Re: Parking Garage Sprinkler System

2008-02-01 Thread Todd Williams - FPDC
One more thing, make sure that your churn pressure on the pump plus the elevation gain going down the two levels does not exceed 175 psi. This may be the pressure the system feels when the system first trips (or in the case of an accidental trip) At 11:17 AM 1/31/2008, you wrote: Hi All,

RE: Anti freeze leaking

2008-02-01 Thread Matthew J. Willis
Is there a backflow involved for this system??? Matt Matthew J. Willis Living Water Fire Protection, LLC. 1160 McKenzie Rd. PO Box 877 Cantonment, FL. 32533 850-937-1850 Voice 850-937-1852 Facsimile [EMAIL PROTECTED] - -Original Message- - From: [EMAIL PROTECTED] -

Re: Funny - or not - inspection story.

2008-02-01 Thread douglas hicks
Here is another inspection story. I was waiting for an inspection on a UL 300 fire suppression system, and the inspector was late. When he showed up, he was in a bad mood. He had just been on a fire alarm test and the stupid contractor did not know how to hydro the fire alarm panel.

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Reza Esmaeili
Dears friends Craig, Travis, Kurt Todd, Many thanks for your detailed answer, your answers were very helpful,. I will use the sprinkler piping for my fire hoses to save some pipe, after calculation, the water velocity in piping is about 20 ft/s and the capacity of sprinkler piping in each

RE: Funny - or not - inspection story.

2008-02-01 Thread Dusha, Richard P. Mr.
I've never heard of a hydrostatic test on a fire alarm panel. I'm thinking 200 psi of water pressure might damage the panel. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of douglas hicks Sent: Friday, February 01, 2008 9:43 AM To:

RE: Parking Garage Sprinkler System

2008-02-01 Thread Reza Esmaeili
Mike, Thanks for your kind email, I would be very grateful if you send it to me, it is a real pleasure to have help from an expert in Reliable Sprinkler. Please send to [EMAIL PROTECTED] Thanks, Reza Mike Brown (TECH- GVL) [EMAIL PROTECTED] wrote: If you would like one I will send you a

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread George Church
Is there a code requirement to provide hose valves in a parking garage in a 2-story? Would it make sense to toss em in the stairs and connect only to an FDC to effect a dry standpipe ? FDT water delivery would answer your question on how long it will take to trip/fill/and spurt water outa the

RE: Funny - or not - inspection story.

2008-02-01 Thread Chuck Bowman
Just to add to the madness, we have a reviewer in Virginia asking for a second backflow at the riser inside the building per plumbing code. There is already one in the underground run-in right outside. No, there is no plumbing coming off of the run-in. How do you educate someone like this? It must

RE: Parking Garage Sprinkler System

2008-02-01 Thread Mike Brown (TECH- GVL)
If you would like one I will send you a copy of my Rules of Thumb for designing large dry systems. You can contact me off line at [EMAIL PROTECTED] MLB -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili Sent: Thursday, January 31, 2008 11:17

RE: Anti freeze leaking

2008-02-01 Thread David M. Canham
Yes and expansion chamber as well -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matthew J. Willis Sent: Friday, February 01, 2008 7:52 AM To: sprinklerforum@firesprinkler.org Subject: RE: Anti freeze leaking Is there a backflow involved for this

RE: Funny - or not - inspection story.

2008-02-01 Thread Craig.Prahl
But what do I do with those 460 panels? Wood ya think I might be needin too pumps? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED]

RE: Anti freeze leaking

2008-02-01 Thread Matthew J. Willis
We can assume then it is properly sized? How about a hole in the check valve (if provided)? Is this a steel or plastic job? If this is plastic, what kind of anti-freeze? R/ Matt Matthew J. Willis Living Water Fire Protection, LLC. 1160 McKenzie Rd. PO Box 877 Cantonment, FL. 32533

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Craig.Prahl
Larger is better when it comes to getting the air out. I would not use any 2.8K heads. Work with your pipe sizes on the branch lines to consume some of the extra pressure and if it is still too high and beyond reason due to the higher pressure needed for the hose, you may have to run separate

Re: Parking Garage Sprinkler System

2008-02-01 Thread Jim . Roberts
Forumites: It's not often that we all get to see the fruits of our labors. In 1986 I designed a dry pipe system for a 7-8 level parking garage for a high riser building. 14 years later I had an NSPE state convention, which my Piedmont Chapter was sponsoring. While there a car caught fire

Re: Parking Garage Sprinkler System ***

2008-02-01 Thread Ron Greenman
Consider low pressure DPVs if you have no way to determine trip time (the expensive program). low pressure DPVs work on about a 30:1 differential rather than the more typical 6:1. On Feb 1, 2008 7:06 AM, George Church [EMAIL PROTECTED] wrote: Is there a code requirement to provide hose valves in

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Reza Esmaeili
Thanks Craig, As I am connecting fire hoses to my sprinkler system, then the system pressure would be high to comply with NFPA-14 minimum residual pressure requirements at the outlet of most remote 1 1/2 in. hose station which is 65 psi. In this case my fire pump minimum head would be around

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Sal Izzo (TECH- 103)
I believe NFPA 13 allows the use of small orifice sprinklers on light hazard, wet systems only. Salvatore Izzo, P.E. Relible Automatic Sprinkler Company, Inc. From: [EMAIL PROTECTED] on behalf of Reza Esmaeili Sent: Fri 2/1/2008 10:48 To:

RE: Funny - or not - inspection story.

