Am I right in thinking that one should edit 21 13 00.00 40 for the piping
leading into the fire riser room and delete the references to the sprinkler
system (and any other unused interior piping) and specify the sprinkler system
from the riser into the occupied space(s) using 21 13 13?
Distribution Way. Suite 14
Vista, CA. 92081
M:858-722-1470
O:760-295-3436
F:760-295-3437
su...@titanfpinc.com
www.titanfpinc.com<http://www.titanfpinc.com>
-Original Message-
From: Sprinklerforum On Behalf
Of David Williams via Sprinklerforum
Sent: Thursday, December 2, 2021 1
Having sprinkler contractors reprice an Air Force housing project we are
working on. The RFP is a steel only job (tried to get approval for CPVC but no
go). What are you seeing for materials that provide some cost control… Sch 7,
galv thin wall, ??
David Toshio Williams, PE*, FPE – Lead MEP/FP
no plans reviewer is going to count on a spk contractor
getting out their checkbook.
Best.
Bruce Verhei
> On 09/17/2021 2:30 PM David Williams via Sprinklerforum
> wrote:
>
>
> I’ve been asked to look at a new industrial building, generally unoccupied
> except for servicin
I’ve been asked to look at a new industrial building, generally unoccupied
except for servicing, that has a fire and gas detection system and audible and
visual notification devices.
At this point I’m not sure this facility actually requires a FA system, as it
might just be an owner
We do a fair amount of design at an Air National Guard base that has a HP fire
line to service various hangers and the associated AFFF systems. This system
was installed before my time, but it does have a few hydrants on the system, I
think mainly for flow testing as the system expands. I will
Or you “shed” the refrigeration from the generator sizing during a fire event.
That much ice cream will stay cold for the period of time the fire pump needs
the power.
David Toshio Williams, PE*, FPE
(*Registered in MN, WI, MI, IA, IL, IN, ND, VT)
(218) 279-2436 direct | (218) 310-2446 cell
We have a transformer yard at grade that is located under an multistory open
parking structure. We caught it in time to have FR3 oil supplied in the non-FM
utility company transformers and we believe we have the proper separation
distances according to FM 5-4. We have 5 feet from
Many times there is a topping slab that can cover a through bolt and backing
plate, or the precaster “could” install embedments. Takes lots of coordination!
I like to spec embedments in parking ramp decks for the mains as it is such a
corrosive environment and I can’t count on SS drill in
member of the NFPA
Installation of Private Fire Service Mains and their Appurtenances Committee in
accordance with the NFPA Regulations Governing Committee Projects and should
therefore not be considered, nor relied upon, as the official position of the
NFPA or its Committees
On 5/7/2021 8:21 AM, David Wi
A civil engineer friend of mine is working on a state project in California and
there is a fight between the water purveyor and the state fire marshal as to
the location of the hydrant valves. The water purveyor wants the valves to be
right off the main and does not feel a need to keep the
I had a high school project about ten years ago on a green field site and we
had access to a small high pressure low volume system and a low pressure low
volume system. We ended up using the high pressure system to feed the domestic
water and sprinkler (not the standpipes) system but the City
.
Thanks,
Skyler Bilbo
1700 S. Raney Street
Effingham, IL 62401
217-819-6404 Direct
217-347-7315 Fax
sbi...@wenteplumbing.com
www.wenteplumbing.com<http://www.wenteplumbing.com>
On Thu, Mar 4, 2021 at 8:54 AM David Williams via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org>
We have a community college client that wants to replace standard ACT with a
perforated metal mesh tile that is 60% open. My assumption is that change would
require installation of heads above the ceiling in the area of the metal mesh,
perhaps putting a bulkhead around the area with the mesh
Hey Scott and other cold weather practitioners in Fire Protection. Any feed
back on the “new” Tyco LFP antifreeze. Looks like it may have some use in
southern MN locations, but with Duluth at annual 99% extreme of -24.9 and 50
year extreme at -36.6 maybe not such a good idea yet. We plan on
That’s funny as I have in design right now an exterior standpipe that has a
wrap-around stairway so that the landings are separated both horizontally and
vertically by a substantial amount as the stair wraps around the end of the
building. So both types of standpipes in one! Due to the
In Minnesota there are State Fire Marshal rules that allow rural sites to use
the domestic well as a fire sprinkler source. They do put some testing
requirements in place, minimum well bore size, and minimum flow criteria. I
have not recommended this solution as I feel there is a risk of the
I was just looking at this issue for a turbine floor FP installation: FM data
sheet 7-83 has some guidance on the spill control and drainage sizing for
flammable liquid areas..
David Toshio Williams, PE, FPE
(218) 279-2436 direct | (218) 310-2446 cell
LHB, Inc. | PERFORMANCE DRIVEN DESIGN
We are “fixing” a similar arrangement at an Air National Guard Base. Originally
they brought fire water used on site to two large underground storage tanks,
then had electric and diesel vertical inline pumps to serve high pressure fire
flow needs, think AFFF & HEF. At some point they installed
Our office will always provide pdf, AutoCAD (if the job was created in it) or
Revit, but we WILL ask you to sign a release/NDA on our part of the work. There
are some military jobs we do that we “need” Revit coordination drawing due to
the RFP and sometimes finding contractors in a given area
I’ve used the forms that are produced by 185 graph (http://www.reckonit.com/)
as you can put your logo on them $250 and does some tree/branch hydraulic
calculations if you don’t have or need a full featured hydraulic calculation
program like sprinkcad. 30 day demo.
Alternate
rongreen...@gmail.com<mailto:rongreen...@gmail.com>
253.576.9700
The Universe is monstrously indifferent to the presence of man. -Werner Herzog,
screenwriter, film director, author, actor and opera director (1942-)
On Thu, Aug 15, 2019 at 12:41 PM David Williams via Sprinkle
n via:
https://www.hightail.com/u/MFPDesign
Sent from my iPhone
On Aug 15, 2019, at 12:02 PM, David Williams via Sprinklerforum
mailto:sprinklerforum@lists.firesprinkler.org>>
wrote:
Thanks.. I didn’t see it either but I wanted to see if there were other
opinions/options.
David T Williams – Lead ME
-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
On Behalf Of David Williams via Sprinklerforum
Sent: Thursday, August 15, 2019 1:43 PM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firespri
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of David Williams via Sprinklerforum
Sent: Thursday, August 15, 2019 12:43 PM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: David Williams
Subject: Attic/Concealed space
At least one of the Twin Cities local jurisdictions want to see these system or
fire protection sprinklers installed in all kitchen hoods. The Fire Marshall
want to have protection even when the agent has been expended (such as an agent
only system). (they also want sprinklers to back up clean
I have a project intended to be fully sprinkled with a combustible attic that
tapers from 2' to 4 ' without being filled to within 2 inches of the deck with
insulation. So I am planning on a dry pipe system with standard heads as the
design of the attic does not allow the effective use of