School fire

2009-12-17 Thread A.P.Silva
To answer some of your questions: Personally, I don't think the exposed cpvc was at fault. I have seen a Blazemaster test report which indicates exposed cpvc with sprinkler heads being subject to a 30 minute fire test. Initially, temperature on pipe rises to 1560 deg.F. Sprinkler heads fuse in 50

Rubber links that compress around pipe and concrete holes

2009-12-17 Thread George Medina Jr
Can anyone tell me who makes the rubber links that we put around underground pipe when it comes through concrete holes (subterranean garage). I installed some about twenty years ago and can't recall the name of the product or the manufacturer. Thanks to anyone that can help, George Medina Jr.

RE: Rubber links that compress around pipe and concrete holes

2009-12-17 Thread John Drucker
Link Seal http://www.linkseal.com/htmlPages/base_ls.htm Hope that helps John Drucker -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina Jr Sent: Thursday, December 17, 2009 4:58 AM To:

ESFR DOES WHAT???

2009-12-17 Thread Vince Sabolik
Good morning, forum -- I want to use control mode heads in an existing warehouse building under 30 ft in height. Somebody (working for the owner) says that he would prefer ESFR heads because (his thought) it eliminates the requirement for heat and smoke vents. If that's true, I would have

RE: School fire

2009-12-17 Thread George Church
Please do update us, Tony- I can't think the 200*F heads- required in unventilated attic- are the cause. And the code DOES allow exposed CPVC in OH2 if 400 SF in light hazard building, and with spacing and elevation restrictions. glc -Original Message- From:

RE: ESFR DOES WHAT???

2009-12-17 Thread Ken Holsopple (forum)
Vince, From IBC 2006 910.1 General. Where required by this code or otherwise installed, smoke and heat vents or mechanical smoke exhaust systems and draft curtains shall conform to the requirements of this section. Exceptions: 1. Frozen food warehouses used solely for storage of Class I and

RE: ESFR DOES WHAT???

2009-12-17 Thread George Church
Vince, we did a job last year where our variance was approved and here's the logic train: Egress distance can be increased past 250' if heat and smoke vents are provided. So we pencil vents in. Then we provide an ESFR system so the vents aren't required, erase them. Extended egress distance in

RE: ESFR DOES WHAT???

2009-12-17 Thread Craig.Prahl
We got a similar response where the vents were used for the increased distance. The Underwriter required the vents to be either manual or have links at a higher temp rating than the sprinklers and the AHJ concurred. Vents had to go in. Craig L. Prahl, CET Fire Protection Specialist

RE: ESFR DOES WHAT???

2009-12-17 Thread Matt Grise
My understanding is that smoke vents impair the function of esfr systems by drafting heat away from the fire area and setting off sprinklers that don't help with suppression. Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS MO 913.888.0647 ph 913.888.0618 f

RE: ESFR DOES WHAT???

2009-12-17 Thread Smith, Steven D. (CSFD)
Yes. That is a valid concern. We offset that here by requiring the operation temp of the vents to be significantly higher than the ESFR temp ratings. Steve -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of

RE: Drop Wood Ceiling

2009-12-17 Thread Letterman, Todd
I 3rd... Todd Letterman Fire Protection Engineer Riverside County Fire Department (951) 955-5273-Fax(951) 955-4886 todd.letter...@fire.ca.gov Life's not about waiting for the storms to pass... It's about learning to dance in the rain. -Original Message- From: Law, Kevin W

RE: Drop Wood Ceiling

2009-12-17 Thread Letterman, Todd
Ok, I have a question, I'm still waking up with morning coffee, but was the installation installed to manufacturers specifications in this building? I know with Blazemaster they have very specific criteria for exposed installations. They even have exposed riser applications and their paragraphs

ESFR DOES WHAT???

2009-12-17 Thread Vince Sabolik
--- So the consensus of opinion is that requirement of smoke and heat vents will or will not be required depending on the AHJ and whether or not he buys into IFC. Kinda what I thought... hope I don't get the guy that held up a plan approval because we didn't put heads under a couple of

RE: ESFR DOES WHAT???

2009-12-17 Thread Chris Cahill
No the consensus was if not for exiting exceptions vents are not required by the IFC. Assuming the IFC is adopted without amendment as LAW the LAW allows this omission. The only further exception is if the AHJ has changed the LAW and is legally allowed to change the LAW. For example in MN

RE: ESFR DOES WHAT???

2009-12-17 Thread George Church
I learned an interesting phrase from a former staff liason at NFPA; during committee meetings he'd observe: Since I'm not on the committee, I'm not entitled to an opinion. But if I were, I'd .. Nice caveat, he could participate without participating. And as a PE, he would otherwise BE

RE: ESFR DOES WHAT???

