. State is asking me to hang a partial certification
( yellow tag) . has anyone else dealt with this detection being used for a
pre-action system in a detention center? Any help would be appreciated
Gregg Key
General Manager
Key Fire Protection Enterprises,LLC
3200 Mike Padgett Hwy
Augusta
Greetings, Is it common to install a double interlock Pre-action system in the
cell pod areas in correction facilities?
Gregg Key
General Manager
Key Fire Protection Enterprises,LLC
3200 Mike Padgett Hwy
Augusta GA, 30906
O-706-790-3473
C- 706-220-8821
F- 706-738-2119
<mailto
Does anyone know how much UL charges to test sprinkler heads? I called and left
a message for them but kinda need an answer now. Thanks
Gregg Key
General Manager
Key Fire Protection Enterprises,LLC
3200 Mike Padgett Hwy
Augusta GA, 30906
O-706-790-3473
C- 706-220-8821
F- 706-738-2119
gr
Steve, I don't believe you are supposed to use air in a cpvc system. We used
to use some cheap cologne in the steel systems but not in plastic.
How bad is the leak?
Maybe you could put water back on it slowly and find it that way.
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project
:27 AM, Gregg Key gr...@keyfps.com wrote:
Our inspector ask an interesting question today. How long is too long
of a time for a dry valve to trip before it is considered a
deficiency? 25 does not specify but 15 min seams too long. Don't have
the previous report to compare it to.
C.Gregg
Our inspector ask an interesting question today. How long is too long of a
time for a dry valve to trip before it is considered a deficiency? 25 does
not specify but 15 min seams too long. Don't have the previous report to
compare it to.
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project
Formites and fire protection friends,
Has anyone here ever installed an electric fire pump on these spring type
isolators? We usually install them on a pad, but recently had someone
require us to install on the isolators. Any help would be appreciated.
C.Gregg Key, SET
Key Fire Protection
anything to back
up my gut opinion. I'm curious as to what others think and know.
On Mon, Oct 1, 2012 at 11:18 AM, Gregg Key gr...@keyfps.com wrote:
Formites and fire protection friends,
Has anyone here ever installed an electric fire pump on these spring
type isolators? We usually install
Forum, if you were inspecting a building and found some pendant sprinklers with
the heat collectors installed, would you write it up as a deficiency and why?
Many moons ago they were accepted but later research proved they did not work.
C.Gregg Key, SET
Key Fire Protection Services,Inc
www.petcosky-sons.com
607-797-0160 Ext.105
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Gregg Key
Sent: Thursday, July 26, 2012 3:08 PM
To: sprinklerforum@firesprinkler.org
Subject: sprinkler head quick cut off
The C-900 pipe is approved and listed for underground use and not above
ground usage. Not suppose to use it to come up thru the floor.
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821
-Original Message-
From:
...@cox.nete-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.comwebsite
On 2/29/2012 12:58 PM, Gregg Key wrote:
The C-900 pipe is approved and listed for underground use and not
above ground usage. Not suppose to use it to come up thru the floor.
C.Gregg Key, SET
Key Fire Protection
What is the preferred method of protecting the Pendent Sprinklers in a
racquetball court? The head guards from FPPI state that they are not
designed for impact?
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821
-- next part --
An HTML attachment was scrubbed...
URL:
Does anyone know if a spring loaded plate exist that replaces the Star LD2
plate. It was a very good idea but cant seem to find them Thanks
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821
___
Now that brings back memories. Having to buy 3/8 solid rod and thread it in
the field. Takes a lot more time if you have to recut hangers. Should be
able to buy 3/8 solid rod from steel plant. Fab shops should be able to
provide it.
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project
WOW , He sent word that the reference is NFPA 13 2010
ed.A.8.17.4.6.1
A.8.17.4.6.1 The full flow test of the backflow prevention
valve can be performed with a test header or other connection
downstream of the valve. A bypass around the check valve in
the fire department connector line
Ok now that I got past that, Any reason that the 2 main drain could not be
used if the required flow could be achieved. System demand + hose allowance?
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821
Gerald, I must be having a senior moment, Does the solenoid cut the system
on or off? I assume on since you said it is activated by the flow switch. So
we have a system with a closed control valve(solenoid) and when a head goes
off how does the flow switch work since no water is in the system??
, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com
From: sprinklerforum-boun...@firesprinkler.org on behalf of Gregg Key
Sent: Thu 5/19/2011 3:55 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Limited Area Systems
Eric, We have inspected a few of these systems. Since you are installing a
flow switch, you will need to install an inspectors test. I never seen a FDC
installed on them but have seen 1 1/2 FDC's installed on small residential
systems. Never seen a solenoid operated cut off valve installed, What
Brian, You can buy a DCVA with a PIV installed on the bottom of it. We have
used it in the past to meet that requirement
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
-220-8821
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Gregg Key
Sent: Friday, March 11, 2011 4:10 PM
To: sprinklerforum@firesprinkler.org
Subject: misalignment question
Would anyone please give an example
Would anyone please give an example of what a misalignment of the sprinkler
pipe would mean as far as nfpa 25 2002 edition 5.2.2.1 Thanks
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821
___
It has been a while since I have been on and I think this has been discussed
before but cant find it in the archives so here I go.
