whose Trace DR 1524 inverter (yes, it's an old system) fan is running constantly. I haven't been to the site (3 hour drive, 1 hour boat ride) but I am guessing that it's a failure of a temperature sensor. Does anyone have experience with something like this? Eric Smiley, MASc

Re: [RE-wrenches] fortress power question

2021-02-01 Thread Eric Smiley
board. Eric Smiley, MASc Project Manager, North Island E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250-703-6004 W: viridianenergy.ca <http://www.viridianenergy.ca> <http://www.viridianenergy.ca/> RENEWABLE POWER NOW On Mon, 1 Feb 2021 at 14:01, Jason Szu

[RE-wrenches] MidNite SOB problem and possible solution

2020-12-16 Thread Eric Smiley
and/or solution. Eric Smiley, MASc Project Manager, North Island E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250-703-6004 W: viridianenergy.ca <http://www.viridianenergy.ca> <http://www.viridianenergy.ca/> RENEWAB

Re: [RE-wrenches] Disconnects for "ungrounded" arrays

2020-10-08 Thread Eric Smiley
You may be thinking of the change to not requiring overcurrent protection on both conductors. Eric Smiley, MASc Project Manager, North Island E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250-703-6004 W: viridianenergy.ca <http://www.viridianenergy.ca>

Re: [RE-wrenches] Solar Edge optimizer attachment using EcoFoot 2 mounting

2020-08-31 Thread Eric Smiley
We have similar curiosity but using Tigo. We also would like to use APS QS1 micro-inverters and the MLPE mounts that Ecolibrium has don't really fit the bill. Eric Smiley, P.Eng. Project Manager, North Island E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250-703-6004 W

Re: [RE-wrenches] Programs for one line DWGs.

2020-06-18 Thread Eric Smiley
Draftsight is pretty good if you're familiar with AutoCad. The basic version is an autocad Lt clone. Eric Smiley, P.Eng. Project Manager, North Island E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250-703-6004 W: viridianenergy.ca On Thu., Jun. 18, 2020, 4:14 p.m. Jamie Rennie

Re: [RE-wrenches] Programs for one line DWGs.

2020-05-19 Thread Eric Smiley
I have been using DraftSight. It's an AutoCAD LT clone. Handy for when clients that send me AutoCAD (dwg) files. However, they have brought out a 3D version. Eric Smiley, P.Eng. Project Manager, North Island E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250-703-6004 W

Re: [RE-wrenches] Rapid Shutdown Compliance

2020-05-05 Thread Eric Smiley
Canadian EC requires) which is hundreds of feet away. In this circumstance but without back-up, we would usually just use an AC disconnect near the meter to initiate RS, but now we're facing the prospect of running a new control circuit all the way back to the pole or requesting a variance. Eric

Re: [RE-wrenches] Problems with Conext SW inverter

2020-02-04 Thread Eric Smiley
to compensate clients and installers who have wasted far too much time and money trying to make it work as promised. Eric Smiley, P.Eng. Project Manager, North Island E: e...@vecoop.ca T: 1-888-386-0116 ext 702 (toll free) C: 250-703-6004 W: viridianenergy.ca <http://www.viridianenergy

[RE-wrenches] Problems with Conext SW inverter

2020-01-31 Thread Eric Smiley
. The problem is when Equalize is enabled, the system goes through Bulk and Absorption just fine. However, when it switches to Equalize it doesn't actually equalize. What I observed was the voltage actually decreased to 0.5 V below the Absorption Voltage setting. Eric Smiley, P.Eng. Project Manager

Re: [RE-wrenches] merging PV data from different dashboards

2019-05-26 Thread Eric Youngren
of in Myanmar. All the best Eric On Sun, May 26, 2019 at 5:22 AM Kirk Herander wrote: > Hi All, > > I have a premium client I’ve done multiple systems for over the years with > multiple inverter monitoring platforms (SolarEdge, Enphase, Fronius, > Outback, etc.). I h

[RE-wrenches] PV waste problem

2019-04-20 Thread Eric Stikes
look for them, you're likely to find others like us closer to you. Organizations like RecyclePV are focused more on recycling for mods that are not reusable. There are options. So please be responsible and do not throw used mods in the landfill. Thanks for giving me a soapbox for a moment. * Eric

Re: [RE-wrenches] wireless relays for load shedding?

