I would do a load test on the inverter. It may have a damaged FET or
two. They do not last forever! Good Luck
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[2]https://offgridsolar1.com/ [3] [2]
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-09-08 12:30 pm, Darryl
Yes Iron Edison is closed. They had an out of business sale earlier this
year.
The epoxy fix of leaking fluids is best done by using a fast cure blend
and expanding out until the leak stops. You can do this with a diesel
fuel tank leak or an oil pan leak. It just needs to be clean and dry
Iron Edison or the MFG company in China? Just curious as I have a few
clients with their LFP and they are concerned.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[2]https://offgridsolar1.com/ [3] [2]
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-08-30 12:19 pm,
have them install 1/2 HP pump, also
Franklin soft start seems to help, low cost but I do not know how it
works, it has a start capacitor I think.
On Wed, Oct 11, 2023, 1:23 PM James Jarvis via RE-wrenches
wrote:
On Wed, Oct 11, 2023 at 1:14 PM Dave Angelini Offgrid Solar via
RE-wrenches wro
Look at a variable speed pump from Grundfos. Not as many choices for
large pumping apps.
The SQ Flex pump is basically a VFD when used with the controller. It
can direct run from solar which tells
you there is no surge. Even the SQ pump without the controller will soft
start and should
Not getting this Kevin, AC2 has always been the generator input as it
allows wider frequency and voltage settings for drifting gensets.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso...@sti.net
text 209 813 0060
On
uot;
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-10-25 12:06 pm, Dave Angelini Offgrid Solar via RE-wrenches
wrote:
Not getting this Kevin, AC2 has always been the generator input as it
allows wider frequency and voltage settings for drifti
Kirk,
Can you reference your paper on this? So many variables and each
location will be different. Most dual axis
trackers can always be left flat or any angle so that does not make
sense to me.
You have to design for winter offgrid if the location is worth it. Or,
alot of hours on a
9 813 0060
On 2023-10-24 10:38 am, Dave Angelini Offgrid Solar via RE-wrenches
wrote:
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-10-23 8:16 pm, Vince McClellan via RE-wrenche
Hi Chad,
Yes XWpro 6848 is a drop-in replacement. Exact fit & all connections
are the same as way back to 2006 when the "grey box" XW 6048 was sold.
You need a connext insight home or facility device to do the initial
configuration.
It is a one time need for the insight home device to set
Hi Howie !
I see the same thing except if you read the last line, they are saying
soon on the cloud. Good that it is working local though!
Version: v1.18 Build 041 [25 July 2023]
Please clear your web browser cache before logging in to web GUI.
Download the latest firmware (.epkg) from
I would trigger genset on Soc. Is that what you are doing?
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[2]https://offgridsolar1.com/ [3] [2]
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-09-25 9:20 am, Chris Daum via RE-wrenches wrote:
Hi folks:
We have a
No experience but I am interested. I see your pump but it has not been
out there long. I can't find it a Home Depot which I depend on for
really remote clients. Can you get one fixed in the US or parts? Will it
be affected by well water?
The Scala2 has had failures and seems to last 3 years
Happiness is a great stove! Can I get the Viking model number Dana.
Please PM or Wrench it!
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-09-26 4:16 pm, Dana Orzel via RE-wrenches
Hey David,
I wish I could convince my clients to use a no AC power source ignition
for baking and broiling. I gave up years ago and never could convince my
wife.
The power system needs enough storage for winter use of appliances. The
ranges now all have convection cooking and some can air
They do come in the XWP box. You can contact me off list for one.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[2]https://offgridsolar1.com/ [3] [2]
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-10-05 9:46 am, Chris Schaefer via RE-wrenches wrote:
G'day All,
Interesting and the closest I have done to this is a ballast mount.
I will say I have broken quite a few cordless drills and killed Lithium
batteries with big torque.
My vote is a genset/ extension cord. Good Luck!
Dave Angelini Offgrid Solar
"we go where powerlines don't"
Definitely heard stories and have seen a few insurance claims for
cracked glass.
I have had clients send me pictures of "solar" guys walking on the
panels on their roof.
