Re: [RE-wrenches] 90 degree wire bends

2011-11-19 Thread Larry Crutcher, Starlight Solar Power Systems
. This time as the energy explodes from the wire to find a path of lesser resistance. That about sums it up. I love it when I see lightning protection installations with neatly formed wires following every turn and contour tightly. Bang. Larry Crutcher Starlight Solar Power Systems On Nov 16

Re: [RE-wrenches] High-power MPPT/Charge Controllers?

2011-11-18 Thread Larry Crutcher, Starlight Solar Power Systems
Sounds like a project for Sunny Island and the Boy's. Larry Crutcher Starlight Solar Power Systems On Nov 18, 2011, at 10:49 AM, Exeltech wrote: Need info on MPPT/charge controllers able to output up to 500A at 48Vdc. High-voltage DC input (up to 300Vdc) preferred. Units will connect

Re: [RE-wrenches] intermittent battery problem; The Last Word

2011-11-17 Thread Larry Crutcher, Starlight Solar Power Systems
. And such waste of money, time and resources just bugs me! Larry Crutcher Barer of Bad News Starlight Solar Power Systems On Nov 17, 2011, at 5:17 AM, penobscotso...@midmaine.com wrote: Ron, I'm going to reiterate what Jeff says here. It is similar to what I had said in my email. The charge rate must

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Larry Crutcher, Starlight Solar Power Systems
fact. ;-) Larry Crutcher Starlight Solar Power Systems On Nov 16, 2011, at 12:20 AM, Ron Young wrote: Hi Larry, no amp hour meter installed yet as the customer is penny pinching. We're trying to solve the problem first and I've been out there twice, once to do general diagnostics and check

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Larry Crutcher, Starlight Solar Power Systems
, Larry Crutcher, Starlight Solar Power Systems wrote: Hi Ron, Accurate SG readings are not simple. Was temperature compensation properly employed? Have they been keeping a log book to identify changes? How accurate is the hydrometer? How skilled is the person taking the reading? Most

Re: [RE-wrenches] Small Off-Grid Inverter Recommendation

2011-11-11 Thread Larry Crutcher, Starlight Solar Power Systems
://samlexsolar.com/solar-products/pure-sine-wave-inverters/sa-series Larry Crutcher Starlight Solar Power Systems On Nov 11, 2011, at 7:45 AM, Jeff Irish wrote: Any recommendations from those of you with extensive off grid experience for a small inverter, sine wave, 500-1000 watt range 120 vac output, 12

Re: [RE-wrenches] federal tax credit

2011-11-11 Thread Larry Crutcher, Starlight Solar Power Systems
Stange but true...many of my customers are claiming the credit for their RV PV solar system and a few have reported back: no problems. For some, the motorhome or trailer is their primary residence but for most it is just used part time. Larry Crutcher Starlight Solar Power Systems On Nov 10

Re: [RE-wrenches] High Voltage MPPT units; Adding battery backup

2011-11-09 Thread Larry Crutcher, Starlight Solar Power Systems
. Larry Crutcher Starlight Solar Power Systems On Nov 9, 2011, at 1:55 PM, Drake wrote: Any amount of power will AC couple. If you use an off grid inverter, such as an Outback, to feed the protected load panel, the inverter should be fed by grid AC power to supply loads, when the grid

Re: [RE-wrenches] Canadian Solar blemish

2011-11-09 Thread Larry Crutcher, Starlight Solar Power Systems
Oops. My picture is of a blemished Evergreen 210. I saw the orange substance on your picture and thought that is what you were referring to. ...My Bad. Larry On Nov 9, 2011, at 1:41 PM, penobscotso...@midmaine.com wrote: Hello all, We have a customer who has acquired, over the last ten

Re: [RE-wrenches] High Voltage MPPT units

2011-11-07 Thread Larry Crutcher, Starlight Solar Power Systems
this design. Sounds like a product for Midnite Solar to build. Larry Crutcher Starlight Solar Power Systems On Nov 6, 2011, at 1:42 PM, Glenn Burt wrote: Siemens makes a line that are UL listed. Their VBII series like HNF361PV – 30A -Glenn

Re: [RE-wrenches] High Voltage MPPT units

2011-11-07 Thread Larry Crutcher, Starlight Solar Power Systems
the battery. That means any off-grid inverter/charger or even low cost separate inverters and chargers may be used, a very economical solution. However, the idea may be of no value because it appears no one makes a transfer switch. Larry Crutcher Starlight Solar Power Systems On Nov 7, 2011, at 11:32

