[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-10 Thread matthew.willis1
Friday, March 10, 2023 8:29 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Duct obstruction criteria in LH attic In our situation we are 3" above the duct but can locate the uprights as far as 2 ft away horizontally. The next line

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-10 Thread Brett Peters
> IMHO Because it specifically says “structural members only shall be > considered” I believe the intent of this section is to allow for us to not > provide sprinklers on both side to a reasonable degree, meaning we’re able > to get water on both sides of the obstruction as long

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-10 Thread Anthony Johnson
w.FergusonFire.com <http://www.fergusonfire.com/>* > > > > *From:* Kevin Hall > *Sent:* Thursday, March 9, 2023 6:38 PM > *To:* Discussion list on issues relating to automatic fire sprinklers < > sprinklerforum@lists.firesprinkler.org> > *Subject:* [Sprinklerforum] Re:

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-10 Thread matthew.willis1
PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Duct obstruction criteria in LH attic I’m not sure where you are getting that requirement from the annex section: A.10.2.7.3.1.4 It is the intent of this section to exempt nonstructural elements in lig

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-10 Thread Anthony Johnson
t;> For me I would start at *8.6.5.2 Obstructions to Sprinkler >>>>>>> Discharge Pattern Development.* >>>>>>> >>>>>>> >>>>>>> >>>>>>> *8.6.5.2.1.1 *Continuous or noncontinuous obstruction

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-10 Thread Anthony Johnson
deflector that prevent the pattern from fully >>>>>> developing shall comply with >>>>>> >>>>>> 8.6.5.2. >>>>>> >>>>>> >>>>>> >>>>>> The section above lays the groun

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Brett Peters
; >>>>> *8.6.5.2.1.4* *For light and ordinary hazard occupancies, structural >>>>> >>>>> members only shall be considered when applying the requirements >>>>> >>>>> of 8.6.5.2.1.3. >>>>> >>&

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Kevin Hall
both side to a reasonable degree, meaning we’re able >>>> to get water on both sides of the obstruction as long as its not a >>>> structural member. >>>> >>>> >>>> >>>> Thanks, >>>> >>>> >>>> &

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Brett Peters
long as its not a >>> structural member. >>> >>> >>> >>> Thanks, >>> >>> >>> >>> >>> >>> >>> >>> >>> >>> *Dane Long, AET* >>> *Engineering Technician *| *Bamfor

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Greg McGahan
gt; >>> >>> >>> Thanks, >>> >>> >>> >>> >>> >>> >>> >>> >>> >>> *Dane Long, AET* >>> *Engineering Technician *| *Bamford Fire Sprinkler Co., Inc.* >>> P:*785.825.771

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Kevin Hall
t; >> >> >> >> >> *Dane Long, AET* >> *Engineering Technician *| *Bamford Fire Sprinkler Co., Inc.* >> P:*785.825.7710* >> F:*785.825.0667* >> A: *1383 W. North Street Salina, KS 67401* >> >> >> >> >> >>

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Greg McGahan
t; P:*785.825.7710* > F:*785.825.0667* > A: *1383 W. North Street Salina, KS 67401* > > > > > > *From:* Anthony Johnson > *Sent:* Thursday, March 9, 2023 2:26 PM > *To:* Discussion list on issues relating to automatic fire sprinklers < > sprinklerforum@list

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Dane Long
From: Anthony Johnson Sent: Thursday, March 9, 2023 2:26 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Duct obstruction criteria in LH attic The 3x rule is the only one we think would apply but it only applies to structural

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Taylor Schumacher
Office: 320.656.0847 | Direct: 320.640.7050 From: Anthony Johnson Sent: Thursday, March 09, 2023 2:26 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Duct obstruction criteria in LH attic The 3x rule is the only one we think would apply but i

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Greg McGahan
>> >> *Taylor Schumacher* >> >> Security Fire Sprinkler <http://www.j-berd.com/> >> >> 1 Industrial Blvd | Sauk Rapids, MN 56379 >> >> Office: 320.656.0847 | Direct: 320.640.7050 >> >> >> >> *From:* matthew.will...@ferguson.c

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Anthony Johnson
*To:* sprinklerforum@lists.firesprinkler.org > *Subject:* [Sprinklerforum] Re: Duct obstruction criteria in LH attic > > > > I believe however, the intent of the section must still be applied. Water > on both sides. > > Not sure in the 13 edition the location, but in the 19 it is

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Taylor Schumacher
Security Fire Sprinkler<http://www.j-berd.com/> 1 Industrial Blvd | Sauk Rapids, MN 56379 Office: 320.656.0847 | Direct: 320.640.7050 From: matthew.will...@ferguson.com Sent: Thursday, March 09, 2023 12:37 PM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] Re: Duct obstr

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread matthew.willis1
I believe however, the intent of the section must still be applied. Water on both sides. Not sure in the 13 edition the location, but in the 19 it is 10.2.7.1.2. We are referred back to it as applicable from the 3 times section. Sprinklers spaced on opposing sides, not to exceed the max half

[Sprinklerforum] Re: Duct obstruction criteria in LH attic

2023-03-09 Thread Brett Peters
I think you also need to look at the 18" requirement for the sprinkler deflector clearance, if there is only 3" between the sprinkler and the duct than the sprinkler cannot produce a proper spray pattern. Thanks Brett Peters General Manager Installation & Design Proudline Fire Protection