I guess it is OK to do this if you change your business name every 5
years
Dave Angelini Offgrid Solar
"we go where
It must be an XW+ that died. The XW pro field circuit validation testing
beta was complete in early 2019.
That XWP is still working fine for me. Not many failures unless the
installer did not use surge protection.
If it was an XWP and you filled out the 10 year warranty, they might
have
Eric has been great! You may have to remind him in a follow-up as he has
a very busy schedule.
I know he appreciates the people who show-up for the training webinars.
I must say that I hardly ever see anyone from the list here in the live
webinars. Maybe they watch the replays?
I also am
In the dead of winter a client paid over 2K$ for the PCB. He now has
surge protection on the lines from gen out to the XW. I did not say to
him I told you so, but I am saying here.
Pop a midnite spd on gensets that stay connected all year. If it was
nearby lightning, he was lucky it did not
How is the quality (sediment) of the water? Most of the Scala1 and
Scala2 series will not last more than 3 years without really good
filtration. I have lost a few to rainwater also The MQ series is not
made anymore so check for warranty.
Nice quiet pumps but
Dave Angelini Offgrid
Mick,
I would look at the workings of the Schneider back-up control switch and
it's internal watt node. Recent webinar training. This will allow AC
coupled power to show on Insight. I am not advocating it though,
certainly not for offgrid.
Dave Angelini Offgrid Solar
"we go where
I think Fronius has left the building. The reason I know is they stopped
sending me AFCI repairs about 2 years ago. There was not any support
from their installers in remote places like the Sierra range.
I would second Tump on picking a good company with real money and
products. Below is a
Just did one.
You have to do the math for costing the grid, a genset, and solar
direct.
The genset usually wins if the grid is not an option. You can easily
find/replace pumps that are not solar direct.
If you do the solar, you still need a genset and the electronics to
support it.
It is
Lones,
I did not see any batteries that were closed loop between outback and
the battery BMS on your link. Did I missed something?
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
On 2022-10-18
This is a new product from Schneider to solve a few of the issues. A
recent webinar had the 3 phase issue brought up and this 200A pre wired
panel. The 3 phase webinar is next, I heard.
https://solar.se.com/us/en/?s=865-BCS-2200
Whole home backup or subpanel backup with up to 200
A
Webinar tomorrow on SW inverters.
Subscribe to our news [1]
View this email in your browser [2]
At Schneider Electric, we support you in your business. Read below our
upcoming in-person and online events, as well as a new product we just
launched.
WEBINAR: SW INVERTER ADVANCED FEATURES
My comment would be in a closed loop battery power system the BMS is in
charge and feeds back into faults and warnings about the battery,
Inverter/charger, and other devices. Open loop does not integrate all of
the devices. Closed loop is all we should be using these days, in my
opinion!
It can be done but it is not an easy job. You are 2 generations of XW
back.
XW+ was good at this and XW pro was designed for this
along with being able to charge based on Soc (from the BMS) as well as
voltage.
Is this an insured home? You might need a permit as this has to be
legal for
Fortress has been great for me/and my clients and they have webinars all
the time.Not sure why you guy's are not going to them?
Below is one this week.
The easy answer is try another genset ! You have to be more specific,
did it ever work? Is it new? etc. Good Luck !
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
On 2022-12-16 10:04 am, Chris
Cheers to all ! I had this problem for years but my Canadian friends
finally listened to me/others and built a smart 200A panel for my
clients.
Not going to help your situation Dana but an FYI.
When paired with Schneider Electric XW Pro inverters [3], the Backup
Control Switch (BCS)
That is not my experience with all of the xanbus model AES. Maybe the
ones from 2018? All of the others will shut down the contactor and you
will lose inverter to protect from charging at temps below 32F. There
will be plenty of warnings and a fault event into the Conext Cloud
devices or
Another reason as Bradley suggests to avoid all of these problems and
only install a closed loop battery power system. Zero problems since
Discover
came out with the AES in 2018 or so. A 25% gain in charge time that
genset users will love by closing the loop. Lot's more also!