2018-05-23 Thread Eric Youngren
the loads directly (and charges the battery), there are no pass-through loads on the inverter output. On Wed, May 23, 2018 at 12:16 PM William Miller <will...@millersolar.com> wrote: > Eric: > > Any reason not putting these loads on a gen-fed panel? > > William > > > On M

[RE-wrenches] wireless relays for load shedding?

2018-05-23 Thread Eric Youngren
. Has any of you done this kind of thing? Any suggestions on equipment or best practices? THANKS! Eric Youngren ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings:

[RE-wrenches] Ibew is working to exclude C-46 contractor’s from installing Batteries.

2018-03-23 Thread eric
will seek to add the C10 license, as would I. Until then, I will join CalSSA in advocating for the status quo.Thanks for sharing, Jason. Peter, you can reach me through Byers Solar, we're a CalSSA member and C46 contractor (under my license).Eric StikesSunHarvest Solar

[RE-wrenches] 3-Phase SolarEdge L-L 215v

2018-02-13 Thread Eric Stikes
pole breakers but everything is pretty much 1-phase I believe. I'm wondering if I should consider reconfiguring the system with 1-Ph inverters tied in to only 2 of the utility legs. I asked SolarEdge weeks ago but getting nothing from them. Any thoughts? Thanks! Eric Stikes SunHarvest Solar +1 (530)

[RE-wrenches] GSM modem to connect MATE3 to the internet?

2017-11-17 Thread Eric Youngren
? I've searched around on the internet but I can't find any good information. Eric Youngren Rainshadow Solar Island Energy Systems Orcas Island, WA capillary.systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org

Re: [RE-wrenches] Polaris gone bad?

2017-04-10 Thread eric
me astray! Eric Stikes SunHarvest - Original Message - Subject: Re: [RE-wrenches] Polaris gone bad? From: "William Miller" <will...@millersolar.com> Date: 4/8/17 2:48 pm To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org> Wrenches: I am

[RE-wrenches] Polaris gone bad?

2017-04-06 Thread eric
seeing this? Wondering if this is an industry-wide issue regarding a Polaris manufacturing defect or if we're still in the realm of isolated flukes. Eric SunHarvest (530) 559-5023 ___ List sponsored by Redwood Alliance List Address: RE-wrenches

[RE-wrenches] NM Cable temp rating, ampacity, application

2017-04-04 Thread eric
ited ampacity of the 6AWG Romex. Can someone illuminate this issue for me as to whether or not NM cable is rated at 90 degrees AND therefore a 6AWG conductor in NM cable would have a 75A rating? Cheers, Eric SunHarvest ___ List sponsored by Red

Re: [RE-wrenches] Undercurrent Protection?

2016-11-01 Thread eric
, always learning, Eric Stikes Founding Director & CEO Good Sun Solar, A CA non-profit corp. www.goodsun.life (530)798-3738 - Original Message - Subject: Re: [RE-wrenches] Undercurrent Protection? From: e...@harvesthesun.com Date: 11/1/16 11:01 am To: "RE-wrenches"

Re: [RE-wrenches] Undercurrent Protection?

2016-11-01 Thread eric
, right?...unless I am missing something. I won't blame you if you decide you have more important things to attend than educating me on the nuances of the NEC. I'm still learning and I do greatly appreciate your insight! Eric - Original Message - Subject: Re: [RE-wrenches]

[RE-wrenches] Undercurrent Protection?