2009-12-17 Thread Chris Cahill
And the reality is there are many, many people out there practicing w/o a lic that I'd put their opinion way before many, many with a lic. The other reality is cases of action against people w/o a lic are very, very rare. It's all semantics. I'm not a PE, so I'm not entitled to an opinion. But

Class III-A Combustible Liquids

2009-12-17 Thread Jim Johnston
Got a design criteria trivial question for some of the more experienced (PC for the old geezers, lol). A system installed in 1992 protecting Class III-A Combustible liquids in 55 gallon non-relieving drums stored 3 high was designed as a dry system and to Ordinary II (.20 / 1950). By today's

Re: ESFR DOES WHAT???

2009-12-17 Thread Todd - FPDC
I'm a PE am entitled to an opinion, but if I wasn't, I could give one and wouldn't be held liable for it. Sent from my iPhone On Dec 17, 2009, at 11:45 AM, George Church for...@ptd.net wrote: I learned an interesting phrase from a former staff liason at NFPA; during committee meetings

RE: Class III-A Combustible Liquids

2009-12-17 Thread Craig.Prahl
I've found a lot of chemical protection systems designed per NFPA 13 with no regard to any other Standard. Using the text in Chapter 5 within the various Hazards they base their design solely on the description of conditions and words such as moderate or substantial. Protection of

Standpipe control

2009-12-17 Thread Keith Pepin
Is it the intent of NFPA 14 to require isolation of individual standpipes without interrupting the supply to other standpipes from the same source on a manual-dry system feed from an FDC? Thanks ___ Sprinklerforum mailing list

Fire Protection Handbook

2009-12-17 Thread Brian Harris
Not sure if this is against the rules but I just picked up the 19th edition of the Fire Protection Handbook, 2 volume set for $23! Attached is the link for eBay, my office just ordered (3) sets two days ago and they came in today, all books are in excellent shape. FYI.

RE: Class III-A Combustible Liquids

2009-12-17 Thread Jim Johnston
Craig, The liquid is spearmint oil flash point 143 F, the oil is stored in non-relieving steel drums. I have looked at the MSDS sheets and 2008 NFPA 30 as well as a small section of NFPA 30 - 1993. I am pretty comfortable with requirements of 1993 and 2008 just don't have the backing of what

RE: Fire Protection Handbook

2009-12-17 Thread Brian Harris
For some reason the link got truncated, you need to combine both lines. Sorry. http://cgi.ebay.com/Fire-Protection-Handbook-Hardcover-2003_W0QQitemZ3412923 68536QQcmdZViewItemQQptZLH_DefaultDomain_0?hash=item4f769c4298 Brian Harris FDFP INC. -Original Message- From:

RE: Class III-A Combustible Liquids

2009-12-17 Thread Craig.Prahl
OH II, no, don't think so. Plus you may have issues with extinguishment based on water alone since it's SG=.91 and is insoluble. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC

Re: Fire Protection Handbook

2009-12-17 Thread Stewart Kidd
I'm still using the 16th edition - wonder what the postage would be to the UK ? Stewart On 17 Dec 2009, at 20:09, Brian Harris wrote: For some reason the link got truncated, you need to combine both lines. Sorry. http://cgi.ebay.com/Fire-Protection-Handbook-Hardcover-2003_W0QQitemZ3412923

RE: Fire Protection Handbook

2009-12-17 Thread Brian Harris
Shoot the guy an email, he was quick to get back with me. Either way for $23 plus shipping you'd still come out way ahead. Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Stewart

ASCOA Sprinklers

2009-12-17 Thread Jay White
Anyone know where to get information on ASCOA sprinklers? Nothing online. Model 246G SSU. Trying to find information on this sprinkler. Jay White Estimator/Design Manager Dynamic Fire Protection 1807 Hwy. 25 South Starkville, MS 39759 Phone: 662-324-1550 Fax: 662-324-1545 Cell:

RE: Class III-A Combustible Liquids

2009-12-17 Thread Jim Johnston
Unfortunately the person who designed this did it as Ord II and the AHJ bought off on it. I am pretty certain the codes never allowed this hazard as Ord II, I just wanted to have some backing since I don't anything (NFPA 30) prior to 1993. Nothing like trying to solve someone else's mistake.

RE: Class III-A Combustible Liquids

2009-12-17 Thread Todd Williams
Was the building originally designed for the drum storage? Almost sounds like it was supposed to house something else. At 05:21 PM 12/17/2009, you wrote: Unfortunately the person who designed this did it as Ord II and the AHJ bought off on it. I am pretty certain the codes never allowed this

RE: Class III-A Combustible Liquids

2009-12-17 Thread Jim Johnston
It was existing at the time, so the hazard was present when originally installed. Jim Johnston, P.E. Fire Protection Engineer Inland Fire Protection, Inc 1100 Ahtanum Road Yakima, WA 98903 Phone 509-248-4471 Fax 509-248-1180 j...@inlandfireprotection.com -Original Message- From: Todd