Dave
There is not anything I know of that will out surge XW pro 6948. A great
monitoring platform and much better support/installer training in the
last 18 months. Perfect for a shop with unknown peak surges.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
- Original message------
From: Dave Angelini Offgrid Solar via RE-wrenches
Date: Fri, Jan 13, 2023 3:55 PM
To: RE-wrenches;
Cc: Dave Angelini Offgrid Solar;
Subject:Re: [RE-wrenches] Low Frequency transformer off-grid inverter
options
There is not anything I know of that will out surge XW pro 6948
The LG Prime is an NMC chemistry Lithium I believe. It probably needs as
much protection as possible from thermal runaway as it is a definitely
not as safe as LFP Lithium. I hope I am wrong but that is what I know
at this time.
The first system I saw that met UL9540 was the pairing of
I wish I shared your optimism Scott on the LG Prime 16 being better
battery than the LG Resu10. When I field tested the Resu 10 with
Schneider in 2017,
the specs on the unleased 48VResu 16 were the same for charge and
discharge as the Resu10. You would think the larger battery would be
10.
From: RE-wrenches On Behalf
Of Dave Angelini Offgrid Solar via RE-wrenches
Sent: Monday, November 14, 2022 10:24 AM
To: RE-wrenches
Cc: Dave Angelini Offgrid Solar
Subject: Re: [RE-wrenches] LG Chem RESU warranty
I wish I shared your optimism Scott on the LG Prime 16 being better
ba
Depends on how close and how strong the pulse or strike is. In Mil
satellites, the same thing. You can harden but are dreaming if you think
your electronics can really survive it. Even harder to protect
electronics that are powered on. The KH series spy sats I saw schematics
for had
olar Power Systems
On Mar 9, 2023, at 11:18 AM, Marco Mangelsdorf via RE-wrenches
wrote:
Hmmm...I wonder how much SolArk is dreaming.
https://www.sol-ark.com/e-m-p/
On Thu, Mar 9, 2023 at 9:58 AM Dave Angelini Offgrid Solar via
RE-wrenches wrote:
Depends on how close and how strong the pulse
Another reason why I never put solar panels on a dwelling roof.
However, it seems crazy to be drilling holes to find the rafter still in
2023. $.02
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
My metrology experience is he needs to prove it with a second meter. In
a lab setting, at least 2 of 3 calibrated meters need to agree.
I would also ask Fluke. They have been really good over the years. Good
Luck.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
5 years old on 3 strings, it might not matter to mix, better get ready
for a new bank.
I have never used more than 1 string for my clients and get closer to 10
years life, so maybe there is better advice out there.
Good Luck!
Dave Angelini Offgrid Solar
"we go where powerlines don't"
You should tell Schneider this! I have been for a year now. There was
not enough SCP memory for new XWP functions and a component became
unavailable.
The Connext Home and Facility are definitely not for the non savvy as
you say. They are easy for most to install and the non savvy can have
This just went up on the Schneider website thanks to Eric Bentsen. A
complete guide on how to do this with a Samsung tablet
https://solar.se.com/us/wp-content/uploads/sites/7/2022/02/Tablet-Setup-for-InsightLocal-e-Guide.pdf
It is under the Insight down loads at the bottom of page.
Dave
Saying this again, you all should tell Schneider this.
BTW, a tablet can wifi station mode connect to a non internet installed
"conext home" with a saved password. It also can be set-up as a "user"
and no password is required. Neither of these require wifi at the home.