Re: [RE-wrenches] Battery idle losses; Deka AGM

2011-11-02 Thread Larry Crutcher, Starlight Solar Power Systems
over 1 year. Since it only has a 1 year replacement, my customers are VERY upset. After speaking with my Deka rep. last week and I have decided to advise customers to not purchase the Deka 8D's. Larry Crutcher Starlight Solar Power Systems On Oct 31, 2011, at 8:20 PM, William Miller wrote

Re: [RE-wrenches] Battery idle losses; Sunny Island overhead

2011-11-02 Thread Larry Crutcher, Starlight Solar Power Systems
, 1.5kWh, concerns me. Larry Crutcher Starlight Solar Power Systems On Nov 2, 2011, at 4:42 PM, Jeff Irish wrote: William, I did a 2 year long study on a Sunny Island 5048 grid-intertie battery back-up system and found the SI and batteries used about 1.5kWh per day in overhead

[RE-wrenches] Connecting charge controller to grid tie inverter

2011-10-27 Thread Larry Crutcher, Starlight Solar Power Systems
Solar Power Systems ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-24 Thread Larry Crutcher, Starlight Solar Power Systems
Hi Ron,Accurate SG readings are not simple. Was temperature compensation properly employed? Have they been keeping a log book to identify changes? How accurate is the hydrometer? How skilled is the person taking the reading?Most of the Battery Wrench responses suggest equalization but I don't see

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-23 Thread Larry Crutcher, Starlight Solar Power Systems
and have used it twice in 40 years, it seems to work) Thanks again great piece of writing and explanation, everyone should read Darryl From: Larry Crutcher, Starlight Solar Power Systems la...@starlightsolar.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Sent: Saturday, October 22

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-22 Thread Larry Crutcher, Starlight Solar Power Systems
been detected and perhaps prevented if they had one. Larry Crutcher Starlight Solar Power Systems On Oct 21, 2011, at 11:39 AM, Ron Young wrote: Hi Maverick everyone, I visited the site a couple of days ago and load tested the batteries, checked individual voltages in the string of six

Re: [RE-wrenches] Instruction manual / User interface rant

2011-10-19 Thread Larry Crutcher, Starlight Solar Power Systems
Solar Power Systems On Oct 18, 2011, at 7:11 AM, Larry Crutcher, Starlight Solar Power Systems wrote: I second the vote for Magnum Energy remotes. When combined with the BMK battery monitor and AGS, there is simply nothing better on the market as far as function and ease of use. The new ME

Re: [RE-wrenches] Instruction manual / User interface rant

2011-10-18 Thread Larry Crutcher, Starlight Solar Power Systems
than the any of the other Made in China products. Larry Crutcher Starlight Solar Power Systems On Oct 18, 2011, at 3:16 AM, PRP wrote: Magnum with the standard control. Have yet to have a end user mess it up that can't be fixed with a phone call. In fact with over 8 systems out there only

Re: [RE-wrenches] intermittent battery problem; AH Metering is Important

2011-10-09 Thread Larry Crutcher, Starlight Solar Power Systems
the inverter still works. AH metering will expose these events and will keep the user well informed. Larry Crutcher Starlight Solar Power Systems On Oct 8, 2011, at 11:31 AM, Ron Young wrote: There is no amp hour meter in the system. The dump load on the Whisper sounds like a possibility

Re: [RE-wrenches] What's the right action?

2011-10-06 Thread Larry Crutcher, Starlight Solar Power Systems
I think you hit it on the head, an honest, simple explanation. If he is unreasonable, just go buy him some Johnson Control specials for $68 at Sams Club. Larry Crutcher Starlight Solar Power Systems On Oct 6, 2011, at 3:32 AM, Allan Sindelar wrote: OK, here's one way off the beaten path

Re: [RE-wrenches] Re-configuring expanded array

2011-09-30 Thread Larry Crutcher, Starlight Solar Power Systems
of potential power when using MPPT controllers. However, you don't have much choice from an economic standpoint. Just try to match the Vmp between the strings. Larry Crutcher Starlight Solar Power Systems On Sep 30, 2011, at 7:23 AM, Allan Sindelar wrote: Holt, The string of two

Re: [RE-wrenches] battery cycle life, US Battery

2011-09-17 Thread Larry Crutcher, Starlight Solar Power Systems
not had a single failure yet. Larry Crutcher Starlight Solar Power Systems On Sep 17, 2011, at 10:36 AM, toddc...@finestplanet.com wrote: What about the 2 volt L-16 versions? Has anyone had success with them for larger banks? I work alone and HUPs are too heavy to lift on my own... however

Re: [RE-wrenches] battery cycle life, US Battery

2011-09-16 Thread Larry Crutcher, Starlight Solar Power Systems
Ray, If we were comparing the T-105 to the Trojan L-16 in a single string, I agree the T-105 will provide more life cycles. Been there, done that. But that was not the comparison. Having 6-8 parallel strings of golf cart batteries is a terrible idea no matter how much better the GC2 may be.