2016-10-31 Thread eric
continuous per-phase current rating or 42 percent of the continuous-current rating of any seriesconnected devices in the autotransformer neutral connection. Eric Stikes Founding Director & CEO Good Sun Solar, A CA non-profit corp. www.goodsun.life (530) 559-

Re: [RE-wrenches] Bypassing a broken PV module

2016-07-23 Thread eric
believe you made the right call by refusing to do the work as you may be liable in the (however unlikely) event of catastrophic failure at the mod in question. The array won't look so nice anymore if half of it is melted and charred. Play it safe. Get rid of it. Eric Stikes Founding Director

Re: [RE-wrenches] FW: Solmetric News - SunEye Discontinued

2016-04-08 Thread eric
Picking up this issue after some time has passed... Has anyone found, or received any news on, a replacement for the Solmetric SunEye other than Pathfinder? Eric Stikes Founding Director & CEO Good Sun Solar, A CA non-profit corp. www.goodsun.life (530)798-3738 - Original Mes

[RE-wrenches] 120% Rule on subpanel or main

2016-03-31 Thread eric
uctor ampacity aside). Cheers, Eric Stikes Founding Director & CEO Good Sun Solar, A CA non-profit corp. www.goodsun.life (530)798-3738 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email

Re: [RE-wrenches] poly pipe welding/fusing machines

2015-11-23 Thread Eric Youngren
difficult and time consuming part.The McElroy equipment is much easier, faster and reliable for professional use. Best, Eric On Sun, Nov 22, 2015 at 3:55 PM, jay <jay.pe...@gmail.com> wrote: > I’m looking into buying a poly pipe welding/fusing machine. > 1”-2” sizes > > Does any

[RE-wrenches] Old or Damaged PV Modules

2015-08-24 Thread eric
we have projects in Rwanda, Ecuador, India, and here in the USA. We donate materials and labor to communities, schools, medical facilities, and tribal nations. Help us help those in need. Don't throw it away, recycle it! Eric Stikes Founding Director Good Sun Solar, A CA non-profit corp

Re: [RE-wrenches] Old or Damaged Modules

2015-08-24 Thread eric
Sharps, we have a project ready to go. Thanks! Eric Stikes Founding Director CEO Good Sun Solar, A CA non-profit corp. www.goodsun.life (530)798-3738 - Original Message - Subject: Old or Damaged Modules From: Garrison Riegel garri...@solarserviceinc.com Date: 8/24/15 12:04 pm

[RE-wrenches] PV Mod skylight (clear backsheet)

2015-03-19 Thread eric
Anyone have a recommendation for a PV module that doubles as a skylight, i.e., has a clear backsheet? I have a client who would like to explore the option of putting solar on his greenhouse. I mentioned that the sunlight transmission would be significantly reduced but he saw it in action

Re: [RE-wrenches] Solar cooker plans request

2015-03-12 Thread Eric Youngren
weather or at night.That is more of a project than your friends in Guatemala will probably be able to tackle but I think its a cool innovation in solar cooking. all the best, Eric On Wed, Mar 11, 2015 at 11:54 PM, Allan Sindelar al...@sindelarsolar.com wrote: Wrenches, Our closest rural

Re: [RE-wrenches] Cable crimper question

2015-02-06 Thread Eric Youngren
value. All the best, Eric *Eric YoungrenSolar Nexus International* PO Box 894 1016 Discovery Way Eastsound, WA 98245 USA (360) 376-6842 www.solarnexusinternational.com w http://www.solarnexus.wordpress.com/ww.picopowerboss.com Skype name: ericyoungren On Fri, Feb 6, 2015 at 3:35 PM, Allan Sindelar

Re: [RE-wrenches] Grid-tied Trace SW

2014-09-09 Thread Eric . Bentsen
to sell back. This would be up to AHJ. Rgds, _ Eric Bentsen | Schneider Electric | Customer Care Center | Advanced Technical Support | Technical Support Engineer Phone: 866-519-1470 option #1