It is all in the 3
On 2023-04-06 8:43 am, Dave Angelini Offgrid Solar via RE-wrenches
wrote:
And the next step for hi reliability offgrid is to have both types of
battery in there own independent inverter power systems. Just switch
the DC bus from one power system or the other. I like the LFP just
turned off
And the next step for hi reliability offgrid is to have both types of
battery in there own independent inverter power systems. Just switch the
DC bus from one power system or the other. I like the LFP just turned
off sitting as a spare power system. You can rotate or do a monthly test
like
Evansville |
Indianapolis
513-448-5176 (mobile)
877-312-7456 (Main Office)
da...@sesre.com
From: RE-wrenches On Behalf
Of Dave Angelini Offgrid Solar via RE-wrenches
Sent: Monday, April 3, 2023 4:34 PM
To: RE-wrenches
Cc: Dave Angelini Offgrid Solar
Subject: Re: [RE-wrenches] replace part of rolls ba
It will be some work to make this work right for you! The XWP is based
on Soc and or V. If you use the Schneider bat mon, it will be a settings
guess for Soc. You will have to do this yearly to compare BMS Soc to the
input you set for the bat mon. I doubt you will get this to work closed
It will be some work to make this work right for you! The XWP is based
on Soc and or V. If you use the Schneider bat mon, it will be a settings
guess for Soc. You will have to do this yearly to compare BMS Soc to the
input you set for the bat mon. I doubt you will get this to work closed
Thanks Glen ! I will ask him on Thursday at a webinar.
Register here:
https://solar.se.com/us/en/event/webinar-backup-control-switch-launch/
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
On
Agree Will and adding that for generator users closed loop will save 25%
or more on fuel.
I know alot of you folks do not use Schneider but it is so easy to close
loop for offgrid. You just plug Xanbus into one battery and the whole
group gets closed loop charged and discharged by XW and
Super helpful Scott ! Really appreciate it.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-06-14 11:02 am, Scot Arey via RE-wrenches wrote:
I figured it had enough of a niche product that
Hi Kent, How is output and how old are the panels?
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-07-16 2:58 pm, Kent via RE-wrenches wrote:
Found some damage to a customer's Grape
I think I would try eliminating things. Turn off the AC coupling for a
few days and get results. Turn of DC solar and get results. Measure AC
voltage with a scope or just observe voltage during the flicker. Are all
of the lights flickering? Are they on dimmers? Are there any loads
failing
September 2008 Schneider bought Xantrex Inverters & Solar. The XW and
later CSW became a Schneider brand and the Marine and Mobile stayed
Xantrex. Schneider later built the first 600vdc MPPT. Later Combox
built an excellent Cloud based monitor Insight.
It is good news that the SCP will be
Need a solar person near Durango Colorado who can onsite troubleshoot a
Discover AES battery / XWpro at an Offgrid Cabin. Good Owner.
Please contact me off-list
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text
Bill, I remember the warranty was not great and the ones I had
experience were not top Tier. I am thinking dumb looks are still free
and a Seventeen year old installation is going to be more free time for
you. I hope I am wrong, good luck!
Dave Angelini Offgrid Solar
"we go where powerlines
Hey Adam,
Creative solution #1 Do not install solar on any roof if you can ground
mount it.
Is this He Adam or the Him Adam?
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-06-05 3:47
I am not having any problem. Doing what Mav does or the wifi.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-05-23 10:37 am, Maverick Brown via RE-wrenches wrote:
I connected the Insight to
It is pretty well laid out on the website for 3 + years that you need to
use Insight.
You should also read the installer info.
https://solar.se.com/us/en/2021/06/29/essential-advanced-resources-for-installers/
SCP will work for some basic functions but is out of memory for XWP. Use
for
It is pretty well laid out on the website for 3 + years that you need to
use Insight.
You should also read the installer info.
https://solar.se.com/us/en/2021/06/29/essential-advanced-resources-for-installers/
SCP will work for some basic functions but is out of memory for XWP. Use
for
between the 2 inverters causing this issue.
Has anyone dealt with this issue before? Does anyone have any
suggestions for dealing with this, short of replacing the SolarEdge
with a Schneider high voltage Charge Controller?
Thanks,
Howie
On Mon, Jul 3, 2023, 7:09 PM Dave Angelini Offgrid
Hey Howie, Can't remember but did you try disabling the charger in XW+
for a pulsation test ?
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-07-23 9:37 pm, Howie Michaelson via
firmware might help this issue. Without knowing what revisions you have
now, and the fact that XW+ is really only a voltage based charger...
XWpro is voltage and Soc based and is really the best choice for this
combo. There will be some things you just can't do with XW+ and I'd say
if you
Very nice Install Michael! Was that the project on the xxCloud River we
talked about?