Doing a NFPA 25 inspection and find a medical storage room with rolling
files that are within 8 of the sprinklers. Sprinklers spaced 12x12. This
system has 8 rolling
To help me understand, if a sprinkler goes off in building 4 then all 4
systems will show a water flow thus have all 4 alarms?
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821
-Original Message-
From:
Good reason to install flow switches on the riser and let wmag give local
alarms
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
to: techsupp...@firesprinkler.org
To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
begin:vcard
fn: Gregg Key
n:Key; Gregg
org:Fire Technology LLC;Fire Sprinkler Division
adr;dom:;;2005 Westside Drive;Augusta ;GA;30907
email
an email to: techsupp...@firesprinkler.org
To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
begin:vcard
fn: Gregg Key
n:Key; Gregg
org:Fire Technology LLC;Fire Sprinkler Division
adr;dom:;;2005 Westside Drive;Augusta ;GA;30907
...@firesprinkler.org
To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
begin:vcard
fn: Gregg Key
n:Key; Gregg
org:Fire Technology LLC;Fire Sprinkler Division
adr;dom:;;2005 Westside Drive;Augusta ;GA;30907
email;internet:gre
?
Some discussion was had if this was a recall or replacement.
http://www.cpsc.gov/cpscpub/prerel/prhtml01/01201.html
begin:vcard
fn:C Gregg Key
n:Key;C Gregg
org:Fire Technology;Fire Sprinkler Division
adr;dom:;;3124 Washington Road;Augusta ;GA;30907
email;internet:[EMAIL PROTECTED
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
begin:vcard
fn:C Gregg Key
n:Key;C Gregg
org:Fire
] 05/30/08 8:56 AM
That's funny. I'm pretty taciturn and your word elicited an out loud chuckle.
On Fri, May 30, 2008 at 8:47 AM, Fletcher, Ron [EMAIL PROTECTED] wrote:
six
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
Sent: Friday, May 30
outlet.
Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
701.280.8591
[EMAIL PROTECTED]
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
Sent: Friday, May 30, 2008 12:23 PM
To: sprinklerforum@firesprinkler.org
@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
begin:vcard
fn:C Gregg Key
n:Key;C Gregg
org:Fire Technology;Fire Sprinkler Division
adr;dom:;;3124 Washington Road;Augusta
field)
begin:vcard
fn:C Gregg Key
n:Key;C Gregg
org:Fire Technology;Fire Sprinkler Division
adr;dom:;;3124 Washington Road;Augusta ;GA;30907
email;internet:[EMAIL PROTECTED]
title:Project Manager
tel;work:706-650-7730
tel;fax:706-650-7731
tel;cell:706-412-1281
url:www.firetecheng.com
version:2.1
If I may tap into the collective memory bank of sprinkler knowledge, How
long have sprinklers been required in coolers/freezers per NFPA 13?
Thanks Gregg
begin:vcard
fn:C Gregg Key
n:Key;C Gregg
org:Fire Technology;Fire Sprinkler Division
adr;dom:;;3124 Washington Road;Augusta ;GA;30907
email
Brian,
What is/was the water flow numbers?
Gregg
begin:vcard
fn:C Gregg Key
n:Key;C Gregg
org:Fire Technology;Fire Sprinkler Division
adr;dom:;;3124 Washington Road;Augusta ;GA;30907
email;internet:[EMAIL PROTECTED]
title:Project Manager
tel;work
a tamper switch on it. but I have not seen the
ball valve for the alarm line even sealed . does any one seal or lock them?
8.16.1.4.3 does this one nullify 8.16.1.4.1? if so does it still need
to meet the requirement of 8.16.1.4.2?
thanks
begin:vcard
fn:C Gregg Key
n:Key;C Gregg
Hey Matt, good link but I think you missed the last 2 numbers in the link
http://cms.firehouse.com/content/article/article.jsp?sectionId=39id=56032
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt Willis
Sent: Tuesday, August 21, 2007 7:16 AM
To:
You are right Bob, especially when is a Gov. Job. We are suppose to have a
clause in our contract that states that if we have to pay for drawings it
will be an extra to the contract. So cost of work goes up. Gov has already
paid for it once.
Gregg
-Original Message-
From:
David, Does that mean that WA. Has adapted the green, yellow red tag system
to use with NFPA 25?
And also, would the state happened to have provided guidelines on applying
the 3 tag system to NFPA 25?
Gregg Key, SET Project Manager Augusta Fire Protection
For those wondering, WA state
Does anyone know where a stash of these plates can be found? Viking states
that they are not available and we have a place of business that has some of
these plates missing. Any help would be appreciated. Gregg
___
Sprinklerforum mailing list
Todd, The fitter was probably telling you the truth, which is that he was
taught to close both valves. When I started in the field in the late 70's, I
was taught the same thing. This is a good reason to promote the AFSA
apprenticeship program so the fitters coming up now can be taught the
correct
.
Gregg Key
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)