Re: [RE-wrenches] Grid-tied Trace SW

2014-09-09 Thread Eric . Bentsen
Hi William, Please remember the GTI is not compatible with SW models manufactured prior to 2002. Rgds. _ Eric Bentsen | Schneider Electric | Customer Care Center | Advanced Technical Support

Re: [RE-wrenches] trace SW plus fan

2014-09-08 Thread Eric . Bentsen
, 135.5CFM/12VDC/3000RPM Rgds, _ Eric Bentsen | Schneider Electric | Customer Care Center | Advanced Technical Support | Technical Support Engineer Phone: 866-519-1470 option #1 | Schneider

[RE-wrenches] A legal PV install in CA

2014-08-22 Thread eric
California Wrenchers,I have a C-46. A company with which I subcontract has a C-10 but uses non-licensed, non-journeyman, non-apprenticed laborers to complete all phases of their PV installations, including the final tie-in and commissioning. These guys are working under no supervision. I have the

Re: [RE-wrenches] Trace SW4024 LCD display problem

2014-06-27 Thread Eric . Bentsen
Hi Larry, We may still have a few display boards left. Call in to the number below and we can check P A. Rgds, Eric _ Eric Bentsen | Schneider Electric | Customer Care Center | Advanced Technical

Re: [RE-wrenches] Modified sine deterioration

2014-05-20 Thread Eric . Bentsen
repairable, although parts supplies are dwindling. The cost of true sine wave inverters has come down significantly in recent years. That way you don't need to worry about compatibility. Rgds, _ Eric Bentsen

Re: [RE-wrenches] Charge Controller with Configurable Maximum Output Current

2014-01-03 Thread Eric . Bentsen
Hi Jason, Both the XW MPPT60 (865-1030-1) and MPPT80 (865-1032) models can have the charge % adjusted using the SCP (865-1050). Advanced SettingsCharger SettingsMax Chg Rate Rgds, _ Eric Bentsen

Re: [RE-wrenches] Higher LVR to force full re-charge in small OGPV systems

2013-12-31 Thread Eric Youngren
for this tender. Thanks again folks! Lets hope we win the bid! Eric On Tue, Dec 31, 2013 at 12:01 PM, Ray Walters r...@solarray.com wrote: I'll chime back in on a few points: To MPPT or not: It all gets down to the budget: I find the tipping point to be around 250 to 400 watts. My small

[RE-wrenches] Higher LVR to force full re-charge in small OGPV systems

2013-12-30 Thread Eric Youngren
as possible. That's the idea, anyway. I'd appreciate any advice from you all. Thanks! Wishing you all a happy and productive 2014! Best energy, Eric ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email

Re: [RE-wrenches] Remote monitoring for off-grid system

2013-12-05 Thread Eric Youngren
=Q2uU2oQ0vI6a. best regards, Eric On Thu, Dec 5, 2013 at 1:03 PM, Davis Terrell da...@mckernongroup.comwrote: Hi Wrenches, I am evaluating remote monitoring solutions for an off-grid project and wanted to get any feedback people were willing to share. I see my three main choices as Outback

Re: [RE-wrenches] SW repair

2013-12-04 Thread Eric . Bentsen
that may be able to repair at a component level, you need to email them for a quote : phantompowerservices.com Rgds, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-11 Thread Eric . Bentsen
, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001# | Email: eric.bent...@schneider-electric.com | Site: www.schneider-electric.com

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-08 Thread Eric . Bentsen
Hi Kirpal, All Square D safety switches are UL tested in the Vertical position ONLY, so if someone is trying to install a switch in any other position other than vertical, that will be between them and the inspector. Hope this helps. Eric

Re: [RE-wrenches] Hidden freight damage

2013-11-04 Thread Eric . Bentsen
not sign anything until then. Sometimes, the manufacturer may step up and cover shipping damage to keep the customer happy. Eric _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES

Re: [RE-wrenches] Trace 2548 intermittent power problem...55 not 25

2013-10-17 Thread Eric . Bentsen
Hi Eric, Sounds like a bad control board. Swap the inverter and you should be back in business. Rgds, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support

Re: [RE-wrenches] GTBB resistance

2013-10-10 Thread Eric . Bentsen
to pass a federal law so these utility companies will stop obstructing clean energy. Rgds, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative

Re: [RE-wrenches] parallel stacking SW

2013-10-04 Thread Eric . Bentsen
, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001# | Email: eric.bent...@schneider-electric.com | Site: www.schneider-electric.com/solar | Address

Re: [RE-wrenches] Trace SWs in Energy Management Mode

2013-10-04 Thread Eric . Bentsen
, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001# | Email: eric.bent...@schneider-electric.com | Site: www.schneider-electric.com/solar

Re: [RE-wrenches] Trace SWs in Energy Management Mode

2013-10-04 Thread Eric . Bentsen
, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001# | Email: eric.bent...@schneider-electric.com | Site: www.schneider-electric.com/solar | Address

Re: [RE-wrenches] Search mode

2013-09-10 Thread Eric . Bentsen
because certain loads require continuous AC, i.e. the clock on your microwave, or a fridge,etc. The power draw in search is 8W, and no load draw when inverting is approx 25W. Hope that helps, Eric _ Eric Bentsen

[RE-wrenches] Fw: Conext inverter

2013-08-29 Thread Eric . Bentsen
Hi Allen, Conext SW is available in 24V models only (not 12V). Rgds, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237

Re: [RE-wrenches] Xantrex XW system stability

2013-08-26 Thread Eric . Bentsen
power for Xanbus (AUX port can be used for this). Rgds, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001

Re: [RE-wrenches] PV Assist

2013-08-16 Thread Eric . Bentsen
% discharge more accurately, and minimizes user interaction. Try to calculate the total daily kWhrs and match the demand with RE as closely as possible. Hope that helps, Rgds, _ Eric Bentsen | Schneider

Re: [RE-wrenches] Mouse pee in the SW

2013-08-15 Thread Eric . Bentsen
, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001# | Email: eric.bent...@schneider-electric.com | Site: www.schneider-electric.com/solar

Re: [RE-wrenches] SW AGS

2013-08-07 Thread Eric . Bentsen
Hi Eric, Sounded like bad batteries to me also (I think he called in this AM). He has (2) XW6048 units that are capable of 200ADC between them, and he also has 1260Ah of flooded capacity. DC Start V is set for 46.5V, so if we assume he was close to 50% discharge (depending on load

Re: [RE-wrenches] Trojan L-16s

2013-08-07 Thread Eric . Bentsen
sulfation easier? Rgds, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001# | Email: eric.bent...@schneider

Re: [RE-wrenches] SW AGS

2013-08-07 Thread Eric . Bentsen
Rgds, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001# | Email: eric.bent...@schneider-electric.com | Site

[RE-wrenches] Fw: Trojan L-16s

2013-08-07 Thread Eric . Bentsen
/L16REA_TrojanRE_Data_Sheets.pdf http://www.trojanbatteryre.com/PDF/datasheets/T105_TrojanRE_Data_Sheets.pdf Rgds, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical

Re: [RE-wrenches] SW AGS

2013-08-07 Thread Eric . Bentsen
Absorption Time for stop parameter, but if set to 0 would accomplish the same as stop absorb. Eric _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative

Re: [RE-wrenches] BIG dual axis trackers

2013-08-01 Thread Eric . Bentsen
Hi , Deger 5000HD and Sentinel Solar make large trackers. http://www.dommelvalley.ca/data/DEGERtraker-5000HD-dommelvalley.pdf http://www.sentinelsolar.com/ Eric _ Eric Bentsen | Schneider Electric