It looks like you have kept the gutter heat gain down to protect
electronics. "the rule of thumb is that every 10°C increase in
temperature reduces component life by half"
You saw the back-up control switch from Schneider? Probably not what you
want. https://solar.se.com/us/en/product/backup-control-switch/
Might be good for something else?
Whole home or partial home backup made easy. When paired with Schneider
Electric
XW Pro inverters, the Backup Control
Steve, you folks still sell the Discover 6650 ? that I use alot. It is
faster than C2, they claim. Not that one would want that offgrid where
long life is required. Pretty amazing battery for winter genset use.
ROLLS S24-2800LFP & S48-6650LFP ESS OPERATING MANUAL
ENHANCED RUNTIME
*
Hi David,
I own and tested the 48V version Resu10, not the 10H that you have. On
the one I have, the battery needs a heartbeat signal to operate.
Without that signal from the inverter or a device that talks to LG
battery the contactor will open and shut down the battery.
This was a pretty
I lived in Mariposa CA before moving to Nevada. The workaround was to
buy a metal roof structure like a car barn and cover the M home with it.
The metal car barn had the snow load engineering. This made the building
department happy. I definitely would not put solar on a manufactured
home
Jay, I do not know/use this brand. Got this off the internet. Looks to
me like they are telling you max charge is 100A but max life is 30 - 50a
charge.
only a 5 year warranty so Good Luck !
Voltage 51.2V
Capacity 100Ah
Charging Voltage (Bulk/Absorb) 56.2V (+/- 0.2V)
Float 54V (+/-
ood
performance for this very patient customer!
All the best,
Greg Egan
Remote Power Inc.
Fairbanks, AK
Dave Angelini Offgrid Solar via RE-wrenches [1] Sun, 11 Jun 2023
15:31:28 -0700 [2]
It is pretty well laid out on the website for 3 + years that you need
to use Insight.
You should
Hi Mac,
Below is what I use from Schneider for 200A grid-tie. They finally made
it easy, not inexpensive though. Offgrid version firmware out in the
fall.
https://solar.se.com/us/en/product/backup-control-switch/
Dave Angelini Offgrid Solar
"we go where powerlines don't"
* You do need Xanbus and all of the following
One of the reasons I always post here to not use a roof for offgrid is
rapid disco. There are a few others also. It is the last thing you want
offgrid and if for some reason you can't find a reasonable way to please
an inspector, install
Component parts become unavailable, the engineering to make backward
compatibles, the liability, and time spent in support can make a company
unprofitable. Often the secondary market will step up if there is enough
demand.
This is nothing new BTW. You have to be in business to do business.
NAZ is an extremely well run company ! Love those guys!
On 2023-05-18 8:42 am, Michael Morningstar via RE-wrenches wrote:
My question is: how/why is it that NAZ and the likes sell equipment for
less than what I pay wholesale?
On Thu, May 18, 2023 at 4:15 AM Jason Szumlanski via
Hi Peter,
I was called in to consult on a new existing 4x Fortress E flex /
Schneider XWP system that worked fine open loop but never communicated
with the Schneider gateway. Fortress to their credit sent a tech out and
he did Fortress FW and a PC exchange. Still not working.
The owner was
So this is all open loop with outback correct? I can't even get into
Simplyphi. website today. Maybe the windows update...
The battery below was suppose to be networkable but it looks like not
much progress.
* Model: AmpliPHI 3.8kWh
* Inverter compatibility: Sol-Ark, SMA (coming
om/ [8] [7]
e-mail offgridso...@sti.net
text 209 813 0060
Original Message
Subject:
Re: [RE-wrenches] EG4 Equipment
Date:
2024-02-16 3:11 pm
From:
Dave Angelini Offgrid Solar via RE-wrenches
To:
RE-wrenches
Cc:
Dave Angelini Offgrid Solar
Reply-To:
offgridso...@
nd nothing but the
installation manual on the internet).
Many thanks for any insights.
Tom McCalmont
On Feb 20, 2024, at 8:59 AM, Dave Angelini Offgrid Solar via
RE-wrenches wrote:
Someone asked about the loss on the discover AES rackmount.