Re: [RE-wrenches] battery cycle life, US Battery

2011-09-15 Thread Larry Crutcher, Starlight Solar Power Systems
/interstate.htm) I consider Rolls a superior long life battery compared to any other L16's. Curious here: why are you comparing an L-16 to a GC2? US Battery also makes a floor scrubber version, model US16HC XC. Larry Crutcher Starlight Solar Power Systems On Sep 15, 2011, at 4:23 PM, RM You wrote: Hi

Re: [RE-wrenches] unique battery bank design question

2011-09-02 Thread Larry Crutcher, Starlight Solar Power Systems
voltage across the two batteries. I'm not sure I said it better the Michael, just different for more clarity. Are you sure you are not a REAL wrench? Larry Starlight Solar Power Systems On Sep 2, 2011, at 9:45 AM, Michael Welch wrote: What the Vanner Voltmaster equalizer does is track

Re: [RE-wrenches] unique battery bank design question

2011-09-02 Thread Larry Crutcher, Starlight Solar Power Systems
. The equalizer then shares current from the 24 volt tap to the 12 volt tap to maintain equal voltage across the two batteries. I'm not sure I said it better the Michael, just different for more clarity. Are you sure you are not a REAL wrench? Larry Starlight Solar Power Systems

Re: [RE-wrenches] Jacobs Wincharger Book, 1978?

2011-08-25 Thread Larry Crutcher, Starlight Solar Power Systems
by Windy Dankoff. Allan Sindelar On Wed, Aug 24, 2011 at 9:56 PM, Larry Crutcher, Starlight Solar Power Systems la...@starlightsolar.com wrote: This one's for you old timer wind wrenches. Back in 1978 I bought a book on wind generators and rebuilding the Jacobs Winchargers

Re: [RE-wrenches] Jacobs Wincharger Book, 1978?

2011-08-25 Thread Larry Crutcher, Starlight Solar Power Systems
Thanks but I just bought one for $2.77. I actually saw someone asking for $75! With perfect pleasure I shall peruse the pages as I post in the privy. Just like old days. Larry On Aug 25, 2011, at 12:35 PM, Dan Fink wrote: We plan to start carrying both of Hackleman's books very soon in the

[RE-wrenches] Jacobs Wincharger Book, 1978?

2011-08-24 Thread Larry Crutcher, Starlight Solar Power Systems
a copy they would part with? Let's see how many of you have been around long enough to remember that one! Thanks. Larry Crutcher Starlight Solar Power Systems 11871 S Fortuna Road, #210 Yuma, AZ 85367 la...@starlightsolar.com (928) 342-9103 ___ List

Re: [RE-wrenches] Pump

2011-08-23 Thread Larry Crutcher, Starlight Solar Power Systems
We've had very good service from Sunpumps: http://www.sunpumps.com/ProductsClient.aspx 800-370-8115 Larry Crutcher Starlight Solar Power Systems 11871 S Fortuna Road, #210 Yuma, AZ 85367 la...@starlightsolar.com (928) 342-9103 On Aug 23, 2011, at 11:54 AM, Peter Talmage wrote: Does any

Re: [RE-wrenches] shatterproof PV (Durable Uni-Solar)

2011-07-28 Thread Larry Crutcher, Starlight Solar Power Systems
Crutcher Starlight Solar Power Systems On Jul 27, 2011, at 9:26 PM, Ray Walters wrote: My mistake, I just found a spec sheet on the Unisolar 64, and it specifically advertises No glass and unbreakable. I worked on systems with them before, but never sold them, so I assumed the textured top

Re: [RE-wrenches] Uni-Solar

2011-07-27 Thread Larry Crutcher, Starlight Solar Power Systems
We sold tons of the 62 and 64 watt framed modules. If any were available, I would have bought them years ago after they canceled production. Larry Crutcher Starlight Solar Power Systems On Jul 27, 2011, at 10:51 AM, Marco Mangelsdorf wrote: OK, I guess that it had to happen someday. I