Re: [RE-wrenches] C60 setpoint question

2013-08-01 Thread Eric . Bentsen
Hi Allen, The absorption time is actually only 1 hour for the C-series controllers. Battery manufacturers are always the final authority on how their batteries should be charged. If they say you can charge at 14.2-14.4V indefinitely, then increase the float setting. Eric

Re: [RE-wrenches] Tri-Star MPPT

2013-07-24 Thread Eric . Bentsen
do know it usually results in the need to replace the batteries. Rgds _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237

Re: [RE-wrenches] Tri-Star MPPT

2013-07-24 Thread Eric . Bentsen
to be absorbing the charge happens more often with sealed batteries. Maybe it is related to the degree of sulfation. Rgds _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical

Re: [RE-wrenches] Battery bank during peak times

2013-06-25 Thread Eric . Bentsen
. Rgds, Eric _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001# | Email: eric.bent...@schneider-electric.com

Re: [RE-wrenches] generator support mode

2013-06-21 Thread Eric . Bentsen
Hi Lee, The MC version is similar to the standard SW, but does not have grid usage menu (no sell/lbx), and does not give AC1 priority (assuming both inputs are present). It will support the generator with battery power whenever the load exceeds the AC2 Amps setting in Menu 11. Eric

Re: [RE-wrenches] NEC 690.55 - maximum operating voltage

2013-06-11 Thread Eric . Bentsen
of grounded conductor. Eric _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001# | Email: eric.bent...@schneider

Re: [RE-wrenches] Battery Damage

2013-06-10 Thread Eric . Bentsen
Hi Will, Flooded (or wet cell batteries) are typically much more forgiving than a sealed battery. Check S.G. (≈1.265 at rest) and load test. Equalize if necessary (if .05 difference in S.G. cell-to-cell). Eric

Re: [RE-wrenches] 24V charging with 60 cell modules

2013-06-06 Thread Eric . Bentsen
the feedback. Eric Bentsen _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support Representative Phone: +(650) 351-8237 ext. 001# | Email: eric.bent...@schneider

Re: [RE-wrenches] Old Modules for GIT system?

2013-06-05 Thread Eric . Bentsen
guess it boils down to what the customer wants. You can always sell the Trace inverter to someone off grid and use the proceeds toward a new grid-tie inverter. Eric _ Eric Bentsen | Schneider Electric

Re: [RE-wrenches] 24V charging with 60 cell modules

2013-06-04 Thread Eric . Bentsen
battery types, it should allow the module to operate very close to Vmp. Typically, MPPT controllers require a higher Vmp than the target charge voltage. Eric Bentsen _ Eric Bentsen | Schneider Electric

Re: [RE-wrenches] Reliable Cheap Modsine Inverter

2013-03-13 Thread Eric Youngren
listing make a difference in your markets?Small scale off-grid systems are often (usually?) not inspected, so maybe listing is not a requirement... I'd love any advice or feedback you guys might have. Thanks. Best energy, Eric Youngren Solar Nexus International

Re: [RE-wrenches] getting PV modules up to the roof

2013-02-07 Thread Eric Youngren
and haul them up, or secure them on a sloped roof before installation. How many installers would be interested in something like that?? How much would you be willing to pay for it? Eric Solar Nexus International On Thu, Feb 7, 2013 at 12:03 PM, Garrison Riegel garri...@solarserviceinc.com wrote

Re: [RE-wrenches] graphic software for mac

2012-10-22 Thread Eric Youngren
I like OmniGraffle http://www.omnigroup.com/products/omnigraffle/features/ Pro for 2D schematics and layout drawings on a Mac. and SketchUp is great for 3D drawings and renderings Eric Youngren On Mon, Oct 22, 2012 at 3:15 PM, Jonathan Hill solar...@gmail.com wrote: Inkscape doesn't appear