"The contactor is bi-stable so it doesn't require extra
can
help? Is there a service manual for the LG RESU battery that explains
how to recharge it in this situation (again, can find nothing but the
installation manual on the internet).
Many thanks for any insights.
Tom McCalmont
On Feb 20, 2024, at 8:59 AM, Dave Angelini Offgrid Solar via
RE-wrenc
Surrette and Full river AGM's Been berry berry good to me!
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso...@sti.net
text 209 813 0060
On 2024-02-17 9:43 am, Drake Chamberlin via RE-wrenches wrote:
I fully agree that off
Howie, I think you should also look again at the Discover rack mount
system in the link below. Nice 75 year old company that made it's name
on Locomotive batteries. Their prices are way down around 14 K for 30Kwh
with heaters. If you have not looked at Lynk2 their gateway closed loop
into SMA,
Did you try it on another ISP? I sometimes hear this about Schneider
Insight and it never is down. It always is the ISP or cell. Good Luck
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso...@sti.net
text 209 813 0060
On
You said that very nicely Kevin !
If this were for offgrid, I would make the inspector happy and do even
more than Kevin suggests after he is gone.
Link to RS shutdown
https://www.youtube.com/watch?v=wMoVXq4m1wk=10s
Dave Angelini Offgrid Solar
"we go where powerlines don't"
Hi August,
I was told Tesla has LFP battery now. True? Thanks !
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[3]https://offgridsolar1.com/ [4] [3]
e-mail offgridso...@sti.net
text 209 813 0060
On 2024-01-10 3:25 pm, August Goers via RE-wrenches wrote:
We're starting to
Picture tells one alot also. You can't have 2 or more sources without
isolation, batteries or not. Cheers!
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-12-01 4:16 pm, Jerry Shafer
10+ years ago I thought that Sunpower Solar wrote the best info. Their
module technology was superior and the classic 327 module output was
amazing in high temperature and also in cloudy skies. They were the
first to have really good warranty for both workmanship and output over
time.
I have
I wish bob and the boyz good luck on this product. Always support North
American companies!!
I do not have much experience in the all in ones, but the one thing I
would look for is how it responds to imbalance
on split phase loads. The bad experiences on (won't say the Chinese name
of
It depends on how the BMS shares with the new BMS. A state of life
measurement, the charge algorithm, and ? has to account for this for
them to charge and discharge well together.
Pretty safe to say one year for many makes of battery. Kind of like
bussbar use in large systems, is a way to
Not being helpful but I walk away from these. It will come back to
you.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso...@sti.net
text 209 813 0060
On 2024-04-23 2:40 pm, Jason Szumlanski via RE-wrenches wrote:
I have
al (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208
On Tue, Apr 23, 2024 at 5:47 PM Dave Angelini Offgrid Solar via
RE-wrenches wrote:
Not being helpful but I walk away from these. It will come back to
you.
Dave Angelini Offgrid Solar
To be fare, Schneider does tell you to follow the commissioning guide.
It should be in the firmware though and should be a warning. It is only
an issue with older XWP BTW.
Let us know what you end up doing Kevin please.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
Good advice Michael! I had one that the grid code got set by FW and
reverting did not help. Had to start fresh.
I certainly would try the revert as it is so much easier. There just
is too much grid firmware being changed and it does
not need to be done offgrid. I beg people and
Kent, Battery monitor is internal to 6650 battery. No bat mon! Probably
as you said the xanbus comms need a look as Mac said.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso...@sti.net
text 209 813 0060
On 2024-05-03 10:24
Which model? Do you see the same dips in voltage? Probably yes.
Are all the batts the same firmware?
The AES dashboard can be useful for finding a differing module.
No I have not seen this and only have had one bad battery that was
replaced by AES. Yes check all wiring. Good Luck!
Dave
Never heard of one with LFP. The cobalt and Magnesium Lions are
definitely out there. Was this a 6650 model Michael?
Going to be fun times doing a failure analysis on this one.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail
1 - 100 of 123 matches