Re: [RE-wrenches] Magnum MMS inverter / Honda 3000i charger problems

2011-07-08 Thread Larry Crutcher, Starlight Solar Power Systems
voltage but always return to normal operation after the power quality is within spec. Bottom line is I would not be looking at the Magnum as the problem UNLESS a parameter or wiring was changed. Larry Crutcher Starlight Solar Power Systems 11871 S Fortuna Road, #210 Yuma, AZ 85367 la

Re: [RE-wrenches] Sealed L-16 size batteries / battery terminals

2011-06-29 Thread Larry Crutcher, Starlight Solar Power Systems
/admin/upfile/Terminaltorque.pdf Larry Crutcher Starlight Solar Power Systems 11871 S Fortuna Road, #210 Yuma, AZ 85367 la...@starlightsolar.com (928) 342-9103 On Jun 27, 2011, at 3:33 PM, William Miller wrote: Colleagues I need to replace batteries for a customer. They have Trojan L-16

[RE-wrenches] Why I sell China made batteries

2011-06-29 Thread Larry Crutcher, Starlight Solar Power Systems
know my position I'll let you decide. Life's a bitch sometimes. Larry Crutcher Starlight Solar Power Systems On Jun 29, 2011, at 11:08 AM, Bob-O Schultze wrote: Need we mention here that Fullriver batteries are made in China as are so many of the PVs flooding the market these days? Honestly

Re: [RE-wrenches] Kyocera followup

2011-06-08 Thread Larry Crutcher, Starlight Solar Power Systems
in their back yard, I can't buy from them. Now they are drumming up business. That's just odd. Larry Crutcher Starlight Solar Power Systems 11871 S Fortuna Road, #210 Yuma, AZ 85367 la...@starlightsolar.com (928) 342-9103 On Jun 8, 2011, at 11:26 AM, Allan Sindelar wrote: Wrenches, A year

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Larry Crutcher, Starlight Solar Power Systems
Wayne, Whenever possible, always design a battery bank for a single series string. Parallel strings require more attention and increase the probability of early failure due to unequal charging. Larry Crutcher Starlight Solar Power Systems 11871 S Fortuna Road, #210 Yuma, AZ 85367 la

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Larry Crutcher, Starlight Solar Power Systems
Oops! Guess I should have read all the posts before I reply;- Larry Crutcher On May 31, 2011, at 5:23 PM, Wayne Irwin wrote: I think the verdict is 12 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) and one dry spare in storage is the best case scenario! Wayne Irwin, EE Director of

[RE-wrenches] Lifeline Battery scammer...Confirmed

2011-05-10 Thread Larry Crutcher, Starlight Solar Power Systems
sent an address to me for shipment of: 330 N Marine Ave., Wilmington, CA 90744. According to a reliable source, he owes a distributor $20,000, writes bad checks and uses credit cards that do not go through. Let the seller beware. Larry Crutcher Starlight Solar Power Systems 11871 S Fortuna

Re: [RE-wrenches] Tiny load problem

2010-05-11 Thread Starlight Solar Power Systems
wave since many small load items like battery chargers, electric blanket control, electric toothbrush, etc., fail with MSW inverters. Contact me off list if you don't have a resource for small 12, 24 and 48 volt inverters. Larry Crutcher Starlight Solar Power Systems (928) 342-9103 Mailing

Re: [RE-wrenches] KD135 source?

2010-04-20 Thread Starlight Solar Power Systems
Are you looking for grid tie or the J-box? I have some of the J-box 135's. Just FYI, the 135's are a larger module at 59.1 x 26.3. The discontinued 120's, 125's and 130's were all 56.1 x 25.7. Larry Crutcher Starlight Solar Power Systems (928) 342-9103 Mailing Address: 11881 S. Fortuna Road

Re: [RE-wrenches] windenergy7

2010-04-01 Thread Starlight Solar Power Systems
/index.php/Directory:Home_Generation:Wind_Turbine Larry Crutcher Starlight Solar Power Systems (928) 342-9103 Mailing Address: 11881 S. Fortuna Road, #210 Yuma, AZ 85367 Retail Store Shipping Address: 2998 Shari Ave. Yuma, Az 85365 - Original Message - From: Kirk Herander, VSE

[RE-wrenches] MC4's in stock (missing MC4)

2010-03-25 Thread Starlight Solar Power Systems
I have 80 each MC4's available. PV-KST4/6II MALE6 - 9 mm gland range and 12 - 10 AWG conductor range PV-KST4/6II FEM6 - 9 mm gland range and 12 - 10 AWG conductor range Contact me off list. la...@starlightsolar.com Larry Crutcher Starlight Solar Power Systems (928) 342-9103 Mailing