RE: Standpipe control

2009-12-17 Thread Steve Leyton
) __ Information from ESET NOD32 Antivirus, version of virus signature database 4697 (20091217) __ The message was checked by ESET NOD32 Antivirus. http://www.eset.com http://www.eset.com/ ___ Sprinklerforum mailing list Sprinklerforum

RE: Class III-A Combustible Liquids

2009-12-17 Thread Scott A. Futrell
Your research needs to include the Building and Fire Code enforceable at the time of the original construction. That will tell you what it should have been designed to, whether it was or wasn't won't be known until you start there. Chris C. had a post about the LAW earlier today on another

C factor in old copper pipe

2009-12-17 Thread Todd Williams
I am working on a 13D system which is fed by a copper pipe from the public supply. I have been asked by the water company (who has review authority in this situation) to decrease the C factor for the copper pipe from 150 to 120 due to age. I have done this several times in steel and CI pipe,

RE: C factor in old copper pipe

2009-12-17 Thread Matt Grise
My reference manual lists the range for copper as 150-120. So I would say it is within reason. Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -Original Message- From:

RE: Class III-A Combustible Liquids

2009-12-17 Thread David de Vries
Note all that Scott and Craig said about codes and physical properties, but FYI the 1987 edition of NFPA 30 says for solid pile or palletized storage of metal containers greater than 5 gal. up to 3 containers high Class III should be 0.25/3000 for high temp or 0.25/5000 for intermediate temp

RE: Class III-A Combustible Liquids

2009-12-17 Thread Jim Johnston
I already tried that approach, the records are archived at the Counties Office the representative from the Fire Marshals office dug thru the files for this facility unfortunately; everything prior to 1996 is gone. The applicable codes at the time should have been 1991 UBC UFC. It's possible

Re: Standpipe control

2009-12-17 Thread Keith Pepin
...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 4697 (20091217) __ The message was checked by ESET NOD32

RE: C factor in old copper pipe

2009-12-17 Thread Todd Williams
The 13 handbook commentary for 14.4.4.5 (2002) does not include any decrease for copper and I have never used one. 2010 has similar language. The FP handbook does not address it. My questioning is on the degradation of copper pipe and decrease in C Factor because of it. Never heard of it

RE: Class III-A Combustible Liquids

2009-12-17 Thread Todd Williams
Were the Codes set by the State, County or Local authorities? At 06:58 PM 12/17/2009, you wrote: I already tried that approach, the records are archived at the Counties Office the representative from the Fire Marshals office dug thru the files for this facility unfortunately; everything prior to

RE: Class III-A Combustible Liquids

2009-12-17 Thread Jim Johnston
I completely agree with you David, I have this information in the 1993 edition that you provided for me on a different issue at a different site built in 1993. I get stuck being the bad guy when the owners of these facilities call and say their insurance guy is coming up with different criteria

RE: Class III-A Combustible Liquids

2009-12-17 Thread Jim Johnston
Should be State, but when community is agricultural based and Billy Bob is the local elected official anything is possible. Jim Johnston, P.E. Fire Protection Engineer Inland Fire Protection, Inc 1100 Ahtanum Road Yakima, WA 98903 Phone 509-248-4471 Fax 509-248-1180

Re: Fire Protection Handbook

2009-12-17 Thread Richard Lindner
They are all gone (damn firewall at work, I couldn't get to Ebay till now!!) On Thu, Dec 17, 2009 at 4:17 PM, Brian Harris br...@firstdefensefire.comwrote: Shoot the guy an email, he was quick to get back with me. Either way for $23 plus shipping you'd still come out way ahead. Brian

Re: Class III-A Combustible Liquids

2009-12-17 Thread Ron Greenman
Jim, I have code sets going back into the 80s. Do you know what edition of 13 is referenced in the 91 UBC 'cause I don't think I have that. Perhaps 30 is also directly referenced but if not it would be referred to in 13. On Thu, Dec 17, 2009 at 4:08 PM, Jim Johnston j...@inlandfireprotection.com

QR and SR seperation

2009-12-17 Thread Greg McGahan
If you have a storage room defined by the EOR as a .222/2,000 remote area in the back of a retail store with NO separation to the retail area and you conform to both requirements (15' of the greater hazard and 30' of 286 deg heads) into the retail space: Does this lock you out of changing to EC

RE: QR and SR seperation

2009-12-17 Thread Greg McGahan
Ok, to make it more confusing, the EC heads I was going to use are UL Listed as QR for 14x14 (which I need) and SR for 16x16 - which would mean by increasing the spacing I could use the exact same head? AND, the FM rating is SR for 14x14...I want to do this right and for the heads to operate as

RE: Class III-A Combustible Liquids

2009-12-17 Thread David de Vries
Jim:   The 1991 UFC Table 79.203-C has the same criteria as the 1987 NFPA 30, i.e. 0.25/3000 and 5000 for high and intermed temp sprinklers respectively. I can fax you a copy of the reqs from it if you need it. Dave David A. de Vries, P.E., CSP Firetech Engineering Incorporated --- On