2008-02-01 Thread George Church
I think you only hydro High Voltage panels, not the typical low voltage used today. The high voltage can withstand the 200 psi; 270 PSI if it's a 220 volt panel, 50 PSI over the normal working voltage. I don't blame you for not asking any questions.but a high-pressure air test would be far

Re: Parking Garage Sprinkler System ***

2008-02-01 Thread Joe Hankins
Reza, Be careful when you start selecting low K-factor sprinklers just because the numbers work. Contrary to what you might infer from some standards, density is not a direct measure of sprinkler performance. A 0.25 density from a K5.6 sprinkler is much less effective than from a K11.2

Re: Parking Garage Sprinkler System ***

2008-02-01 Thread steve
Reza: If the building code requires standpipes in this building, you may not supply the hose connections directly off the sprinkler mains. There is a distinct difference between a standpipe system and small hose connections as might be found in a storage occupancy. Sent from my Verizon

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread art
Per NFPA 13 2002 section 8.16.5.1.3 Hose connections are to be connected to wet systems only. This is due to time delay of dry system. Fire fighter is holding a hose with 100 psi air blowing out and no water till system fills - bad idea. Also unless code required does not require NFPA 14 rules.

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread George Church
I'm still wondering why the dry-pipe sprinkler system needs to feed a small hose station with 65 PSI in a 2-story parking garage. Are you trying to balance the hose and sprinklers? Do you even need the hose, and wouldn't the pumper truck furnish the hose demand pressure requirements? Note to

Re[2]: Funny - or not - inspection story.

2008-02-01 Thread Charles Thurston
Hello all, To put fuel on a fire so to say The Electrician had disconnected the air compressor on Friday for this dry system to install a proper Disconnect (I raised hades about the light Switch). Well our crew had left for the day and the electrician did not finish the disconnect. We

Re: Sprinkler Zones for Horizontal Exit Building

2008-02-01 Thread Ed Vining
The fire can be in any of the three buildings. If I am standing in a corridor by a horizontal exit and hear the alarm, I look up at the exit sign and go through that exit. That exit sign just told me I was going to a safe place. It can very well send me into the fire area. Ed Vining 4819

RE: Sprinkler Zones for Horizontal Exit Building

2008-02-01 Thread John Denhardt
Each building should be on a zone. Each building should have its own fire alarm panel. Separate buildings, separate systems. However, new language in NFPA 13 was added to allow one building to feed another building within certain guidelines. Hope this helps, John John August Denhardt, P.E.

Firesprinkler.org

2008-02-01 Thread A.P.Silva
I get e-mail from a firesprinkler.org, giving me a URL to visit for customizing my subscription info. I've always deleted them. Any others receiving it? Is it legitimate? Tony ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org

RE: Funny - or not - inspection story.

2008-02-01 Thread Todd Williams - FPDC
Craig, Call me and let me know when you do this. I'm gonna set up across the street with a lawn chair and a six pack and watch the explosion. Todd At 10:13 AM 2/1/2008, you wrote: But what do I do with those 460 panels? Wood ya think I might be needin too pumps? Craig L. Prahl, CET Fire

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Todd Williams - FPDC
Reza, If it doesn't work and you have to install two extra dry valves, that would most likely be a very expensive operation. Is it worth the chance? As Clint Eastwood once said, Do you feel lucky? Todd At 09:40 AM 2/1/2008, you wrote: Dears friends Craig, Travis, Kurt Todd, Many

RE: Firesprinkler.org

2008-02-01 Thread Brian Harris
I get em' an delete em' too Brian Harris FDFP INC. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva Sent: Friday, February 01, 2008 11:26 AM To: sprinklerforum@firesprinkler.org Subject: Firesprinkler.org I get e-mail from a

RE: Re[2]: Funny - or not - inspection story.

2008-02-01 Thread Jim Smyrl
-Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Charles Thurston Sent: Friday, February 01, 2008 11:13 AM To: sprinklerforum@firesprinkler.org Subject: Re[2]: Funny - or not - inspection story. Hello all, To put fuel on a fire so to say The

Re: Parking Garage Sprinkler System /FDT program

2008-02-01 Thread Todd Williams - FPDC
How accurate is the FDT program based on comparison to field tests? At 11:27 AM 2/1/2008, you wrote: Reza: As Ron points out the FDT program is expensive, but you may actually save the cost of the program in this one installation if you can reduce from 4 dry systems to just 2. We all need

RE: Firesprinkler.org

2008-02-01 Thread George Church
Legitimate? It's the AFSA that hosts it. Since we members fund this whole thing, they don't ask for your credit card or mother's maiden name. Yes, its legitimate, self-explanatory, and helpful if you need the current passwords for any of the Lists. This is just one of several the AFSA runs in

RE: Anti freeze leaking

2008-02-01 Thread Todd Williams - FPDC
Dave, I would see exactly what anti-freeze was used and look for a chemical compatibility problem. Where was it leaking? Steel fittings? Gasketed fittings? Pin-holes in pipe? Todd At 01:02 PM 2/1/2008, you wrote: It's steel and with the expansion chamber and backflow no hole is required.

RE: Parking Garage Sprinkler System /FDT program

2008-02-01 Thread Travis Mack, SET
://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) __ NOD32 2844 (20080201) Information __ This message was checked by NOD32 antivirus system. http://www.eset.com

sales guys with computers

2008-02-01 Thread George Church
I have NEVER seen Jim this quiet EVER. LOL glc -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jim Smyrl Sent: Friday, February 01, 2008 12:18 PM To: sprinklerforum@firesprinkler.org Subject: RE: Re[2]: Funny - or not - inspection story. -Original

RE: Anti freeze leaking

2008-02-01 Thread David M. Canham
It's steel and with the expansion chamber and backflow no hole is required. There has not been any pressure build-up noticed. Dave -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matthew J. Willis Sent: Friday, February 01, 2008 8:46 AM To:

Re: Parking Garage Sprinkler System /FDT program

2008-02-01 Thread Thom McMahon
FDT is the base program for the Quell systems and the accuracy is right on! (Tyco put a lot into this programs development, and studied a lot of existing systems and ran comparisons to actual.) Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952

RE: Anti freeze leaking

2008-02-01 Thread Rod DiBona
Dave, I was told by our labor sup some time ago that we were having the same problem. I know the topic of viscosity came up. Not sure if that is valid or not as it seems that water would have a low viscosity and it doesn't seem that a water antifreeze mix would be lower as it seems that this

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Mike Brown (TECH- GVL)
Reza Take a look at your available pressure and choke down your branch line sizes and look at your cross main and feed main sizes as well. If you can reduce them this makes the system volume less as well as makes the system more economical. If you have a lot of pressure and the structure will

Re: Anti freeze leaking

2008-02-01 Thread Ron Greenman
Most, if not all, anti-freezes used in fire protection have wetting agents in them. This is like detergent added to water and breaks down surface tension. Although the solution will seem more viscose the individual molecules will be more slippery and be better able to escape. On Feb 1, 2008 11:45

RE: Parking Garage Sprinkler System /FDT program

2008-02-01 Thread George Church
FDT Software $5,000 Vehicles $500,000 Lifts and Boom $125,00 Insurance $320,000 3 hydraCAD seats, pc, custom workstations, 6 21 monitors AutoCAD$15,000 OT Redesign and 2- DPV and 500' of 6 galv installed on OT Labor $20,000 Liquidated Damages 2,000 Oh, boy- can't afford that FDT software

Re: Firesprinkler.org

2008-02-01 Thread Steve Muncy
I get them also, and I usually trash them, but always save one copy. The links allow you to customize what you receive from all of the email lists AFSA offers and how you receive them. - Want to go on vacation and suspend activity for awhile? USE THE LINK. - Changed email address and need to

Re[2]: Firesprinkler.org

2008-02-01 Thread Charles Thurston
Hello Steve, But but but .. if we USE THE LINK How much fun would that be for us to think of you pulling your hair out when we email and ask you to change these things for us? and to borrow your comment I'm sorry - its Friday and I just could not resist. Thanks for all you do

RE: Anti freeze leaking

2008-02-01 Thread David M. Canham
I have done a lot of anti freeze system in the last 30 years and only recently has this been coming up, is something different about the anti freeze? Is there any documented testing that has been published? David Canham Fire Systems Solitions -Original Message- From: [EMAIL PROTECTED]

RE: Sprinkler Zones for Horizontal Exit Building

2008-02-01 Thread Chappell, Carl
From what we have experienced, the intent of the horizontal exit is to be supplemental to the stairs and other egress components. However, as currently done the horizontal exit also acts as an audible zone boundary. This implies that the notification appliances connected to the fire alarm system

Re: Anti freeze leaking

2008-02-01 Thread Joe Hankins
Ron, I don't know which FM Rep you talked to, but the issue with large drop sprinklers had nothing to do with calibrating the calorimeter. The calorimeter doesn't even use sprinklers. The problem arose when repeating full-scale tests in the new test facility did not produce the same results

RE: Sprinkler Zones for Horizontal Exit Building

2008-02-01 Thread Chappell, Carl
The reason for the term supplemental is that as the stairs are not sufficient the horizontal exit will supplement (increase) the exit capacity of the building. My opinion would be that you would not want the other two buildings / zones to alarm because as you pointed out the occupants would be

Re: Anti freeze leaking

2008-02-01 Thread Ron Greenman
OK Joe. Me reading more into things than were said. What you said better explains the root of the issue. I must have mixed up different parts of the conversation. I noticed that you didn't comment on the kraft paper so I'm guessing I got that part right which was the piece I was using for the